Home |
Search |
Today's Posts |
![]() |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
|
#1
![]() |
|||
|
|||
![]()
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.
This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Reason is I have plenty of (free) #10 on hand and tube capacity is slightly better with #10's. thanks bill |
#2
![]() |
|||
|
|||
![]()
I guess derating would apply (6x 10ga THHN +8ga grounding) , in which case a
50a breaker may suffice? bill "rider89" wrote in message .. . wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT. This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Reason is I have plenty of (free) #10 on hand and tube capacity is slightly better with #10's. thanks bill |
#3
![]() |
|||
|
|||
![]()
In article , "rider89" wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT. This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Yes, there is. Section 310-4 explicitly *permits* parallelling conductors of size 1/0 or *larger*, and thus by implication prohibits it for smaller conductors. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#4
![]() |
|||
|
|||
![]()
bummer..
thanks doug bill "Doug Miller" wrote in message .. . In article , "rider89" wrote: wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT. This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Yes, there is. Section 310-4 explicitly *permits* parallelling conductors of size 1/0 or *larger*, and thus by implication prohibits it for smaller conductors. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#5
![]() |
|||
|
|||
![]()
Just wonder why parallel wires are permitted for #10 and lower and
prohibited for smaller wire sizes? |
#6
![]() |
|||
|
|||
![]()
i would imagine that the theory is that smaller wire sizes are too easy to
tinker with regarding the clamping hardware at breakers, etc. If one of the parallel wires became disconnected, there could be a severe overload on the remaining conductor. Bill "Sasha" wrote in message ups.com... Just wonder why parallel wires are permitted for #10 and lower and prohibited for smaller wire sizes? |
#7
![]() |
|||
|
|||
![]()
rider89 wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT. This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Reason is I have plenty of (free) #10 on hand and tube capacity is slightly better with #10's. thanks bill 310.4 Conductors in Parallel. Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor). copyright 2002 National Fire Protection Association. -- Tom Horne Well we aren't no thin blue heroes and yet we aren't no blackguards to. We're just working men and woman most remarkable like you. |
#8
![]() |
|||
|
|||
![]()
According to HorneTD :
rider89 wrote: wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT. This may be a stupid question, but is there anything in the NEC to prohibit using double #10's to get the amperage? Reason is I have plenty of (free) #10 on hand and tube capacity is slightly better with #10's. 310.4 Conductors in Parallel. Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor). Does it not also say that _each_ conductor must be the same size, and each capable of carrying the full breaker current? [Our code does.] Which basically means you can parallel conductors to reduce end-to-end resistance (voltage drop), but NOT to increase circuit ampacity. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Electric baseboard heat question | Home Repair | |||
Electric baseboard heat question | Home Ownership | |||
Yale Electric Chain Hoist Question | Metalworking | |||
Grizzly electric 5 hp motor question..... Problem.... Weard..... | Metalworking | |||
Electrical service question - old house, new addition - expert advice needed | Home Repair |