pbs June 19th 06 09:28 PM

PVC Conduit Fill Rating?
 
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


pbs June 19th 06 09:57 PM

PVC Conduit Fill Rating?
 

wrote:
On 19 Jun 2006 13:28:36 -0700, "pbs" wrote:

Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks



Table C10 says 25 #12 THHN will fit is 1" sch 40 PVC rigid nonmetalic
conduit


Thanks. I had also intended to ask if the PVC conduit is permitted for
interior residential applications (this would run up through a chase)


Pete C. June 19th 06 10:01 PM

PVC Conduit Fill Rating?
 
pbs wrote:

wrote:
On 19 Jun 2006 13:28:36 -0700, "pbs" wrote:

Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks



Table C10 says 25 #12 THHN will fit is 1" sch 40 PVC rigid nonmetalic
conduit


Thanks. I had also intended to ask if the PVC conduit is permitted for
interior residential applications (this would run up through a chase)


That would likely be a local code issue, it's not something in the NEC.
I doubt you'd have an issue since PVC DWV stacks do the same thing with
the same materials.

Pete C.

PipeDown June 19th 06 11:39 PM

PVC Conduit Fill Rating?
 

"Pete C." wrote in message
...
pbs wrote:

wrote:
On 19 Jun 2006 13:28:36 -0700, "pbs" wrote:

Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


Table C10 says 25 #12 THHN will fit is 1" sch 40 PVC rigid nonmetalic
conduit


Thanks. I had also intended to ask if the PVC conduit is permitted for
interior residential applications (this would run up through a chase)


That would likely be a local code issue, it's not something in the NEC.
I doubt you'd have an issue since PVC DWV stacks do the same thing with
the same materials.

Pete C.


I found that PVC ENT systems have far fewer choices when it comes to J-boxes
and those J-boxes tended to have a different standard for hole position so
that you had to use the more expensive covers.

Metal may be a bit more work cutting the tubing and connecting ground
pigtails at each J box but you will have lots more options at the ends of
the tubing to put those fixtures on. Transitioning to cable (romex) is
easier too using a simple clamp to hold the cable.

What money you may save using PVC conduit you will loose buying more
expensive plastic J boxes, elbows and tees.

On the other hand, you can drill a 3/4" hole in the side of a plastic J box
and thread a 1/2" male adapter to create more options (3 and 4 way J-boxes
for example). Don't know if that is to code but I don't really see a reason
for it not to be as long as you observe other rules about fill and glue all
connections.



Tom Horne, Electrician June 20th 06 05:38 AM

PVC Conduit Fill Rating?
 
pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


Actually One inch Electro Metallic Tubing has a table fill of 26 Number
12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25
conductors. The question then becomes why. With more than 20
conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so
#12 could not be used for even a fifteen ampere circuit. You're allowed
fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty
amperes for 10 to 20 conductors you could use them for twenty ampere
circuits.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison

volts500 June 20th 06 05:45 AM

PVC Conduit Fill Rating?
 
pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


Table C10 allows 25 THHN conductors in a 1 inch schedule 40 conduit.
That's how many THHN conductors that are PHYSICALLY permited. More
important is DERATING of those conductors. IOW one _CANNOT_ pull 25
THHN conductors in a 1 inch PVC conduit and expect that they will be
rated for the full allowed 20 amps.....they won't. One needs to look
at Table 310.15(B)(2)a for conductors with no load diversity (All
conductors in the raceway are loaded to their maximum rated load) or
Table B.310.11 in Annex B for conductors with 50% load diversity.

Both Tables are the same until one gets to over 10 current carrying
conductors. #12 THHN can be derated from the 90 degree column in Table
310.16 which is 30 amps, HOWEVER the #12 conductors _CANNOT_ be fused
at over 20 amps. For derating, an equipment grounding conductor is
not counted as a current carrying conductor Also, for Residential
Single Phase 120/240, a true neutral (shared between two hots from
opposite legs) is not counted as a current carrying conductor. A
"neutral from a two wire circuit _IS_ counted.

In your case (from the above Tables) for #12 THHN conductors:

4 to 6 conductors must be derated at 80% 30 amps x .8 = 24 amps
7 to 9 conductors must be derated at 70% 30 amps x .7 = 21 amps.

You can safely install 9 current carrying #12 THHN conductors in that
conduit.

To install more conductors, the Tables differ.

With no diversity (fully loaded):
10 to 20 conductors must be derated at 50% 30 amps x .5 = 15 amps
Now there is a problem!!!!!! If you install more than 9 current
carrying conductors (up to and the physically allowed 20 conductors)
you MUST either use 15 amp breakers on the #12 THHN conductors or
increase the size of ALL wires to #10 THHN since, from the 90 degree
column in Table 310.16 one can derate from 40 amps for #10 THHN:
40 amps x .5 = 20 amps (you must still use a 20 amp breaker.)

HOWEVER, if load diversity is 50% (from Table B)
10 to 24 conductors must be derated at 70% 30 amps x .7 = 21 amps.

You must ALSO derate for ambient temperature, especially if more than
10% of the conduit is in an attic. Table 310.16 is only good for
ambient temperatures of 30 C (86 F)

To be safe, I would strongly recommend that you use #10 conductors in
the 1 inch conduit(s) if you are going to use 20 amp breakers. If you
set J-boxes in the basement and the attic, you can use the existing #12
Romex elsewhere, just use #10 in the conduit(s).

This is one reason why Romex is used in houses......it is inherently
derated for use in attics, basically being dummy proof as long as one
stays with the common #14 Romex = 15 amp breakers, #12 Romex = 20 amp
breakers and #10 Romex = 30 amp breakers. When one starts installing
conductors in conduit, ya gotta watch your P and Q's.


pbs June 20th 06 04:49 PM

PVC Conduit Fill Rating?
 
Very very helpful, Thanks!

volts500 wrote:
pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


Table C10 allows 25 THHN conductors in a 1 inch schedule 40 conduit.
That's how many THHN conductors that are PHYSICALLY permited. More
important is DERATING of those conductors. IOW one _CANNOT_ pull 25
THHN conductors in a 1 inch PVC conduit and expect that they will be
rated for the full allowed 20 amps.....they won't. One needs to look
at Table 310.15(B)(2)a for conductors with no load diversity (All
conductors in the raceway are loaded to their maximum rated load) or
Table B.310.11 in Annex B for conductors with 50% load diversity.

Both Tables are the same until one gets to over 10 current carrying
conductors. #12 THHN can be derated from the 90 degree column in Table
310.16 which is 30 amps, HOWEVER the #12 conductors _CANNOT_ be fused
at over 20 amps. For derating, an equipment grounding conductor is
not counted as a current carrying conductor Also, for Residential
Single Phase 120/240, a true neutral (shared between two hots from
opposite legs) is not counted as a current carrying conductor. A
"neutral from a two wire circuit _IS_ counted.

In your case (from the above Tables) for #12 THHN conductors:

4 to 6 conductors must be derated at 80% 30 amps x .8 = 24 amps
7 to 9 conductors must be derated at 70% 30 amps x .7 = 21 amps.

You can safely install 9 current carrying #12 THHN conductors in that
conduit.

To install more conductors, the Tables differ.

With no diversity (fully loaded):
10 to 20 conductors must be derated at 50% 30 amps x .5 = 15 amps
Now there is a problem!!!!!! If you install more than 9 current
carrying conductors (up to and the physically allowed 20 conductors)
you MUST either use 15 amp breakers on the #12 THHN conductors or
increase the size of ALL wires to #10 THHN since, from the 90 degree
column in Table 310.16 one can derate from 40 amps for #10 THHN:
40 amps x .5 = 20 amps (you must still use a 20 amp breaker.)

HOWEVER, if load diversity is 50% (from Table B)
10 to 24 conductors must be derated at 70% 30 amps x .7 = 21 amps.

You must ALSO derate for ambient temperature, especially if more than
10% of the conduit is in an attic. Table 310.16 is only good for
ambient temperatures of 30 C (86 F)

To be safe, I would strongly recommend that you use #10 conductors in
the 1 inch conduit(s) if you are going to use 20 amp breakers. If you
set J-boxes in the basement and the attic, you can use the existing #12
Romex elsewhere, just use #10 in the conduit(s).

This is one reason why Romex is used in houses......it is inherently
derated for use in attics, basically being dummy proof as long as one
stays with the common #14 Romex = 15 amp breakers, #12 Romex = 20 amp
breakers and #10 Romex = 30 amp breakers. When one starts installing
conductors in conduit, ya gotta watch your P and Q's.



[email protected] June 20th 06 07:45 PM

PVC Conduit Fill Rating?
 
On Tue, 20 Jun 2006 04:38:08 GMT, "Tom Horne, Electrician"
wrote:

pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks


Actually One inch Electro Metallic Tubing has a table fill of 26 Number
12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25
conductors. The question then becomes why. With more than 20
conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so
#12 could not be used for even a fifteen ampere circuit. You're allowed
fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty
amperes for 10 to 20 conductors you could use them for twenty ampere
circuits.



So then it would make more sense to run 20 #20 wires, and run ONE amp
thru each wire (with a one amp breaker on each wire). You'd still end
up with 20amps at the end of the run.

Pila

Thomas D. Horne, FF EMT June 21st 06 05:04 AM

PVC Conduit Fill Rating?
 
wrote:
On Tue, 20 Jun 2006 04:38:08 GMT, "Tom Horne, Electrician"
wrote:

pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks

Actually One inch Electro Metallic Tubing has a table fill of 26 Number
12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25
conductors. The question then becomes why. With more than 20
conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so
#12 could not be used for even a fifteen ampere circuit. You're allowed
fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty
amperes for 10 to 20 conductors you could use them for twenty ampere
circuits.



So then it would make more sense to run 20 #20 wires, and run ONE amp
thru each wire (with a one amp breaker on each wire). You'd still end
up with 20amps at the end of the run.

Pila


Please don't feed the troll people. That will just encourage it.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.

-------------@------------- June 21st 06 06:31 AM

PVC Conduit Fill Rating?
 
On Wed, 21 Jun 2006 04:04:51 GMT, "Thomas D. Horne, FF EMT"
wrote:

wrote:
On Tue, 20 Jun 2006 04:38:08 GMT, "Tom Horne, Electrician"
wrote:

pbs wrote:
Hi:
Can #12 THHN be run through 1' gray PVC Electrical conduit?

If Yes, what is the code fill rate for 1" PVC? ( I believe that 1" EMT
can handle 18 #12 THHN maximum.)

Thanks

Actually One inch Electro Metallic Tubing has a table fill of 26 Number
12 American Wire Gage (AWG) conductors. Schedule 40 PVC is allowed 25
conductors. The question then becomes why. With more than 20
conductors in the raceway the ampacity of #12 THHN is 13.5 amperes. so
#12 could not be used for even a fifteen ampere circuit. You're allowed
fifteen #10 AWG wires in 1" PVC and at an allowable ampacity of twenty
amperes for 10 to 20 conductors you could use them for twenty ampere
circuits.



So then it would make more sense to run 20 #20 wires, and run ONE amp
thru each wire (with a one amp breaker on each wire). You'd still end
up with 20amps at the end of the run.

Pila


Please don't feed the troll people. That will just encourage it.


The "Troll People" ? Is that a new band like the Village People?



All times are GMT +1. The time now is 12:19 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter