Default Holes through floor joists for 10/2?

So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill the
smallest possible hole to minimize weakening the joists and then pulling the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am I
making too much out of this?


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default Holes through floor joists for 10/2?


Toller wrote:
So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill the
smallest possible hole to minimize weakening the joists and then pulling the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am I
making too much out of this?



Best to drill joists in center of the joist depth, never in the center
1/3 of the span and 6" or mare from the bearing ends

Max hole size is 1/3 the joist depth & min edge distance is 2"

From the Inrenational Residential Code 2003 Edition, Chapter 5 Floors,

Section R502.8.1 Sawn Lumber:

"The diameter of holes bored or cut into members shall not exceed
one-third the depth of the member. Holes shall not be closer than 2
inches to the top or bottom of the member, or to any other hole located
in the member. Where the member is also notched, the hole shall not be
closer than 2 inches to the notch."



Now as to multiple holes...hmmm... a single large hole would easilt
accomdate all but not after they're already there.

If you're gutsy, careful & lucky you could enlarge an existing hole
with the wire still in place OR remove the wire & hole sawa bigger
hole OR just drill another hole....I'd want at least 2 or 3 hole
diameters of "meat" between the holes...if my thinking is correct 1"
holes could be drilled 3 or 4" apart (min) seems resonable

IMO the single large hole is looking better & better


this code passage says 2" minimum "meat" between holes...my concept
depends on hole diameter...I like mine better...... code passage
allows 3" holes in a 2x10 with only 2" of meat between them ...that
makes me nervous

cheers
Bob

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Holes through floor joists for 10/2?


"BobK207" wrote in message
ps.com...

Toller wrote:
So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill
the
smallest possible hole to minimize weakening the joists and then pulling
the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am
I
making too much out of this?



Best to drill joists in center of the joist depth, never in the center
1/3 of the span and 6" or mare from the bearing ends

Max hole size is 1/3 the joist depth & min edge distance is 2"

From the Inrenational Residential Code 2003 Edition, Chapter 5 Floors,

Section R502.8.1 Sawn Lumber:

"The diameter of holes bored or cut into members shall not exceed
one-third the depth of the member. Holes shall not be closer than 2
inches to the top or bottom of the member, or to any other hole located
in the member. Where the member is also notched, the hole shall not be
closer than 2 inches to the notch."



Now as to multiple holes...hmmm... a single large hole would easilt
accomdate all but not after they're already there.

If you're gutsy, careful & lucky you could enlarge an existing hole
with the wire still in place OR remove the wire & hole sawa bigger
hole OR just drill another hole....I'd want at least 2 or 3 hole
diameters of "meat" between the holes...if my thinking is correct 1"
holes could be drilled 3 or 4" apart (min) seems resonable

IMO the single large hole is looking better & better


this code passage says 2" minimum "meat" between holes...my concept
depends on hole diameter...I like mine better...... code passage
allows 3" holes in a 2x10 with only 2" of meat between them ...that
makes me nervous

Thanks, my holes are only like 3/4" so I seem to have a pretty big safety
margin.
Yeah bigger holes would have saved a great deal of work, but so would a
subpanel in the shop. But those boats have sailed.
Though maybe not; perhaps I should bit the bullet and replace one of the
12/2 cables with a 8/3 to a subpanel. It is too late at night to be
thinking about such things.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 191
Default Holes through floor joists for 10/2?

Toller wrote:
"BobK207" wrote in message
ps.com...

Toller wrote:

So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill
the
smallest possible hole to minimize weakening the joists and then pulling
the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am
I
making too much out of this?



Best to drill joists in center of the joist depth, never in the center
1/3 of the span and 6" or mare from the bearing ends

Max hole size is 1/3 the joist depth & min edge distance is 2"

From the Inrenational Residential Code 2003 Edition, Chapter 5 Floors,

Section R502.8.1 Sawn Lumber:

"The diameter of holes bored or cut into members shall not exceed
one-third the depth of the member. Holes shall not be closer than 2
inches to the top or bottom of the member, or to any other hole located
in the member. Where the member is also notched, the hole shall not be
closer than 2 inches to the notch."



Now as to multiple holes...hmmm... a single large hole would easilt
accomdate all but not after they're already there.

If you're gutsy, careful & lucky you could enlarge an existing hole
with the wire still in place OR remove the wire & hole sawa bigger
hole OR just drill another hole....I'd want at least 2 or 3 hole
diameters of "meat" between the holes...if my thinking is correct 1"
holes could be drilled 3 or 4" apart (min) seems resonable

IMO the single large hole is looking better & better


this code passage says 2" minimum "meat" between holes...my concept
depends on hole diameter...I like mine better...... code passage
allows 3" holes in a 2x10 with only 2" of meat between them ...that
makes me nervous


Thanks, my holes are only like 3/4" so I seem to have a pretty big safety
margin.
Yeah bigger holes would have saved a great deal of work, but so would a
subpanel in the shop. But those boats have sailed.
Though maybe not; perhaps I should bit the bullet and replace one of the
12/2 cables with a 8/3 to a subpanel. It is too late at night to be
thinking about such things.



You do not want to pull more than one cable through a hole;
theoretically the currents in any given cable sum to zero but if you are
pulling a LOT of current and there's a cable smack up against another
one, you could get some induced voltages.

nate

--
replace "fly" with "com" to reply.
http://home.comcast.net/~njnagel
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Holes through floor joists for 10/2?

Wouldn't that imply that everyone is getting lots of induced voltages
at the load panel where all the circuits meet and some are "smack up
against another" as they run into the box? I have a some romex
connectors with 2 and 3 circuits passing through them into the box.

Would the very short distance of "smack up against another" in these
cases make the induced voltages negligible?

Thanks!


Nate Nagel wrote:


You do not want to pull more than one cable through a hole;
theoretically the currents in any given cable sum to zero but if you are
pulling a LOT of current and there's a cable smack up against another
one, you could get some induced voltages.

nate

--
replace "fly" with "com" to reply.
http://home.comcast.net/~njnagel




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 136
Default Holes through floor joists for 10/2?

I think it was Nate Nagel who stated:


You do not want to pull more than one cable through a hole;
theoretically the currents in any given cable sum to zero but if you are
pulling a LOT of current and there's a cable smack up against another
one, you could get some induced voltages.


True, in theory. And in practice in some places, homes not being one
of them for typical home wiring, which is, I believe, what the OP is
talking about.

The amount of induced voltage in home installations is irrelevant and
can be ignored, as evidenced by MANY power cables sharing MANY holes
with impunity in every home I've ever lived in.
--
"Trust me, there is NO way to nonchalantly conceal the fact that you have a
power tool in your head, no matter what you do." -- El Gato
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Holes through floor joists for 10/2?


Don Fearn wrote:
I think it was Nate Nagel who stated:


You do not want to pull more than one cable through a hole;
theoretically the currents in any given cable sum to zero but if you are
pulling a LOT of current and there's a cable smack up against another
one, you could get some induced voltages.


True, in theory. And in practice in some places, homes not being one
of them for typical home wiring, which is, I believe, what the OP is
talking about.

The amount of induced voltage in home installations is irrelevant and
can be ignored, as evidenced by MANY power cables sharing MANY holes
with impunity in every home I've ever lived in.
--
"Trust me, there is NO way to nonchalantly conceal the fact that you have a
power tool in your head, no matter what you do." -- El Gato



That's for sure. If just having one AC cable next to another was a
problem, there would be a lot of screwed up houses, including new
constructions. Any induced voltage is going to be so small that it's
nothing compared to the fluctuations caused by normal powerline
transients, turning on/off large loads, etc.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,270
Default Holes through floor joists for 10/2?

What hole size is recommended for 10/2 in floor joists?

I usually drill 5/8" holes for 14/2 and 12/2 wiring. I think 10/2 wiring
fits too, but it has been a while since I wired our house. You could easily
switch to 3/4" if needed. Basically, the hole should be big enough for the
wire to pass through easily without binding or damaging the cable sheath.
Anything bigger just weakens the joists/studs.

Still, if you have lots of wiring to run, it's easier to drill a bunch of
equal sized holes, even if you're running different cable sizes. This also
lets you buy a good quality self-feeding auger bit, instead of a bunch of
cheap bits in multiple sizes.

I only run one cable through each hole and try to space multiple holes at
least 4" apart (center to center). Try to drill your holes in the center of
the joist (vertically) when possible, and never near the upper or lower two
inches. Space multiple holes along the length of the joist, not on top of
each other vertically.

Anthony
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 41
Default Holes through floor joists for 10/2?

On Sat, 09 Dec 2006 06:25:10 GMT, "Toller" wrote:


"BobK207" wrote in message
ups.com...

Toller wrote:
So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill
the
smallest possible hole to minimize weakening the joists and then pulling
the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am
I
making too much out of this?



Best to drill joists in center of the joist depth, never in the center
1/3 of the span and 6" or mare from the bearing ends

Max hole size is 1/3 the joist depth & min edge distance is 2"

From the Inrenational Residential Code 2003 Edition, Chapter 5 Floors,

Section R502.8.1 Sawn Lumber:

"The diameter of holes bored or cut into members shall not exceed
one-third the depth of the member. Holes shall not be closer than 2
inches to the top or bottom of the member, or to any other hole located
in the member. Where the member is also notched, the hole shall not be
closer than 2 inches to the notch."



Now as to multiple holes...hmmm... a single large hole would easilt
accomdate all but not after they're already there.

If you're gutsy, careful & lucky you could enlarge an existing hole
with the wire still in place OR remove the wire & hole sawa bigger
hole OR just drill another hole....I'd want at least 2 or 3 hole
diameters of "meat" between the holes...if my thinking is correct 1"
holes could be drilled 3 or 4" apart (min) seems resonable

IMO the single large hole is looking better & better


this code passage says 2" minimum "meat" between holes...my concept
depends on hole diameter...I like mine better...... code passage
allows 3" holes in a 2x10 with only 2" of meat between them ...that
makes me nervous

Thanks, my holes are only like 3/4" so I seem to have a pretty big safety
margin.
Yeah bigger holes would have saved a great deal of work, but so would a
subpanel in the shop. But those boats have sailed.
Though maybe not; perhaps I should bit the bullet and replace one of the
12/2 cables with a 8/3 to a subpanel. It is too late at night to be
thinking about such things.


A 3/4" hole should be able to fit 3 12-2 cables.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default Holes through floor joists for 10/2? Warning Toller troll

Toller posted for all of us...

So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill the
smallest possible hole to minimize weakening the joists and then pulling the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am I
making too much out of this?



Toller is Google still broke for you? Do you post to get permission to take a
**** and how many times to wipe. ALL asked before
--
Tekkie Don't bother to thank me, I do this as a public service.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Holes through floor joists for 10/2? Warning Toller troll


"Tekkie®" wrote in message
...
Toller posted for all of us...

So far I have run 3 new circuits from the breaker box on one side of the
house to the workshop and garage on the other. I have to run a 4th.

What hole size is recommended for 10/2 in floor joists? I alway drill
the
smallest possible hole to minimize weakening the joists and then pulling
the
cable is an ordeal.
Is it necessary to keep the holes any distance from existing holes, or am
I
making too much out of this?



Toller is Google still broke for you? Do you post to get permission to
take a
**** and how many times to wipe. ALL asked before
--

If I took a ****, you would be gone!


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default Holes through floor joists for 10/2? Warning Toller troll

Toller posted for all of us...

--

If I took a ****, you would be gone!

Because you would flush yourself away you fundy idiot.
--
Tekkie Don't bother to thank me, I do this as a public service.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Drilling holes in floor joists jimbob Home Repair 4 October 6th 06 04:26 AM
Filling holes in joists The3rd Earl Of Derby UK diy 10 September 5th 06 11:49 PM
Drill holes, cables and joists Jim Ingram UK diy 1 February 11th 06 11:41 PM
holes in floor joists - where? [email protected] Home Repair 10 October 21st 05 01:59 PM
Drilling holes in joists Dave UK diy 5 October 4th 04 08:06 PM


All times are GMT +1. The time now is 07:08 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"