I bought an old Army Corps of engineers 30kw 3 phase genset with Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming out.
There are 3big split bolt connectors coming out and one smaller one which
appears to be the neutral or ground. Right now, 125v is measured from this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well pumps
and put the well pumps on the second phase. That is because the amps per
phase is listed as only 57 amps in this configuration and I figure I since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase. This
leaves the third phase not connected to anything(open circuit.) as a spare.
I bought some transfer panels(double pole double throw) and have brought
the well pump 30amp dp breaker wires out to a separate 60a transfer panel
and connected it to one of the phases of the genset. the other phase I put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?



  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default hookup of 3phase genset as home backup

If your single phase pumps are designed for 240 volt, I wouldn't use the 208
volt tap. Your phases are 1-2, 2-3, 1-3, so if you are using two of them as
single phase, you are doubling up on one leg, so it does limit the capacity.
You may be better off to connect it as a Delta, and just use the single
phase 120-240 volt taps



"desperado" wrote in message
.. .
I bought an old Army Corps of engineers 30kw 3 phase genset with Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one which
appears to be the neutral or ground. Right now, 125v is measured from this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well pumps
and put the well pumps on the second phase. That is because the amps per
phase is listed as only 57 amps in this configuration and I figure I since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have brought
the well pump 30amp dp breaker wires out to a separate 60a transfer panel
and connected it to one of the phases of the genset. the other phase I put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?





  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default hookup of 3phase genset as home backup

desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming out.
There are 3big split bolt connectors coming out and one smaller one which
appears to be the neutral or ground. Right now, 125v is measured from this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well pumps
and put the well pumps on the second phase. That is because the amps per
phase is listed as only 57 amps in this configuration and I figure I since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase. This
leaves the third phase not connected to anything(open circuit.) as a spare.
I bought some transfer panels(double pole double throw) and have brought
the well pump 30amp dp breaker wires out to a separate 60a transfer panel
and connected it to one of the phases of the genset. the other phase I put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?


If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it online
somewhere, perhaps the Kohler or Onan sites.
  #4   Report Post  
Posted to alt.home.repair
EXT EXT is offline
external usenet poster
 
Posts: 1,661
Default hookup of 3phase genset as home backup

Agreed. 12 lead generators can be set up in a number of 3 phase and single
phase and voltage configurations including 120/240 volt single phase to
match your current house system. If you can locate the wiring diagram, it
will simplify tying into the house wiring. I have one and it is set up this
way.

"Pete C." wrote in message
...
desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with
Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one
which
appears to be the neutral or ground. Right now, 125v is measured from
this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well pumps
and put the well pumps on the second phase. That is because the amps per
phase is listed as only 57 amps in this configuration and I figure I
since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have brought
the well pump 30amp dp breaker wires out to a separate 60a transfer panel
and connected it to one of the phases of the genset. the other phase I
put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?


If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it online
somewhere, perhaps the Kohler or Onan sites.



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15
Default hookup of 3phase genset as home backup

thanks for the response. I will keep looking for the wiring diagram for the
120/240 before giving it the smoke test.

Right now, only 3 diagrams are printed on the bus bar panel.

I forgot to mention that all the neutrals of both genset and mains are
connected together. I just got thru talking to a retired electrician and he
said that is a no no. Got to disconnect the neutral of the mains when
working off backup genset. This explains possibly why, when I did try to
throw the transfer switch on the pumps, that the breaker in the main panel
tripped to this particular circuit.
All equipment is still ok. I will put in a separate switch to switch out the
neutral to the mains when on backup.
I was also worried about being unbalanced loads in each phase I am using,
but the electrician said that wasn't a problem.
I will educate myself a bit more about transfer panel setups before
throwing any more switches and am also trying to find the service and
operator manual for this particular genset.
Thanks
--
don paolino
"EXT" wrote in message
anews.com...
Agreed. 12 lead generators can be set up in a number of 3 phase and single
phase and voltage configurations including 120/240 volt single phase to
match your current house system. If you can locate the wiring diagram, it
will simplify tying into the house wiring. I have one and it is set up

this
way.

"Pete C." wrote in message
...
desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with
Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V

single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one
which
appears to be the neutral or ground. Right now, 125v is measured from
this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well

pumps
and put the well pumps on the second phase. That is because the amps

per
phase is listed as only 57 amps in this configuration and I figure I
since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have

brought
the well pump 30amp dp breaker wires out to a separate 60a transfer

panel
and connected it to one of the phases of the genset. the other phase I
put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?


If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it online
somewhere, perhaps the Kohler or Onan sites.







  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default hookup of 3phase genset as home backup

desperado wrote:

thanks for the response. I will keep looking for the wiring diagram for the
120/240 before giving it the smoke test.

Right now, only 3 diagrams are printed on the bus bar panel.

I forgot to mention that all the neutrals of both genset and mains are
connected together. I just got thru talking to a retired electrician and he
said that is a no no. Got to disconnect the neutral of the mains when
working off backup genset. This explains possibly why, when I did try to
throw the transfer switch on the pumps, that the breaker in the main panel
tripped to this particular circuit.
All equipment is still ok. I will put in a separate switch to switch out the
neutral to the mains when on backup.
I was also worried about being unbalanced loads in each phase I am using,
but the electrician said that wasn't a problem.
I will educate myself a bit more about transfer panel setups before
throwing any more switches and am also trying to find the service and
operator manual for this particular genset.
Thanks
--
don paolino
"EXT" wrote in message
anews.com...
Agreed. 12 lead generators can be set up in a number of 3 phase and single
phase and voltage configurations including 120/240 volt single phase to
match your current house system. If you can locate the wiring diagram, it
will simplify tying into the house wiring. I have one and it is set up

this
way.

"Pete C." wrote in message
...
desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with
Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V

single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one
which
appears to be the neutral or ground. Right now, 125v is measured from
this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well

pumps
and put the well pumps on the second phase. That is because the amps

per
phase is listed as only 57 amps in this configuration and I figure I
since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have

brought
the well pump 30amp dp breaker wires out to a separate 60a transfer

panel
and connected it to one of the phases of the genset. the other phase I
put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?

If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it online
somewhere, perhaps the Kohler or Onan sites.




Here is the "zig zag" low voltage 120/240V single phase connection
diagram for a 12 lead generator:

http://www.marathonelectric.com/gene...t/14X00903.pdf

I wouldn't worry about the solid neutral at this point, it's unlikely to
be the source of the problem and it is not always required to be
switched. The vast array of commercial transfer switch gear with solid
neutrals wouldn't exists if it was.

Pete C.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default hookup of 3phase genset as home backup

"Pete C." wrote:

desperado wrote:

thanks for the response. I will keep looking for the wiring diagram for the
120/240 before giving it the smoke test.

Right now, only 3 diagrams are printed on the bus bar panel.

I forgot to mention that all the neutrals of both genset and mains are
connected together. I just got thru talking to a retired electrician and he
said that is a no no. Got to disconnect the neutral of the mains when
working off backup genset. This explains possibly why, when I did try to
throw the transfer switch on the pumps, that the breaker in the main panel
tripped to this particular circuit.
All equipment is still ok. I will put in a separate switch to switch out the
neutral to the mains when on backup.
I was also worried about being unbalanced loads in each phase I am using,
but the electrician said that wasn't a problem.
I will educate myself a bit more about transfer panel setups before
throwing any more switches and am also trying to find the service and
operator manual for this particular genset.
Thanks
--
don paolino
"EXT" wrote in message
anews.com...
Agreed. 12 lead generators can be set up in a number of 3 phase and single
phase and voltage configurations including 120/240 volt single phase to
match your current house system. If you can locate the wiring diagram, it
will simplify tying into the house wiring. I have one and it is set up

this
way.

"Pete C." wrote in message
...
desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with
Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V

single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one
which
appears to be the neutral or ground. Right now, 125v is measured from
this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well

pumps
and put the well pumps on the second phase. That is because the amps

per
phase is listed as only 57 amps in this configuration and I figure I
since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have

brought
the well pump 30amp dp breaker wires out to a separate 60a transfer

panel
and connected it to one of the phases of the genset. the other phase I
put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?

If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it online
somewhere, perhaps the Kohler or Onan sites.



Here is the "zig zag" low voltage 120/240V single phase connection
diagram for a 12 lead generator:

http://www.marathonelectric.com/gene...t/14X00903.pdf

I wouldn't worry about the solid neutral at this point, it's unlikely to
be the source of the problem and it is not always required to be
switched. The vast array of commercial transfer switch gear with solid
neutrals wouldn't exists if it was.

Pete C.


Oh yea, you also have to derate slightly when in a "zig zag"
configuration:

"You can “estimate” the Zig Zag power rating by dividing the three phase
power rating by 1.2.
i.e. 58,000 W / 1.2 = 48,333 Watts (single phase Zig Zag)"

Pete C.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15
Default hookup of 3phase genset as home backup

Thanks Pete. I was going to try and search for this zig zag on Google. Sure
saves me a lot of time.
Will back off on neutral switch for the moment and check recheck all box
wiring.
I will have to translate the zig zag diagram field connections into the
specific bus bars on my genset but I think I can do that since there is a
schematic printed on a brass plate on the control panel doors.
I was thinking if that didn't work I might be better off going to
transformer configuration, but that could get expensive and still might be
tricky as I don't know how to spec the transformer.
OK on the derate. looks like 25kw. I would think that would be enough in
an emergency situation. If things get tight I have a couple of smaller sets
I use in the field to power small hand tools and motors, so I think I am ok.


"Pete C." wrote in message
...
"Pete C." wrote:

desperado wrote:

thanks for the response. I will keep looking for the wiring diagram

for the
120/240 before giving it the smoke test.

Right now, only 3 diagrams are printed on the bus bar panel.

I forgot to mention that all the neutrals of both genset and mains are
connected together. I just got thru talking to a retired electrician

and he
said that is a no no. Got to disconnect the neutral of the mains when
working off backup genset. This explains possibly why, when I did try

to
throw the transfer switch on the pumps, that the breaker in the main

panel
tripped to this particular circuit.
All equipment is still ok. I will put in a separate switch to switch

out the
neutral to the mains when on backup.
I was also worried about being unbalanced loads in each phase I am

using,
but the electrician said that wasn't a problem.
I will educate myself a bit more about transfer panel setups before
throwing any more switches and am also trying to find the service and
operator manual for this particular genset.
Thanks
--
don paolino
"EXT" wrote in message
anews.com...
Agreed. 12 lead generators can be set up in a number of 3 phase and

single
phase and voltage configurations including 120/240 volt single phase

to
match your current house system. If you can locate the wiring

diagram, it
will simplify tying into the house wiring. I have one and it is set

up
this
way.

"Pete C." wrote in message
...
desperado wrote:

I bought an old Army Corps of engineers 30kw 3 phase genset with
Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have

240V
single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for

120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load

coming
out.
There are 3big split bolt connectors coming out and one smaller

one
which
appears to be the neutral or ground. Right now, 125v is measured

from
this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the

well
pumps
and put the well pumps on the second phase. That is because the

amps
per
phase is listed as only 57 amps in this configuration and I

figure I
since
the pumps take 9 amps each running and there are two of them,

that this
would leave more amps available to power the house on the other

phase.
This
leaves the third phase not connected to anything(open circuit.)

as a
spare.
I bought some transfer panels(double pole double throw) and have
brought
the well pump 30amp dp breaker wires out to a separate 60a

transfer
panel
and connected it to one of the phases of the genset. the other

phase I
put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was

microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?

If it's a 12 lead reconnectible alternator, there is a "zig zag"
configuration used to get single phase power. I don't recall the
connection sequence offhand, but you should be able to find it

online
somewhere, perhaps the Kohler or Onan sites.



Here is the "zig zag" low voltage 120/240V single phase connection
diagram for a 12 lead generator:

http://www.marathonelectric.com/gene...t/14X00903.pdf

I wouldn't worry about the solid neutral at this point, it's unlikely to
be the source of the problem and it is not always required to be
switched. The vast array of commercial transfer switch gear with solid
neutrals wouldn't exists if it was.

Pete C.


Oh yea, you also have to derate slightly when in a "zig zag"
configuration:

"You can "estimate" the Zig Zag power rating by dividing the three phase
power rating by 1.2.
i.e. 58,000 W / 1.2 = 48,333 Watts (single phase Zig Zag)"

Pete C.



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15
Default hookup of 3phase genset as home backup

It looks like most of the crisis is over. It turns out that there is a
voltage regulator knob control which if you turn, you can vary the voltage
on the 208 tap up to 240.
I have worked the pumps off backup power now for the first time and all
appears ok.
I did find a wiring error at the pump subpanel which explained why that
breaker tripped at the SEP when I first tried all this.
Also, I did not have to disconnect the neutrals of the mains and backup
power; I can switch between the two entirely at the transfer panels.
A lot of good came of all this as I have learned a lot more about 3 phase
power and backup generators.
Thanks for everybody's help.


--
don paolino
"RBM" rbm2(remove wrote in message
...
If your single phase pumps are designed for 240 volt, I wouldn't use the

208
volt tap. Your phases are 1-2, 2-3, 1-3, so if you are using two of them

as
single phase, you are doubling up on one leg, so it does limit the

capacity.
You may be better off to connect it as a Delta, and just use the single
phase 120-240 volt taps



"desperado" wrote in message
.. .
I bought an old Army Corps of engineers 30kw 3 phase genset with

Hercules
DD298ER 6cyl motor.

The numbers on it say GE 5SJ4324Y2Y6

Jetta power
stock no 6115 976 8982
mfg 1964

I want to use it to back up my main power on my ranch. I have 240V

single
phase service coming in from Southern Calif. Edison.
My main panel is 100Amp single phase.
Genset has a busbar of 12 leads which can be reconfigured for 120/208
240/416 or 120volt delta .
Right now the 120/208 has been chosen. I measured 217V no load coming
out.
There are 3big split bolt connectors coming out and one smaller one

which
appears to be the neutral or ground. Right now, 125v is measured from

this
point to each of the big split bolts.
I decided to use one phase to power the whole house less the well pumps
and put the well pumps on the second phase. That is because the amps per
phase is listed as only 57 amps in this configuration and I figure I

since
the pumps take 9 amps each running and there are two of them, that this
would leave more amps available to power the house on the other phase.
This
leaves the third phase not connected to anything(open circuit.) as a
spare.
I bought some transfer panels(double pole double throw) and have brought
the well pump 30amp dp breaker wires out to a separate 60a transfer

panel
and connected it to one of the phases of the genset. the other phase I

put
into the 100amp main breaker and a 100 amp transfer panel.
I am a retired electrical engineer but my specialty was microwave and
antenna design and not power engineering.
Is this setup ok or do I have to install more equipment?







Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Backup Generators: Which One?? HugeBob Home Repair 18 January 17th 07 03:08 AM
My first attempt in 3phase with a VFD Rick Cox Woodworking 9 December 3rd 05 02:27 PM
A couple 3phase questions... Toller Home Repair 23 November 24th 05 02:14 PM
5-7hp 3phase motor needed Awesomewiz Metalworking 28 May 19th 05 09:12 AM
Installed new battery backup for home alarm Redtag UK diy 68 December 17th 03 09:41 AM


All times are GMT +1. The time now is 04:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"