Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 14:22:28 -0000, "Billy H"
m Gave us:

That's a good idea.


Not necessarily.

The problem of lost contact area is assuaged somewhat
by the fact of coating the wire and the terminal with solder.


Crimped connections using the proper wire size, and connector do not
"lose contact area".

Other problems
inside the connection are negated.


What problems? Done correctly, the area of contact is gas tight.

That still does not negate the fact that it is outside the spec for
the terminal lug to add solder to it.

Roy L. Fuchs February 5th 06 06:33 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.

Billy H February 5th 06 06:58 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.



And nobody apologises for making fools of themselves in public



Billy H February 5th 06 07:01 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 13:56:21 -0000, "Billy H"
m Gave us:


"Harry Muscle" wrote in message
roups.com...
Does coating stranded copper wire with solder and then connecting it to
a standard outlet cause any issues or break any codes?

I have a small project I put together (this is all inside of a big box
... ie: not inside a wall or part of the house ... but I still would
like to make sure it's safe and meets any code requirements as if it
was inside a wall or part of the house) which uses stranded copper wire
(14AWG). I coated the ends with solder and then bend them to shape
before connecting them to standard outlets (screwed on, not the push
in). Will this cause any problems or break any electrical codes (I'm
located in Ontario, Canada in case that matters).

The reason why I'm asking is because I've been doing a whole bunch of
reading about issues with aluminum wire, one of the issues being the
thermal expansion problems caused by the aluminum wire expanding at a
different rate than the screw connector it's connected to on an
outlet/switch/etc. So this made me wonder if the solder will cause any
problems with thermal expansion of it being different than the screw
that it's screwed on to, etc.?

Thanks for any info you share,
Harry



Copper wires melt at a higher temperature to any solde you may use.



Bull**** Copper has a higher melt point temperature than any solder
you may use. You MIGHT have been attempting to refer to the
insulation on SOME types of wire. If so, you failed miserably.



Good jump, paradoxical, but good.

Musta made a whole six foot by now!!



If there is a lot of heat generated in the circuitry you could melt the
solder.


Odd statement there. If there is that much heat generated at a
connection node, the wiring installation has much more deeper seated
problems than melted solder.


Agreed. Possibly bad design, hence design for terminals and build them
correctly.



The orders of magnitude of *linear* expansion of the metals you refer to

Aluminium (pure) alpha = 23*10^-6 (20 at 200K, 23.2 at 300K, 24.9 at
400K,
26.4 at 500K, 28.3 600, 33.8 at 800K you could graph it from that)

Copper (pure) alpha = 13.7 *10^-6 (15.1 at 200K, 16.8, 17.7, 18.3, 18.9,
20
at 800K)

per deltaKelvin.

melting point Al= 933K, Cu=1356.

if you find the data for the solder you use you can calculate your
expansion
characteristics (absolute and relative) and also check to see if your
solder
will melt.


Jeez, you are so far off base. It is truly pathetic. Solder creep
has to do with physical, mechanical stress, not temperature.

Using the data for the thermo-electric effects and the dimensions of the
lines inquestion you cna calculate the heat evolved by the current in the
lines, terminals and all.


The heat in ANY properly installed circuit will never reach the
melting point of ANY metal used in the industry.



If you design with inherent flaws and then install it it'll be flawed.
Period.



Roy L. Fuchs February 5th 06 07:03 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 14:28:48 -0000, "Billy H"
m Gave us:

If you *get inside* a soldered or tinned end and think of the strands, how
the electricity actually *moves* then the concept begins to open up.
Electricity travels on the surface of the circuitry.


No, it does not. High frequency AC current moves the travel toward
the surface, but low frequency AC and DC does not.

For wires the area of
travel is the surface area of the cable, Length*Pi*diameter.


Where are you getting this crap? Skin depth at 60Hz is huge.

Adding solder
changes the surface areas and if you blob the terminal rather than tin the
strands you change the surface area of the wire and hence the physical
characteristics of the cable.


You are trying to get too deep into a mechanical structure here.

The term "blob" also has little technical depth. The tinning action
of a metal by tin lead solder is called "wetting". The "blob" you
refer to would be called a "dry solder joint" where the wetting action
failed to take place. Still a rather inappropriate term to use here.

Wetting itself is the result of the action of the solder flux. It
de-oxidizes the metals on the surfaces involved, and allows the molten
solder to make a cohesive "inter-metallic" bond with them. The
wetting action then works by the physical mechanism known as
"capillary attraction". The surface tension of the molten solder
alloy gives the final solder joint its shape. Any REAL soldering
personage can tell by the appearance of this finished solder joint
whether or not it was done properly. The REAL soldering inspector can
tell at a mere glance.

So, even the use of the term "coating" in the topic header is
incorrect. It leans toward the description of a failed solder joint.
A good solder joint has an integrated appearance.

Roy L. Fuchs February 5th 06 07:12 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 14:47:54 -0000, "Billy H"
m Gave us:

Bull****.

The only true understanding is a true interpretation.

Corinthians 2:36


Technical specifications ARE understood, HAVE been laid out, and ARE
NO LONGER open to negotiation after they have been set forth. AT
least not by some lame inspector.

That IS the interpretation. Trying to mute them while in the
position of an inspector is one of the most retarded behaviors in the
industry, and shows said inspector to be of less understanding than
his position dictates. In other words, he was promoted beyond his
level of competency.


All statutes are open for interpretation, a judge in court interprets the
statute when he passes judgement, he can do no more.


Very people oriented... how nice. The same is NOT true for
scientific and technical specifications.

Try to pull that bull**** in the pharmaceutical industry or the
chemical industry.. you won't have a job for a very long time.

Shame the same doesn't hold true in electronics. There would be a
better understanding among pros and lay persons if it were.


It's the only due reason I give to politicians who wish to change the
present law if it is old but correct.


Why is it legal to make U-turns in some states, but not others?
Politicians are basically very lame when it comes to actually knowing
about the technical aspects of what they are in control of.


Old English language is more difficult
for the lay person to interpret and hence to understand than modern
language.


No ****. Especially with all these mosh pit, pants down past their
ass, uneducated punks we have in the world today.


But then we are not all of the same intellect, patience or will.

Abso-****ing-lutely true.

Billy H February 5th 06 07:13 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 14:28:48 -0000, "Billy H"
m Gave us:

If you *get inside* a soldered or tinned end and think of the strands, how
the electricity actually *moves* then the concept begins to open up.
Electricity travels on the surface of the circuitry.


No, it does not. High frequency AC current moves the travel toward
the surface, but low frequency AC and DC does not.

For wires the area of
travel is the surface area of the cable, Length*Pi*diameter.


Where are you getting this crap? Skin depth at 60Hz is huge.

Adding solder
changes the surface areas and if you blob the terminal rather than tin the
strands you change the surface area of the wire and hence the physical
characteristics of the cable.


You are trying to get too deep into a mechanical structure here.

The term "blob" also has little technical depth. The tinning action
of a metal by tin lead solder is called "wetting". The "blob" you
refer to would be called a "dry solder joint" where the wetting action
failed to take place. Still a rather inappropriate term to use here.

Wetting itself is the result of the action of the solder flux. It
de-oxidizes the metals on the surfaces involved, and allows the molten
solder to make a cohesive "inter-metallic" bond with them. The
wetting action then works by the physical mechanism known as
"capillary attraction". The surface tension of the molten solder
alloy gives the final solder joint its shape. Any REAL soldering
personage can tell by the appearance of this finished solder joint
whether or not it was done properly. The REAL soldering inspector can
tell at a mere glance.

So, even the use of the term "coating" in the topic header is
incorrect. It leans toward the description of a failed solder joint.
A good solder joint has an integrated appearance.



But reduced area for the electricity to run along all the same.




Roy L. Fuchs February 5th 06 07:14 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 15:02:55 -0000, "Billy H"
m Gave us:

My apologies

2 corinthians chapter 3 line 6.

"Who also hath made us able ministers of the new testament; not of the
letter, but of the spirit:for the letter killeth, but the spirit giveth
life."

http://www.bible-sermons.org.uk/bible/2-Corinthians_3/



There is a big difference between words that surround the laws and
actions of people, and the words, laws, and technical specifications
of a scientific standard.

You do not get to mix the two.

Roy L. Fuchs February 5th 06 07:15 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 15:17:30 -0000, "Billy H"
m Gave us:



You have bored me stupid.

Should I give a fat flying **** about your condition?

Billy H February 5th 06 07:22 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 14:47:54 -0000, "Billy H"
m Gave us:

Bull****.

The only true understanding is a true interpretation.

Corinthians 2:36


Technical specifications ARE understood, HAVE been laid out, and ARE
NO LONGER open to negotiation after they have been set forth. AT
least not by some lame inspector.

That IS the interpretation. Trying to mute them while in the
position of an inspector is one of the most retarded behaviors in the
industry, and shows said inspector to be of less understanding than
his position dictates. In other words, he was promoted beyond his
level of competency.


All statutes are open for interpretation, a judge in court interprets the
statute when he passes judgement, he can do no more.


Very people oriented... how nice. The same is NOT true for
scientific and technical specifications.

Try to pull that bull**** in the pharmaceutical industry or the
chemical industry.. you won't have a job for a very long time.

Shame the same doesn't hold true in electronics. There would be a
better understanding among pros and lay persons if it were.


It's the only due reason I give to politicians who wish to change the
present law if it is old but correct.


Why is it legal to make U-turns in some states, but not others?
Politicians are basically very lame when it comes to actually knowing
about the technical aspects of what they are in control of.


Old English language is more difficult
for the lay person to interpret and hence to understand than modern
language.


No ****. Especially with all these mosh pit, pants down past their
ass, uneducated punks we have in the world today.


But then we are not all of the same intellect, patience or will.

Abso-****ing-lutely true.


LMAO

I'm not an inspector, I see your point about regs, this is a wire, it melts
at xx degrees etc. don't use it with an electrolytic connection etc.

Science IS science, law is law.

and scientific law is, well, a bit complex!



Roy L. Fuchs February 5th 06 07:22 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 5 Feb 2006 18:58:26 -0000, "Billy H"
m Gave us:


"Roy L. Fuchs" wrote in message
.. .
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.



And nobody apologises for making fools of themselves in public

Including you, with your "I crossed this to yada yada yada group,
where you quoted the entire 110 line post... again.

If you want to be so conformal, why don't you learn a little about
this forum called Usenet that you have decided to invade?

http://en.wikipedia.org/wiki/Top-post

http://www.ietf.org/rfc/rfc1855.txt

Otherwise, you aren't any better than anyone else, and particularly
not any better than anyone you deride here.

Billy H February 5th 06 07:27 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 18:58:26 -0000, "Billy H"
m Gave us:


"Roy L. Fuchs" wrote in message
. ..
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.



And nobody apologises for making fools of themselves in public

Including you, with your "I crossed this to yada yada yada group,
where you quoted the entire 110 line post... again.

If you want to be so conformal, why don't you learn a little about
this forum called Usenet that you have decided to invade?

http://en.wikipedia.org/wiki/Top-post

http://www.ietf.org/rfc/rfc1855.txt

Otherwise, you aren't any better than anyone else, and particularly
not any better than anyone you deride here.



It was a totally relevant cross posting, why you didn't reply with what you
said earlier is beyond me, it'd maybe educate any wannaba lawyers in there
some.

Anyway if I carry on like this I'll be more of a hypocrite than I laready
am.



Billy H February 5th 06 07:34 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Billy H" m wrote in
message ...

"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 18:58:26 -0000, "Billy H"
m Gave us:


"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run
by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.


And nobody apologises for making fools of themselves in public

Including you, with your "I crossed this to yada yada yada group,
where you quoted the entire 110 line post... again.

If you want to be so conformal, why don't you learn a little about
this forum called Usenet that you have decided to invade?

http://en.wikipedia.org/wiki/Top-post

http://www.ietf.org/rfc/rfc1855.txt

Otherwise, you aren't any better than anyone else, and particularly
not any better than anyone you deride here.



It was a totally relevant cross posting, why you didn't reply with what
you said earlier is beyond me, it'd maybe educate any wannaba lawyers in
there some.

Anyway if I carry on like this I'll be more of a hypocrite than I laready
am.


Just for the record, that was a form of apology for cross posting your
message.



Pop February 6th 06 12:08 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
....
:
: Otherwise, you aren't any better than anyone else, and
particularly
: not any better than anyone you deride here.

Well, I dunno 'bout that: if you're included, then he's
certainly better than you, that's a given. Fuchsy is a closed
mind with a large bowel, I'm afraid. Nuff said




Roy L. Fuchs February 6th 06 12:24 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Mon, 06 Feb 2006 00:08:07 GMT, "Pop"
Gave us:

...
:
: Otherwise, you aren't any better than anyone else, and
particularly
: not any better than anyone you deride here.

Well, I dunno 'bout that: if you're included, then he's
certainly better than you, that's a given. Fuchsy is a closed
mind with a large bowel, I'm afraid. Nuff said


Problem is, you haven't said a damned thing, **** mouth.

Keith February 6th 06 02:03 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 05 Feb 2006 19:27:37 +0000, Billy H wrote:


"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 18:58:26 -0000, "Billy H"
m Gave us:


"Roy L. Fuchs" wrote in message
...
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools' gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.


And nobody apologises for making fools of themselves in public

Including you, with your "I crossed this to yada yada yada group,
where you quoted the entire 110 line post... again.

If you want to be so conformal, why don't you learn a little about
this forum called Usenet that you have decided to invade?

http://en.wikipedia.org/wiki/Top-post

http://www.ietf.org/rfc/rfc1855.txt

Otherwise, you aren't any better than anyone else, and particularly
not any better than anyone you deride here.



It was a totally relevant cross posting, why you didn't reply with what you
said earlier is beyond me, it'd maybe educate any wannaba lawyers in there
some.

Anyway if I carry on like this I'll be more of a hypocrite than I laready
am.


Ignore Fuchs. If you challenge his "perfection" he'll simply slither away
and you'll feel dirty in the morning.

--
Keith

Roy L. Fuchs February 6th 06 02:18 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Sun, 05 Feb 2006 21:03:55 -0500, Keith Gave us:


Ignore Fuchs. If you challenge his "perfection" he'll simply slither away
and you'll feel dirty in the morning.


Unlike yourself. You ARE dirty every morning, noon, and night.

Your stalking baby bull**** proves it.

Keith February 6th 06 02:24 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Mon, 06 Feb 2006 02:18:51 +0000, Roy L. Fuchs wrote:

On Sun, 05 Feb 2006 21:03:55 -0500, Keith Gave us:


Ignore Fuchs. If you challenge his "perfection" he'll simply slither away
and you'll feel dirty in the morning.


Unlike yourself. You ARE dirty every morning, noon, and night.


Nope, I always take a shower after trying to teach you something about
engineering. Actually I don't care a **** for you, but others deserve
better.

Your stalking baby bull**** proves it.


Stalking? You are some fuk'n pot.

--
Keith

Billy H February 6th 06 11:45 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
LAR DEE ****IN DAR





Roy L. Fuchs February 7th 06 12:30 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Mon, 6 Feb 2006 23:45:46 -0000, "Billy H"
m Gave us:

LAR DEE ****IN DAR


That would be:

La Di Dah

Lar dee dar is from the movie "Blazing Saddles"

Does the "H" stand for "Hill"? as in Hillbilly...

[email protected] February 7th 06 07:47 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
Harry Muscle wrote:
Does coating stranded copper wire with solder and then connecting it to
a standard outlet cause any issues or break any codes?

I have a small project I put together (this is all inside of a big box
... ie: not inside a wall or part of the house ... but I still would
like to make sure it's safe and meets any code requirements as if it
was inside a wall or part of the house) which uses stranded copper wire
(14AWG). I coated the ends with solder and then bend them to shape
before connecting them to standard outlets (screwed on, not the push
in). Will this cause any problems or break any electrical codes (I'm
located in Ontario, Canada in case that matters).

The reason why I'm asking is because I've been doing a whole bunch of
reading about issues with aluminum wire, one of the issues being the
thermal expansion problems caused by the aluminum wire expanding at a
different rate than the screw connector it's connected to on an
outlet/switch/etc. So this made me wonder if the solder will cause any
problems with thermal expansion of it being different than the screw
that it's screwed on to, etc.?

Thanks for any info you share,
Harry


Before I retired I was an electronics design Engineer. I remember one
time I ran into a situation where I was wondering if the wires ought to
be soldiered before being placed into a connector. I checked with both
the vendor (probably Molex) and our manufacturing department. I
remember the answer was a resounding NO. You never soldier wires that
are going to be placed in a connector.

However, sometime around 1980, after I had just moved into the house
I'm in now, I had a problem with a three-way switch that didn't work in
my basement and the basement was completely sheet rocked. The previous
owner/amateur electrician had fouled up on the wiring. A couple of
years later, I had to remove the sheet rock underneath a cold air
return to facilitate the addition of a new room and I was able to fish
some wire through the ceiling and fix the problem. However, this
necessitated a connection that would be covered by sheet rock (no
lectures please). So I put the wires in an electrical box and twisted
them and put a light coat of soldier on them. Then I put wire nuts on
top of that. That was 25 years ago and I have never had any problems.

In regard to aluminum house wiring (single-strand), aluminum wiring is
very dangerous when used inside of a house. It's one of the easiest way
I can think of to get your house burned down. Putting copper and
aluminum together causes a corrosive chemical reaction. It's use should
be restricted to service entrance wires only and even then you should
double check to make sure the connector is marked for aluminum. As I
recall, these special connectors are marked "AL/CU".

If you happen to be unfortunate enough to have single-strand aluminum
wire inside your house, then you need to make sure that all of the
connectors (switches and outlets) are marked "AL/CU". These special
switches and outlets are relatively expensive. If you need to connect
an aluminum wire and copper wire together, there are special wire nuts
available for doing that (also expensive). There is also some
antioxidant cream available that you can use for copper/aluminum
connections.


Roy L. Fuchs February 7th 06 07:57 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On 6 Feb 2006 23:47:50 -0800, Gave us:

So I put the wires in an electrical box and twisted
them and put a light coat of soldier on them. Then I put wire nuts on
top of that. That was 25 years ago and I have never had any problems.


You won't see a solder creep issue with that scenario. For one thing,
the twisted SOLID strand wires cinch together fairly tightly even
before they are soldered. Then, the CONICAL wire nut will likely
always have more than enough pressure on the union for solder creep to
never be a problem. Finally, the joint itself, by your own
description only has a very light fill. For the solder creep to
become a big problem, there would have to be so much of it that the
cross sectional area of it is thick enough that solder creep could
even be an issue.
Also, solder creep also likes some constant stress be on the joint.
The twisted SOLID wire bundles likely have no mechanical stress on
them in several locations throughout the twisted assembly.

Though not spec, I see a very carefully constructed union like this
as not being a problem. That is a personal view though, and an actual
inspection would be required for me to conclude that the joints are
truly integral.

Roy L. Fuchs February 7th 06 08:00 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On 6 Feb 2006 23:47:50 -0800, Gave us:

In regard to aluminum house wiring (single-strand), aluminum wiring is
very dangerous when used inside of a house. It's one of the easiest way
I can think of to get your house burned down. Putting copper and
aluminum together causes a corrosive chemical reaction. It's use should
be restricted to service entrance wires only and even then you should
double check to make sure the connector is marked for aluminum. As I
recall, these special connectors are marked "AL/CU".


I agree with this. I hate Al wiring as the connections are not gas
tight, and heat more than copper nodes do.

I have also seen many folks die in Al wired commercial
establishments. The AL was not the immediate culprit. loose,
improperly install unions were. However, copper unions sporting the
same issues don't heat up as much, and would likely have never
generated the fatal problem.

Roy L. Fuchs February 7th 06 08:02 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On 6 Feb 2006 23:47:50 -0800, Gave us:

If you happen to be unfortunate enough to have single-strand aluminum
wire inside your house, then you need to make sure that all of the
connectors (switches and outlets) are marked "AL/CU". These special
switches and outlets are relatively expensive. If you need to connect
an aluminum wire and copper wire together, there are special wire nuts
available for doing that (also expensive). There is also some
antioxidant cream available that you can use for copper/aluminum
connections.


Yes, and ALL nodes being very tight is paramount.

Running an all copper refit will improve the house value, and be
safer and better, however.

Billy H February 7th 06 01:36 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Mon, 6 Feb 2006 23:45:46 -0000, "Billy H"
m Gave us:

LAR DEE ****IN DAR


That would be:

La Di Dah

Lar dee dar is from the movie "Blazing Saddles"

Does the "H" stand for "Hill"? as in Hillbilly...



No It is Russian.


Noshart is it's pronunciation. Means 'one who shakes the sphere.'




Bud-- February 7th 06 05:00 PM

Does coating stranded copper wire with solder cause any issuesor break any codes?
 
wrote:
In regard to aluminum house wiring (single-strand), aluminum wiring is
very dangerous when used inside of a house. It's one of the easiest way
I can think of to get your house burned down. Putting copper and
aluminum together causes a corrosive chemical reaction. It's use should
be restricted to service entrance wires only and even then you should
double check to make sure the connector is marked for aluminum. As I
recall, these special connectors are marked "AL/CU".

If you happen to be unfortunate enough to have single-strand aluminum
wire inside your house, then you need to make sure that all of the
connectors (switches and outlets) are marked "AL/CU". These special
switches and outlets are relatively expensive. If you need to connect
an aluminum wire and copper wire together, there are special wire nuts
available for doing that (also expensive). There is also some
antioxidant cream available that you can use for copper/aluminum
connections.

The best information I have seen on making aluminum wire branch circuit
connections and fixing old installations is at:
http://www.inspect-ny.com/aluminum/alreduce.htm
It is based extensive research, primarily for the Consumer Product
Safety Commission, which looked at causes of failures of aluminum
connections. The paper gives detailed procedures for making different
kinds of connections and also other advice. A common theme is that
aluminum oxide is a major cause of failure and aluminum wires should
have antioxide paste applied then the wire abraded to remove oxides
before making a connection. The author specifically does not like the
Ideal #65 wire nut which, as far as I know, is the only wire nut that
has been UL listed for aluminum wire.

Aluminum oxide, an insulator, forms very rapidly on a clean aluminum
surface. Its formation is produced by the high reactivity of aluminum,
not aluminum to other metal contact.

Devices for aluminum wire are marked CO/ALR.

bud--

not i February 7th 06 07:05 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Thu, 02 Feb 2006 22:56:25 GMT, "Toller" wrote:


"Roy L. Fuchs" wrote in message
.. .
On Thu, 02 Feb 2006 11:55:00 -0600, Bud--
Gave us:

The question I asked was for a single tinned stranded wire in a pressure
connection.



Stranded wire in a pressure connection cannot be soldered.


I am not doubting you, but can you give a reference for that?
(I always crimp fitting on stranded, but was unaware of this prohibition...)




This is from The Canadian Electrical Code Rule 12-112 Conductor
joints and splices
(1) Unless made with solderless wire connectors,joints or spices in
insulated conductors shall be soldered, but they shall first be made
mechanically and electrically secure.


Rule 12-116 Termination of conductors
(1) The portion of stranded conductors to be held by wire-binding
terminals or solderless wire connectors shall have the strands
confined so that there will be no stray strands to cause either
short-circuits or grounds.




My Interpretation : Solder could be used to confine the strands!

Roy L. Fuchs February 7th 06 08:30 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Tue, 07 Feb 2006 14:05:19 -0500, not i Gave us:

This is from The Canadian Electrical Code Rule 12-112 Conductor
joints and splices
(1) Unless made with solderless wire connectors,joints or spices in
insulated conductors shall be soldered, but they shall first be made
mechanically and electrically secure.


Rule 12-116 Termination of conductors
(1) The portion of stranded conductors to be held by wire-binding
terminals or solderless wire connectors shall have the strands
confined so that there will be no stray strands to cause either
short-circuits or grounds.


My Interpretation : Solder could be used to confine the strands!


What part of "Unless made with solderless wire connectors" do you not
understand?

http://m-w.com/dictionary/unless

The remark about exposed strands is so that assemblers and inspectors
can keep vigilant about making sure that their strip lengths and
insertion depths are kept tightly spec'd when using crimp style
connectors.

http://m-w.com/dictionary/confined

It isn't something you "interpret". It IS something where you follow
the instructions given you by an inspector that DOES know what is
going on. You obviously do not.

Sometimes I think that some of you "interpret" people need to be
"confined" so that there will be no stray bull**** spewed into a
technical newsgroup.

Spokesman February 7th 06 11:41 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in message
...
On Sat, 04 Feb 2006 02:57:22 GMT, "Long Ranger"
Gave us:


"Roy L. Fuchs" wrote in message
.. .
On 3 Feb 2006 11:35:47 -0800, "Harry Muscle"



Screw terminals that have a "captivated" screw need a
"spade lug" used on them.


By far my favorite line from this knave.

Bugger off, troll dip****!



Hey Dark Matter, You sure told him!



Phil Scott February 9th 06 06:07 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Andrew Gabriel" wrote in
message .. .
In article
. com,
"Harry Muscle" writes:
Does coating stranded copper wire with solder and then
connecting it to
a standard outlet cause any issues or break any codes?

I have a small project I put together (this is all inside
of a big box
... ie: not inside a wall or part of the house ... but I
still would
like to make sure it's safe and meets any code requirements
as if it
was inside a wall or part of the house) which uses stranded
copper wire
(14AWG). I coated the ends with solder and then bend them
to shape
before connecting them to standard outlets (screwed on, not
the push
in). Will this cause any problems or break any electrical
codes (I'm
located in Ontario, Canada in case that matters).

The reason why I'm asking is because I've been doing a
whole bunch of
reading about issues with aluminum wire, one of the issues
being the
thermal expansion problems caused by the aluminum wire
expanding at a
different rate than the screw connector it's connected to
on an
outlet/switch/etc. So this made me wonder if the solder
will cause any
problems with thermal expansion of it being different than
the screw
that it's screwed on to, etc.?


You should not solder stranded wire prior to putting it into
a screw terminal. Solder creeps under pressure, so the
contact
pressure will steadily reduce over time until it forms a bad
contact. Strands which are tinned during the cable
manufacture
are OK, as the solder layer thickness is controlled and very
thin.
I'm not familiar with your local regulations, but in cases
of
stranded wire connecting to terminations which don't work
well
with stranded wire, the normal method is to crimp on a
bootlace
ferrule or an eyelet, depending on the terminal style.



I am in the industrial controls business and work with
stranded wire extensively, especially finely stranded wire in
challenging environments. It is almost pervasively common
that manufacturers supply equipment with the wire ends dipped
in solder, I have never seen those loosen to any degree more
than non soldered ends,

the soldered ends seem to be much more reliable and preferred.
Thats after 40 years in the business across a broad spectrum
of industrial applications, nuclear, petrochemical,
semiconductor, food and marine applications.... including DDC
applications.

Crimp connectors also work. they are less reliable than
factory or field soldered ends under a screw in marine or
industrial corrosive environments however.


Phil Scott

--
Andrew Gabriel




Phil Scott February 9th 06 06:10 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"repatch" wrote in message
...
On Fri, 03 Feb 2006 05:38:28 +0000, Roy L. Fuchs wrote:

On Fri, 03 Feb 2006 02:00:19 GMT, "Pop"
Gave
us:

In other words, it's an interpretation of the standardS
rather than a
written rule?

Pop


Absolutely not.

Solder creep is a well known phenomena. It is a bad
practice for any
compression type connection.


Just curious, what is the opinion for the following:
crimping the
connection, and THEN soldering it?


that would be good, especially in a corrosive environment.

RE the govt training courses on the issue, one of the primary
features one notices with government is incompetence, followed
closely by insanity and bad practices. Thank god very few
industrial controls manufacturers adopt such loopy practices.




Phil Scott

TTYL




Roy L. Fuchs February 9th 06 07:07 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Thu, 9 Feb 2006 10:10:49 -0800, "Phil Scott"
Gave us:

that would be good, especially in a corrosive environment.

RE the govt training courses on the issue, one of the primary
features one notices with government is incompetence, followed
closely by insanity and bad practices. Thank god very few
industrial controls manufacturers adopt such loopy practices.


I suggest that you contact AMP or MOLEX and ask them.

Your remarks about the military show a lack of knowledge as well.

Pop February 9th 06 10:01 PM

OT: Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Phil Scott" wrote in message
...
:
: "repatch" wrote in message
: ...
: On Fri, 03 Feb 2006 05:38:28 +0000, Roy L. Fuchs wrote:
:
: On Fri, 03 Feb 2006 02:00:19 GMT, "Pop"
: Gave
: us:
:
: In other words, it's an interpretation of the standardS
: rather than a
: written rule?
:
: Pop
:
: Absolutely not.
:
: Solder creep is a well known phenomena. It is a bad
: practice for any
: compression type connection.
:
: Just curious, what is the opinion for the following:
: crimping the
: connection, and THEN soldering it?
:
: that would be good, especially in a corrosive environment.
:
: RE the govt training courses on the issue, one of the primary
: features one notices with government is incompetence, followed
: closely by insanity and bad practices. Thank god very few
: industrial controls manufacturers adopt such loopy practices.

Such a blanket statement, although true in some areas, is far
from true as a blanket, plus exposes the fact that you have no
real familiarity with the subject at hand. Not only that, but if
you think "industrial controls manufacturer" don't and haven't
used things like soldering techinques and methodologies, you're
going to be grossly wrong in your overal picture you're trying to
paint.
You, along with several others have taken a good question
asked by one who only needed a simple but reliable answer and
have turned it into a crapfest of who knows what about what, and
very few of the comments have had any real basis in fact, let
along related to the OP's quest.




Roy L. Fuchs February 10th 06 12:45 AM

Does coating stranded copper wire with solder cause any issues or break any codes?
 
On Thu, 09 Feb 2006 22:01:25 GMT, "Pop"
Gave us:

You, along with several others have taken a good question
asked by one who only needed a simple but reliable answer and
have turned it into a crapfest of who knows what about what, and
very few of the comments have had any real basis in fact, let
along related to the OP's quest.

You are one lost mother ****er, boy.

There have been several posts which are based on FACT. Just not many
if not any of yours.

You deride him for his comments on the military, but you essentially
said the same thing with your "open to interpretation" post. It was
from that point on that YOU discontinued actually speaking on the
topic, and started acting like a ****ing wussy.

Go back and read the posts. There are many that have it right, and
many that have it wrong, and in case you are still lost, this group is
for exactly what you claim we are all doing wrong.

Usenet is a crapfest and that is why your lame ass is in the barrel.

And the thread is NOT off topic, dip****.

I'll say it again. Crimped on, compression style connectors should
NOT be soldered. Not after the connector is crimped on, nor the wire
before it is inserted.

Call AMP or MOLEX and they'll explain it to your ass as well. You
seem to think no one in the groups here know what they are talking
about.

You're a goddamned loser if you think you can get away with that
baby bull****.

Phil Scott February 10th 06 07:53 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 


You might find these links interesting Roy.

220,000 hits... lots of good articles on the first page.
http://www.google.com/search?hl=en&q...=Google+Search

There is a time and a place to solder crimped or non crimped
terminals and bare wire ends to be fit under a screw head....
and a time when that is not a good idea (hot running
situations, although Ive seen pure silver or brazed
connections in those locations)


Phil Scott



"Roy L. Fuchs" wrote in
message ...
On Thu, 09 Feb 2006 22:01:25 GMT, "Pop"

Gave us:

You, along with several others have taken a good question
asked by one who only needed a simple but reliable answer
and
have turned it into a crapfest of who knows what about what,
and
very few of the comments have had any real basis in fact,
let
along related to the OP's quest.

You are one lost mother ****er, boy.

There have been several posts which are based on FACT. Just
not many
if not any of yours.

You deride him for his comments on the military, but you
essentially
said the same thing with your "open to interpretation" post.
It was
from that point on that YOU discontinued actually speaking
on the
topic, and started acting like a ****ing wussy.

Go back and read the posts. There are many that have it
right, and
many that have it wrong, and in case you are still lost,
this group is
for exactly what you claim we are all doing wrong.

Usenet is a crapfest and that is why your lame ass is in
the barrel.

And the thread is NOT off topic, dip****.

I'll say it again. Crimped on, compression style connectors
should
NOT be soldered. Not after the connector is crimped on, nor
the wire
before it is inserted.

Call AMP or MOLEX and they'll explain it to your ass as
well. You
seem to think no one in the groups here know what they are
talking
about.

You're a goddamned loser if you think you can get away with
that
baby bull****.




Phil Scott February 10th 06 07:55 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

wrote in message
oups.com...
First, I do not have a copy of the current Canadian
Electrical Code. I
would call a Provincial or local building official for a
proper answer.
But in the USA....
Using solder on stranded building wire used in building
electrical
systems is not a normal trade practice.


absolutely correct in almost all applications including large
commercial applications.

In industrial and marine applications and of course with
electronics the practice is common and on corrosive
environments, necessary.

here are some links


220,000 hits... lots of good articles on the first page.
http://www.google.com/search?hl=en&q...=Google+Search

There is a time and a place to solder crimped or non crimped
terminals and bare wire ends to be fit under a screw head....
and a time when that is not a good idea (hot running
situations, although Ive seen pure silver or brassed
connections in those locations)


Phil Scott







First, it is not economical,
and secondly, there are too many different methods and
materials that
can be used to solder. Soldering can be more damaging than
helpful if
not done properly. For instance wicking can cause wires to
become
brittle and permit breakage. There are many alloys of
solder some
requiring the use of resin core others the use of acid for
soldering.
Soldering, in short, introduces a whole range of variables
that cannot
be controlled in the field. But the main reason it is not
done is it
simply takes too much time and is not necessary. For
splicing, wire
nuts are commonly used. For terminations, buy receptacles
and switches
that are listed for use with stranded wire. If you have to
use solid
wire for terminations, then attach a pigtail then wire nut
the solid
wire to the stranded wire. Better yet, replace the stranded
wire with
solid. The NEC Section requiring that the listing
instructions be
followed is 110.3(B). This has been in the (USA) National
Electrical
Code for as long as I can remember.

References:
From the 2005 NEC


110.3(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any
instructions
included in the listing or labeling.

110.14 Electrical Connections. Because of different
characteristics
of dissimilar metals, devices such as pressure
terminal or pressure splicing connectors and soldering lugs
shall be identified for the material of the conductor and
shall be properly installed and used. Conductors of
dissimilar
metals shall not be intermixed in a terminal or splicing
connector where physical contact occurs between dissimilar
conductors (such as copper and aluminum, copper and
copper-clad aluminum, or aluminum and copper-clad aluminum),
unless the device is identified for the purpose and
conditions of use. Materials such as solder, fluxes,
inhibitors,
and compounds, where employed, shall be suitable for
the use and shall be of a type that will not adversely
affect
the conductors, installation, or equipment.
FPN: Many terminations and equipment are marked with
a tightening torque.
(A) Terminals. Connection of conductors to terminal parts
shall ensure a thoroughly good connection without damaging
the conductors and shall be made by means of pressure
connectors
(including set-screw type), solder lugs, or splices to
flexible leads. Connection by means of wire-binding screws
or
studs and nuts that have upturned lugs or the equivalent
shall
be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals
used to connect aluminum shall be so identified.




Phil Scott February 10th 06 08:50 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"not i" wrote in message
...
On Thu, 02 Feb 2006 22:56:25 GMT, "Toller"
wrote:


"Roy L. Fuchs" wrote in
message
. ..
On Thu, 02 Feb 2006 11:55:00 -0600, Bud--

Gave us:

The question I asked was for a single tinned stranded wire
in a pressure
connection.


Stranded wire in a pressure connection cannot be
soldered.


I am not doubting you, but can you give a reference for
that?
(I always crimp fitting on stranded, but was unaware of this
prohibition...)




This is from The Canadian Electrical Code Rule 12-112
Conductor
joints and splices
(1) Unless made with solderless wire connectors,joints or
spices in
insulated conductors shall be soldered, but they shall first
be made
mechanically and electrically secure.


Rule 12-116 Termination of conductors
(1) The portion of stranded conductors to be held by
wire-binding
terminals or solderless wire connectors shall have the
strands
confined so that there will be no stray strands to cause
either
short-circuits or grounds.




My Interpretation : Solder could be used to confine the
strands!



Not only correct but the only way to go in many cases... it
seems most on the NG are house wiring guys and applying NEC as
they see it in homes etc...but not of course in the industrial
markets.

..
In corrosive environments, stranded wire will corrode into the
crimmped terminal and around the wire, insulating the wire
from the terminal slightly causing it to burn, then fail..
thats common.

Accordingly battery cable manufacturers most often solder
their wire into the crimped terminal ends.

This practice is seen pervasively in marine environments on
both low amperage control circuits, and on power circuits.



Use of solder on power circuit terminals however has many
problems, namely the solder melting out of the joint if the
wire warms too much...and extrusion of the solder under
compressive stress if screw connectors are used.. the military
specs some are referring to cover that aspect... but not the
other aspects.


Use of solder in an already crimped terminal serves to
increase the electrical contact area, thats good, and to
preclude corrosive gases, vapors and oils from the joint (by
wicking up the bare wire).... that is seen commonly be the
cause of failure in those situations.


For the last 100 years... and currently.... most if not all
controls systems and component manufacturers dip wire ends in
solder that are to be fit under screw head connectors... the
practice is at least 90% common.... thats with *control
circuits.

The practice is not common with power circuits for the reasons
mentioned but is still seen in some situations (primarily
corrosive environments... anyone can purchase NEC approved
soldered connectors of course for those purposes... those are
also pervasively common, especially in the electronics
industry.)



Phil Scott
Mechanical/ Electrical engineer and industrial controls
contractor since 1852 (I'm very old)




Phil Scott February 10th 06 08:56 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

wrote in message
oups.com...
Harry Muscle wrote:
Does coating stranded copper wire with solder and then
connecting it to
a standard outlet cause any issues or break any codes?

I have a small project I put together (this is all inside
of a big box
... ie: not inside a wall or part of the house ... but I
still would
like to make sure it's safe and meets any code requirements
as if it
was inside a wall or part of the house) which uses stranded
copper wire
(14AWG). I coated the ends with solder and then bend them
to shape
before connecting them to standard outlets (screwed on, not
the push
in). Will this cause any problems or break any electrical
codes (I'm
located in Ontario, Canada in case that matters).

The reason why I'm asking is because I've been doing a
whole bunch of
reading about issues with aluminum wire, one of the issues
being the
thermal expansion problems caused by the aluminum wire
expanding at a
different rate than the screw connector it's connected to
on an
outlet/switch/etc. So this made me wonder if the solder
will cause any
problems with thermal expansion of it being different than
the screw
that it's screwed on to, etc.?

Thanks for any info you share,
Harry


Before I retired I was an electronics design Engineer. I
remember one
time I ran into a situation where I was wondering if the
wires ought to
be soldiered before being placed into a connector. I checked
with both
the vendor (probably Molex) and our manufacturing
department. I
remember the answer was a resounding NO. You never soldier
wires that
are going to be placed in a connector.


Correct...you do not solder wire before it goes into a
crimped connector...but you do after it goes into a solder
socket connector and there are crimped connectors made to be
soldered as well of course.

..
In corrosive environments, stranded wire will corrode into the
crimmped terminal and around the wire, insulating the wire
from the terminal slightly causing it to burn, then fail..
thats common.

Accordingly battery cable manufacturers most often solder
their wire into the crimped terminal ends.

This practice is seen pervasively in marine environments on
both low amperage control circuits, and on power circuits.



Use of solder on power circuit terminals however has many
problems, namely the solder melting out of the joint if the
wire warms too much...and extrusion of the solder under
compressive stress if screw connectors are used.. the military
specs some are referring to cover that aspect... but not the
other aspects.


Use of solder in an already crimped terminal serves to
increase the electrical contact area, thats good, and to
preclude corrosive gases, vapors and oils from the joint (by
wicking up the bare wire).... that is seen commonly be the
cause of failure in those situations.


For the last 100 years... and currently.... most if not all
controls systems and component manufacturers dip wire ends in
solder that are to be fit under screw head connectors... the
practice is at least 90% common.... thats with *control
circuits.

The practice is not common with power circuits for the reasons
mentioned but is still seen in some situations (primarily
corrosive environments... anyone can purchase NEC approved
soldered connectors of course for those purposes... those are
also pervasively common, especially in the electronics
industry.)



Phil Scott
Mechanical/ Electrical engineer and industrial controls
contractor since 1852 (I'm very old)



However, sometime around 1980, after I had just moved into
the house
I'm in now, I had a problem with a three-way switch that
didn't work in
my basement and the basement was completely sheet rocked.
The previous
owner/amateur electrician had fouled up on the wiring. A
couple of
years later, I had to remove the sheet rock underneath a
cold air
return to facilitate the addition of a new room and I was
able to fish
some wire through the ceiling and fix the problem. However,
this
necessitated a connection that would be covered by sheet
rock (no
lectures please). So I put the wires in an electrical box
and twisted
them and put a light coat of soldier on them. Then I put
wire nuts on
top of that. That was 25 years ago and I have never had any
problems.

In regard to aluminum house wiring (single-strand), aluminum
wiring is
very dangerous when used inside of a house. It's one of the
easiest way
I can think of to get your house burned down. Putting copper
and
aluminum together causes a corrosive chemical reaction. It's
use should
be restricted to service entrance wires only and even then
you should
double check to make sure the connector is marked for
aluminum. As I
recall, these special connectors are marked "AL/CU".

If you happen to be unfortunate enough to have single-strand
aluminum
wire inside your house, then you need to make sure that all
of the
connectors (switches and outlets) are marked "AL/CU". These
special
switches and outlets are relatively expensive. If you need
to connect
an aluminum wire and copper wire together, there are special
wire nuts
available for doing that (also expensive). There is also
some
antioxidant cream available that you can use for
copper/aluminum
connections.




Phil Scott February 10th 06 09:12 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Roy L. Fuchs" wrote in
message ...
On Sat, 04 Feb 2006 22:34:11 -0500, Keith
Gave us:


Of course not. It's *his* standard.


..
In corrosive environments, stranded wire will corrode into the
crimped terminal and around the wire, insulating the wire
from the terminal slightly causing it to burn, then fail..
thats common.

Accordingly battery cable manufacturers most often solder
their wire into the crimped terminal ends.

This practice is seen pervasively in marine environments on
both low amperage control circuits, and on power circuits.



Use of solder on power circuit terminals however has many
problems, namely the solder melting out of the joint if the
wire warms too much...and extrusion of the solder under
compressive stress if screw connectors are used.. the military
specs some are referring to cover that aspect... but not the
other aspects.


Use of solder in an already crimped terminal serves to
increase the electrical contact area, thats good, and to
preclude corrosive gases, vapors and oils from the joint (by
wicking up the bare wire).... that is seen commonly be the
cause of failure in those situations.


For the last 100 years... and currently.... most if not all
controls systems and component manufacturers dip wire ends in
solder that are to be fit under screw head connectors... the
practice is at least 90% common.... thats with *control
circuits.

The practice is not common with power circuits for the reasons
mentioned but is still seen in some situations (primarily
corrosive environments... anyone can purchase NEC approved
soldered connectors of course for those purposes... those are
also pervasively common, especially in the electronics
industry.)

..

220,000 hits... lots of good articles on the first page.
http://www.google.com/search?hl=en&q...=Google+Search

There is a time and a place to solder crimped or non crimped
terminals and bare wire ends to be fit under a screw head....
and a time when that is not a good idea (hot running
situations, although Ive seen pure silver or brassed
connections in those locations)



Phil Scott
Mechanical/ Electrical engineer and industrial controls
contractor since 1852 (I'm very old)




You're a ****ing retard, boy.




Phil Scott February 10th 06 09:18 PM

Does coating stranded copper wire with solder cause any issues or break any codes?
 

"Billy H" m
wrote in message
...

"Roy L. Fuchs" wrote in
message ...
On Sun, 5 Feb 2006 14:25:43 -0000, "Billy H"
m Gave us:




Slagging matches so **** me off in usenet posting.

Life is too short to be caught up reading about some fools'
gripes with
another in the middle of a serious discussion.


Makes it sound like Parliament. Part of the reason the
country is run by
lawyers methinks.


So ask the retarded *******s why they jumped on me for
making a
perfectly good, technical point.

If you jump, I will jump back. That's all there is to it.



And nobody apologises for making fools of themselves in
public



Maybe our friend Roy will.

..
In corrosive environments, stranded wire will corrode into the
crimmped terminal and around the wire, insulating the wire
from the terminal slightly causing it to burn, then fail..
thats common.

Accordingly battery cable manufacturers most often solder
their wire into the crimped terminal ends.

This practice is seen pervasively in marine environments on
both low amperage control circuits, and on power circuits.



Use of solder on power circuit terminals however has many
problems, namely the solder melting out of the joint if the
wire warms too much...and extrusion of the solder under
compressive stress if screw connectors are used.. the military
specs some are referring to cover that aspect... but not the
other aspects.


Use of solder in an already crimped terminal serves to
increase the electrical contact area, thats good, and to
preclude corrosive gases, vapors and oils from the joint (by
wicking up the bare wire).... that is seen commonly be the
cause of failure in those situations.


For the last 100 years... and currently.... most if not all
controls systems and component manufacturers dip wire ends in
solder that are to be fit under screw head connectors... the
practice is at least 90% common.... thats with *control
circuits.

The practice is not common with power circuits for the reasons
mentioned but is still seen in some situations (primarily
corrosive environments... anyone can purchase NEC approved
soldered connectors of course for those purposes... those are
also pervasively common, especially in the electronics
industry.)

..

220,000 hits... lots of good articles on the first page.
http://www.google.com/search?hl=en&q...=Google+Search

There is a time and a place to solder crimped or non crimped
terminals and bare wire ends to be fit under a screw head....
and a time when that is not a good idea (hot running
situations, although Ive seen pure silver or brassed
connections in those locations)



Phil Scott
Mechanical/ Electrical engineer and industrial controls
contractor since 1852 (I'm very old)