rider89 August 21st 05 07:30 PM

branch electric box question
 
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to prohibit
using double #10's to get the amperage?
Reason is I have plenty of (free) #10 on hand and tube capacity is slightly
better with #10's.

thanks
bill


rider89 August 21st 05 07:49 PM

I guess derating would apply (6x 10ga THHN +8ga grounding) , in which case a
50a breaker may suffice?


bill


"rider89" wrote in message
.. .
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to
prohibit using double #10's to get the amperage?
Reason is I have plenty of (free) #10 on hand and tube capacity is
slightly better with #10's.

thanks
bill



Doug Miller August 21st 05 08:18 PM

In article , "rider89" wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to prohibit
using double #10's to get the amperage?


Yes, there is. Section 310-4 explicitly *permits* parallelling conductors of
size 1/0 or *larger*, and thus by implication prohibits it for smaller
conductors.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

rider89 August 21st 05 08:49 PM

bummer..

thanks doug

bill

"Doug Miller" wrote in message
.. .
In article , "rider89"
wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to
prohibit
using double #10's to get the amperage?


Yes, there is. Section 310-4 explicitly *permits* parallelling conductors
of
size 1/0 or *larger*, and thus by implication prohibits it for smaller
conductors.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.



HorneTD August 22nd 05 05:43 AM

rider89 wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to
prohibit using double #10's to get the amperage?
Reason is I have plenty of (free) #10 on hand and tube capacity is
slightly better with #10's.

thanks
bill


310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and
larger, comprising each phase, neutral, or grounded circuit conductor,
shall be permitted to be connected in parallel (electrically joined at
both ends to form a single conductor). copyright 2002 National Fire
Protection Association.
--
Tom Horne


Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.

Sasha August 22nd 05 01:12 PM

Just wonder why parallel wires are permitted for #10 and lower and
prohibited for smaller wire sizes?


rider89 August 22nd 05 04:15 PM

i would imagine that the theory is that smaller wire sizes are too easy to
tinker with regarding the clamping hardware at breakers, etc.
If one of the parallel wires became disconnected, there could be a severe
overload on the remaining conductor.
Bill

"Sasha" wrote in message
ups.com...
Just wonder why parallel wires are permitted for #10 and lower and
prohibited for smaller wire sizes?



Chris Lewis August 23rd 05 06:39 PM

According to HorneTD :
rider89 wrote:
wanting to feed a branch box with a 60a breaker (#6 copper) thru EMT.

This may be a stupid question, but is there anything in the NEC to
prohibit using double #10's to get the amperage?
Reason is I have plenty of (free) #10 on hand and tube capacity is
slightly better with #10's.


310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and
larger, comprising each phase, neutral, or grounded circuit conductor,
shall be permitted to be connected in parallel (electrically joined at
both ends to form a single conductor).


Does it not also say that _each_ conductor must be the same size, and
each capable of carrying the full breaker current?

[Our code does.]

Which basically means you can parallel conductors to reduce end-to-end
resistance (voltage drop), but NOT to increase circuit ampacity.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.

Chris Lewis August 26th 05 09:12 PM

According to :
On Tue, 23 Aug 2005 17:39:59 -0000, (Chris
Lewis) wrote:

Does it not also say that _each_ conductor must be the same size, and
each capable of carrying the full breaker current?

[Our code does.]

Which basically means you can parallel conductors to reduce end-to-end
resistance (voltage drop), but NOT to increase circuit ampacity.


No you add the ampacity of paralleled conductors but bear in mind they
must be 1/0 or larger (about 10mm).
The reason you can parallel conductors is to use a size that is more
easily handled in large ampacity circuits.


As I mentioned, _not_ in our code.

You can only parallel conductors to decrease voltage drop. The individual
conductors must still be large enough to take the full ampacity.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.

SQLit August 26th 05 09:20 PM


"Chris Lewis" wrote in message
...
According to :
On Tue, 23 Aug 2005 17:39:59 -0000, (Chris
Lewis) wrote:

Does it not also say that _each_ conductor must be the same size, and
each capable of carrying the full breaker current?

[Our code does.]

Which basically means you can parallel conductors to reduce end-to-end
resistance (voltage drop), but NOT to increase circuit ampacity.


No you add the ampacity of paralleled conductors but bear in mind they
must be 1/0 or larger (about 10mm).
The reason you can parallel conductors is to use a size that is more
easily handled in large ampacity circuits.


As I mentioned, _not_ in our code.

You can only parallel conductors to decrease voltage drop. The individual
conductors must still be large enough to take the full ampacity.


What code do you operate under?

I can not imagine trying to pull a conductor for a 2000 amp service. We
parallel conductors for load all of the time. It is not practical to use
any conductor larger than 1000 circular mills. I just do not have the sand
in the ass any more to handle wire that big.
Commonly 750 mcm is the largest conductor used where I live.