Property is in south Florida Miami, so the temperature rise is not as much
as other locations.

I am looking to get a Stiebel Eltron Tempra 36. It will give me 4.5GPM with
55 degree rise. This will do what I need being a 2 bath house. The
technical specs a

Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper

I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that goes to
the current (to be replaced) hot water tank. My electric meter outside has
this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30

Not sure what some of those mean. Can one tell if what I have matches up
with what is needed? What electrical service do I need, if any?

Thanks,

MC


  #2   Report Post  
Edwin Pawlowski
 
Posts: n/a
Default


"miamicuse" wrote in message
I am looking to get a Stiebel Eltron Tempra 36.
Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper



That should be 15A 3600 divided by 240 = 15


I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that goes
to
the current (to be replaced) hot water tank. My electric meter outside
has
this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30


The meter does not matter, but the main breaker does. It is 200A? if so,
you have plenty of power coming itn. The blank spots may be used.
Depending on the existig wire, that may or may not be used. An electrician
can tell you what size it is. It may be printed on the insulation.


Not sure what some of those mean. Can one tell if what I have matches up
with what is needed? What electrical service do I need, if any?


You most likely have what you need for power. Your electrician will supply
the proper breaker and wire. It would be a good idea to have him check it
out before you buy the new heater though.


  #3   Report Post  
miamicuse
 
Posts: n/a
Default

"Edwin Pawlowski" wrote in message
.. .

"miamicuse" wrote in message
I am looking to get a Stiebel Eltron Tempra 36.
Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper



That should be 15A 3600 divided by 240 = 15


I rechecked the data sheet it says 150A.

It has several models:

Tempra 12 needs 50A, Tempra 20 needs 80 A, 24 needs 100 A, 29 needs 120 A
and 36 needs 150 A.

Unless the document is in error? You can see the data he

http://www.stiebel-eltron-usa.com/HT...e20_specs.html


I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that goes
to
the current (to be replaced) hot water tank. My electric meter outside
has
this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30


The meter does not matter, but the main breaker does. It is 200A? if so,
you have plenty of power coming itn. The blank spots may be used.
Depending on the existig wire, that may or may not be used. An

electrician
can tell you what size it is. It may be printed on the insulation.


Not sure what some of those mean. Can one tell if what I have matches

up
with what is needed? What electrical service do I need, if any?


You most likely have what you need for power. Your electrician will supply
the proper breaker and wire. It would be a good idea to have him check it
out before you buy the new heater though.




  #4   Report Post  
Olaf
 
Posts: n/a
Default


"Edwin Pawlowski" wrote in message
.. .

"miamicuse" wrote in message
I am looking to get a Stiebel Eltron Tempra 36.
Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper



That should be 15A 3600 divided by 240 = 15


36 kW = 36000

36000 / 240 = 150

Holy **** I think I'd rather have a tank if there was room.




I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that goes
to
the current (to be replaced) hot water tank. My electric meter outside
has
this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30


The meter does not matter, but the main breaker does. It is 200A? if so,
you have plenty of power coming itn. The blank spots may be used.
Depending on the existig wire, that may or may not be used. An

electrician
can tell you what size it is. It may be printed on the insulation.


Not sure what some of those mean. Can one tell if what I have matches

up
with what is needed? What electrical service do I need, if any?


You most likely have what you need for power. Your electrician will supply
the proper breaker and wire. It would be a good idea to have him check it
out before you buy the new heater though.




  #5   Report Post  
Edwin Pawlowski
 
Posts: n/a
Default


"Olaf" wrote in message

That should be 15A 3600 divided by 240 = 15


36 kW = 36000

36000 / 240 = 150

Holy **** I think I'd rather have a tank if there was room.


Yes, I dropped a zero. Crap, that is a LOT of power. No, the OP does have
enough power to the house to do that.




  #6   Report Post  
miamicuse
 
Posts: n/a
Default

Do I really have enough power or does it depend on what appliances may be
drawing power at the same time (refrig, microwave, AC etc...)?

MC

"Edwin Pawlowski" wrote in message
.. .

"Olaf" wrote in message

That should be 15A 3600 divided by 240 = 15


36 kW = 36000

36000 / 240 = 150

Holy **** I think I'd rather have a tank if there was room.


Yes, I dropped a zero. Crap, that is a LOT of power. No, the OP does have
enough power to the house to do that.




  #7   Report Post  
Harry
 
Posts: n/a
Default

Tankless water heaters come in electric and gas versions.

For an electric one - you need a very heavy power line directly to the
unit. The unit is small but it calls for a lot of power when it snaps on.

The gas version is very nice - above two cubic feet. The ones we looked
at cost around $2000 - but they tested out well. Very efficient - plenty
of hot water when you want it.

Here is Tallahassee - the city own the electric and gas company. They
offer a rebate of $450 for every water heater you convert from electric
or gas - probably to cut down on peak loads. Since our home has two
electric water heaters - we plan to convert them over to gas and get a
$900 rebate - which will more than cover the conversion if we put
conventional gas tank heaters in.

When the energy auditor was here - he figured the pay back for putting
in two tankless gas heaters was over 10 years. If we chose the tank gas
water heaters and the rebates - payback would be immediate.

I really like the tankless gas units - but right now will chose tank gas
water heaters.

Harry
  #8   Report Post  
Olaf
 
Posts: n/a
Default


"miamicuse" wrote in message
...
Do I really have enough power or does it depend on what appliances may be
drawing power at the same time (refrig, microwave, AC etc...)?

MC

"Edwin Pawlowski" wrote in message
.. .

"Olaf" wrote in message

That should be 15A 3600 divided by 240 = 15

36 kW = 36000

36000 / 240 = 150

Holy **** I think I'd rather have a tank if there was room.


Yes, I dropped a zero. Crap, that is a LOT of power. No, the OP does

have
enough power to the house to do that.





It really depends on how many amps are available from the main panel. Even a
200 amp panel would not be able to handle that heater realistically unless
there were no other heavy load 220 appliances (like a range, water heater,
dryer, etc.) . My guess is that each 60 amp breaker would be hooked to
separate heaters within the unit. the heater will turn on as many heaters as
necessary to heat up to the 4.5 gpm.


  #9   Report Post  
Olaf
 
Posts: n/a
Default


"Olaf" wrote in message
...

"miamicuse" wrote in message
...
Do I really have enough power or does it depend on what appliances may

be
drawing power at the same time (refrig, microwave, AC etc...)?

MC

"Edwin Pawlowski" wrote in message
.. .

"Olaf" wrote in message

That should be 15A 3600 divided by 240 = 15

36 kW = 36000

36000 / 240 = 150

Holy **** I think I'd rather have a tank if there was room.

Yes, I dropped a zero. Crap, that is a LOT of power. No, the OP does

have
enough power to the house to do that.





It really depends on how many amps are available from the main panel. Even

a
200 amp panel would not be able to handle that heater realistically unless
there were no other heavy load 220 appliances (like a range, water heater,
dryer, etc.) . My guess is that each 60 amp breaker would be hooked to
separate heaters within the unit. the heater will turn on as many heaters

as
necessary to heat up to the 4.5 gpm.



Oops, that was supposed to be a response to the OP. No biggie.

I can just imagine the lights dimming when someone jumps in the shower or
fills the tub.


  #10   Report Post  
Richard J Kinch
 
Posts: n/a
Default

miamicuse writes:

I don't know if I have the proper electrical set up.


You don't. This is a bad idea in general. It will be much cheaper and
safer to use conventional water heaters.


  #11   Report Post  
Joseph Meehan
 
Posts: n/a
Default

miamicuse wrote:
Property is in south Florida Miami, so the temperature rise is not as
much as other locations.

I am looking to get a Stiebel Eltron Tempra 36. It will give me
4.5GPM with 55 degree rise. This will do what I need being a 2 bath
house. The technical specs a

Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper

I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that
goes to the current (to be replaced) hot water tank. My electric
meter outside has this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30

Not sure what some of those mean. Can one tell if what I have
matches up with what is needed? What electrical service do I need,
if any?

Thanks,

MC


You have already worked out the numbers and you know you are going to
need some additional electrical work to use this puppy. They are nice, but
they use an extreme amount of power for short periods of time. The cost of
operation (ignoring cost of replacement and maintenance cost) is going to be
less than the like cost of the usual tank type heater. The overall cost
however is not likely to be less unless you have some other factors like
limited space, unique usage cycles etc.

--
Joseph Meehan

Dia duit


  #12   Report Post  
RBM
 
Posts: n/a
Default

What this unit requires is three sets of two cables each. Each set connected
to a 60 amp double pole breaker. Your 200 amp service would be fine ONLY if
you didn't need electricity for the rest of your house



"miamicuse" wrote in message
...
Property is in south Florida Miami, so the temperature rise is not as much
as other locations.

I am looking to get a Stiebel Eltron Tempra 36. It will give me 4.5GPM
with
55 degree rise. This will do what I need being a 2 bath house. The
technical specs a

Voltage 240 V
Wattage 36 kW
Amperage 150 A
Minimum Required Circuit Breaker Size 3x60 A
Recommended Wire Size 3x8 AWG Copper

I don't know if I have the proper electrical set up. I have four more
unused slots in my electrical panel, there is an existing wire that goes
to
the current (to be replaced) hot water tank. My electric meter outside
has
this:

120/240V AC
3 WIRE
MAX 200 AMP
CL 200 * 240V * 3W * FM2S * TA30

Not sure what some of those mean. Can one tell if what I have matches up
with what is needed? What electrical service do I need, if any?

Thanks,

MC




  #13   Report Post  
z
 
Posts: n/a
Default


Richard J Kinch wrote:
miamicuse writes:

I don't know if I have the proper electrical set up.


You don't. This is a bad idea in general. It will be much cheaper and
safer to use conventional water heaters.


Yeah, according to Consumer Reports, conventional water heaters these
days are well enough insulated that the majority of the energy goes
into heating the water, and not much into replacing leaked heat, given
a normal amount of use per day. My "experiments" with turning the
heater off and not noticing a difference in water temp the next day
tend to confirm this. In which case, you wouldn't save much at all from
a tankless heater.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AquaTherm Furnace - No Hot Water Issue David Home Repair 11 January 25th 18 08:44 PM
Tankless water heaters Edward Grant Home Repair 11 September 13th 05 12:42 AM
Power cost of idle electric water heater Phil Sherrod Home Ownership 50 April 2nd 04 04:55 PM
Thankless or Tankless hot water heaters [email protected] Home Repair 6 January 29th 04 03:01 AM
Flushing / Cleaning Hot Water Heater Help Needed Cuse Home Repair 38 December 1st 03 02:01 AM


All times are GMT +1. The time now is 04:04 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"