Dan_Musicant wrote:
After the 3/4" water main was installed I am finding that my water
pressure is very much improved. I don't notice it so much when using a
tap or whatever. What I'm noticing is when I use more than one thing.
For instance, I can flush the toilet and not have my shower lose 2/3 of
its flow! It's a major improvement. The interior piping is still very
old 1/2" galvanized almost entirely, but it appears that the old 1/2"
galvanized water main was severely corroded, both on the interior and
exterior. Well, whether it was interior or exterior, combined they were
enough to make the pipe so fragile as to break in the first place,
leading to the necessary replacement.

Dan



Dan-

Here is a link to a pressure drop table for copper tubing as long as
the flows through your mainline are reasonable 10 gpm....your pressure
drop will be small

I had my mainline replace ~25 years ago & my pressure / flow to the
house is great. I can run the yard sprinklers & not notice any loss in
the house.

But when I run a second item IN the house it will steal flow /
pressure from the original use.

That's because the supply line in the house is 1930 glav steel 3/4 to
the water heater & 1/2 from there on.

The 1/2" I've removed has been so rusted / built up inside that it is
impossible to see through a 1' length.

As long as the supply to a branching point can supply the total demand
AT that branching point with small pressure drop.......demand beyond
that will not be effected by additional demand.

That's why a properly supplied "home run" manifold system will not
suffer pressure loss at the remote points.

cheers
Bob

  #42   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default 3/4" or 1" meter

I just discovered (after 15 years) that I've been paying
a premium to the water district for the privilege of
having a 1" water meter (about $15/month more than a
3/4" meter). I don't know of any good reason for needing
the larger meter since we don't use water for anything
unusual. Would it be worth the trouble to make the
change to the meter size?

[It's no problem getting to the meter since our lines are
so shallow (about 6" below ground).]
  #43   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default 3/4" or 1" meter


"Everett M. Greene" wrote in message
...
Would it be worth the trouble to make the
change to the meter size?


It will save you $80 a year, and if you have 3/4" lines, the larger meter
does no good.


  #44   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 265
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 16 Jan 2007 16:47:03 -0800, "
wrote:

:
an_Musicant wrote:
: After the 3/4" water main was installed I am finding that my water
: pressure is very much improved. I don't notice it so much when using a
: tap or whatever. What I'm noticing is when I use more than one thing.
: For instance, I can flush the toilet and not have my shower lose 2/3 of
: its flow! It's a major improvement. The interior piping is still very
: old 1/2" galvanized almost entirely, but it appears that the old 1/2"
: galvanized water main was severely corroded, both on the interior and
: exterior. Well, whether it was interior or exterior, combined they were
: enough to make the pipe so fragile as to break in the first place,
: leading to the necessary replacement.
:
: Dan
:
:time to replace the remainder before it leaks and does damage
:
:the improved pressure and flow may lead to other faster failures

Thanks! At the very least, I'll be keeping an eye on it. I can and
should have a look at the meter occasionally to see if the dial is
moving when it is not supposed to. That would be the easiest and only
foolproof method of determining if there's a leak, seems to me.

Dan

  #45   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 265
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 16 Jan 2007 20:39:15 -0800, "BobK207" wrote:

:
an_Musicant wrote:
: After the 3/4" water main was installed I am finding that my water
: pressure is very much improved. I don't notice it so much when using a
: tap or whatever. What I'm noticing is when I use more than one thing.
: For instance, I can flush the toilet and not have my shower lose 2/3 of
: its flow! It's a major improvement. The interior piping is still very
: old 1/2" galvanized almost entirely, but it appears that the old 1/2"
: galvanized water main was severely corroded, both on the interior and
: exterior. Well, whether it was interior or exterior, combined they were
: enough to make the pipe so fragile as to break in the first place,
: leading to the necessary replacement.
:
: Dan
:
:
an-
:
:Here is a link to a pressure drop table for copper tubing as long as
:the flows through your mainline are reasonable 10 gpm....your pressure
:drop will be small
:
:I had my mainline replace ~25 years ago & my pressure / flow to the
:house is great. I can run the yard sprinklers & not notice any loss in
:the house.
:
:But when I run a second item IN the house it will steal flow /
ressure from the original use.
:
:That's because the supply line in the house is 1930 glav steel 3/4 to
:the water heater & 1/2 from there on.
:
:The 1/2" I've removed has been so rusted / built up inside that it is
:impossible to see through a 1' length.
:
:As long as the supply to a branching point can supply the total demand
:AT that branching point with small pressure drop.......demand beyond
:that will not be effected by additional demand.
:
:That's why a properly supplied "home run" manifold system will not
:suffer pressure loss at the remote points.
:
:cheers
:Bob

Thanks Bob. I'm rubbing my chin on that one and trying to understand it.
You forgot the link!

Dan



  #46   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 399
Default 3/4" or 1" meter

Everett M. Greene wrote:
I just discovered (after 15 years) that I've been paying
a premium to the water district for the privilege of
having a 1" water meter (about $15/month more than a
3/4" meter). I don't know of any good reason for needing
the larger meter since we don't use water for anything
unusual. Would it be worth the trouble to make the
change to the meter size?

[It's no problem getting to the meter since our lines are
so shallow (about 6" below ground).]


You need to find out what a change would involve.
It may not be just the size of the meter that
needs to be changed.
  #47   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 265
Default 3/4" or 1" meter

On Wed, 17 Jan 2007 23:50:06 GMT, "George E. Cawthon"
wrote:

:Everett M. Greene wrote:
: I just discovered (after 15 years) that I've been paying
: a premium to the water district for the privilege of
: having a 1" water meter (about $15/month more than a
: 3/4" meter). I don't know of any good reason for needing
: the larger meter since we don't use water for anything
: unusual. Would it be worth the trouble to make the
: change to the meter size?
:
: [It's no problem getting to the meter since our lines are
: so shallow (about 6" below ground).]
:
:You need to find out what a change would involve.
: It may not be just the size of the meter that
:needs to be changed.
I just had my water main replaced and on recommendation first called the
utility. They said I was on my own. I asked them what size the meter was
and they said I had 5/8" at the meter. Some people have 5/8 some 3/4. I
asked if they could change me to 3/4 and they quoted some ridiculous
figure and forgot all about it.

If they'll change you to 3/4 without charging you (much) then you'd save
$15/month, as you say. I'd imagine you'd not notice any change in your
service other than smaller bills.
  #48   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3/4" or 1" copper water main pipe? Result is good, anyway.


Dan_Musicant wrote:
On 16 Jan 2007 20:39:15 -0800, "BobK207" wrote:

:
an_Musicant wrote:
: After the 3/4" water main was installed I am finding that my water
: pressure is very much improved. I don't notice it so much when using a
: tap or whatever. What I'm noticing is when I use more than one thing.
: For instance, I can flush the toilet and not have my shower lose 2/3 of
: its flow! It's a major improvement. The interior piping is still very
: old 1/2" galvanized almost entirely, but it appears that the old 1/2"
: galvanized water main was severely corroded, both on the interior and
: exterior. Well, whether it was interior or exterior, combined they were
: enough to make the pipe so fragile as to break in the first place,
: leading to the necessary replacement.
:
: Dan
:
:
an-
:
:Here is a link to a pressure drop table for copper tubing as long as
:the flows through your mainline are reasonable 10 gpm....your pressure
:drop will be small
:
:I had my mainline replace ~25 years ago & my pressure / flow to the
:house is great. I can run the yard sprinklers & not notice any loss in
:the house.
:
:But when I run a second item IN the house it will steal flow /
ressure from the original use.
:
:That's because the supply line in the house is 1930 glav steel 3/4 to
:the water heater & 1/2 from there on.
:
:The 1/2" I've removed has been so rusted / built up inside that it is
:impossible to see through a 1' length.
:
:As long as the supply to a branching point can supply the total demand
:AT that branching point with small pressure drop.......demand beyond
:that will not be effected by additional demand.
:
:That's why a properly supplied "home run" manifold system will not
:suffer pressure loss at the remote points.
:
:cheers
:Bob

Thanks Bob. I'm rubbing my chin on that one and trying to understand it.
You forgot the link!

Dan


http://www.engineeringtoolbox.com/pr...pes-d_930.html

  #50   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 265
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 17 Jan 2007 23:34:25 -0800, "BobK207" wrote:

: Thanks Bob. I'm rubbing my chin on that one and trying to understand it.
: You forgot the link!
:
: Dan
:
:http://www.engineeringtoolbox.com/pr...pes-d_930.html

Ah, thanks. The subject is:

"Pressure Loss of Water Due to Friction in Copper Tubes"

My intuition on this is that the friction component using copper tubing
(especially new) is going to be WAY less than my old rusty galvanized
1/2". Add to that the fact that the cross section of the interior of
3/4" pipe is 2.25 times that of 1/2" pipe, and you have MUCH better
water flow and pressure. That's intuitive, of course. The linked page
and it's table is based on engineering science.

Dan


  #52   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

Dan_Musicant wrote:
On 17 Jan 2007 23:34:25 -0800, "BobK207" wrote:

: Thanks Bob. I'm rubbing my chin on that one and trying to understand it.
: You forgot the link!
:
: Dan
:
:http://www.engineeringtoolbox.com/pr...pes-d_930.html

Ah, thanks. The subject is:

"Pressure Loss of Water Due to Friction in Copper Tubes"

My intuition on this is that the friction component using copper tubing
(especially new) is going to be WAY less than my old rusty galvanized
1/2". Add to that the fact that the cross section of the interior of
3/4" pipe is 2.25 times that of 1/2" pipe, and you have MUCH better
water flow and pressure. That's intuitive, of course. The linked page
and it's table is based on engineering science.

Dan



Your intuition is correct.......YEARS ago (1979) I was having the
shower feeds in my 1930 house redone

I was so fed up with low water pressure I was going to make the plumber
replace my 59 year old 1/2 galv with 3/4" cooper feeding first floor
shower & then onto the 2nd floor.

I really water 3/4" copper the plumber talked me out of it....saying
the "flow factor" of old copper tube is way better than new glav. I
went with 1/2" copper.

Fast forward to 2007 & now I finally getting around to doing the rest
of the house.

I'm going to use PEX w/ a home run system. I'm torn about replacing
the perfectly still good copper but I may as well since the walls will
be open.

The 16' run to 1st floor shower & the 26' run to second floor

Worst case with 125F hot water & 45F cold water (that's pretty cold)
......I'll need 1.5 gpm hot & .5 gpm cold to service a 2gpm shower

A run of 1/2" PEX 26' long will only drop ~1.8psi

My house is fed with 1" copper (~50' to the street) another 25' of 1"
PEX to the hot/cold split

1" feeding the cold manifold & 1" feeding the hot manifold

If I run the dishwasher (~2gpm) & two showers (2 gpm ea) I'll need
~6gpm to the house & 5 gpm hot water


The thing that causes problems is not only the pressure drop but the
change in pressure drop as water demand increases or decreases. When
you're taking a shower & you have the temp adjust you don't want
significant increases or decreases in water pressure where you're using
it....reduction is total pressure is annoying enough but when the hot
or cold pressure changes alone...it can be more than annoying.

Unfortunately that table of copper tube pressure drops leaves a little
to be desires wrt significant figures......only one in most of the
entries

anyway if you play around with the numbers you'll probably find that a
3/4" line will supply most reasonable home usage without significant
pressure drop.....unless you get the washer going, the dishwasher, two
showers & a random toilet flushing.

But hey, I'm just happy if I can take a shower & not be bothered by
one or two other water usages.

cheers
Bob

  #53   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 2007-01-19, BobK207 wrote:

1" feeding the cold manifold & 1" feeding the hot manifold


Bob,

Isn't 1" feeding the hot manifold overkill? The downside of
oversizing hot water supply pipes is that you have to empty them every
time you want hot water at a fixture. That's roughly true, as my
experience has been that the period between hot water uses usually
exceeds the cooling time of the water in the pipe, even if the pipe is
insulated. Emptying the pipes wastes water (unless you have a point
of use pump) and energy, the heat loss of the water that had been hot.

Just a thought.

Cheers, Wayne

  #54   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3/4" or 1" copper water main pipe? Result is good, anyway.


Wayne Whitney wrote:
On 2007-01-19, BobK207 wrote:

1" feeding the cold manifold & 1" feeding the hot manifold


Bob,

Isn't 1" feeding the hot manifold overkill? The downside of
oversizing hot water supply pipes is that you have to empty them every
time you want hot water at a fixture. That's roughly true, as my
experience has been that the period between hot water uses usually
exceeds the cooling time of the water in the pipe, even if the pipe is
insulated. Emptying the pipes wastes water (unless you have a point
of use pump) and energy, the heat loss of the water that had been hot.

Just a thought.

Cheers, Wayne


Wayne-

You are absolutely correct on that, 1" is way over kill for a supply to
a normal house hot water manifold

Except in my installation the tube run from the WH to the manifold will
be about 6' max. I didn't want to buy a roll of 3/4" just for that
short run. The rest of my installation will be 1/2" (~500') plus about
20' of 1"

So I really don't need much 3/4 or 1". Got a source short lengths of
3/4" & 1" ?

cheers
Bob

  #55   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 265
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 19 Jan 2007 00:42:14 -0800, "BobK207" wrote:

an_Musicant wrote:
: On 17 Jan 2007 23:34:25 -0800, "BobK207" wrote:
:
: : Thanks Bob. I'm rubbing my chin on that one and trying to understand it.
: : You forgot the link!
: :
: : Dan
: :
: :http://www.engineeringtoolbox.com/pr...pes-d_930.html
:
: Ah, thanks. The subject is:
:
: "Pressure Loss of Water Due to Friction in Copper Tubes"
:
: My intuition on this is that the friction component using copper tubing
: (especially new) is going to be WAY less than my old rusty galvanized
: 1/2". Add to that the fact that the cross section of the interior of
: 3/4" pipe is 2.25 times that of 1/2" pipe, and you have MUCH better
: water flow and pressure. That's intuitive, of course. The linked page
: and it's table is based on engineering science.
:
: Dan
:
:
:Your intuition is correct.......YEARS ago (1979) I was having the
:shower feeds in my 1930 house redone
:
:I was so fed up with low water pressure I was going to make the plumber
:replace my 59 year old 1/2 galv with 3/4" cooper feeding first floor
:shower & then onto the 2nd floor.
:
:I really water 3/4" copper the plumber talked me out of it....saying
:the "flow factor" of old copper tube is way better than new glav. I
:went with 1/2" copper.

Today I had a look at the old water main shutoff valve that they cut out
when they replaced the water main. On either side is galvanized pipe and
on one side I could see rust that reduced the 1/2" internal diameter by
at least a factor of 2. And that is just one spot. And the knobby rusty
obstruction was clearly doing more than restricting flow by reducing the
effective diameter. It was adding a tremendous amount of turbulence,
which would very significantly reduce the gpm delivered to various
sytems in my house. I'm contemplating replacing some of the interior
piping, but I really have no good reason to do so presently. My
pressures are good, at least partly because of the high pressure
delivered to the house. I should probably actually have a pressure
reduction valve where the main surfaces at the front of the house. A
Plumber told me they are $100 and I believe they only reduce the psi by
5-7 psi.
:
:Fast forward to 2007 & now I finally getting around to doing the rest
f the house.
:
:I'm going to use PEX w/ a home run system. I'm torn about replacing
:the perfectly still good copper but I may as well since the walls will
:be open.
:
:The 16' run to 1st floor shower & the 26' run to second floor
:
:Worst case with 125F hot water & 45F cold water (that's pretty cold)
:.....I'll need 1.5 gpm hot & .5 gpm cold to service a 2gpm shower

My requirements are different because I live alone. I envision selling
the house, so the buyer's requirements will be greater than mine.

Myself, I have an on demand WH, which has a remote and I keep the
temperature at the lowest, which is 100 degrees. When I take a shower, I
push that to 110 in the summer and 115 in winter. When it's chilly, 115
delivers a perfect shower using hot water only. I guess that even if
someone were to flush a toilet while I was taking a shower it wouldn't
much affect the water temperature.

If you have a lot of people in the house, measures like mine aren't
practical, obviously. You have constant hot water temperature and deal
with it.
:
:A run of 1/2" PEX 26' long will only drop ~1.8psi
:
:My house is fed with 1" copper (~50' to the street) another 25' of 1"
:PEX to the hot/cold split
:
:1" feeding the cold manifold & 1" feeding the hot manifold
:
:If I run the dishwasher (~2gpm) & two showers (2 gpm ea) I'll need
:~6gpm to the house & 5 gpm hot water

I don't have a dishwasher yet.
:
:
:The thing that causes problems is not only the pressure drop but the
:change in pressure drop as water demand increases or decreases. When
:you're taking a shower & you have the temp adjust you don't want
:significant increases or decreases in water pressure where you're using
:it....reduction is total pressure is annoying enough but when the hot
r cold pressure changes alone...it can be more than annoying.

I'm amazed that my shower flow doesn't appear to drop much AT ALL, when
I flush the toilet now with my new water main installed.
:
:Unfortunately that table of copper tube pressure drops leaves a little
:to be desires wrt significant figures......only one in most of the
:entries
:
:anyway if you play around with the numbers you'll probably find that a
:3/4" line will supply most reasonable home usage without significant
ressure drop.....unless you get the washer going, the dishwasher, two
:showers & a random toilet flushing.
:
:But hey, I'm just happy if I can take a shower & not be bothered by
ne or two other water usages.

That would be nice.

:cheers
:Bob



  #56   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default 3/4" or 1" copper water main pipe? Result is good, anyway.

On 2007-01-19, BobK207 wrote:

So I really don't need much 3/4 or 1". Got a source short lengths of
3/4" & 1" ?


Use copper for the 3/4"? If you bump a pipe up from 3/4" to 1",
assuming the ID is the nominal diameter (which it isn't), then for
every one foot length of the increased size, the pipe takes 1 second
longer to empty at 1.0 gpm.

Cheers, Wayne
  #57   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 798
Default 3/4" or 1" meter

"Edwin Pawlowski" writes:
"Everett M. Greene" wrote in message
...
Would it be worth the trouble to make the
change to the meter size?


It will save you $80 a year, and if you have 3/4" lines, the larger meter
does no good.


I get 15*12= $180/year
  #58   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default 3/4" or 1" meter


"blueman" wrote in message


It will save you $80 a year, and if you have 3/4" lines, the larger meter
does no good.


I get 15*12= $180/year


so did I, but the "1" key was not hit hard enough. I'll make up for it now.
1 1 1 1 1 1 1 1 1


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing water main with MDPE pipe - will it help my pressure? Lobster UK diy 10 August 30th 04 02:14 PM
A/C Drainage Pipe clogged... water backing up into hallway Ringo Langly Home Repair 5 August 19th 04 02:50 PM
A/C Drainage Pipe clogged... water backing up into hallway Ringo Langly Home Repair 6 August 17th 04 09:15 PM
laundry faucets - water coming out from drainage pipe YesBalala Home Repair 2 August 6th 04 11:08 PM
Replacing old steel water main supply pipe Pandora UK diy 3 January 24th 04 08:53 AM


All times are GMT +1. The time now is 04:10 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"