  #1   Report Post  
OldSalt
 
Posts: n/a
Default Carrier hp system install nightmare

We live in the panhandle of Florida. We have a two story house and had
a 30 year old 4 ton system. We upgraded to two 2ton Carrier infinity
systems. The upstairs unit does not cool properly. The unit comes on
about 10am and runs all day on max until about 11pm. Some things I
have noticed is that they installed the thermostat at the top of the
stairs. seems to me that would be a hotshot that also has no
registers. Second the coolant line running from the compressor is 68
feet in length. reading the install instructions that came with the
units it states that vapor line lengths in excess of 50 feet require
up sizing from 5/8 to 3/4. This was not done. Also the vapor line had
6 (yes 6) 90degree elbows. three of these elbows were at the air
handler. They ran the tubing up 8 in. past the air handler connection
then used three elbows to loop back down and into the air handler.
There reply is that Carrier told them to do it. They could not say
why!! At least two of the other elbows could have been eliminated in
this run. The first floor unit was installed in the cabinet flush
against the side wall covering up the dedicated 110 receptacle for the
electronic air filter. the installer now wants to rewire the
electrical disconnect to add another receptacle.

Now I'm paying a very large amount of money for all this. Is this the
quality workmanship acceptable? The warrantee will run out before we
get this payed off.

If there is any one here that is a Carrier dealer/ installer could you
answer:

Should 3/4 tubing been used? Is it necessary for the tubing be looped
up, over and back down at the air handler?? Should I move the
thermostat to another room?

Thanks for your time
  #2   Report Post  
SQLit
 
Posts: n/a
Default


"OldSalt" wrote in message
...
We live in the panhandle of Florida. We have a two story house and had
a 30 year old 4 ton system. We upgraded to two 2ton Carrier infinity
systems. The upstairs unit does not cool properly.



Were manual calculation done? It is pretty typical for the upstairs to be
hotter, heat rises. I once saw a guy put a 5 and 2 on a two story home. The
small unit cooled the master bedroom and it never shut off in the summer. We
ended up remodeling a new home to put doors at the top of the stairs to
solve the problem. Home owner did not want to cut the exterior walls.



The unit comes on
about 10am and runs all day on max until about 11pm. Some things I
have noticed is that they installed the thermostat at the top of the
stairs. seems to me that would be a hotshot that also has no
registers.


T-stats are usually located under the return air.


Second the coolant line running from the compressor is 68
feet in length. reading the install instructions that came with the
units it states that vapor line lengths in excess of 50 feet require
up sizing from 5/8 to 3/4. This was not done.


Not following the manufacture instructions is always a good way to void the
warranty.


Also the vapor line had
6 (yes 6) 90degree elbows. three of these elbows were at the air
handler. They ran the tubing up 8 in. past the air handler connection
then used three elbows to loop back down and into the air handler.
There reply is that Carrier told them to do it. They could not say
why!! At least two of the other elbows could have been eliminated in
this run. The first floor unit was installed in the cabinet flush
against the side wall covering up the dedicated 110 receptacle for the
electronic air filter. the installer now wants to rewire the
electrical disconnect to add another receptacle.

Now I'm paying a very large amount of money for all this. Is this the
quality workmanship acceptable? The warrantee will run out before we
get this payed off.


Workmanship is a sore point for a lot of people. What is acceptable for one
is not for another.
Covering the outlet is a code violation.

Were there permits pulled? Has there been an inspection? If you have not
paid them do not until they make everything right.


If there is any one here that is a Carrier dealer/ installer could you
answer:

Should 3/4 tubing been used? Is it necessary for the tubing be looped
up, over and back down at the air handler?? Should I move the
thermostat to another room?


I have seen some pretty ugly air handler runs. But never one with as many
90's as you describe. Smells of inexperence or lack of knowlege.




Thanks for your time



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Baxi 'System' Boiler - pressure question kmillar UK diy 6 February 4th 05 04:35 PM
Sealed heating system design/conversion - Cue Ed or Andy H Set Square UK diy 8 February 4th 05 10:53 AM
more fun with air conditioning J Jensen Home Repair 93 September 7th 04 10:39 AM
more fun with air conditioning J Jensen Home Ownership 56 September 7th 04 06:20 AM
Central A/C cooling fine but humidity seems high D- Home Repair 6 July 3rd 03 08:40 PM


All times are GMT +1. The time now is 01:04 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"