Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default OIL Furnaces with Air Conditioning - Most Have Air Flow Problems

Consumer Warning: OIL Furnaces with Air Conditioning - Most Have Air
Flow Problems
The design of the oil furnace with its ultra large heat exchanger coming
to near the top of the furnace and the blower set to the side of the
furnace represents an engineering airflow problem. The blower set to the
side blows against the heat exchanger and the back of the furnace which
blocks directional airflow velocity thus generating high initial
velocity & static back pressures against the blower.

Most installers set the A-Coil directly on top of the furnace with no
transitions resulting in another restriction and more blocking of
directional velocity air flow and a huge leap in (ESP) static
pressures'. Thermo pride states that the E-Coil must be at least 3"
above the furnace. That might work for a small 1.5 or 2-ton A/C, but
what about required airflow for 3 to 5-ton A/C's?

In my opinion, these low boy oil furnaces should be designed with space
above the heat exchanger depending on the airflow requirements of the
air conditioning application size to be used. There should also be a
transition beginning at the top of the heat exchanger and transitioning
to the intake area of the evaporator coil. This would greatly reduce the
backpressure and improve airflow. The worst place to lose velocity and
generate static back-pressure is below the evaporator coil. Where it
needs the velocity and static pressures' is at the diffusers.

The low airflow probable cause is "an unbalanced airflow heatload
through the evaporator coil, along with "back pressure and extreme
turbulence," due to the evaporator coil being too close to the very
large oil furnace heat exchanger.

With the DX coil set perhaps illegally close to the heat exchanger thus
causing an airflow restriction and wicked turbulence problem, a few of
the coil's circuits may be unevenly heatloaded. Since the liquid
refrigerant is not completely evaporated it will cause the outlet line
that the TXV sensor bulb is on to be too cold and the TEV will shut-down
the refrigerant flow, which can greatly reduce the BTUH capacity of the
DX coil and the entire system. On piston refrigerant control systems, it
may flood back liquid, which could damage the compressor.
My scan of my Thermopride OL 11's - Blower Curve - with a quarter HP
blower motor & only 700-rpm with .5" ESP it won't support 1.5-ton of
cooling airflow!
Study the blower curve graph: .5" ESP equals 400-CFM, that is about
right for only one ton of cooling, not 1.5-ton of cooling! Get what you
paid for!
http://www.udarrell.com/Blower_Curve_Graph.tif

- Darrell - udarrell

--
Air Conditioning's Affordable Path to the "Human Comfort Zone Goal"
http://www.udarrell.com/air-conditio...tent-heat.html
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shower Flow Problems [email protected] UK diy 10 August 22nd 05 01:19 PM
TRVs, flow switches and boiler cycling Mike Clarke UK diy 18 November 8th 04 05:00 PM
Natural Gas Excess Flow Valve Install? Oscar_Lives Home Repair 1 October 21st 04 07:02 AM
CH - alpha pumps FrancisJK UK diy 45 September 23rd 04 08:06 PM
Water flow rate problem and Combi boiler Andrew Beck UK diy 15 September 3rd 04 11:00 PM


All times are GMT +1. The time now is 02:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"