Home Electrical Question
Can I use a 16AWG x 3 for a 30 foot run to a 220v 20amp breaker?
Details: This is what the installation manual for my wifes new habatchi grill requires. The manual says "This appliance must be hardwired. The mains connecting cable must be at least correspond to the type SJTO 3x16 AWG 105*C" The guys at Lowes and all the old timers say that you can't use 16 gage wire on a 220 breaker. I say this is a new appliance and isnt it possible that someone has designed a way that you can, why would the book call for it? The tech data states Total connected load: 1500 W, AC 208/220-240 V / 60 Hz. Now I know the formula for amps is I = W / V. 1500W / 208 = 7.2 amps. The specs for a 16x3 AWG 105*C is rated at 13 amps 250 volts. So, why is everyone here telling me that this won't work? Please help....I don't want to burn this grill up, my wife will kill me.. |
#2
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
|
#3
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
"Speedy Jim" wrote in message
. com... (I don't understand what they meant by "hard-wired". That might cloud it.) Jim Hard-wired means "not plugged in", "connected with wire nuts", "not easily disconnected", etc. |
#4
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
|
#5
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
wrote in message oups.com... Can I use a 16AWG x 3 for a 30 foot run to a 220v 20amp breaker? Details: This is what the installation manual for my wifes new habatchi grill requires. The manual says "This appliance must be hardwired. The mains connecting cable must be at least correspond to the type SJTO 3x16 AWG 105*C" The guys at Lowes and all the old timers say that you can't use 16 gage wire on a 220 breaker. I say this is a new appliance and isnt it possible that someone has designed a way that you can, why would the book call for it? The tech data states Total connected load: 1500 W, AC 208/220-240 V / 60 Hz. Now I know the formula for amps is I = W / V. 1500W / 208 = 7.2 amps. The specs for a 16x3 AWG 105*C is rated at 13 amps 250 volts. So, why is everyone here telling me that this won't work? Please help....I don't want to burn this grill up, my wife will kill me.. Any wiring on a 20A breaker must be 12 ga or larger regardless of what will be connected to it. A 15A breaker can use 14 ga wires but I don't think you will find a 15A 220V breaker readily on the shelf. You won't find house wiring smaller than 14 ga. and you can't use bulk appliance or lamp cord for permanent wiring for anything. I would use 12/3 romex from the breaker to your new electrical box then 12/3 armored cable from the new box to your grill. Kevin |
#6
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
Thanks guys, I understand. I will go with 12/3 romex instead since I
can't readily find a 15 amp 220 breaker, only 20 amp. I misunderstood and was thinking of it backwards, that the breaker would protect the grill. Only one more question, I am going to hard wire it in since it is getting mounted in the countertop and is going to be a permenante fixture. The unit came assembled with a 16/3, 2 foot long pigtail for connection. I assume that I will just connect the 16/3 to the 12/3 at the junction box? Is that correct? Should I expect any problems with that? Thanks again for all ya'lls help, I really appreciate it. |
#7
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
Charz ) said...
Only one more question, I am going to hard wire it in since it is getting mounted in the countertop and is going to be a permenante fixture. The unit came assembled with a 16/3, 2 foot long pigtail for connection. I assume that I will just connect the 16/3 to the 12/3 at the junction box? Is that correct? Should I expect any problems with that? No, that is perfectly acceptable. In case anyone posts a "20A circuits must use 12 gauge wire" in the context of that 16 gauge piece that comes out of the unit, the code that dictates short sections that are factory-assemled to approved appliances has different sets of rules concerning the ampacity of various gauges of wires. It the branch circuit it is connected to is protected by a 20 A breaker, it must use 12 gauge cable, but connecting the short section from the unit that is only 16 gauge is perfectly fine. -- Calvin Henry-Cotnam "I really think Canada should get over to Iraq as quickly as possible" - Paul Martin - April 30, 2003 ------------------------------------------------------------------------- NOTE: if replying by email, remove "remove." and ".invalid" *** Free account sponsored by SecureIX.com *** *** Encrypt your Internet usage with a free VPN account from http://www.SecureIX.com *** |
#8
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
Charz wrote: Thanks guys, I understand. I will go with 12/3 romex instead since I can't readily find a 15 amp 220 breaker, only 20 amp. I misunderstood and was thinking of it backwards, that the breaker would protect the grill. Only one more question, I am going to hard wire it in since it is getting mounted in the countertop and is going to be a permenante fixture. The unit came assembled with a 16/3, 2 foot long pigtail for connection. I assume that I will just connect the 16/3 to the 12/3 at the junction box? Is that correct? Should I expect any problems with that? What you propose is fine. It's covered under the tap rule. DO NOT run romex straight to the unit. Romex is only rated for 90C and the unit needs 105C wire (as it came from the factory). Use the j-box and the pigtail, as you said. |
#9
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
|
#10
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
You are correct Jeff, I believe it originated in Germany. the company
is Gaggenau and the link to the grill is: http://www.gaggenau.com/US_en/Modula...tentId=6312143 |
#11
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
Charz wrote:
You are correct Jeff, I believe it originated in Germany. the company is Gaggenau and the link to the grill is: http://www.gaggenau.com/US_en/Modula...tentId=6312143 Interesting. I particularly liked that "Vacation Lock" feature. Their website says: ******************* Vacation lock After running for four hours, the appliance automatically switches itself off if it receives no operator commands during this time. ******************* Can't recall seeing anything like that on a domestic appliance other than the electric blanket on our bed, which shuts itself off about 12 hours after it's been turned on and requires pushing a button on one of the controllers to restart it. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Truth exists; only falsehood has to be invented." |
#12
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
According to Jeff Wisnia :
wrote: Can I use a 16AWG x 3 for a 30 foot run to a 220v 20amp breaker? The tech data states Total connected load: 1500 W, AC 208/220-240 V / 60 Hz. Your quote from the manual didn't say anything about breakers or fuses, so I believe it was making a correct statement engineering wise, PROVIDING there was a breaker or fuse of appropriate size at the start of the run to protect that No. 16 wire from overload. And, that device would have to be rated at less than 15 amps, which is not a very standard item. Methinks that manual may contain a literal translation of text originally intended for units sold elsewhere in the world, without regard for US codes. I'm not sure that US codes would allow No. 16 wire to be used for a 220 volt circuit "hard wired" in a home. One of the code mavins here can likely tell us. Methinks the he's misquoting the manual or it's not written very well. Since it mentions North American wire designations, the manual is targetted for North America, and it wouldn't get UL or CSA approval if it specified Sxxx cable for an inwall permanent installation. Sxxx cable is _not_ to be used in permanent wiring. The manual is spec'ing an _extension_ cord to be used between the hibachi and a 240V outlet. [Tho, I'd personally prefer to use SOW 14/3, 16ga is a little skimpy for this ampacity in my personal opinion for a heating device at this ampacity, and SO/SOW is heavier duty insulation] For a permanent in-wall installation, he should be using 12/3 NMD-90 (solid core). Even better: it's cheaper than Sxxx. If the wiring is going to be exposed on wall surfaces, he has to consider conduit. If he's been confused this way by the manual, I think he needs to read a good book on electrical wiring, or hire an electrician - especially if it's not a straight-forward in-wall installation. He's going to need to double check whether the thing is four wire or three wire. If it's only three (pure 240V circuit), he can use 12/2 NMD (or 12/2 Sx) - the wire designation usually doesn't count the ground. US wiring designation tend to say something like 12/2 w/g to make it clear that the ground is _extra_. In canada, we don't need to say w/g, because house wire always comes with ground. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#13
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
Chris Lewis wrote:
According to Jeff Wisnia : wrote: Can I use a 16AWG x 3 for a 30 foot run to a 220v 20amp breaker? The tech data states Total connected load: 1500 W, AC 208/220-240 V / 60 Hz. Your quote from the manual didn't say anything about breakers or fuses, so I believe it was making a correct statement engineering wise, PROVIDING there was a breaker or fuse of appropriate size at the start of the run to protect that No. 16 wire from overload. And, that device would have to be rated at less than 15 amps, which is not a very standard item. Methinks that manual may contain a literal translation of text originally intended for units sold elsewhere in the world, without regard for US codes. I'm not sure that US codes would allow No. 16 wire to be used for a 220 volt circuit "hard wired" in a home. One of the code mavins here can likely tell us. Methinks the he's misquoting the manual or it's not written very well. Since it mentions North American wire designations, the manual is targetted for North America, and it wouldn't get UL or CSA approval if it specified Sxxx cable for an inwall permanent installation. Sxxx cable is _not_ to be used in permanent wiring. The manual is spec'ing an _extension_ cord to be used between the hibachi and a 240V outlet. [Tho, I'd personally prefer to use SOW 14/3, 16ga is a little skimpy for this ampacity in my personal opinion for a heating device at this ampacity, and SO/SOW is heavier duty insulation] For a permanent in-wall installation, he should be using 12/3 NMD-90 (solid core). Even better: it's cheaper than Sxxx. If the wiring is going to be exposed on wall surfaces, he has to consider conduit. If he's been confused this way by the manual, I think he needs to read a good book on electrical wiring, or hire an electrician - especially if it's not a straight-forward in-wall installation. He's going to need to double check whether the thing is four wire or three wire. If it's only three (pure 240V circuit), he can use 12/2 NMD (or 12/2 Sx) - the wire designation usually doesn't count the ground. US wiring designation tend to say something like 12/2 w/g to make it clear that the ground is _extra_. In canada, we don't need to say w/g, because house wire always comes with ground. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. Sxxx *IS* approved for permanent installations in the US. It is approved for flexible cord drops service a single device as long as appropriate strain relief is used at it's connection point. Pete C. |
#14
Posted to alt.home.repair
|
|||
|
|||
Home Electrical Question
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Desperate for advice on replacing dead 255K BTU furnace in 3200 sq foot house | Home Ownership | |||
Desperate for advice on replacing dead 255K BTU furnace in 3200 sq foot house | Home Repair | |||
Electrical Line Noise and Home Theater | Home Repair | |||
Basic Home Electrical Question | Home Repair |