The thermostat settings currently are LO = 130F and HI = 160F. But the
furnace comes on when the water temperature guage reads 160F, and shuts
off when the temperature gauge reads 185F. The temperature gauge
continues to climb to about 190F after the furnace shuts off, due (I
think) to the lag time for the water temp to stabilize.

Does this sound normal? Why doesn't the temperature gauge track with
the thermostat settings? Should I lower the settings?

This is a Burnham V83 boiler in an oil / hot water heating system with
a coil inside the boiler for hot water.

Thanks,
Art Harris

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default Boiler Temperature Setting Question


wrote in message
oups.com...
The thermostat settings currently are LO = 130F and HI = 160F. But the
furnace comes on when the water temperature guage reads 160F, and shuts
off when the temperature gauge reads 185F. The temperature gauge
continues to climb to about 190F after the furnace shuts off, due (I
think) to the lag time for the water temp to stabilize.

Does this sound normal? Why doesn't the temperature gauge track with
the thermostat settings? Should I lower the settings?


No, your furnace should not come on because of the water temerature. It has
nothing to do with it. What? You don't have a furnace? Right, you have a
boiler. Boilers heat water or make steam. They do thes with burners.
Furnaces heat air.

But your thermostat should be set for a comfort level of about 66 to 70
degrees. You'll never get the house up that high no matter where you set
the thermostat.

Now, we can talk Aquastats. That is what you have inside the boiler to
measure the water temperature. Yes, the setting are about right.

Before you think I'm just busing your ass about terminology, there is good
reason to use the right terms. It helps to understand how the system works,
what "stat" controls what part of the system. Taking this one more step,
the thermostats for the room temperature does not control the heater. It
just tells the circulator (or zone valves) that you want heat and the water
will start moving through the radiators. It is the aquastat inside the
boiler that is telling the burner to go on and then off again as needed.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Boiler Temperature Setting Question

Paul Flansburg wrote:
wrote:
The thermostat settings currently are LO = 130F and HI = 160F. But the
furnace comes on when the water temperature guage reads 160F, and shuts
off when the temperature gauge reads 185F. The temperature gauge
continues to climb to about 190F after the furnace shuts off, due (I
think) to the lag time for the water temp to stabilize.

Does this sound normal? Why doesn't the temperature gauge track with
the thermostat settings? Should I lower the settings?

This is a Burnham V83 boiler in an oil / hot water heating system with
a coil inside the boiler for hot water.

All wrong answers......Take a look at the aquastat. This is NOT a
thermostat, but an Aquastat for maintaining the operating temperature
of the boiler. There should be 3 dials on the aquastat. Lo and hi
cutoff and the differential setting. It sounds like the diferential
dial setting is set at 25. This is not a problem!!! Figure out which
manufacturer you have, most are Honeywell, and do a google on the
manufac. and model number. All of your questions will be answered once
you find the correct document.


Thanks for your reply. The Aquastat is a Honeywell Model L4081B. I
googled and found the data on it.

http://customer.honeywell.com/Techli...0s/60-2105.pdf

My unit only has two dials, HI and LO. The manual states that HI sets
the boiler temperature, and LO controls the circulator. It doesn't
describe how to set the "differential" temperature.

My question still is: With HI set to 160F, why does my gauge show
temperatures as high as 185F? The diagram in the manual shows that the
burner shuts off at the HI set point.

Art Harris

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 63
Default Boiler Temperature Setting Question

In article .com, on
15 Dec 2006 05:32:39 -0800, wrote:

The thermostat settings currently are LO = 130F and HI = 160F. But the
furnace comes on when the water temperature guage reads 160F, and shuts
off when the temperature gauge reads 185F. The temperature gauge
continues to climb to about 190F after the furnace shuts off, due (I
think) to the lag time for the water temp to stabilize.

Does this sound normal? Why doesn't the temperature gauge track with
the thermostat settings? Should I lower the settings?

This is a Burnham V83 boiler in an oil / hot water heating system with
a coil inside the boiler for hot water.


The manual for your boiler:

http://www.burnham.com/pdfs/CurrentPDFfiles/V8_I&O.pdf

See page 47. Low limit gets set at 190, with 25 degree differential -
i.e., on at 165, off at 190. High limit (emergency) shutdown set at 210.

Sounds like your aquastat is miscalibrated, but has been corrected for
by actual measurement.

It appears your boiler is working as intended. Are you having any
problems? If not, stop messing with it! ;-)


--
Seth Goodman
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 32
Default Boiler Temperature Setting Question


wrote:
Paul Flansburg wrote:
wrote:
The thermostat settings currently are LO = 130F and HI = 160F. But the
furnace comes on when the water temperature guage reads 160F, and shuts
off when the temperature gauge reads 185F. The temperature gauge
continues to climb to about 190F after the furnace shuts off, due (I
think) to the lag time for the water temp to stabilize.

Does this sound normal? Why doesn't the temperature gauge track with
the thermostat settings? Should I lower the settings?

This is a Burnham V83 boiler in an oil / hot water heating system with
a coil inside the boiler for hot water.

All wrong answers......Take a look at the aquastat. This is NOT a
thermostat, but an Aquastat for maintaining the operating temperature
of the boiler. There should be 3 dials on the aquastat. Lo and hi
cutoff and the differential setting. It sounds like the diferential
dial setting is set at 25. This is not a problem!!! Figure out which
manufacturer you have, most are Honeywell, and do a google on the
manufac. and model number. All of your questions will be answered once
you find the correct document.


Thanks for your reply. The Aquastat is a Honeywell Model L4081B. I
googled and found the data on it.

http://customer.honeywell.com/Techli...0s/60-2105.pdf

My unit only has two dials, HI and LO. The manual states that HI sets
the boiler temperature, and LO controls the circulator. It doesn't
describe how to set the "differential" temperature.

My question still is: With HI set to 160F, why does my gauge show
temperatures as high as 185F? The diagram in the manual shows that the
burner shuts off at the HI set point.

Art Harris


Art, There are tolerances in everything.....You have a built-in
differential of 10 degree's on the HI limit. That puts you at 170
degree's to start with. Then, there are tolerances built into the
temp. gauge. So, with a stack up of all of the tolerances and the
differential I'd say your okay.

Questions: Is there an actual problem with the boiler that made you
look into the temperature gauge? OR did you happen to notice that the
temp. and the settings were not making sense? If there's an issue,
then let's talk about it?

Do you have plenty of heat and hot water?
Does the boiler fire on and off smoothly, no bangs, hesitations, smell
of oil or smoke?

-paul

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Boiler Temperature Setting Question

Paul Flansburg wrote:
Art, There are tolerances in everything.....You have a built-in
differential of 10 degree's on the HI limit. That puts you at 170
degree's to start with. Then, there are tolerances built into the
temp. gauge. So, with a stack up of all of the tolerances and the
differential I'd say your okay.

Questions: Is there an actual problem with the boiler that made you
look into the temperature gauge? OR did you happen to notice that the
temp. and the settings were not making sense? If there's an issue,
then let's talk about it?


I just had a leaking 8-year-old Burnham V73 block replaced under
warranty with the V83. That's why I'm looking closely at everything.


Do you have plenty of heat and hot water?
Does the boiler fire on and off smoothly, no bangs, hesitations, smell
of oil or smoke?


Yes, plenty of hot water (my wife says it's _too_ hot). I'm just trying
to make sense out of what I'm seeing, and be sure there isn't a
problem. Sounds like all is well.

Art Harris



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 32
Default Boiler Temperature Setting Question


wrote:
Paul Flansburg wrote:
Art, There are tolerances in everything.....You have a built-in
differential of 10 degree's on the HI limit. That puts you at 170
degree's to start with. Then, there are tolerances built into the
temp. gauge. So, with a stack up of all of the tolerances and the
differential I'd say your okay.

Questions: Is there an actual problem with the boiler that made you
look into the temperature gauge? OR did you happen to notice that the
temp. and the settings were not making sense? If there's an issue,
then let's talk about it?


I just had a leaking 8-year-old Burnham V73 block replaced under
warranty with the V83. That's why I'm looking closely at everything.


Do you have plenty of heat and hot water?
Does the boiler fire on and off smoothly, no bangs, hesitations, smell
of oil or smoke?


Yes, plenty of hot water (my wife says it's _too_ hot). I'm just trying
to make sense out of what I'm seeing, and be sure there isn't a
problem. Sounds like all is well.

Art Harris


The most important item you need to understand is that your boiler is
NOT a cold fired boiler. What this means is that you need to maintain
at least a temperature of somewhere in the oder of 140 F. Having the
boiler continuosly go from 0 F to operating temp is not good for the
seals. You have a cast iron boiler, and if I remember correctly it's
probably a 4 section. The seals are what make the connection between
the sections and the seals do not like to expand and contract with
large temperature swings. The reason why I mention this is because you
mentioned that your previous boiler leaked.

Is your domestic hot water made by a tankless coil? If so, adjust the
tempering value. If this doesn't work, replace it! Probably cost
about $10 or so dollars and your time.

-paul

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Boiler Temperature Setting Question

In article . com, "Paul Flansburg" wrote:
The most important item you need to understand is that your boiler is
NOT a cold fired boiler. What this means is that you need to maintain
at least a temperature of somewhere in the oder of 140 F. Having the
boiler continuosly go from 0 F to operating temp is not good for the
seals.


There won't be much left of that boiler if it ever gets down to 0 F !!

And I suspect that the homeowner would notice that the house was intolerably
cold long before it got even close.

You have a cast iron boiler, and if I remember correctly it's
probably a 4 section. The seals are what make the connection between
the sections and the seals do not like to expand and contract with
large temperature swings.


The water returning to the boiler from the radiators can't possibly be any
colder than room temperature (typically about 68 F), which limits the possible
temperature swing to a little over seventy degrees if the operating temp is
set at 140 F. In practice, the temperature of the return water is much, much
higher than room temperature, and the temperature swings experienced by the
boiler are correspondingly smaller.


The reason why I mention this is because you
mentioned that your previous boiler leaked.


I very much doubt that the leaking was caused by one hundred forty degree
temperature swings.


--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Boiler Temperature Setting Question

replying to n2ah, Abel wrote:
how do you set TIC in the boiler

--
for full context, visit https://www.homeownershub.com/mainte...on-175973-.htm


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
VAILLANT COMBI-BOILER - need help with setting it up! [email protected] UK diy 5 February 7th 06 06:56 PM
boiler thermostat setting sPoNiX UK diy 5 December 12th 05 04:32 PM
Temperature setting for PEX radiant heat [email protected] Home Repair 1 November 17th 05 02:35 PM
boiler thermostat setting andyd UK diy 7 October 20th 04 05:57 PM
boiler thermostat temperature manoman UK diy 11 November 1st 03 12:50 PM


All times are GMT +1. The time now is 01:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"