I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing)
with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver |
#2
|
|||
|
|||
"Jim Beaver" writes:
I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? One more option, that I'd consider as more likely than a panel or wiring issue: the air conditioning compressor's start up current may be unusually large (perhaps out of spec) and exceeding the rating of the service momentarily. However, I'd call the electric company and put the onus on them--their transformer may not be doing its job and might be the root cause of your house voltage wilting under teh start up load of your A/C compressor. They should have a voltage recorder that you can use in your home that can quantify the problem. This can be tricky to diagnose though, and fingerpointing will surely be involved, and perhaps a visit from an electrician and/or an HVAC guy. In the mean time, I'd check into the an APC Smart UPS with brownout/sag protection for that computer in a hurry. It's nice to have, regardless. Best Regards, -- Todd H. http://www.toddh.net/ |
#3
|
|||
|
|||
Jim Beaver wrote:
I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver You might want to verify the various wire connections in the panel are tight and well connected (but only if you are comfortable with things electrical) A bad connection will cause a voltage drop under load. begin sidebar By any chance... are you using Aluminum wire? If so, i highly recommend you rip it all out and get what you can for scrap price out of it. AL is ok in very large sizes (as long as its correctly installed with proper torque and an anti-oxidant on good clean connections), oh say above 00 but even still, I'd go all copper if i possibly could. end sidebar I really doubt its a utility transformer problem, but I'll bet dimes to donuts its either a bad main breaker or a bad connection in your panel, either at the mains, the meter or one of the bus bars in the panel. Eric |
#4
|
|||
|
|||
Jim Beaver wrote:
I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver Are those lights on the same circuit as the A/C? If your a/c was drawing unusually high current I would expect occasional breaker trips. Anything that does not trip the breaker should be suppliable by the transformer. I would call power company. Also high chance of loose connection, which is dangerous. -- Respectfully, CL Gilbert |
#5
|
|||
|
|||
"Jim Beaver" wrote in message ... I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver Hard to point you in a direction. Can you measure the voltage at the panel? What is it? What is it when the a/c starts? I would do this before you call the utility. They will be not surprisingly SLOW to respond to something vague like this. Other poster have suggested that checking the connections in the panel would be a good idea. I concur. Was the panel changed/moved for the remodel? Was any work done near the grounding of the panel? Water/gas bond still connected? Is the ground still connected? If your the only load on the transformer then MAYBE it is unique to your home. Odds are it is on your side. |
#6
|
|||
|
|||
"SQLit" wrote in message ... "Jim Beaver" wrote in message ... I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver Hard to point you in a direction. Can you measure the voltage at the panel? What is it? What is it when the a/c starts? I would do this before you call the utility. They will be not surprisingly SLOW to respond to something vague like this. Other poster have suggested that checking the connections in the panel would be a good idea. I concur. Was the panel changed/moved for the remodel? Was any work done near the grounding of the panel? Water/gas bond still connected? Is the ground still connected? If your the only load on the transformer then MAYBE it is unique to your home. Odds are it is on your side. Normally, when you have this, dimming when the AC comes on, the lights that are dimming are on a loose neutral. |
#7
|
|||
|
|||
"Jim Beaver" wrote in message ... I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver This is Turtle. In this age and time , anything is possible. Check the voltage at the service pannel and if you see this dip in the voltage there. Call the power company. If you don't see any dip in the voltage at the pannel . You have a problem inside your house. call a electricial to come fix it. The Cheapest might be to call the power company and let them see as to the low volage when the A/C comes on. If there is a drop of voltage at the meter pan. It's their problem. If not , it's your to fix inside your house. TURTLE |
#8
|
|||
|
|||
In alt.home.repair on Fri, 29 Jul 2005 21:21:49 -0700 Eric
posted: Jim Beaver wrote: I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver You might want to verify the various wire connections in the panel are tight and well connected (but only if you are comfortable with things electrical) A bad connection will cause a voltage drop under load. This sounds right to me. If the AC and the lights are on different circuits, and they almost certainly are, that would mean the bad connection is at the junction or closer to the street than the junction of them. That is, where the main enters and connects to the fusebox. I've done this with my car battery with my bare hand, but I think doing it with a bare hand in a fuse box would kill me, literally (and literally doesn't mean figuratively, like people seem to use it.) But... Is there any sort of rubber glove that the OP could wear that would insulate from the electricity, but allow him to feel if the connection is hot, physcially. That's how I could tell where the bad connection was on the car battery. The good one was cold, the bad one was almost too hot to touch. Of course that was a really bad connection, so bad the car stalled and wouldn't crank fast enough to restart. The op's connection is still working, but I think it would be warm all the time, and a bit hotter right after the AC starts up. Or is it too dangerous and he should just tighten that connection with a well insulated screw driver and gloves? begin sidebar By any chance... are you using Aluminum wire? If so, i highly recommend you rip it all out and get what you can for scrap price out of it. AL is ok in very large sizes (as long as its correctly installed with proper torque and an anti-oxidant on good clean connections), oh say above 00 but even still, I'd go all copper if i possibly could. end sidebar I really doubt its a utility transformer problem, but I'll bet dimes to donuts its either a bad main breaker or a bad connection in your panel, either at the mains, the meter or one of the bus bars in the panel. Eric Meirman -- If emailing, please let me know whether or not you are posting the same letter. Change domain to erols.com, if necessary. |
#9
|
|||
|
|||
meirman wrote:
In alt.home.repair on Fri, 29 Jul 2005 21:21:49 -0700 Eric posted: Jim Beaver wrote: I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver You might want to verify the various wire connections in the panel are tight and well connected (but only if you are comfortable with things electrical) A bad connection will cause a voltage drop under load. This sounds right to me. If the AC and the lights are on different circuits, and they almost certainly are, that would mean the bad connection is at the junction or closer to the street than the junction of them. That is, where the main enters and connects to the fusebox. I've done this with my car battery with my bare hand, but I think doing it with a bare hand in a fuse box would kill me, literally (and literally doesn't mean figuratively, like people seem to use it.) But... Is there any sort of rubber glove that the OP could wear that would insulate from the electricity, but allow him to feel if the connection is hot, physcially. That's how I could tell where the bad connection was on the car battery. The good one was cold, the bad one was almost too hot to touch. Of course that was a really bad connection, so bad the car stalled and wouldn't crank fast enough to restart. The op's connection is still working, but I think it would be warm all the time, and a bit hotter right after the AC starts up. Or is it too dangerous and he should just tighten that connection with a well insulated screw driver and gloves? begin sidebar By any chance... are you using Aluminum wire? If so, i highly recommend you rip it all out and get what you can for scrap price out of it. AL is ok in very large sizes (as long as its correctly installed with proper torque and an anti-oxidant on good clean connections), oh say above 00 but even still, I'd go all copper if i possibly could. end sidebar I really doubt its a utility transformer problem, but I'll bet dimes to donuts its either a bad main breaker or a bad connection in your panel, either at the mains, the meter or one of the bus bars in the panel. Eric Meirman -- If emailing, please let me know whether or not you are posting the same letter. Change domain to erols.com, if necessary. FIRST: dont be doing that kind of crap on electrical equipment. Use the proper tools. Do it right and get good results with no damage to the equipment or injuries to yourself or others. OK: Its easier and much safer to just measure the voltage drop across the connection with a voltmeter, here's a sample of measuring the drop across the L2 connection. --------@------- L1 -----------@---- N -------@-------- L2 ^ ^ | voltmeter| notice I'm measuring NOT line to line or line to neutral? I'm measuring across the connection on a single line. The idea is to see how much voltage is dropped across the connection and thus to gain an idea of how good the connection is. Ideally you would read Zero volts if the connection were perfect. Of course this all has to be measured with a fair amount of current flowing through the connection - I'd recommend at least 25% of its rated load if its possible and 100% of its "normal" (not rated, but normal - what it usually runs at) load is great. If you know the exact amps then measuring the drop will allow you to calculate the actual connection resistance. But barring that, if you put a decent load on it and measure anything more than a few volts its a problem. Also, just cuz your measuring on a single line dont forget it can kill you in a heartbeat. Be Carefull! Think about keeping yourself out of contact with the line wires and bus bars etc, put on shoes with rubber soles, dont do it in your garage in bare feet. Eric |
#10
|
|||
|
|||
"Eric" wrote in message ... meirman wrote: In alt.home.repair on Fri, 29 Jul 2005 21:21:49 -0700 Eric posted: Jim Beaver wrote: I've got a newly-built house (well, actually, it's 2/3 new, 1/3 existing) with new wiring from the panel in. It's got a 200 amp rating at the panel. But whenever the air conditioning comes on, the lights dim and power dips much more than I've ever seen in another house, even ones with lower amps and older wiring. Sometimes it's enough to shut down my computer or TV. The wire coming in from the pole is what was here when only the existing house was here. How likely is it that a problem like this is on the city's side of the breaker panel? Jim Beaver You might want to verify the various wire connections in the panel are tight and well connected (but only if you are comfortable with things electrical) A bad connection will cause a voltage drop under load. This sounds right to me. If the AC and the lights are on different circuits, and they almost certainly are, that would mean the bad connection is at the junction or closer to the street than the junction of them. That is, where the main enters and connects to the fusebox. I've done this with my car battery with my bare hand, but I think doing it with a bare hand in a fuse box would kill me, literally (and literally doesn't mean figuratively, like people seem to use it.) But... Is there any sort of rubber glove that the OP could wear that would insulate from the electricity, but allow him to feel if the connection is hot, physcially. That's how I could tell where the bad connection was on the car battery. The good one was cold, the bad one was almost too hot to touch. Of course that was a really bad connection, so bad the car stalled and wouldn't crank fast enough to restart. The op's connection is still working, but I think it would be warm all the time, and a bit hotter right after the AC starts up. Or is it too dangerous and he should just tighten that connection with a well insulated screw driver and gloves? begin sidebar By any chance... are you using Aluminum wire? If so, i highly recommend you rip it all out and get what you can for scrap price out of it. AL is ok in very large sizes (as long as its correctly installed with proper torque and an anti-oxidant on good clean connections), oh say above 00 but even still, I'd go all copper if i possibly could. end sidebar I really doubt its a utility transformer problem, but I'll bet dimes to donuts its either a bad main breaker or a bad connection in your panel, either at the mains, the meter or one of the bus bars in the panel. Eric Meirman -- If emailing, please let me know whether or not you are posting the same letter. Change domain to erols.com, if necessary. FIRST: dont be doing that kind of crap on electrical equipment. Use the proper tools. Do it right and get good results with no damage to the equipment or injuries to yourself or others. OK: Its easier and much safer to just measure the voltage drop across the connection with a voltmeter, here's a sample of measuring the drop across the L2 connection. --------@------- L1 -----------@---- N -------@-------- L2 ^ ^ | voltmeter| notice I'm measuring NOT line to line or line to neutral? I'm measuring across the connection on a single line. The idea is to see how much voltage is dropped across the connection and thus to gain an idea of how good the connection is. Ideally you would read Zero volts if the connection were perfect. Of course this all has to be measured with a fair amount of current flowing through the connection - I'd recommend at least 25% of its rated load if its possible and 100% of its "normal" (not rated, but normal - what it usually runs at) load is great. If you know the exact amps then measuring the drop will allow you to calculate the actual connection resistance. But barring that, if you put a decent load on it and measure anything more than a few volts its a problem. Also, just cuz your measuring on a single line dont forget it can kill you in a heartbeat. Be Carefull! Think about keeping yourself out of contact with the line wires and bus bars etc, put on shoes with rubber soles, dont do it in your garage in bare feet. Eric Second that...some dont have a clue how many MILIamps it takes to kill a person. |
#11
|
|||
|
|||
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1 On Wed, 3 Aug 2005 03:55:28 -0400, "Carolina Breeze HVAC" wrote: ...some dont have a clue how many MILIamps it takes to kill a person. How about 6 AMPS? http://image04.webshots.com/4/8/61/7...2kvWLzu_ph.jpg -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQvCKxAIk7T39FC4ZEQLrUwCePCUEKotc3LO0OiUs4Dj3GN 5dTQMAoLDq GMUCsGHcxrP8a8ZdIdsqQYjh =v7KO -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |
#12
|
|||
|
|||
~^Johnny^~ wrote:
On Wed, 3 Aug 2005 03:55:28 -0400, "Carolina Breeze HVAC" wrote: ...some dont have a clue how many MILIamps it takes to kill a person. How about 6 AMPS? How about 100mA (0.1A) for 3 seconds. At 16mA you may not be able to let go. Bud-- |
#13
|
|||
|
|||
According to Bud :
~^Johnny^~ wrote: On Wed, 3 Aug 2005 03:55:28 -0400, "Carolina Breeze HVAC" wrote: ...some dont have a clue how many MILIamps it takes to kill a person. How about 6 AMPS? How about 100mA (0.1A) for 3 seconds. At 16mA you may not be able to let go. 20ma under reasonably ordinary conditions is quite lethal. The question is how much of the current flow actually goes through your body (versus somewhere else) and how long it happens. Skin resistance, parallel paths, etc. etc. etc. Under extra-ordinary conditions, MUCH lower currents can be lethal. In surgery, currents on the order of a few _microamps_ can be fatal. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#14
|
|||
|
|||
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1 On Wed, 03 Aug 2005 10:54:10 -0500, Bud wrote: ~^Johnny^~ wrote: On Wed, 3 Aug 2005 03:55:28 -0400, "Carolina Breeze HVAC" wrote: ...some dont have a clue how many MILIamps it takes to kill a person. How about 6 AMPS? How about 100mA (0.1A) for 3 seconds. At 16mA you may not be able to let go. =whoosh!= I guess you didn't click the link. If you did, you would see I was being facetious. -----BEGIN PGP SIGNATURE----- Version: PGP 7.1 iQA/AwUBQvEmfgIk7T39FC4ZEQLRvgCg5tBkBZhc2PWIZV0UEydKTf PeOqcAoMzJ T9mZ10xgxO5tmmEBJtiKzWku =K+l3 -----END PGP SIGNATURE----- -- -john wide-open at throttle dot info |