PVC Conduit Fill Rating?
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks |
#2
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
pbs wrote:
Hi: Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks Actually One inch Electro Metallic Tubing has a table fill of 26 Number 12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25 conductors. The question then becomes why. With more than 20 conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so #12 could not be used for even a fifteen ampere circuit. You're allowed fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty amperes for 10 to 20 conductors you could use them for twenty ampere circuits. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#3
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
On Tue, 20 Jun 2006 04:38:08 GMT, "Tom Horne, Electrician"
wrote: pbs wrote: Hi: Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks Actually One inch Electro Metallic Tubing has a table fill of 26 Number 12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25 conductors. The question then becomes why. With more than 20 conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so #12 could not be used for even a fifteen ampere circuit. You're allowed fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty amperes for 10 to 20 conductors you could use them for twenty ampere circuits. So then it would make more sense to run 20 #20 wires, and run ONE amp thru each wire (with a one amp breaker on each wire). You'd still end up with 20amps at the end of the run. Pila |
#4
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
|
#5
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
On Wed, 21 Jun 2006 04:04:51 GMT, "Thomas D. Horne, FF EMT"
wrote: wrote: On Tue, 20 Jun 2006 04:38:08 GMT, "Tom Horne, Electrician" wrote: pbs wrote: Hi: Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks Actually One inch Electro Metallic Tubing has a table fill of 26 Number 12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25 conductors. The question then becomes why. With more than 20 conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so #12 could not be used for even a fifteen ampere circuit. You're allowed fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty amperes for 10 to 20 conductors you could use them for twenty ampere circuits. So then it would make more sense to run 20 #20 wires, and run ONE amp thru each wire (with a one amp breaker on each wire). You'd still end up with 20amps at the end of the run. Pila Please don't feed the troll people. That will just encourage it. The "Troll People" ? Is that a new band like the Village People? |
#6
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
pbs wrote:
Hi: Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks Table C10 allows 25 THHN conductors in a 1 inch schedule 40 conduit. That's how many THHN conductors that are PHYSICALLY permited. More important is DERATING of those conductors. IOW one _CANNOT_ pull 25 THHN conductors in a 1 inch PVC conduit and expect that they will be rated for the full allowed 20 amps.....they won't. One needs to look at Table 310.15(B)(2)a for conductors with no load diversity (All conductors in the raceway are loaded to their maximum rated load) or Table B.310.11 in Annex B for conductors with 50% load diversity. Both Tables are the same until one gets to over 10 current carrying conductors. #12 THHN can be derated from the 90 degree column in Table 310.16 which is 30 amps, HOWEVER the #12 conductors _CANNOT_ be fused at over 20 amps. For derating, an equipment grounding conductor is not counted as a current carrying conductor Also, for Residential Single Phase 120/240, a true neutral (shared between two hots from opposite legs) is not counted as a current carrying conductor. A "neutral from a two wire circuit _IS_ counted. In your case (from the above Tables) for #12 THHN conductors: 4 to 6 conductors must be derated at 80% 30 amps x .8 = 24 amps 7 to 9 conductors must be derated at 70% 30 amps x .7 = 21 amps. You can safely install 9 current carrying #12 THHN conductors in that conduit. To install more conductors, the Tables differ. With no diversity (fully loaded): 10 to 20 conductors must be derated at 50% 30 amps x .5 = 15 amps Now there is a problem!!!!!! If you install more than 9 current carrying conductors (up to and the physically allowed 20 conductors) you MUST either use 15 amp breakers on the #12 THHN conductors or increase the size of ALL wires to #10 THHN since, from the 90 degree column in Table 310.16 one can derate from 40 amps for #10 THHN: 40 amps x .5 = 20 amps (you must still use a 20 amp breaker.) HOWEVER, if load diversity is 50% (from Table B) 10 to 24 conductors must be derated at 70% 30 amps x .7 = 21 amps. You must ALSO derate for ambient temperature, especially if more than 10% of the conduit is in an attic. Table 310.16 is only good for ambient temperatures of 30 C (86 F) To be safe, I would strongly recommend that you use #10 conductors in the 1 inch conduit(s) if you are going to use 20 amp breakers. If you set J-boxes in the basement and the attic, you can use the existing #12 Romex elsewhere, just use #10 in the conduit(s). This is one reason why Romex is used in houses......it is inherently derated for use in attics, basically being dummy proof as long as one stays with the common #14 Romex = 15 amp breakers, #12 Romex = 20 amp breakers and #10 Romex = 30 amp breakers. When one starts installing conductors in conduit, ya gotta watch your P and Q's. |
#7
Posted to alt.home.repair
|
|||
|
|||
PVC Conduit Fill Rating?
Very very helpful, Thanks!
volts500 wrote: pbs wrote: Hi: Can #12 THHN be run through 1' gray PVC Electrical conduit? If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT can handle 18 #12 THHN maximum.) Thanks Table C10 allows 25 THHN conductors in a 1 inch schedule 40 conduit. That's how many THHN conductors that are PHYSICALLY permited. More important is DERATING of those conductors. IOW one _CANNOT_ pull 25 THHN conductors in a 1 inch PVC conduit and expect that they will be rated for the full allowed 20 amps.....they won't. One needs to look at Table 310.15(B)(2)a for conductors with no load diversity (All conductors in the raceway are loaded to their maximum rated load) or Table B.310.11 in Annex B for conductors with 50% load diversity. Both Tables are the same until one gets to over 10 current carrying conductors. #12 THHN can be derated from the 90 degree column in Table 310.16 which is 30 amps, HOWEVER the #12 conductors _CANNOT_ be fused at over 20 amps. For derating, an equipment grounding conductor is not counted as a current carrying conductor Also, for Residential Single Phase 120/240, a true neutral (shared between two hots from opposite legs) is not counted as a current carrying conductor. A "neutral from a two wire circuit _IS_ counted. In your case (from the above Tables) for #12 THHN conductors: 4 to 6 conductors must be derated at 80% 30 amps x .8 = 24 amps 7 to 9 conductors must be derated at 70% 30 amps x .7 = 21 amps. You can safely install 9 current carrying #12 THHN conductors in that conduit. To install more conductors, the Tables differ. With no diversity (fully loaded): 10 to 20 conductors must be derated at 50% 30 amps x .5 = 15 amps Now there is a problem!!!!!! If you install more than 9 current carrying conductors (up to and the physically allowed 20 conductors) you MUST either use 15 amp breakers on the #12 THHN conductors or increase the size of ALL wires to #10 THHN since, from the 90 degree column in Table 310.16 one can derate from 40 amps for #10 THHN: 40 amps x .5 = 20 amps (you must still use a 20 amp breaker.) HOWEVER, if load diversity is 50% (from Table B) 10 to 24 conductors must be derated at 70% 30 amps x .7 = 21 amps. You must ALSO derate for ambient temperature, especially if more than 10% of the conduit is in an attic. Table 310.16 is only good for ambient temperatures of 30 C (86 F) To be safe, I would strongly recommend that you use #10 conductors in the 1 inch conduit(s) if you are going to use 20 amp breakers. If you set J-boxes in the basement and the attic, you can use the existing #12 Romex elsewhere, just use #10 in the conduit(s). This is one reason why Romex is used in houses......it is inherently derated for use in attics, basically being dummy proof as long as one stays with the common #14 Romex = 15 amp breakers, #12 Romex = 20 amp breakers and #10 Romex = 30 amp breakers. When one starts installing conductors in conduit, ya gotta watch your P and Q's. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Road Construction fill dirt situation | Home Repair | |||
Fill Valve/Pressue Problem | Home Repair | |||
Question about car engine horsepower rating | Metalworking | |||
electrical cable next to heating ducts | Home Repair |