Default household voltage results

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?



  #2   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default household voltage results

Bob Bins wrote:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?



That sounds pretty low to me. I generally get pretty close to 120V.
Even today, with the extreme heat and high loads it brings, I still
have 117V.

Are you sure your meter is right?

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default household voltage results

In ,
Bob Bins wrote:
I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have
my two AC window units on it drops to about 109-112. If I then turn
my microwave on it drops to about 102-104. I tested this on two
different circuits both on different sides of the breaker panel.
This voltage sounds low to me. Is this normal or should I be seeing
higher values?


The NEC recommends a voltage drop under load of no more than 5%. If it's
114V with no load, then under load it should be 108V or higher.

Without knowing which appliance is on which circuit or where you are
measuring, I can't comment further.
--
Jim
"Remember, an amateur built the Ark; professionals built the Titanic."


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default household voltage results

In ,
Bob Bins wrote:
I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have
my two AC window units on it drops to about 109-112. If I then turn
my microwave on it drops to about 102-104. I tested this on two
different circuits both on different sides of the breaker panel.
This voltage sounds low to me. Is this normal or should I be seeing
higher values?


The NEC recommends a voltage drop under load of no more than 5%. If it's
114V with no load, then under load it should be 108V or higher.

Without knowing which appliance is on which circuit or where you are
measuring, I can't comment further.
--
Jim
"Remember, an amateur built the Ark; professionals built the Titanic."



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default household voltage results


Bob Bins wrote:
I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?

it could be several things. like loose screws in the panel, meter
socket, bad connection on the pole,too many services on one
transformer,undersized service.
try checking your panel connections at the breakers and nuetral bar.
then with breakers off check voltage if its still 114v the power
company might be willing to up your voltage.
i suppose i should recommend you contact an electrician to safely
perform some of these things.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,392
Default household voltage results

Bob Bins writes:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts.


Confirm the meter reading, then get the utility to buck you up to 120 VAC.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 168
Default household voltage results


"Bob Bins" wrote in message
. ..
I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?


Kind of low. The issue now is whether the cause of the voltage drop is
inside your house or outside.

Do the test again but this time hook up your meter to the panel on the same
phase as the AC and microwave's circuit. It should read 114V. If you can't
tell which phase is the right one, then measure both phases.

Then turn on the AC and microwave. What is the voltage? If it also drops to
102-104, then the problem is outside the panel.


  #8   Report Post  
Posted to alt.home.repair
Bob Bob is offline
external usenet poster
 
Posts: 119
Default household voltage results


"Bob Bins" wrote in message
. ..
I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?


It sound low to me, and I suspect there is a bad connection somewhere.
If you know how to be really careful around high voltage, you could
do the following.

Test the voltage at the breaker panel where the wires come in from the
meter. Measure on the wires from the meter themselves. If you see
the same drop there (Be Cafeful!), call the power company and
have them check their lines.

Next, check across the metal buss bars that those wires attach to.

If the last check was OK, but you have drop here, the screws
holding the wires coming in probably need to be tightened. If
no drop here, check at the output of each breaker, on the metal
of the breaker. If you find drop on a breaker, re-seat or replace
the breaker.

Then test the wire attached to the breaker, and tighten the wire
screw there if this is where the drop occures.

If all the voltages in the breaker box were good, the problem
is in one (or more) of the wiring circuits. You need to figure
out everything (outlets and lights) on each circuit. Turn off
the breaker, and see what doesn't work.

Does every electrical box on the circuit have the problem? If
not, you might be able to isolate the problem by guessing
what is wired to what. The problem is probably at the last
box that tests OK, or the first box that doesn't. Open up
each suspect electrical box on the circuit and tighten all
connections, then test again..


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 215
Default household voltage results

On Sat, 29 Jul 2006 21:04:28 -0400, "Bob Bins"
wrote:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?


See if you can find an IR (infrared) camera and look at your control
panel with your appliances running. I promise you that a drop from
114 to 102 is generating some heat, although it might not be in your
panel.

Carefully feel around for hot breakers and wires.

Complain about the voltage to your power company, but first ask them
if there is a charge.



  #10   Report Post  
Posted to alt.home.repair
sym sym is offline
external usenet poster
 
Posts: 32
Default household voltage results


JimL wrote:
On Sat, 29 Jul 2006 21:04:28 -0400, "Bob Bins"
wrote:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?


See if you can find an IR (infrared) camera and look at your control
panel with your appliances running. I promise you that a drop from
114 to 102 is generating some heat, although it might not be in your
panel.

Carefully feel around for hot breakers and wires.

Complain about the voltage to your power company, but first ask them
if there is a charge.

the power company will most likely tell him to get an eletrician out
there first,thats been my experience.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 215
Default household voltage results

On 30 Jul 2006 14:53:02 -0700, "sym" wrote:


JimL wrote:
On Sat, 29 Jul 2006 21:04:28 -0400, "Bob Bins"
wrote:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?


See if you can find an IR (infrared) camera and look at your control
panel with your appliances running. I promise you that a drop from
114 to 102 is generating some heat, although it might not be in your
panel.

Carefully feel around for hot breakers and wires.

Complain about the voltage to your power company, but first ask them
if there is a charge.


The power company will most likely tell him to get an eletrician out
there first,thats been my experience.


Probably true in many cities. Just a reminder that many
electrician now charge over $120 per hour with a $120 minimum for
showing up.


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default household voltage results


"sym" wrote in message
the power company will most likely tell him to get an eletrician out
there first,thats been my experience.


Maybe. I complained to the power company once. They told me it was
impossible to have the variance I was seeing. But it never happened again
after that. Coincidence?


  #13   Report Post  
Posted to alt.home.repair
sym sym is offline
external usenet poster
 
Posts: 32
Default household voltage results


JimL wrote:
On 30 Jul 2006 14:53:02 -0700, "sym" wrote:


JimL wrote:
On Sat, 29 Jul 2006 21:04:28 -0400, "Bob Bins"
wrote:

I had my digital volt meter hooked up to two outlets during the day. I
noticed that the voltage is normally around 114 volts. When I have my two
AC window units on it drops to about 109-112. If I then turn my microwave
on it drops to about 102-104. I tested this on two different circuits both
on different sides of the breaker panel. This voltage sounds low to me.
Is this normal or should I be seeing higher values?

See if you can find an IR (infrared) camera and look at your control
panel with your appliances running. I promise you that a drop from
114 to 102 is generating some heat, although it might not be in your
panel.

Carefully feel around for hot breakers and wires.

Complain about the voltage to your power company, but first ask them
if there is a charge.


The power company will most likely tell him to get an eletrician out
there first,thats been my experience.


Probably true in many cities. Just a reminder that many
electrician now charge over $120 per hour with a $120 minimum for
showing up.

wow i need to raise my prices

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outdoor Lighting Dr. Edmund M. Hayes Home Repair 4 May 23rd 06 11:00 PM
Effect of high household voltage on TV? Jonathan Grobe Electronics Repair 3 June 15th 04 12:48 AM
voltage regulator that drops out of circuit CampinGazz Electronics 4 February 1st 04 07:14 PM
testing ATX power supply tempus fugit Electronics Repair 12 January 13th 04 05:03 PM
Alternate treatment for depression Chris Carlen Electronics Repair 26 July 13th 03 10:39 AM


All times are GMT +1. The time now is 05:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"