Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. Should I
cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling, or
should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 213
Default What to do with pipe bonding

On Sat, 10 Mar 2007 22:16:19 -0800, "Eigenvector"
wrote:

Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. Should I
cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling, or
should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.


You mean Grounding wire?

  #3   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default What to do with pipe bonding

Your interior metallic piping should be bonded to the service equipment. If
you don't have any, or remove it, there would be nothing to bond. If you are
only removing portions of it, make sure the bonding conductor is continuous
to any piping that remains




"Eigenvector" wrote in message
. ..
Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. Should
I cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling,
or should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default What to do with pipe bonding

On Mar 11, 8:09�am, "RBM" rbm2(remove wrote:
Your interior metallic piping should be bonded to the service equipment. If
you don't have any, or remove it, there would be nothing to bond. If you are
only removing portions of it, make sure the bonding conductor is continuous
to any piping that remains

"Eigenvector" wrote in message

. ..



Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. *I left the galvanized in place,
simply cut them with the Sawsall *and left in place, but the end of the
bonding wire is attached to it. *It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. *Should
I cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling,
or should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?


In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. *The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.- Hide quoted text -


- Show quoted text -


whats your outdoor line made of? if its metal bond to that.

if your replacing the outside line leave the old metal line in place
and ground to that. a 50 foot unused line in the ground is still a
excellent ground addition to your system.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default What to do with pipe bonding

maybe bond to the hot water tank?



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default What to do with pipe bonding


"Eigenvector" wrote in message
. ..
Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. Should

I
cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling,

or
should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.


Since there is nothing to bond to anymore I would just coil it up a bit and
tack it to the wall or ceiling. I suppose that you could cut it back to the
gas pipe, but I'm the type of person who would leave it there in case you
change back to copper in 50 years. There is no need to leave the galvanized
in place since it no longer is functional.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default What to do with pipe bonding

On Sat, 10 Mar 2007 22:16:19 -0800, "Eigenvector"
wrote:

Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire, clamped
to the last portion of the galvanized that I haven't hauled away. Should I
cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling, or
should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.


Assuming your buried outdoor pipe is still metallic, just run a longer
ground wire from the water heater all the way over to your water
entrance pipe, and connect the clamp there. Even if you got to tack
50 feet of wire across your basement rafters, that's still better than
having old sections of galvanized pipe, which serve no purpose if they
are not connected to metal. DO NOT use the gas pipe. Thats a bad
idea. Just get some bare, or green insulated wire of the same or
thicker gauge as what you have now, and run it to your water entrance
pipe, which is usually where the water meter is located.

If you dont have a metallic underground pipe, drive a ground rod
outside and connect to that.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,743
Default What to do with pipe bonding

Eigenvector wrote:
Now that my hot water pipes are replaced with all PEX, I'm left
wondering what I should do with my bonding wire. I left the
galvanized in place, simply cut them with the Sawsall and left in
place, but the end of the bonding wire is attached to it. It's the
end of the bonding wire, clamped to the last portion of the
galvanized that I haven't hauled away. Should I cut the bond wire at
the next pipe in the circuit - in this case the gas line, or should I
simply unclamp it from the pipe and leave it dangling, or should I
leave the galvanized pipe in place even though it doesn't go anywhere
or do anything?
In case it isn't clear, the bonding wire goes from the panel, to the
cold water line, to the gas line, then ends at the hot water line. The
water line was replaced with PEX, but the pipes are still in
place as is the bonding wire.


The purpose of the "bonding" wire is NOT to ground the electrical service.
It's purpose is to ground the plumbing. If the "bonding" wire is attached to
something that can never be touched by a human (instead of plumbing
fixtures), it's irrelevant what you bond it to.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,079
Default What to do with pipe bonding


"John Grabowski" wrote in message
...

"Eigenvector" wrote in message
. ..
Now that my hot water pipes are replaced with all PEX, I'm left wondering
what I should do with my bonding wire. I left the galvanized in place,
simply cut them with the Sawsall and left in place, but the end of the
bonding wire is attached to it. It's the end of the bonding wire,
clamped
to the last portion of the galvanized that I haven't hauled away. Should

I
cut the bond wire at the next pipe in the circuit - in this case the gas
line, or should I simply unclamp it from the pipe and leave it dangling,

or
should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?

In case it isn't clear, the bonding wire goes from the panel, to the cold
water line, to the gas line, then ends at the hot water line. The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.


Since there is nothing to bond to anymore I would just coil it up a bit
and
tack it to the wall or ceiling. I suppose that you could cut it back to
the
gas pipe, but I'm the type of person who would leave it there in case you
change back to copper in 50 years. There is no need to leave the
galvanized
in place since it no longer is functional.


Alright that sounds like a reasonable solution.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,079
Default What to do with pipe bonding


wrote in message
oups.com...
On Mar 11, 8:09�am, "RBM" rbm2(remove wrote:
Your interior metallic piping should be bonded to the service equipment.
If
you don't have any, or remove it, there would be nothing to bond. If you
are
only removing portions of it, make sure the bonding conductor is
continuous
to any piping that remains

"Eigenvector" wrote in message

. ..



Now that my hot water pipes are replaced with all PEX, I'm left
wondering
what I should do with my bonding wire. �I left the galvanized in place,
simply cut them with the Sawsall �and left in place, but the end of the
bonding wire is attached to it. �It's the end of the bonding wire,
clamped
to the last portion of the galvanized that I haven't hauled away.
�Should
I cut the bond wire at the next pipe in the circuit - in this case the
gas
line, or should I simply unclamp it from the pipe and leave it dangling,
or should I leave the galvanized pipe in place even though it doesn't go
anywhere or do anything?


In case it isn't clear, the bonding wire goes from the panel, to the
cold
water line, to the gas line, then ends at the hot water line. �The water
line was replaced with PEX, but the pipes are still in place as is the
bonding wire.- Hide quoted text -


- Show quoted text -


"whats your outdoor line made of? if its metal bond to that.

if your replacing the outside line leave the old metal line in place
and ground to that. a 50 foot unused line in the ground is still a
excellent ground addition to your system."

Perhaps, but like I said the cold water line is already bonded and while I
didn't include this in the original post, I already have a typical grounded
electrical system anyway. I'm gonna go with what Grabowski suggested and
just hang it somewhere out of the way and remove the rest of the galvanized

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding [email protected] UK diy 4 November 6th 06 11:54 PM
Cross-bonding/earth bonding gas meter Jim UK diy 1 July 28th 06 09:19 PM
PVC pipe problem ..what is best for "bonding"?? mrbreeze Home Repair 2 June 18th 05 01:26 AM
PVC pipe problem ..what is best for "bonding"?? mrbreeze Home Repair 0 June 17th 05 10:59 PM
ME Bonding Jon UK diy 0 August 31st 04 04:39 PM


All times are GMT +1. The time now is 11:54 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"