udarrell
 
Posts: n/a
Default AC Choice? My Service Provider TDS Better Stop Blocking my Posts!

In summary, what would be the major difference between these 3 setups?

Setup #1
- 3 ton blower
- 3 ton coil
- 3 ton condenser

Setup #2
- 3 ton blower
-4 ton blower (okay)
- 4 ton coil
- 3 ton condenser

Setup #3
- Reduce the heat-gain/heat-loss
- 3 ton blower
- 3 ton coil
- 2.5 ton condenser

Rumor has it that Setup #2 "may" fish out more cooling during the very
hot days. Reason for going with Setup #2 is that 3 ton blower is
existing and can only accommodate a 3 ton condenser. So to "turbo"
charge the system, a 4 ton coil can be used to give it some extra BTUH's
of cooling. How about choosing #3?

Step #3 if correctly sized will deliver better efficiency.

# 2 depending on climate conditions, in a dry climate operating costs
should be less than #1.

Even in an average humidity climate zone, you may be able to keep your
3-ton evaporator coil and use a humidistat to energize a fan relay
switching to a 350-cfm speed for higher humidity and dropping back to
higher 400 to 450-cfm per ton of cooling. With other load calc reducing
options, maybe even use a 2.5-ton condenser
-----------------------
True or False? Would the operating cost be significantly different?
Which would cost more to run? 3 ton furnace with blower is fairly new
and coil and condenser would be brand new rated at up to 15 SEER. Would
appreciate any feedback.
-------------------------
In a Dry Climate using a larger Evaporator Coil and larger Airhandler to
move more CFM per Ton of cooling, this will increase the ratio of
Sensible BTUH to Latent.
Example: 2-ton condenser at 95-F outdoor temperature, indoor airhandler
at 800-cfm with a return air 67-F wet bulb with a total capacity of
23,000-btuh and 16,500-btuh sensible . Increase the airflow to 900-cfm
at 67-F indoor wet bulb and the system now delivers 18,300 BTUH.

Example: if the Manual S needed 18,000-btuh sensible, by increasing the
airflow 100-cfm in an average or higher humidity climate by using a
humidistat controlled fan relay to change speeds, it could make the
difference between a 2.5-ton or using a lower amp draw, lower initial
cost 2-ton condenser. - udarrell

--
Air Conditioning's Affordable Path to the "Human Comfort Zone Goal"
http://www.udarrell.com/air-conditio...tent-heat.html

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Speedfit technique Arthur UK diy 615 November 23rd 04 11:50 PM
Annual HVAC Service contracts. tflfb Home Repair 7 December 30th 03 02:45 AM
SONY poor service Eric Electronics Repair 2 September 10th 03 04:28 AM


All times are GMT +1. The time now is 12:09 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"