Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
 
Posts: n/a
Default Question about combustion air input on a high efficienct furnace.

wrote:

... I remain skeptical that infiltration induced by non-sealed furnace
combustion will significantly decrease the overall exterior temperature
of conventionally built exterior walls


You may be right.

or make them perform like these Scandanavian walls of which you speak...
It seems to me that even if unidirectional infiltration (i.e. enter
through wall, exit through furnace exhaust stack) were to reduce the
wall exterior surface temperature to outside temp so as to eliminate
heat loss from that surface, it wouldn't eliminate heat loss to the
outdoors altogether. The heat-losing surface has simply relocated to
somewhere within the wall or the living space.


I've run into that kind of problem when thinking about how to preheat the
air that flows in through the wall with outgoing air, using a large poly
film air-air heat exchanger built into the wall. Maybe the heat exchanger
and incoming air filter need to be inside a 4' cube filled with poly film
"plates" on 1/2 inch centers, or several cubes or valances near ceilings.

... If a uniform sheet of outdoor air is slowly flowing towards you from
a wall (at a velocity less than a perceptible draft), you can't lose any
heat to that wall by convection, because the warm air won't travel upwind.
You can still lose heat by radiation to the wall, and it still takes power
to heat the air that flows in through the wall, but the heat loss by
convection through the wall can be close to zero...


http://www.cibse.org/pdfs/8cimbabi.pdf has an equation for the dynamic
metric U-value of a breathing wall, as corrected:

Ud = VRhoaCa/(e^(VRhoaCaRs)-1) W/m^2K, where

V is the air velocity in meters per second,
Rhoa is air density, 1.2 kg/m^3,
Ca is the air's specific heat, 1000 J/(kg-K), and
Rs is the wall's static thermal resistance in m^2-K/W.

Using V = 1/3600 (1 meter per HOUR :-), and Rs = 5.7 m^2K/W (a US R32 wall),
Ud = 0.058 W/m^2, like a US R98 wall. A more typical V = 10 meters per hour
makes Ud = 1.7x10^-8 W/m^2K, like a US wall with an R-value of 334 million :-)

Ud becomes infinite as V becomes 0, which seems odd. And Ud approaches 0 as
V increases, no matter what kind of porous insulation is used. I'm surprised
to see 40 mm (about 1.6 inches) in the pdf. That seems very thick. I thought
Scandinavian breathing walls used something closer to 1/4 inch felt. Would
a single layer of Tyvek or Typar wind barrier work, with a replaceable air
filter? Typar seems to have too much pneumatic resistance. Maybe perforated
"builder's foil." Bucky Fuller wanted to minimize building materials...

With an air-air heat exchanger, we might move, say 240 cfm through 4000 ft^2
of walls and ceilings of a 40x60' house at V = 240/4000 = 0.06 fpm, ie 3.05
x 10^-4 m/s, giving a US R20 (metric R3.5) wall Ud = 1200V/(e^(1200V3.5)-1)
= 0.141 W/m^2K, like a US R40 wall. Doubling V might make it an R93 wall, if
the house were otherwise airtight (a big if, in the US.)

Nick

  #2   Report Post  
 
Posts: n/a
Default Question about combustion air input on a high efficienct furnace.

wrote:

http://www.cibse.org/pdfs/8cimbabi.pdf has an equation for the dynamic
metric U-value of a breathing wall, as corrected:

Ud = VRhoaCa/(e^(VRhoaCaRs)-1) W/m^2K, where

V is the air velocity in meters per second,
Rhoa is air density, 1.2 kg/m^3,
Ca is the air's specific heat, 1000 J/(kg-K), and
Rs is the wall's static thermal resistance in m^2-K/W.

Using V = 1/3600 (1 meter per HOUR :-), and Rs = 5.7 m^2K/W (a US R32 wall),
Ud = 0.058 W/m^2, like a US R98 wall. A more typical V = 10 meters per hour
makes Ud = 1.7x10^-8 W/m^2K, like a US wall with an R-value of 334 million :-)

Ud becomes infinite as V becomes 0, which seems odd...


No... it approaches 1/Rs, like it orta, as e^x -- 1+x :-) For instance,
Rs = 5 and V = 10^-8 makes Ud = 1.2x10^-5/(e^(6x10^-5)-1) = 0.19994...

Profs Imbabi and friends at http://www.environmental-building.com
are now testing a commercial "dynamic breathing wall" product in
Scotland, Holland, Italy and Dubai. Coming soon to the US
(in February in Houston.)

Nick

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
high pitch noise from furnace Bill Home Repair 2 January 29th 04 07:16 PM
forced air furnace blower high or low? barb gee Home Repair 5 January 27th 04 05:16 PM
York Furnace Filter (High velocity)? computer_prog Home Repair 0 January 17th 04 08:16 PM
Is it worth upgrading to High Efficiency furnace? kevins_news Home Repair 49 January 9th 04 05:42 AM
Homebuilding High Temp Furnace. Roger N Metalworking 16 September 3rd 03 06:56 PM


All times are GMT +1. The time now is 03:31 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"