I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr

  #2   Report Post  
zxcvbob
 
Posts: n/a
Default

wrote:

I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr



There's not a lot of difference between a 150A and a 200A service. If
you have anything over 100A, it's probably plenty unless you have a
*huge* house and have electric heating, electric water heater, and
electric stove. I've neve seen a 160A service (is is fuses?) but
there's not a lot to gain by going to 200A, and there probably would be
a lot of expense.

It sounds like someone finished the basement after the house was wired
and they just tapped into the kitchen circuit -- that's very bad. The
kitchen should have 2 *dedicated* 20A circuits, although an older house
might just have one. Nothing else should be on the kitchen circuit
except perhaps a convenience outlet in the dining room. If you split
the basement wiring from the kitchen circuit and put in a new breaker
for the basement, I think it will solve all your problems. If you
replace the 160A panel with a 200A but do not fix the kitchen wiring
problem, it's not going to help.

There are other reasons to replace an electric panel, like maybe if it's
an old Federal Pacific panel with StabLok breakers, or if you just ran
out of spaces. But you wouldn't necessarily have to go with a 200A main
breaker.

Best regards,
Bob
  #3   Report Post  
 
Posts: n/a
Default

We don't have enough details to say if you really need a bigger service
panel. Certainly, if you ever have ti replaced it's probably a good
idea to do so, but not knowing exactly how big the current load is it's
impossible to say over the internet.

Also, in my kitchen I have my microwave on it's own circuit, my
dishwasher on it's own circuit, my toaster oven in it's own circuit,
refrigerator on it's own circuit, and everything else on another
circuit (oven is gas oven). You clearly need more going to the kitchen
unless you don't have things like a dishwasher or microwave, etc.

I don't know what brand of panel OP has, but if he had a FP panel, his
A/C wouldn't be tripping. They are famous for not tripping. D-oh.

  #5   Report Post  
SQLit
 
Posts: n/a
Default


wrote in message
oups.com...
I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr


Not my intention to slam you

Unless your service was custom made there is no such thing as a 160 amp
service.

Unless your adding a new electrical load(s) chances are you do not need a
new service. What you do need is to fix the screw ups from the previous
owner or you as the case may be. A load calculation would be required to
know if you need a new service. If you just bought this place then it
might be time to use the contract to get the previous owner to pay for the
"not to code wiring". Which would need to be disclosed by law at least here
it would.

As others said if you change the service and do not fix the circuitry then
you have not fixed the problem.

Home infectors that use "heavy up" should be shown to the property line with
a double barreled shotgun. Home infectors in general should be shown to the
property line.

Call some licensed, insured and bonded pros and ask for bids to straighten
out the mess.




  #6   Report Post  
Paddlepop
 
Posts: n/a
Default

You ARE KIDDING
wrote in message
oups.com...
I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr



  #7   Report Post  
ccs>ikyr
 
Posts: n/a
Default

Well, the owner wrote "160A" on the service panel, or someone did. I
imagine they meant 150. In fact, on closer inspection, it says "200
Amp Mains", but the 200 is scratched out and 160 is written above it.
Don't know what to make of that.

Previous owner was a real piece of work. As I noted previously, the
basement (excluding the washer/drier and furnace) is run off the
kitchen circuit. What's more, because there's only one outlet in the
basement, this clown had brown appliance wire extension cords running
all over the basement, tacked to the underside of the floor joists, and
plugged into the light sockets. I ripped that garbage out on the first
day. Lucky for me, he didn't make many of these "improvements" or I
would be lying awake at night wondering if the house would burn down by
morning.

Yes, I intend to have a professional take a look around.

Thank you all for your guidance.

  #8   Report Post  
Bill
 
Posts: n/a
Default

Just get a separate circuit installed to the microwave and another to the
basement.

If you have problems with the *main* breaker tripping, then that is when
you would need to consider a larger service.

Of if replacing the main panel due to not enough breaker slots or whatever,
then not much more expensive to go to 200 amps at that time.

Otherwise what you have now is probably good.

FYI - You probably have a main breaker. Look (carefully) for a number on
the breaker (just like the individual breakers will say 15, 20, etc.) Also
look at the number of breakers which are tied together for the main
breaker - could be two breakers or four breakers. Post the info here.


wrote in message
I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr



  #9   Report Post  
Chris
 
Posts: n/a
Default

I'd question anything just hand written. Look for a manufacturers
stamp and check the main breaker rating. I think you have a potential
fire trap going - don't be alarmed, just be careful. If you DO have
excessive amperage and a breaker fails, the wiring heats up until it
something bad happens - lot's of older homes and trailers have gone up
in flames because of faulty wiring. Your kitchen for example, by now
days code would have two dedicated 20amp breakers just for appliance
loads, etc. One for your refrigerator, one for your dishwasher for
example, and then the general branch circuit that is limited by so
many receptacles per breaker.

The only reason I might JUMP and replace the panel would be if the
panel were outdated with obsolete breakers, etc. Otherwise, it sounds
like the lion's share of your issues is not at the panel but rather,
in the field (wiring within your house). Doesn't hurt to have an
amprobe either. This would allow you to read the amperage of the
individual branch circuits to determine if it's a load problem or a
breaker problem (takes a lot of guess work out).

Finally, breakers USED to be guaranteed for only one trip. In other
words, damage from a single trip could damage a breaker making it
unreliable for future trips - all the more reason to purchase an
ampprobe (AC amp meter) to help come to the right conclusions.

Best of luck... Make good decisions and it'll turn out...

Chris

On 25 Aug 2005 10:56:41 -0700, wrote:

I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr

  #10   Report Post  
SQLit
 
Posts: n/a
Default


"ccsikyr" wrote in message
ups.com...
Well, the owner wrote "160A" on the service panel, or someone did. I
imagine they meant 150. In fact, on closer inspection, it says "200
Amp Mains", but the 200 is scratched out and 160 is written above it.
Don't know what to make of that.


I would be checking it out, ASAP. What does the main breaker say? ( on the
handle there should be a number )
They might have added up the breakers inside the panel, ignorant mistake.



Previous owner was a real piece of work. As I noted previously, the
basement (excluding the washer/drier and furnace) is run off the
kitchen circuit. What's more, because there's only one outlet in the
basement, this clown had brown appliance wire extension cords running
all over the basement, tacked to the underside of the floor joists, and
plugged into the light sockets. I ripped that garbage out on the first
day. Lucky for me, he didn't make many of these "improvements" or I
would be lying awake at night wondering if the house would burn down by
morning.

Yes, I intend to have a professional take a look around.

Thank you all for your guidance.






  #11   Report Post  
Chip C
 
Posts: n/a
Default


wrote:
I wonder if some kind soul could check my understanding of how to
evaluate whether I need to "heavy up" my electrical service box.

I currently have a box identified as 160A, with thirty circuits.

The home inspector I used when I bought the place said "you're going to
want to heavy up to 200A".

I'm not so sure.

The breaker for the kitchen appliances trips every so often, but that's
likely because the entire basement is also on that circuit, and there's
a dehumidifier down there. By chance, it occasionally kicks in when
the microwave and toaster are on and overloads the circuit.

Since I have five unused circuits, I figure I can split the basement
and the kitchen on to separate circuits, and add an extra kitchen
appliance circuit for good measure, and one for the basement workshop
tools.

The A/C circuit trips, too, but I believe that's because the A/C is
dying.

The way I see it, and this is my question, as long as the load on no
individual circuit exceeds it's rated amperage, and the load on all
circuits collectively does not exceed 160A, which is the size of the
box, I don't need to "heavy up".

Is that correct?

Thanks for any comments.

ccsikyr


Find your main breakers or fuses and see what they say on them. That's
what tells you how many amps your service is. Like the other posters I
haven't heard of 160A but there's lots I haven't heard of. 150A is now
common but it's odd your electrician would recommend upgrading 150 to
200, and 30 circuits seems kind of low. I'm wondering if you have
*sixty* amp service, which is the very common old level for homes that
don't have electric heat. (The water heater, if electric, may be on an
unmetered flat rate feed that bypasses the panel).

If you can't find your main breakers or fuses, have your electrician
find them pronto. In this house I inherited an old 60A PushMatic panel
with *no* main cutoff. My electrician only wanted to upgrade to 100 but
I insisted on 200.

Chip C
Toronto

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
OT - Global Warming (Was "Lying Liberals.") wmbjk Metalworking 6 June 17th 05 08:11 AM
Electrical Panel Question James \Cubby\ Culbertson Home Repair 21 January 10th 05 06:14 AM
Panel Box Electrical Question HotRod Home Repair 5 January 7th 05 02:11 PM
Help upgrading Service panel from 60A to 125A, please. DaveG Home Repair 33 December 3rd 03 03:57 AM
New Electrical Regs PoP UK diy 22 September 1st 03 08:41 PM


All times are GMT +1. The time now is 12:27 PM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"