  #1   Report Post  
Posted to alt.home.repair
Dave Garrett
 
Posts: n/a
Default Voltage drop - panel or utility issue?

My electrical knowledge is fairly limited, so I'm hoping someone here
can shed some light on this or correct any mistaken assumptions on my
part. Our house is 60+ years old, previous owner worked for a
homebuilder and did a lot of the improvements to the house himself.
We've been here almost 7 years, and have had relatively few problems
outside of the usual age-related ones.

The room being used for an office has two computers, two monitors,
flatbed scanner, inkjet printer, router, cable modem, external drive,
two powered subwoofers, and a small desk lamp. The computers each have
their own UPS (APC Back-UPS ES 650 and 500). Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over. This only lasts about a second or less, and I've observed
the lights in the room flickering just a bit at the same time. I've also
observed lights flickering slightly in other rooms, so it's not limited
to just the office.

So, I decided I'd better get someone out here to look at the panel. I
have a main panel (125A) and a subpanel (75A), and they are both of the
notorious FPE Stab-Lok kind, the evils of which I just learned about
after doing a bit of Googling. The guy that I hired examined both panels
and tightened down all the connections, and said everything looked OK as
far as he could tell, but recommended that when I'm ready to upgrade I
should install a newer panel with more capacity (the breaker on the
subpanel that covers the office also covers two halogen wall-mounted
lights in the hallway, the master bedroom, the guest bedroom, and the
living room. The guest bedroom and the living room are very infrequently
used.). He also reanchored the utility drop where it splits into three
main cables just upstream of the meter (hope I'm using the correct
terminology here), as the cables had come loose from the "anchor"
mounted on the house and were "pulling" on the connectors.

I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again. I'm concerned that this will ultimately cause damage to
the computers or the UPSes, and am wondering whether I need to get a
second opinion from another electrician, or whether I should call the
utility and ask them to put a line monitor just upstream of the meter to
see if it's an issue with their equipment. I'm concerned about the
panels after reading about FPE's failure rates, but unless I get a
professional opinion that they're unsafe and should be replaced
immediately, I'd prefer to defer doing so until a couple of other
expensive improvement projects are completed.

Comments or recommendations?

Thanks in advance,

Dave

  #2   Report Post  
Posted to alt.home.repair
Edwin Pawlowski
 
Posts: n/a
Default Voltage drop - panel or utility issue?


"Dave Garrett" wrote in message

Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over.
I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again.
Comments or recommendations?


Since you have more than one UPS doing the same thing, I'd have to say they
are doing their job.

Why not start with something simple. Buy or borrow a volt meter. Something
accurate enough to see a drop of say, 4 or 5 volts. Plug it into any place
in the house. Actually, try a few places and they should all read the same.
When you hear the UPS engaging, take a voltage reading. Do it a few times
during the day and if you find variations, record them. You may find a
pattern. If you see drops, call the power company. There can be a
differential of a couple of volts during the day as major industry comes on
line or shuts down, hot weather cranks up the AC, etc. Too much = problems

When I had a problem with bulbs burning out, I did some checking and found
morning spikes to 145 volts. There was a problem at a substation
transformer and quickly corrected. You'd think the utility company would
have a better handle on stuff like that, but not always.
--
Ed
http://pages.cthome.net/edhome/


  #3   Report Post  
Posted to alt.home.repair
John Grabowski
 
Posts: n/a
Default Voltage drop - panel or utility issue?


"Dave Garrett" wrote in message
...
My electrical knowledge is fairly limited, so I'm hoping someone here
can shed some light on this or correct any mistaken assumptions on my
part. Our house is 60+ years old, previous owner worked for a
homebuilder and did a lot of the improvements to the house himself.
We've been here almost 7 years, and have had relatively few problems
outside of the usual age-related ones.

The room being used for an office has two computers, two monitors,
flatbed scanner, inkjet printer, router, cable modem, external drive,
two powered subwoofers, and a small desk lamp. The computers each have
their own UPS (APC Back-UPS ES 650 and 500). Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over. This only lasts about a second or less, and I've observed
the lights in the room flickering just a bit at the same time. I've also
observed lights flickering slightly in other rooms, so it's not limited
to just the office.

So, I decided I'd better get someone out here to look at the panel. I
have a main panel (125A) and a subpanel (75A), and they are both of the
notorious FPE Stab-Lok kind, the evils of which I just learned about
after doing a bit of Googling. The guy that I hired examined both panels
and tightened down all the connections, and said everything looked OK as
far as he could tell, but recommended that when I'm ready to upgrade I
should install a newer panel with more capacity (the breaker on the
subpanel that covers the office also covers two halogen wall-mounted
lights in the hallway, the master bedroom, the guest bedroom, and the
living room. The guest bedroom and the living room are very infrequently
used.). He also reanchored the utility drop where it splits into three
main cables just upstream of the meter (hope I'm using the correct
terminology here), as the cables had come loose from the "anchor"
mounted on the house and were "pulling" on the connectors.

I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again. I'm concerned that this will ultimately cause damage to
the computers or the UPSes, and am wondering whether I need to get a
second opinion from another electrician, or whether I should call the
utility and ask them to put a line monitor just upstream of the meter to
see if it's an issue with their equipment. I'm concerned about the
panels after reading about FPE's failure rates, but unless I get a
professional opinion that they're unsafe and should be replaced
immediately, I'd prefer to defer doing so until a couple of other
expensive improvement projects are completed.

Comments or recommendations?

Thanks in advance,

Dave


You mentioned two things that always send up a red flag for me; The
previous owner did a lot of improvements himself and you have a Federal
panel. The electrician was right in checking and tightening all of the
connections in both panels, but you could have one or more bad circuit
breakers that are causing the lights to flicker.

You could also have loose connections in one or more outlets, switches, and
junction boxes on the problem circuits. It could also be a problem with the
electric service coming to the house. The fact that the overhead conductors
were pulling on the connections is an indication that the problem may be
right there. I would call the power company and have them check the service
drop from the pole to the house. The connections inside of the meter should
also be tightened. In the mean time keep a record of time and date when you
have these occurrences. It may be useful in correlating your problem with
something else. Are your neighbors having the same problem?

Regarding the FPE panels. I suggest that you get estimates from several
contractors on the cost to replace them.


John Grabowski
http://www.mrelectrician.tv

  #4   Report Post  
Posted to alt.home.repair
Pete C.
 
Posts: n/a
Default Voltage drop - panel or utility issue?

Edwin Pawlowski wrote:

"Dave Garrett" wrote in message

Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over.
I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again.
Comments or recommendations?


Since you have more than one UPS doing the same thing, I'd have to say they
are doing their job.

Why not start with something simple. Buy or borrow a volt meter. Something
accurate enough to see a drop of say, 4 or 5 volts. Plug it into any place
in the house. Actually, try a few places and they should all read the same.
When you hear the UPS engaging, take a voltage reading. Do it a few times
during the day and if you find variations, record them. You may find a
pattern. If you see drops, call the power company. There can be a
differential of a couple of volts during the day as major industry comes on
line or shuts down, hot weather cranks up the AC, etc. Too much = problems

When I had a problem with bulbs burning out, I did some checking and found
morning spikes to 145 volts. There was a problem at a substation
transformer and quickly corrected. You'd think the utility company would
have a better handle on stuff like that, but not always.
--
Ed
http://pages.cthome.net/edhome/


Certainly old crap panels should be replaced at your earliest
convenience. When you take your voltage readings take them at several
different locations i.e. near the beeping UPS and somewhere close to the
main panel. This will help isolate whether it is a house problem or a
utility problem.

I had an interesting utility issue once. I walked by my server rack and
noticed the UPS was on battery and beeping. Since the power was
obviously not out I checked and the UPS reported input voltage of 135V
and had switched to battery on it's over voltage protection. I got my
Fluke DMM and verified 134.8V at a nearby outlet.

I called the utility and while the CSR I talked to had no idea what I
was talking about, she took the info and within 10 min I got a call back
from a tech. I told him what I had found and in less than 10 min he was
parked in my driveway. Before I even got out to the truck to talk to him
he had confirmed the high voltage and was on the radio to another tech
heading to the regulator back a few miles away. A few more minutes and I
had a reasonable 126V. I was pretty impressed with the utilities
response time.

Pete C.
  #5   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default Voltage drop - panel or utility issue?

how old are the UPS units, after a few years 2 or 3 the batteries go
bad and the units act wierd.Espically bad on small UPS units like those
40 buck units

I have a couple doing that here.

DEFINETELY GET RID OF the FPE panels its a fire waiting to happen!

Put a voltmeter on the line, sometimes minor fluctuatins appear large
to certain lamps. I had some cheap fluroscent shop lights that acted
wierd with a 2 volt drop, a trivial change.



  #6   Report Post  
Posted to alt.home.repair
Pat
 
Posts: n/a
Default Voltage drop - panel or utility issue?

It could be your problem or it could be the utility's problem. Since you
have checked for problems I would try the utility company next.


"Dave Garrett" wrote in message
...
My electrical knowledge is fairly limited, so I'm hoping someone here
can shed some light on this or correct any mistaken assumptions on my
part. Our house is 60+ years old, previous owner worked for a
homebuilder and did a lot of the improvements to the house himself.
We've been here almost 7 years, and have had relatively few problems
outside of the usual age-related ones.

The room being used for an office has two computers, two monitors,
flatbed scanner, inkjet printer, router, cable modem, external drive,
two powered subwoofers, and a small desk lamp. The computers each have
their own UPS (APC Back-UPS ES 650 and 500). Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over. This only lasts about a second or less, and I've observed
the lights in the room flickering just a bit at the same time. I've also
observed lights flickering slightly in other rooms, so it's not limited
to just the office.

So, I decided I'd better get someone out here to look at the panel. I
have a main panel (125A) and a subpanel (75A), and they are both of the
notorious FPE Stab-Lok kind, the evils of which I just learned about
after doing a bit of Googling. The guy that I hired examined both panels
and tightened down all the connections, and said everything looked OK as
far as he could tell, but recommended that when I'm ready to upgrade I
should install a newer panel with more capacity (the breaker on the
subpanel that covers the office also covers two halogen wall-mounted
lights in the hallway, the master bedroom, the guest bedroom, and the
living room. The guest bedroom and the living room are very infrequently
used.). He also reanchored the utility drop where it splits into three
main cables just upstream of the meter (hope I'm using the correct
terminology here), as the cables had come loose from the "anchor"
mounted on the house and were "pulling" on the connectors.

I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again. I'm concerned that this will ultimately cause damage to
the computers or the UPSes, and am wondering whether I need to get a
second opinion from another electrician, or whether I should call the
utility and ask them to put a line monitor just upstream of the meter to
see if it's an issue with their equipment. I'm concerned about the
panels after reading about FPE's failure rates, but unless I get a
professional opinion that they're unsafe and should be replaced
immediately, I'd prefer to defer doing so until a couple of other
expensive improvement projects are completed.

Comments or recommendations?

Thanks in advance,

Dave



  #7   Report Post  
Posted to alt.home.repair
Dave Garrett
 
Posts: n/a
Default Voltage drop - panel or utility issue?

In article ,
says...

You mentioned two things that always send up a red flag for me; The
previous owner did a lot of improvements himself and you have a Federal
panel. The electrician was right in checking and tightening all of the
connections in both panels, but you could have one or more bad circuit
breakers that are causing the lights to flicker.

You could also have loose connections in one or more outlets, switches, and
junction boxes on the problem circuits. It could also be a problem with the
electric service coming to the house. The fact that the overhead conductors
were pulling on the connections is an indication that the problem may be
right there. I would call the power company and have them check the service
drop from the pole to the house. The connections inside of the meter should
also be tightened. In the mean time keep a record of time and date when you
have these occurrences. It may be useful in correlating your problem with
something else. Are your neighbors having the same problem?

Regarding the FPE panels. I suggest that you get estimates from several
contractors on the cost to replace them.


Many thanks to everyone who replied with suggestions. A few additional
comments:

I'm not sure the previous owner did any electrical improvements himself
- he may well have contracted that kind of work out, especially since he
was in a position to have plenty of contacts who would be capable of
doing such work.

The guy that examined everything last week commented that whoever had
installed the panels had done a pretty good job (not that in this
instance that has any bearing on how well they function, obviously). He
did check all the panel connections with a meter after tightening them
down, and didn't see any readings out of the ordinary.

None of the breakers are warm to the touch even slightly. Some of them
have tripped as they were supposed to in the past, but this has not been
a frequent occurrence.

I don't have a voltmeter, but I can certainly borrow one from my dad,
and this will probably be my next step. I'm definitely going to call in
a ticket to the utility as well and have them check the service drop and
meter. Not sure if my neighbors are having problems as well, but I'm
going to talk to them and find out.

Finally, I'm definitely going to have the panels replaced, it's just a
question of when funds become available to do so. Glad I found out about
their history now rather than before they became a more serious problem.

Dave

  #8   Report Post  
Posted to alt.home.repair
Tony Hwang
 
Posts: n/a
Default Voltage drop - panel or utility issue?

Edwin Pawlowski wrote:
"Dave Garrett" wrote in message


Within the past few days,
the UPSes have started clicking several times a day. These UPSes beep
several times when switching over to battery power, and they haven't
done that more than once or twice, but the clicking would seem to
indicate a voltage drop significant enough to cause them to start to
switch over.
I thought this must've fixed the problem, as it was not reproducible
while he was here, but a couple hours after he left, the UPSes started
clicking again.
Comments or recommendations?



Since you have more than one UPS doing the same thing, I'd have to say they
are doing their job.

Why not start with something simple. Buy or borrow a volt meter. Something
accurate enough to see a drop of say, 4 or 5 volts. Plug it into any place
in the house. Actually, try a few places and they should all read the same.
When you hear the UPS engaging, take a voltage reading. Do it a few times
during the day and if you find variations, record them. You may find a
pattern. If you see drops, call the power company. There can be a
differential of a couple of volts during the day as major industry comes on
line or shuts down, hot weather cranks up the AC, etc. Too much = problems

When I had a problem with bulbs burning out, I did some checking and found
morning spikes to 145 volts. There was a problem at a substation
transformer and quickly corrected. You'd think the utility company would
have a better handle on stuff like that, but not always.

Hi,
One thing batteries inside UPS don't last forever.
  #9   Report Post  
Posted to alt.home.repair
twstanley
 
Posts: n/a
Default Voltage drop - panel or utility issue?

We have the same thing happen time to time. As the electrician has
checked the internals and not found anything, I think you
are on the right track contacting the utility and having them check
their side of the hookup.

You might also note the times, is happening about the same time every
day?

Also ask your utility rep if they are having voltage drops or spikes
occasionally, they may be able to advise you or may
need to know about any voltage changes you are seeing.

Hooking up the voltmeter and watching it while the ups's are beeping
and clicking is a good idea.

  #10   Report Post  
Posted to alt.home.repair
Dave Garrett
 
Posts: n/a
Default Voltage drop - panel or utility issue?

In article .com,
says...

We have the same thing happen time to time. As the electrician has
checked the internals and not found anything, I think you
are on the right track contacting the utility and having them check
their side of the hookup.

You might also note the times, is happening about the same time every
day?

Also ask your utility rep if they are having voltage drops or spikes
occasionally, they may be able to advise you or may
need to know about any voltage changes you are seeing.

Hooking up the voltmeter and watching it while the ups's are beeping
and clicking is a good idea.


Well, I reported the problem to the utility today. We'll see how long it
takes them to check it out - the CSR I talked to at the service provider
before I was referred to a different number used to report power outages
said it might take several days before they show up after I described
the problem to him.

It's not happening at the same times, but I did notice today that it
does seem to occur frequently when one of the major appliances like the
refrigerator or dishwasher kicks in. I also noticed it was happening
almost every time the A/C turned on (it's just gotten hot enough here
for it to be in use again).

And to answer a previous question, the UPSes are both relatively new -
less than a year old - so the batteries in them should be fine. The
battery dying in my old UPS was what prompted me to replace it with
these.

Dave


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage drop switching relays? Joe in Bendigo Electronics 10 June 13th 04 06:59 AM
*** Rec.Woodworking Mini-FAQ *** 149, BAD Free David F. Eisan Woodworking 26 June 4th 04 04:36 AM
voltage regulator that drops out of circuit CampinGazz Electronics 4 February 1st 04 07:14 PM
*** Rec.Woodworking Mini-FAQ *** 144, Now made with C5 carbide! David F. Eisan Woodworking 0 January 7th 04 12:49 PM
Since I don't have any plans...whatsa best way to secure desk's back panel to side panels? (and other questions) Leon Woodworking 5 August 27th 03 04:08 AM


All times are GMT +1. The time now is 04:59 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"