Alan, I picked up a little 2 gallon pressure tank for $20 and mounted
it right on the pump, kinda like you recommended. It took care of the
inital surge of pressure and cured my problem. Now when the pump kicks
on at 40psi, the pressure doesn't jump up at all. Before the pressure
would jump up 20+ pounds causing the on off on off pressure switch
problem. The air chamber / snubber cured it completely.

Before trying the snubber, I changed out the 1" pipe I had on the end
of the line going to my pressure tank with 1 1/4" pipe. That didn't
make any difference.

  #42   Report Post  
N:dlzc D:aol T:com \(dlzc\)
 
Posts: n/a
Default

Dear nomad:

"nomad" wrote in message
oups.com...
Alan, I picked up a little 2 gallon pressure tank for
$20 and mounted it right on the pump, kinda like
you recommended. It took care of the inital surge
of pressure and cured my problem. Now when the
pump kicks on at 40psi, the pressure doesn't
jump up at all. Before the pressure would jump
up 20+ pounds causing the on off on off pressure
switch problem. The air chamber / snubber cured
it completely.

Before trying the snubber, I changed out the 1"
pipe I had on the end of the line going to my
pressure tank with 1 1/4" pipe. That didn't
make any difference.


Be prepared to bleed water out/force air into the tank. Over
time this air precharge will bleed off. Additonally, since this
tank is not kept wetted, there will be corrosion at the air-water
interface (assuming either steel or stainless steel tank).

You applied a bandaid, and one that will "become infected" if not
replaced. A timer will work, as will moving the pressure switch
or the tank.

It is your house, your budget, and your time. You get to choose
when and how you spend it.

Good luck!

David A. Smith


  #43   Report Post  
jim
 
Posts: n/a
Default



"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become infected" if not
replaced. A timer will work, as will moving the pressure switch
or the tank.

No he cured the problem your solutions would only mask the problem which
is the the pressure surge on start and stop of the pump. If the 20
gallon tank is designed for what he's using it for (i.e. has a rubber
bladder inside) none of your dire predictions apply.


It is your house, your budget, and your time. You get to choose
when and how you spend it.


Yeah, don't listen to this guy.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #44   Report Post  
Harry K
 
Posts: n/a
Default



jim wrote:
"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become infected" if not
replaced. A timer will work, as will moving the pressure switch
or the tank.

No he cured the problem your solutions would only mask the problem which
is the the pressure surge on start and stop of the pump. If the 20
gallon tank is designed for what he's using it for (i.e. has a rubber
bladder inside) none of your dire predictions apply.


It is your house, your budget, and your time. You get to choose
when and how you spend it.


Yeah, don't listen to this guy.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


"that guy" happens to be right. The fix -is- a bandaid approach to a
non-problem if the system is installed correctly. Your concern about
water hammer is unwarranted or there would be pipes breaking all over
this land of ours. I have never seen a surge tank installed at the
well head and I have seen a lot of systems.

Harry K

  #45   Report Post  
N:dlzc D:aol T:com \(dlzc\)
 
Posts: n/a
Default

Dear jim:

"jim" wrote in message
...


"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become
infected" if not replaced. A timer will work, as will
moving the pressure switch or the tank.

No he cured the problem your solutions would only
mask the problem which is the the pressure surge


And your tank doesn't mask the problem?

on start and stop of the pump. If the 20
gallon tank is designed for what he's using it for
(i.e. has a rubber bladder inside) none of your
dire predictions apply.


It is 2 gallon "pressure tank". Have you *ever* seen this size
for water service? I have seen them for compressed air service.

It is your house, your budget, and your time.
You get to choose when and how you spend it.


Yeah, don't listen to this guy.


You are entitled to your opinion. Fortunately, I don't have to
hear it.

plonk

David A. Smith




  #46   Report Post  
jim
 
Posts: n/a
Default



Harry K wrote:

jim wrote:
"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become infected" if not
replaced. A timer will work, as will moving the pressure switch
or the tank.

No he cured the problem your solutions would only mask the problem which
is the the pressure surge on start and stop of the pump. If the 20
gallon tank is designed for what he's using it for (i.e. has a rubber
bladder inside) none of your dire predictions apply.


It is your house, your budget, and your time. You get to choose
when and how you spend it.


Yeah, don't listen to this guy.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


"that guy" happens to be right. The fix -is- a bandaid approach to a
non-problem if the system is installed correctly. Your concern about
water hammer is unwarranted or there would be pipes breaking all over
this land of ours.


Well all pipes will eventually fail.

He said he eliminated the pressure surge and that was the only reported
problem. Simply moving the pressure switch to where the pressure surge
doesn't exist wouldn't get rid of it. And no, the pressure surge won't
cause his new pipes to fail immediately, but in 20 or 40 years when the
system becomes brittle it will make a difference.
What about this system do you think is not installed correctly? The
surge is caused by the long run from pump to the holding tank. Moving
the holding tank would also eliminate the surge. But putting a surge
tank by the pump also works. That's why plumbing supply stores sell them
in all different sizes.

-jim





I have never seen a surge tank installed at the
well head and I have seen a lot of systems.

Harry K


----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #47   Report Post  
N:dlzc D:aol T:com \(dlzc\)
 
Posts: n/a
Default

Dear Harry K:

"Harry K" wrote in message
oups.com...


jim wrote:
"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become
infected" if not replaced. A timer will work, as will
moving the pressure switch or the tank.

No he cured the problem your solutions would
only mask the problem which is the the
pressure surge on start and stop of the pump.
If the 20 gallon tank is designed for what he's
using it for (i.e. has a rubber bladder inside)
none of your dire predictions apply.


It is your house, your budget, and your time.
You get to choose when and how you spend it.


Yeah, don't listen to this guy.


"that guy" happens to be right. The fix -is- a
bandaid approach to a non-problem if the
system is installed correctly. Your concern
about water hammer is unwarranted or there
would be pipes breaking all over this land of
ours. I have never seen a surge tank installed
at the well head and I have seen a lot of systems.


Do you have any experience/history with soft starts being used
with jet pumps? Since the problem is brought about by the
"starting torque" of the motor, if you slowed the startup, the
"cause" of the problem disappears (and it might even pay for
itself in reduced starting currents). I just don't know how
effective (long lasting) they are for high rpm motors...

Something like the Telemechanique (Square D) Altistart ATS01, or
something of its ilk... (McMaster Carr only has three phase soft
starters available).

Thoughts?

David A. Smith


  #48   Report Post  
Bret Cahill
 
Posts: n/a
Default

Air dissolves into water pretty fast -- a few weeks for two gallons of
air. That was the other reason for bladder tanks besides smaller size.


Bret Cahill

  #49   Report Post  
Harry K
 
Posts: n/a
Default



jim wrote:
Harry K wrote:

jim wrote:
"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become infected" if not
replaced. A timer will work, as will moving the pressure switch
or the tank.

No he cured the problem your solutions would only mask the problem which
is the the pressure surge on start and stop of the pump. If the 20
gallon tank is designed for what he's using it for (i.e. has a rubber
bladder inside) none of your dire predictions apply.


It is your house, your budget, and your time. You get to choose
when and how you spend it.

Yeah, don't listen to this guy.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----


"that guy" happens to be right. The fix -is- a bandaid approach to a
non-problem if the system is installed correctly. Your concern about
water hammer is unwarranted or there would be pipes breaking all over
this land of ours.


Well all pipes will eventually fail.

He said he eliminated the pressure surge and that was the only reported
problem. Simply moving the pressure switch to where the pressure surge
doesn't exist wouldn't get rid of it. And no, the pressure surge won't
cause his new pipes to fail immediately, but in 20 or 40 years when the
system becomes brittle it will make a difference.
What about this system do you think is not installed correctly? The
surge is caused by the long run from pump to the holding tank. Moving
the holding tank would also eliminate the surge. But putting a surge
tank by the pump also works. That's why plumbing supply stores sell them
in all different sizes.

-jim



No, he did -not- say that he eliminated the surge. The surge is still
there but being absorbed by the surge tank, just as it was by the tank,
just as it is in all systems. There will always be a surge at startup
given any pipe at all between pump and tank.

"move to where....surge doesn't exist"??? This is a hydraulic system.
The surge will affect all parts of it.

The surge will NOT (how many times do I have to say it?) affect the
pipes. You are confusing a surge with a water hammer - two different
things. It is a water hammer that causes damage.

Again, adding something at the well head without doing anything else is
a band aid approach to fix a problem that wouldn't exist if it was
correctly installed. Curing the problem by adding unnecessary
equipment is a band-aid approach and poor mechanical work. Were it my
well I might do it but not on any other well I work on (of course had I
installed it, the switch would have been on the tank). There is a
right and wrong way to go about fixing things.

Harry K

  #50   Report Post  
Harry K
 
Posts: n/a
Default



N:dlzc D:aol T:com (dlzc) wrote:
Dear Harry K:

"Harry K" wrote in message
oups.com...


jim wrote:
"N:dlzc D:aol T:com (dlzc)" wrote:


You applied a bandaid, and one that will "become
infected" if not replaced. A timer will work, as will
moving the pressure switch or the tank.

No he cured the problem your solutions would
only mask the problem which is the the
pressure surge on start and stop of the pump.
If the 20 gallon tank is designed for what he's
using it for (i.e. has a rubber bladder inside)
none of your dire predictions apply.


It is your house, your budget, and your time.
You get to choose when and how you spend it.

Yeah, don't listen to this guy.


"that guy" happens to be right. The fix -is- a
bandaid approach to a non-problem if the
system is installed correctly. Your concern
about water hammer is unwarranted or there
would be pipes breaking all over this land of
ours. I have never seen a surge tank installed
at the well head and I have seen a lot of systems.


Do you have any experience/history with soft starts being used
with jet pumps? Since the problem is brought about by the
"starting torque" of the motor, if you slowed the startup, the
"cause" of the problem disappears (and it might even pay for
itself in reduced starting currents). I just don't know how
effective (long lasting) they are for high rpm motors...

Something like the Telemechanique (Square D) Altistart ATS01, or
something of its ilk... (McMaster Carr only has three phase soft
starters available).

Thoughts?

David A. Smith


No, afraid not. I see no reason it won't work and should fix the
problem. It doesn't add more equipment to the system as several others
in the thread want to do.

Harry K



  #51   Report Post  
--
 
Posts: n/a
Default

There is an assumption that those who are reading posts in an engineering
newsgroup have sufficient knowledge to understand enough of the thread so as
to be able to ask for clarification of a post, and to not make stupid
comments until they do.

you know, Dougie, if you have little experience or background in the subject
matter as you appear to have, and your reading skills are as poor as yours,
you should let the engineers who do this regularly, speak.
Especially engineers with decades of experience in the particular subject
and who have several well pumps of their own (two shallow installed 1981
and 1984 and one deep 1978 at the lake places, one jet 1970 at the lodge -
still running with no problems, precharged to 30 psi.)

see below for cites refuting specific neophyte comments

"Doug Miller" wrote in message
...
In article , "--"

wrote:
IMHE, the bladder is pressurized too high for efficiency, AND too

close
to shut-off. The air bladder should be lower than the low switch

setting.

I would first set the bladder charge to 25 psi.


Not if the pump is set to come at at 40. Tank precharge should be
approximately 2psi below pump cut-in pressure.


Who says? For what purpose? One can select a precharge for the parameter
one desires to maximize: for max usable volume, then precharge closer to low
set point, and for max damping of pump-ripple in the water in order to
minimize parts wear or to get maximum control stability, precharge at a
lower setting-- or one can precharge somewhere between, as a compromise.

There are four reasons that 38 psi precharge with a lower set of 40 psi is
narrowly considered and the recommendation is poor engineering. And I don't
care WHICH junior engineer made that recommendation.

First, few people have a water pressure gauge that has better hysterisis
than 2psi, let alone accounting for the system hysterisis, so calling for
38 psi precharge for a 40psi switch setting is total BS from an execution
standpoint.

Second, a precharge of 38 psi on a 40 psi start? So you can have pump
ripple cycle all your control parts? A precharge set above 60% of upper pump
setting would only be made by a pump salesman or switch salesman looking to
sell more repair parts. 38 psi precharge on a pump starting atr 40 psi is
BS from a basic design reliability standpoint.

Third, set for 38 psi so you can have how much water stored under pressure
at 40 psi? Enough to keep the pump from running except on draws above the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60 psi,
and the same five gallon tank gives a gallon and a half reserve at 38 psi
precharge 40-60 psi.

Try the old P1*V1=P2*V2 equation, using the differential from 40 psi and 60
psi.

(Ppchg*Vtank^1.1)/Ppres = Vair-vol^1.1 and then use (Vair-vol 60)-(Vair-vol
40) to find water stored in the operating range

for a given tank V between 60psi and 40 psi, V usable =[(Ppc/40) -(Ppc/60)]
Vtank

Fourth, experienced engineers avoid control settings near system spring
constants unless the controls have dampers or they latch. 38 psi in an air
bag is close enough to the switch setting of 40 psi such that oscillations
in the 38 psi air volume from the moved-water momentum changes can adversely
affect a non-latching switch. And they do.

I also refer you to the Fluid Power Engineers Handbook, Parker Hannifin,
page a-3.

The pump in this thread is closer to isothermal operation, and so I quote

" pre-charge..to about 1/3 to 1/2 system pressure. "

I have gone to a higher precharge than 1/2 for specific design
applications, and I knowingly accepted the loss in the other parameters.


Next, since if the pump is not securely mounted and the switch is on the
pump, the switch will move as the pump moves and the pump motion then

moves
the switch back. I would move the switch/secure the pump and the pump

stand.

If one of these does not work, you might need a 90 degree turn in the

water
line just before the securely mounted switch, but not a 90 turn supported

by
the switch.

one of those should do it.

-------------------------

background---

1) - as incompressible water fills the accumulator tank with a bladder
charged to 20 psi, the compressible air will stay at 20 psi until the

water
pressure rises above 20 psi.


Complete nonsense. As water enters the tank, the volume of air decreases,

and
its pressure necessarily increases immediately.


What, in your world P1*V1 = P2*V2 does not apply?

20psi air pressure*Volume air before water = 20psi air pressure* Volume
after water

means volume of air is constant. Same volume means no water can displace
air.

Apparently in your world, you can compress 20 psi air with 10 psi water and
change its volume without changing its pressure. Patent it , quick.

Neat trick in your mind, but not possible in the real world.

"As water enters the tank, the volume decreases". That "water enter the
tank" cannot happen below the 20 psi of my example, as I said.

perhaps I should have written "tries to fill" rather than "fills"

If the pump isn't developing
more than 20psi, _no_ water will enter the tank whatsoever.


Gee, that is EXACTLY what I said. "The compressible air will stay at 20 psi
until the water pressure rises above 20 psi"


If the pump is
developing more than 20psi, water begins to enter the tank immediately,

and
the air pressure also begins to increase immediately.


Which is what I said.

[snip]

Basically, #1 - if you have the bladder pressure set at the lower
setting, the switch vibrates as part of a spring-mass-spring
rigid-water-mass/pump with the switch spring set at 40 psi fighting the

40
psi air spring of the bladder. Setting the bladder to 25 psi should cure
that.


More nonsense.


You really should not be posting to engineering newsgroups other than to ask
a question.
Read carefully again the comment by one who has done this for decades.

After the initial fill, as water is withdrawn from the tank,
the pump will kick on when the pressure drops to the cut-in setting of the
switch (40psi in this case), regardless of whether the precharge pressure

was
25psi or 38 as it should be. The only difference is that, at the moment

the
pump kicks on at 40psi, there will be more water in the tank if it was
precharged to 25psi than if it was precharged to 38.


In spite of the fact that I was addressing force interactions and you are
fixated on precharge and have wandered off the path, I will comment on your
error.

Contained air is a spring, with a spring constant. The higher the
precharge, the higher the spring constant.
All pump-fluid-control systems are spring -mass systems that interact.
When pumps false start, it is a sign of unintended interaction, There is
no discussion among engineers that changing a spring constant changes the
interaction, only discussion as to what amount.

Either way, the pump
comes on at 40 and shuts off at 60. The precharge pressure does *not*

affect
that.


apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.
In the real world, precharge pressure can and does affect controls.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



  #52   Report Post  
--
 
Posts: n/a
Default

FWIW - you have put a second air spring in parallel with the original air
bladder, and by

1/total spring=1/spring1 + 1/spring2,

you lowered the total system spring constant

(and in so doing, you reduced the peak force the system now sees from the
moving water)

Adding a second air chamber in parallel to the first air chamber had the
same effect on the system as lowering the first tank's precharge in order to
lower the system spring constant.

"nomad" wrote in message
oups.com...
Alan, I picked up a little 2 gallon pressure tank for $20 and mounted
it right on the pump, kinda like you recommended. It took care of the
inital surge of pressure and cured my problem. Now when the pump kicks
on at 40psi, the pressure doesn't jump up at all. Before the pressure
would jump up 20+ pounds causing the on off on off pressure switch
problem. The air chamber / snubber cured it completely.

Before trying the snubber, I changed out the 1" pipe I had on the end
of the line going to my pressure tank with 1 1/4" pipe. That didn't
make any difference.



  #53   Report Post  
Doug Miller
 
Posts: n/a
Default

In article , "--" wrote:

"Doug Miller" wrote in message
m...
In article , "--"

wrote:
IMHE, the bladder is pressurized too high for efficiency, AND too

close
to shut-off. The air bladder should be lower than the low switch

setting.

I would first set the bladder charge to 25 psi.


Not if the pump is set to come at at 40. Tank precharge should be
approximately 2psi below pump cut-in pressure.


Who says? For what purpose?


That's a typical recommendation by manufacturers of well pumps and pressure
tanks.

[snip]
Second, a precharge of 38 psi on a 40 psi start? So you can have pump
ripple cycle all your control parts? A precharge set above 60% of upper pump
setting would only be made by a pump salesman or switch salesman looking to
sell more repair parts. 38 psi precharge on a pump starting atr 40 psi is
BS from a basic design reliability standpoint.


Obviously your experience with the reliability of residential well systems is
purely theoretical.

Third, set for 38 psi so you can have how much water stored under pressure
at 40 psi? Enough to keep the pump from running except on draws above the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60 psi,
and the same five gallon tank gives a gallon and a half reserve at 38 psi
precharge 40-60 psi.

Try the old P1*V1=P2*V2 equation, using the differential from 40 psi and 60
psi.


If you think that 40 and 60 are the right numbers to use, you don't know as
much as you think you do. Hint: pressure guages read -zero- at an actual
pressure of 14.7 psi.
[snippola]
background---

1) - as incompressible water fills the accumulator tank with a bladder
charged to 20 psi, the compressible air will stay at 20 psi until the

water
pressure rises above 20 psi.


Complete nonsense. As water enters the tank, the volume of air decreases,

and
its pressure necessarily increases immediately.


What, in your world P1*V1 = P2*V2 does not apply?


I think I pretty clearly said that it does.

20psi air pressure*Volume air before water = 20psi air pressure* Volume
after water

means volume of air is constant. Same volume means no water can displace
air.

Apparently in your world, you can compress 20 psi air with 10 psi water and
change its volume without changing its pressure. Patent it , quick.

Neat trick in your mind, but not possible in the real world.

"As water enters the tank, the volume decreases". That "water enter the
tank" cannot happen below the 20 psi of my example, as I said.


Read what I wrote.

perhaps I should have written "tries to fill" rather than "fills"


Ya know, I'm not a mind reader. If you don't say what you mean, then you
should expect to be misunderstood.

If the pump isn't developing
more than 20psi, _no_ water will enter the tank whatsoever.


Gee, that is EXACTLY what I said. "The compressible air will stay at 20 psi
until the water pressure rises above 20 psi"


fine...


If the pump is
developing more than 20psi, water begins to enter the tank immediately,

and
the air pressure also begins to increase immediately.


Which is what I said.


No, that's not what you said. But there's not much point in arguing about it.

[snip]

Basically, #1 - if you have the bladder pressure set at the lower
setting, the switch vibrates as part of a spring-mass-spring
rigid-water-mass/pump with the switch spring set at 40 psi fighting the

40
psi air spring of the bladder. Setting the bladder to 25 psi should cure
that.


More nonsense.


You really should not be posting to engineering newsgroups other than to ask
a question.
Read carefully again the comment by one who has done this for decades.

After the initial fill, as water is withdrawn from the tank,
the pump will kick on when the pressure drops to the cut-in setting of the
switch (40psi in this case), regardless of whether the precharge pressure

was
25psi or 38 as it should be. The only difference is that, at the moment

the
pump kicks on at 40psi, there will be more water in the tank if it was
precharged to 25psi than if it was precharged to 38.


In spite of the fact that I was addressing force interactions and you are
fixated on precharge and have wandered off the path, I will comment on your
error.

Contained air is a spring, with a spring constant. The higher the
precharge, the higher the spring constant.
All pump-fluid-control systems are spring -mass systems that interact.
When pumps false start, it is a sign of unintended interaction, There is
no discussion among engineers that changing a spring constant changes the
interaction, only discussion as to what amount.


So whose pump is false-starting? The OP's problem is that it *stops* when it
should not.

Either way, the pump
comes on at 40 and shuts off at 60. The precharge pressure does *not*

affect
that.


apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.


Obviously not, if you've read the entire thread. The pump was shutting off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.

In the real world, precharge pressure can and does affect controls.


The OP's problem was not the precharge pressure; as noted by others in this
thread, his problem is an improperly installed system. As you would know if
you had any _real_world_ experience with residential well systems.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #54   Report Post  
Alan Adrian
 
Posts: n/a
Default

"--" wrote in message
...
FWIW - you have put a second air spring in parallel with the original air
bladder, and by

1/total spring=1/spring1 + 1/spring2,

you lowered the total system spring constant

(and in so doing, you reduced the peak force the system now sees from the
moving water)

Adding a second air chamber in parallel to the first air chamber had the
same effect on the system as lowering the first tank's precharge in order
to
lower the system spring constant.


No one here thinks that the problem is caused by the mass of water that
needs to be accelerated when the pump starts?

That the initial surge of torque in the pump needs to get the mass of water
between the pump and the tank in the house moving, thus the reason for the
higher pressure (seen at the tank) at switch-on?

That moving the pressure switch to the tank end would definately solve the
problem, but that adding a snubber (the OP chose to use a 2 gallon tank)
before the mass of water would cure the problem too, and the OP didn't have
to dig a trench that he didn't want to?

If the air in the tank is going to be absorbed into the water so fast, what
keeps normal snubbers (vertical bits of pipe in your house that stop
hammering when you shut off the taps) from filling up with water?

Al...


  #55   Report Post  
Bret Cahill
 
Posts: n/a
Default

No one here thinks that the problem is

caused by the mass of water that needs to

be accelerated when the pump starts?

Most agreed to that near the beginning of the thread.

I thought a check valve could let a little water through each cycle but
I forgot,

1. the check valve in conventional systems is at the bottom of the
well, and,

2. preloaded check valves are loaded shut, not open.

.. . .


If the air in the tank is going to be absorbed

into the water so fast, what keeps normal

snubbers (vertical bits of pipe in your house

that stop hammering when you shut off the

taps) from filling up with water?

Here are some suspect theories:

1. Maybe the water doesn't flush through or exchange very much.

2. The water is already saturated with air.

3. Very little or zero air is necessary to stop hammer. You really
only need to adjust the volume.

I used a bladderless 40 gallon tank for 4 years and every 6 months I
had to drain the water out because the air somehow escaped.

The water was brought up 50' in turbulent two phase flow and should
have been pretty well aerated for a vacuum.


Bret Cahill



  #56   Report Post  
Alan Adrian
 
Posts: n/a
Default


"Bret Cahill" wrote in message
oups.com...
I used a bladderless 40 gallon tank for 4 years and every 6 months I
had to drain the water out because the air somehow escaped.

The water was brought up 50' in turbulent two phase flow and should
have been pretty well aerated for a vacuum.


Perhaps you had microscopic leaks? Big enough to allow gas through, but too
small for water... I've designed quite a bit of stuff for underwater and
given enough time things can get through... Usually it's the welds, but once
I had leakage past some hydraulic purge caps that were pressed into service
as air bleeders... I got a couple cups of pure tasting water into several
electronics pressure cases that were down ~50m for 2 years... and this was
in the Bosporous.. salty water... The water was so pure we never had any
corrosion or even electronics failures in the cases...

Anyways, I'm guilty of applying my mind to the OP's problem, though I've
never installed a well pump... And as this stuff isn't anything new, he
really shouldn't have asked for help here.... He should have gone to the
place where he bought the well equipment...

But it is fun to think this stuff through and learn a thing or two. And
perhaps he wanted to avoid "the right way" for reasons of his own, in which
case this is exactly the right place to come and get ideas from...

Al...


  #57   Report Post  
Harry K
 
Posts: n/a
Default



Doug Miller wrote:
In article , "--" wrote:

"Doug Miller" wrote in message
m...
In article , "--"

wrote:
IMHE, the bladder is pressurized too high for efficiency, AND too

close
to shut-off. The air bladder should be lower than the low switch

setting.

I would first set the bladder charge to 25 psi.

Not if the pump is set to come at at 40. Tank precharge should be
approximately 2psi below pump cut-in pressure.


Who says? For what purpose?


That's a typical recommendation by manufacturers of well pumps and pressure
tanks.

[snip]
Second, a precharge of 38 psi on a 40 psi start? So you can have pump
ripple cycle all your control parts? A precharge set above 60% of upper pump
setting would only be made by a pump salesman or switch salesman looking to
sell more repair parts. 38 psi precharge on a pump starting atr 40 psi is
BS from a basic design reliability standpoint.


Obviously your experience with the reliability of residential well systems is
purely theoretical.

Third, set for 38 psi so you can have how much water stored under pressure
at 40 psi? Enough to keep the pump from running except on draws above the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60 psi,
and the same five gallon tank gives a gallon and a half reserve at 38 psi
precharge 40-60 psi.

Try the old P1*V1=P2*V2 equation, using the differential from 40 psi and 60
psi.


If you think that 40 and 60 are the right numbers to use, you don't know as
much as you think you do. Hint: pressure guages read -zero- at an actual
pressure of 14.7 psi.
[snippola]
background---

1) - as incompressible water fills the accumulator tank with a bladder
charged to 20 psi, the compressible air will stay at 20 psi until the

water
pressure rises above 20 psi.

Complete nonsense. As water enters the tank, the volume of air decreases,

and
its pressure necessarily increases immediately.


What, in your world P1*V1 = P2*V2 does not apply?


I think I pretty clearly said that it does.

20psi air pressure*Volume air before water = 20psi air pressure* Volume
after water

means volume of air is constant. Same volume means no water can displace
air.

Apparently in your world, you can compress 20 psi air with 10 psi water and
change its volume without changing its pressure. Patent it , quick.

Neat trick in your mind, but not possible in the real world.

"As water enters the tank, the volume decreases". That "water enter the
tank" cannot happen below the 20 psi of my example, as I said.


Read what I wrote.

perhaps I should have written "tries to fill" rather than "fills"


Ya know, I'm not a mind reader. If you don't say what you mean, then you
should expect to be misunderstood.

If the pump isn't developing
more than 20psi, _no_ water will enter the tank whatsoever.


Gee, that is EXACTLY what I said. "The compressible air will stay at 20 psi
until the water pressure rises above 20 psi"


fine...


If the pump is
developing more than 20psi, water begins to enter the tank immediately,

and
the air pressure also begins to increase immediately.


Which is what I said.


No, that's not what you said. But there's not much point in arguing about it.

[snip]

Basically, #1 - if you have the bladder pressure set at the lower
setting, the switch vibrates as part of a spring-mass-spring
rigid-water-mass/pump with the switch spring set at 40 psi fighting the

40
psi air spring of the bladder. Setting the bladder to 25 psi should cure
that.

More nonsense.


You really should not be posting to engineering newsgroups other than to ask
a question.
Read carefully again the comment by one who has done this for decades.

After the initial fill, as water is withdrawn from the tank,
the pump will kick on when the pressure drops to the cut-in setting of the
switch (40psi in this case), regardless of whether the precharge pressure

was
25psi or 38 as it should be. The only difference is that, at the moment

the
pump kicks on at 40psi, there will be more water in the tank if it was
precharged to 25psi than if it was precharged to 38.


In spite of the fact that I was addressing force interactions and you are
fixated on precharge and have wandered off the path, I will comment on your
error.

Contained air is a spring, with a spring constant. The higher the
precharge, the higher the spring constant.
All pump-fluid-control systems are spring -mass systems that interact.
When pumps false start, it is a sign of unintended interaction, There is
no discussion among engineers that changing a spring constant changes the
interaction, only discussion as to what amount.


So whose pump is false-starting? The OP's problem is that it *stops* when it
should not.

Either way, the pump
comes on at 40 and shuts off at 60. The precharge pressure does *not*

affect
that.


apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.


Obviously not, if you've read the entire thread. The pump was shutting off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.

In the real world, precharge pressure can and does affect controls.


The OP's problem was not the precharge pressure; as noted by others in this
thread, his problem is an improperly installed system. As you would know if
you had any _real_world_ experience with residential well systems.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?


Well said! Mr -- apparently knows more than the engineers at the
pump/tank manufacturing plants.

Harry K

  #58   Report Post  
Harry K
 
Posts: n/a
Default


snip all but the below


If the air in the tank is going to be absorbed into the water so fast, what
keeps normal snubbers (vertical bits of pipe in your house that stop
hammering when you shut off the taps) from filling up with water?

Al...


They do. It just takes longer than would one would expect. The water
in the tube is pretty much captive and very little exchange is made.
Given long enough the tube will water lock and need to be drained.

Harry K

  #59   Report Post  
Doug Miller
 
Posts: n/a
Default

In article .com, "Bret Cahill" wrote:

I used a bladderless 40 gallon tank for 4 years and every 6 months I
had to drain the water out because the air somehow escaped.


The air didn't "somehow escape" - it dissolved in the water.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #60   Report Post  
Brian Whatcott
 
Posts: n/a
Default

On Thu, 2 Jun 2005 21:13:27 -0700, "N:dlzc D:aol T:com \(dlzc\)" N:
dlzc1 D:cox wrote:


Do you have any experience/history with soft starts being used
with jet pumps? Since the problem is brought about by the
"starting torque" of the motor, if you slowed the startup, the
"cause" of the problem disappears (and it might even pay for
itself in reduced starting currents). I just don't know how
effective (long lasting) they are for high rpm motors...

Something like the Telemechanique (Square D) Altistart ATS01, or
something of its ilk... (McMaster Carr only has three phase soft
starters available).

Thoughts?

David A. Smith


This line of thought has merit, I reckon. A start current limiter
would have something of the same effect.
Though if it is contactor driven, it's as easy to get burned contacts
as a malfunctioning bladder tank, I suppose.

Then again, something like a light/motor dimmer/controller [cheap!]
could readily be rigged, and the solid state, hands-off use might well
be very reliable, barring lightning induced transients, or some such.

Brian Whatcott Altus OK



  #61   Report Post  
--
 
Posts: n/a
Default


from the original poster:
My problem is that the pressure switch trips or
cycles on off on off on off every second when the pressure reaches
40psi. I noticed when the pump is kicking on and off every second, the
pressure gauge is jumping from 40 to 50 to 40 to 50.


see below -

"Alan Adrian" wrote in message
...
"--" wrote in message
...
FWIW - you have put a second air spring in parallel with the original

air
bladder, and by

1/total spring=1/spring1 + 1/spring2,

you lowered the total system spring constant

(and in so doing, you reduced the peak force the system now sees from

the
moving water)

Adding a second air chamber in parallel to the first air chamber had

the
same effect on the system as lowering the first tank's precharge in

order
to
lower the system spring constant.


No one here thinks that the problem is caused by the mass of water that
needs to be accelerated when the pump starts?


What you note (accelerating a mass of water) would more likely cause a
cavitation problem -
what I addressed is the already moving water (being relatively
incompressible, the water is already moving in under that one second at
start-up, since its response time is much like a steel rod connected to the
impeller) hitting the compressible air and rebounding, and that dynamic
rebound energy being added to the static pressure energy, causing a force
spike that the switch sees as misreads as static pressure- that interaction
a fairly common problem in fluid power.

That the initial surge of torque in the pump needs to get the mass of

water
between the pump and the tank in the house moving, thus the reason for the
higher pressure (seen at the tank) at switch-on?


No, there is always an initial surge of torque with a pump, even when
unloaded ( due to the resistance of the rotor and/or water-mass
accelerating). If the mass of water is too high for the pump, usually it
will either cavitate (make noise and eat impellers) or run hot at start. I
haven't seen an undersized or improperly designed pump cycle the start-up.

That moving the pressure switch to the tank end would definately solve the
problem, but that adding a snubber (the OP chose to use a 2 gallon tank)
before the mass of water would cure the problem too, and the OP didn't

have
to dig a trench that he didn't want to?


Yes, there are many physical ways to remove the symptom and stop the pump
from cycling on start. Once a change is found that works at removing the
symptom, then one should see what change in the scientific parameters the
physcial change made, so as to check if the fix added a future problem.
Occasionally a fix in one area creates a problem in another, and sometimes
the fix could have been done more cheaply and the cost of that experience
can be amortized over furture problems

If the air in the tank is going to be absorbed into the water so fast,

what
keeps normal snubbers (vertical bits of pipe in your house that stop
hammering when you shut off the taps) from filling up with water?


I don't believe I ever claimed that air was entrained in water at
residential pressures. The snubbers don't fill up with water at residential
pressures.

Al...




  #62   Report Post  
--
 
Posts: n/a
Default

Some facts -

I wrote

apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.


Dougie wrote

Obviously not, if you've read the entire thread. The pump was shutting off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.


Original poster Nomad wrote

My problem is that the pressure switch trips or
cycles on off on off on off every second when the pressure reaches
40psi. I noticed when the pump is kicking on and off every second, the
pressure gauge is jumping from 40 to 50 to 40 to 50.


and later, Nomad said again

I am able to get the system up to 60psi by holding the pressure switch
contacts closed for the first few seconds of cut-in at 40psi, when the
contacts are jumping open and closed over and over again.


which explains why Dougie has problems with understanding the poster's
problem

nuff said.........

"Doug Miller" wrote in message
om...
In article , "--"

wrote:

"Doug Miller" wrote in message
m...
In article , "--"

wrote:
IMHE, the bladder is pressurized too high for efficiency, AND too

close
to shut-off. The air bladder should be lower than the low switch

setting.

I would first set the bladder charge to 25 psi.

Not if the pump is set to come at at 40. Tank precharge should be
approximately 2psi below pump cut-in pressure.


Who says? For what purpose?


That's a typical recommendation by manufacturers of well pumps and

pressure
tanks.

[snip]
Second, a precharge of 38 psi on a 40 psi start? So you can have pump
ripple cycle all your control parts? A precharge set above 60% of upper

pump
setting would only be made by a pump salesman or switch salesman looking

to
sell more repair parts. 38 psi precharge on a pump starting atr 40 psi

is
BS from a basic design reliability standpoint.


Obviously your experience with the reliability of residential well systems

is
purely theoretical.

Third, set for 38 psi so you can have how much water stored under

pressure
at 40 psi? Enough to keep the pump from running except on draws above the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60

psi,
and the same five gallon tank gives a gallon and a half reserve at 38 psi
precharge 40-60 psi.

Try the old P1*V1=P2*V2 equation, using the differential from 40 psi and

60
psi.


If you think that 40 and 60 are the right numbers to use, you don't know

as
much as you think you do. Hint: pressure guages read -zero- at an actual
pressure of 14.7 psi.
[snippola]
background---

1) - as incompressible water fills the accumulator tank with a

bladder
charged to 20 psi, the compressible air will stay at 20 psi until the

water
pressure rises above 20 psi.

Complete nonsense. As water enters the tank, the volume of air

decreases,
and
its pressure necessarily increases immediately.


What, in your world P1*V1 = P2*V2 does not apply?


I think I pretty clearly said that it does.

20psi air pressure*Volume air before water = 20psi air pressure*

Volume
after water

means volume of air is constant. Same volume means no water can displace
air.

Apparently in your world, you can compress 20 psi air with 10 psi water

and
change its volume without changing its pressure. Patent it , quick.

Neat trick in your mind, but not possible in the real world.

"As water enters the tank, the volume decreases". That "water enter the
tank" cannot happen below the 20 psi of my example, as I said.


Read what I wrote.

perhaps I should have written "tries to fill" rather than "fills"


Ya know, I'm not a mind reader. If you don't say what you mean, then you
should expect to be misunderstood.

If the pump isn't developing
more than 20psi, _no_ water will enter the tank whatsoever.


Gee, that is EXACTLY what I said. "The compressible air will stay at 20

psi
until the water pressure rises above 20 psi"


fine...


If the pump is
developing more than 20psi, water begins to enter the tank immediately,

and
the air pressure also begins to increase immediately.


Which is what I said.


No, that's not what you said. But there's not much point in arguing about

it.

[snip]

Basically, #1 - if you have the bladder pressure set at the lower
setting, the switch vibrates as part of a spring-mass-spring
rigid-water-mass/pump with the switch spring set at 40 psi fighting

the
40
psi air spring of the bladder. Setting the bladder to 25 psi should

cure
that.

More nonsense.


You really should not be posting to engineering newsgroups other than to

ask
a question.
Read carefully again the comment by one who has done this for decades.

After the initial fill, as water is withdrawn from the tank,
the pump will kick on when the pressure drops to the cut-in setting of

the
switch (40psi in this case), regardless of whether the precharge

pressure
was
25psi or 38 as it should be. The only difference is that, at the moment

the
pump kicks on at 40psi, there will be more water in the tank if it was
precharged to 25psi than if it was precharged to 38.


In spite of the fact that I was addressing force interactions and you are
fixated on precharge and have wandered off the path, I will comment on

your
error.

Contained air is a spring, with a spring constant. The higher the
precharge, the higher the spring constant.
All pump-fluid-control systems are spring -mass systems that

interact.
When pumps false start, it is a sign of unintended interaction, There

is
no discussion among engineers that changing a spring constant changes the
interaction, only discussion as to what amount.


So whose pump is false-starting? The OP's problem is that it *stops* when

it
should not.

Either way, the pump
comes on at 40 and shuts off at 60. The precharge pressure does *not*

affect
that.


apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.


Obviously not, if you've read the entire thread. The pump was shutting off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.

In the real world, precharge pressure can and does affect controls.


The OP's problem was not the precharge pressure; as noted by others in

this
thread, his problem is an improperly installed system. As you would know

if
you had any _real_world_ experience with residential well systems.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



  #63   Report Post  
--
 
Posts: n/a
Default

Harry, I have no problem challenging engineers on the breadth and scope of
their recommendations. My questions have on several occasions caused
industry "rules-of-thumb" to be flat-out changed.
As a chief engineer and principal engineer for almost 30 years, I am not
cowed by an engineer because an engineer was hired by a firm or because he
works there. To increase the firm's engineering team's outlook and
experience and knowledge is often part of my job. Ironically, if the
engineer always does their job right, they never have any problems nor any
non-book feedback to learn from.
Almost all work I do for a firm is done at the firm's request, done when
a firm's engineering teams are unable to solve their company's technical
problems. And often as not, they missed fundamentals and relied on their own
misinterpreted experience.

Engineers are human. Like all humans, they give their best guess based on
their knowledge and experience, and like all humans, their knowledge and
experience may be misapplied or it may be inadequate or through poor
management they may have misinterpreted their own experience. The better
engineers ask, so as to interact and expand their understanding.
Others.........


"Harry K" wrote in message
ups.com...


Doug Miller wrote:
In article , "--"

wrote:

"Doug Miller" wrote in message
m...
In article , "--"
wrote:
IMHE, the bladder is pressurized too high for efficiency, AND

too
close
to shut-off. The air bladder should be lower than the low switch
setting.

I would first set the bladder charge to 25 psi.

Not if the pump is set to come at at 40. Tank precharge should be
approximately 2psi below pump cut-in pressure.

Who says? For what purpose?


That's a typical recommendation by manufacturers of well pumps and

pressure
tanks.

[snip]
Second, a precharge of 38 psi on a 40 psi start? So you can have pump
ripple cycle all your control parts? A precharge set above 60% of upper

pump
setting would only be made by a pump salesman or switch salesman

looking to
sell more repair parts. 38 psi precharge on a pump starting atr 40 psi

is
BS from a basic design reliability standpoint.


Obviously your experience with the reliability of residential well

systems is
purely theoretical.

Third, set for 38 psi so you can have how much water stored under

pressure
at 40 psi? Enough to keep the pump from running except on draws above

the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60

psi,
and the same five gallon tank gives a gallon and a half reserve at 38

psi
precharge 40-60 psi.

Try the old P1*V1=P2*V2 equation, using the differential from 40 psi

and 60
psi.


If you think that 40 and 60 are the right numbers to use, you don't know

as
much as you think you do. Hint: pressure guages read -zero- at an actual
pressure of 14.7 psi.
[snippola]
background---

1) - as incompressible water fills the accumulator tank with a

bladder
charged to 20 psi, the compressible air will stay at 20 psi until

the
water
pressure rises above 20 psi.

Complete nonsense. As water enters the tank, the volume of air

decreases,
and
its pressure necessarily increases immediately.

What, in your world P1*V1 = P2*V2 does not apply?


I think I pretty clearly said that it does.

20psi air pressure*Volume air before water = 20psi air pressure*

Volume
after water

means volume of air is constant. Same volume means no water can

displace
air.

Apparently in your world, you can compress 20 psi air with 10 psi water

and
change its volume without changing its pressure. Patent it , quick.

Neat trick in your mind, but not possible in the real world.

"As water enters the tank, the volume decreases". That "water enter

the
tank" cannot happen below the 20 psi of my example, as I said.


Read what I wrote.

perhaps I should have written "tries to fill" rather than "fills"


Ya know, I'm not a mind reader. If you don't say what you mean, then you
should expect to be misunderstood.

If the pump isn't developing
more than 20psi, _no_ water will enter the tank whatsoever.

Gee, that is EXACTLY what I said. "The compressible air will stay at

20 psi
until the water pressure rises above 20 psi"


fine...


If the pump is
developing more than 20psi, water begins to enter the tank

immediately,
and
the air pressure also begins to increase immediately.


Which is what I said.


No, that's not what you said. But there's not much point in arguing

about it.

[snip]

Basically, #1 - if you have the bladder pressure set at the

lower
setting, the switch vibrates as part of a spring-mass-spring
rigid-water-mass/pump with the switch spring set at 40 psi fighting

the
40
psi air spring of the bladder. Setting the bladder to 25 psi should

cure
that.

More nonsense.

You really should not be posting to engineering newsgroups other than

to ask
a question.
Read carefully again the comment by one who has done this for

decades.

After the initial fill, as water is withdrawn from the tank,
the pump will kick on when the pressure drops to the cut-in setting

of the
switch (40psi in this case), regardless of whether the precharge

pressure
was
25psi or 38 as it should be. The only difference is that, at the

moment
the
pump kicks on at 40psi, there will be more water in the tank if it

was
precharged to 25psi than if it was precharged to 38.

In spite of the fact that I was addressing force interactions and you

are
fixated on precharge and have wandered off the path, I will comment on

your
error.

Contained air is a spring, with a spring constant. The higher the
precharge, the higher the spring constant.
All pump-fluid-control systems are spring -mass systems that

interact.
When pumps false start, it is a sign of unintended interaction,

There is
no discussion among engineers that changing a spring constant changes

the
interaction, only discussion as to what amount.


So whose pump is false-starting? The OP's problem is that it *stops*

when it
should not.

Either way, the pump
comes on at 40 and shuts off at 60. The precharge pressure does *not*
affect
that.


apparently the original poster's comments refute your statement. His

pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi.

Not
off at 60 only, as you claim.


Obviously not, if you've read the entire thread. The pump was shutting

off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.

In the real world, precharge pressure can and does affect controls.


The OP's problem was not the precharge pressure; as noted by others in

this
thread, his problem is an improperly installed system. As you would know

if
you had any _real_world_ experience with residential well systems.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?


Well said! Mr -- apparently knows more than the engineers at the
pump/tank manufacturing plants.

Harry K



  #64   Report Post  
Harry K
 
Posts: n/a
Default


snip

Well said! Mr -- apparently knows more than the engineers at the
pump/tank manufacturing plants.

Harry K


You are obviously well qualified in your field. Your field very
obviously is not in practical applications, at least not from what I
have read. Well systems have been in use since before recorded
history. Insisting that changing an industry standard that has stood
the test of time is not 'practical application'. The '2psi below
cut-in' is the standard and for very good reasons. One is that it
minimizes pump cycle times, i.e., max water delivered between cycles.
That at least is what I was taught. Since it works in practice I see
no need to get a masters in theoretical physics or calculus.

There is fun in trying various things to see if something can be made
to work better but there comes a point in development (well systems for
example) where further tinkering is a dead end.

The guy has a problem with a pressure wave spike going over 60psi at
start-up. He band-aided it. It is not now a problem and would never
have been a problem if the switch had been at the tank to begin with.
That is the simple cut and dried version. All your theoreticals isn't
going to change it.

Harry K

  #65   Report Post  
Doug Miller
 
Posts: n/a
Default

In article , "--" wrote:
Some facts -

I wrote

apparently the original poster's comments refute your statement. His pump
shut off after a second at what appeared to be 40 psi. Off at 40 psi. Not
off at 60 only, as you claim.


Dougie wrote

Obviously not, if you've read the entire thread. The pump was shutting off
_at_60_ due to pressure surge, not at 40 as it _appeared_ to be.


Original poster Nomad wrote

My problem is that the pressure switch trips or
cycles on off on off on off every second when the pressure reaches
40psi. I noticed when the pump is kicking on and off every second, the
pressure gauge is jumping from 40 to 50 to 40 to 50.


and later, Nomad said again

I am able to get the system up to 60psi by holding the pressure switch
contacts closed for the first few seconds of cut-in at 40psi, when the
contacts are jumping open and closed over and over again.


which explains why Dougie has problems with understanding the poster's
problem


Quite the contrary - I've grasped one essential point that has obviously
eluded you, with your purely theoretical understanding of residential water
wells, namely that the surge hits 60psi (shutting off the switch) and drops
back to 40psi, faster than the gauge can react. The apparent pressure shown by
the gauge is not the actual pressure.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?


  #66   Report Post  
Doug Miller
 
Posts: n/a
Default

In article ,
says...
There is an assumption that those who are reading posts in an engineering
newsgroup have sufficient knowledge to understand enough of the thread so as
to be able to ask for clarification of a post, and to not make stupid
comments until they do.


Your own criteria compel you to silence on this subject.

you know, Dougie, if you have little experience or background in the subject
matter as you appear to have, and your reading skills are as poor as yours,
you should let the engineers who do this regularly, speak.


It's pretty clear that you have no practical, real-world experience with
residential water wells whatsoever, and not much more in comprehending
written English.
[snip]

Third, set for 38 psi so you can have how much water stored under pressure
at 40 psi? Enough to keep the pump from running except on draws above the
rule-of-thumb of a gallon?
A five gallon tank gives a gallon reserve at 25 psi precharge 40-60 psi,
and the same five gallon tank gives a gallon and a half reserve at 38 psi
precharge 40-60 psi.


True, but utterly irrelevant - the clear sign of an academic with no
experience in the real world. Who the hell uses a five-gallon pressure
tank on a residential well? If you had any real-world experience with
residential water wells, you would know that (a) forty-gallon and larger
tanks - sometimes *much* larger - are the norm, and (b) *nobody* who has
even the faintest idea of what he's doing installs and configures a
residential well such that the pump kicks on after a drawdown of as
little as gallon. One gallon isn't anybody's "rule of thumb" in the real
world.

Go back to your ivory tower, and leave the discussions of real-world
problems to those who have some actual hands-on experience with the
equipment in the real world.
  #67   Report Post  
jim
 
Posts: n/a
Default



Doug Miller wrote:

Quite the contrary - I've grasped one essential point that has obviously
eluded you, with your purely theoretical understanding of residential water
wells, namely that the surge hits 60psi (shutting off the switch) and drops
back to 40psi, faster than the gauge can react.


That would be a guess. Another guess would be that he simply failed to
observe the brief flutter in the needle.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #68   Report Post  
Bret Cahill
 
Posts: n/a
Default

There is fun in trying various things to see if

something can be made to work better but

there comes a point in development (well

systems for example) where further

tinkering is a dead end.

True in many situations but you'ld be surprised at how often you can
find alternatives in "mature" fields using decades old technology.

I was hooked up to city water that, at times, when the alge mixed with
the chlorine, made it undrinkable. I didn't like hauling water back
from the store, but there was an old deep well out back that hadn't
been used for years.

Wells clog up over several decades and a well driller suggested I first
check the flow rate by pouring water into the well. This is supposed
to be a good indicator of the possible flow rate out. It was only
about a few quarts/ minute under a few feet of head which is probably
why the pump system was removed in the first place.

No common off the shelf system will work at such a low flow rate.

I didn't need a continuous high flow rate so I used a small 1/3 hp
shallow well pump to pump water out of the bottom of a water softener
tank and used the resulting vacuum to bring the water up 50' in a two
phase flow.

Pin holes above the water line allowed in enough air to develop slug
flow. The shallow well pump only saw 25' of liquid, but it was being
used as a deep well pump. A float switch in the tank cut the pump,
opened a solenoid valve and restarted the cycle when the water got low.

It paid for itself in a few months and was a lot of fun. I calculated
the efficiency which compared to conventional systems. I used it for
four years before I moved.

Two phase flow is common in materials handling. Plastic pellets, for
example, are discharged with a similar vacuum/separation tank system

The need will probably never appear in real life but you can always get
a bucket of water from any depth with just 1/4" tubing for capillary
slug flow and a shop vac.


Bret Cahill

  #69   Report Post  
jim
 
Posts: n/a
Default



Harry K wrote:

There is fun in trying various things to see if something can be made
to work better but there comes a point in development (well systems for
example) where further tinkering is a dead end.

The guy has a problem with a pressure wave spike going over 60psi at
start-up. He band-aided it. It is not now a problem and would never
have been a problem if the switch had been at the tank to begin with.


What evidence do you have thatyou keep insisting that your solution is
better than the one Nomad used. The fact is that the pressure spike on a
long run of pipe on start-up (and quite likely on shut-down also) is not
good for the system and will when the pipes get old and rusty (and they
will eventually) lead to an earlier failure of the system. Chances are
good, there is something about the capacity of the pump and the length
of pipe to the house that creates a resonant condition that amplified
the startup pressure pulse. Anyway, it's not good to just ignore the
pressure spike and let it continue.
And sure there is still a pressure pulse in the short length of pipe
from pump to surge tank but that doesn't involve a long column of water
being cracked like a whip (i.e. at a rate faster than the needle moves
on the pressure gauge). And maybe it isn't of the magnitude where the
water column separates and crashes back together but it still isn't good
and he did well to get rid of it.
After he solved the problem there is no benefit to moving the sensor
and incurring the additional cost, work and maintenance that would
involve.

-jim

----== Posted via Newsfeeds.Com - Unlimited-Uncensored-Secure Usenet News==----
http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups
----= East and West-Coast Server Farms - Total Privacy via Encryption =----
  #70   Report Post  
N:dlzc D:aol T:com \(dlzc\)
 
Posts: n/a
Default

Dear --:

"--" wrote in message
...
....
What you note (accelerating a mass of water) would
more likely cause a cavitation problem -


Only on the suction side of the pump. Not where the pressure
switch is reported to have been.

what I addressed is the already moving water (being
relatively incompressible, the water is already moving
in under that one second at start-up, since its
response time is much like a steel rod connected to
the impeller)


And how did this "steel rod" of water become already moving,
since it has distributed inertia? Did it perhaps require
*pressure* and *time* to accelerate? The pressure spike had
nothing to do with:

hitting the compressible air and rebounding,


Acceleration of mass requires force. In the case of a fluid,
this is usually a gradient in pressure, and the line pressure
stays pretty close to tank pressure, even at startup. Note that
the OP indicated that changing to 1.25" line did not have any
effect, where with your "model" it should have had an effect.

David A. Smith




  #71   Report Post  
Harry K
 
Posts: n/a
Default



jim wrote:
Harry K wrote:

There is fun in trying various things to see if something can be made
to work better but there comes a point in development (well systems for
example) where further tinkering is a dead end.

The guy has a problem with a pressure wave spike going over 60psi at
start-up. He band-aided it. It is not now a problem and would never
have been a problem if the switch had been at the tank to begin with.


What evidence do you have thatyou keep insisting that your solution is
better than the one Nomad used. The fact is that the pressure spike on a
long run of pipe on start-up (and quite likely on shut-down also) is not
good for the system and will when the pipes get old and rusty (and they
will eventually) lead to an earlier failure of the system. Chances are
good, there is something about the capacity of the pump and the length
of pipe to the house that creates a resonant condition that amplified
the startup pressure pulse. Anyway, it's not good to just ignore the
pressure spike and let it continue.
And sure there is still a pressure pulse in the short length of pipe
from pump to surge tank but that doesn't involve a long column of water
being cracked like a whip (i.e. at a rate faster than the needle moves
on the pressure gauge). And maybe it isn't of the magnitude where the
water column separates and crashes back together but it still isn't good
and he did well to get rid of it.
After he solved the problem there is no benefit to moving the sensor
and incurring the additional cost, work and maintenance that would
involve.

-jim


What evidence?? 80 years at least of these systems operating in the
field without the dreaded fatigue and pipe failure you are referring
to. There are systems out there with runs of over 1/4 mile from the
pump to the tank with the switch at the tank. Again: A pressure pulse
is NOT a water hammer. The pressure pulse damps out at the first
opportunity - the tank before he did it, the surge tank after he
installed it.

A "long water column being cracked like a whip"???. You push on one
end of the colume, pressure builds on that end and propagates along the
colume. Just where is this dreaded 'crack like a whip'??

As to the benefit of moving the switch after he put the surge tank in.
Correct, very little except for the occasional maintenance of having to
air up the surge tank. It still comes down to a band-aid approach to a
non-problem if done correctly to begin with.

Harry K

  #72   Report Post  
Brian Whatcott
 
Posts: n/a
Default

On Sat, 04 Jun 2005 02:42:03 GMT, Brian Whatcott
wrote:

On Thu, 2 Jun 2005 21:13:27 -0700, "N:dlzc D:aol T:com \(dlzc\)" N:
dlzc1 D:cox wrote:


Do you have any experience/history with soft starts being used
with jet pumps? Since the problem is brought about by the
"starting torque" of the motor, if you slowed the startup, the
"cause" of the problem disappears (and it might even pay for
itself in reduced starting currents). I just don't know how
effective (long lasting) they are for high rpm motors...

Something like the Telemechanique (Square D) Altistart ATS01, or
something of its ilk... (McMaster Carr only has three phase soft
starters available).

Thoughts?

David A. Smith


This line of thought has merit, I reckon. A start current limiter
would have something of the same effect.
Though if it is contactor driven, it's as easy to get burned contacts
as a malfunctioning bladder tank, I suppose.

Then again, something like a light/motor dimmer/controller [cheap!]
could readily be rigged, and the solid state, hands-off use might well
be very reliable, barring lightning induced transients, or some such.

Brian Whatcott Altus OK



Here's a more radical thought. The thread seems to have converged on a
pressure pulse occuring at motor on. Why an over pressure pulse.

One way to explain it is to use the transmission line electrical
analogy.

Put a voltage step onto a transmission line (like a co ax) and the
pulse travels to the far end - and stops there if the end is matched
to the line.

If the line is open circuit at the far end, the pulse gets to the far
end and bounces back at double height.
If the line is shorted at the far end, the pulse bounces back as a
negative image of the incident pulse.

In this case, because the start pulse seems to come back twice as high
- assume that the far end is terminated in a high impedence.
So the far end pipework narrows or the far end bladder is too stiff.

THERE's a new insight!

Brian W
  #73   Report Post  
N:dlzc D:aol T:com \(dlzc\)
 
Posts: n/a
Default

Dear Brian Whatcott:

"Brian Whatcott" wrote in message
...
On Sat, 04 Jun 2005 02:42:03 GMT, Brian Whatcott
wrote:

On Thu, 2 Jun 2005 21:13:27 -0700, "N:dlzc D:aol T:com
\(dlzc\)" N:
dlzc1 D:cox wrote:


Do you have any experience/history with soft starts
being used with jet pumps? Since the problem is
brought about by the "starting torque" of the motor,
if you slowed the startup, the "cause" of the
problem disappears (and it might even pay for
itself in reduced starting currents). I just don't
know how effective (long lasting) they are for high
rpm motors...

Something like the Telemechanique (Square D)
Altistart ATS01, or something of its ilk...
(McMaster Carr only has three phase soft
starters available).

Thoughts?


This line of thought has merit, I reckon. A start
current limiter would have something of the same
effect. Though if it is contactor driven, it's as easy
to get burned contacts as a malfunctioning bladder
tank, I suppose.

Then again, something like a light/motor
dimmer/controller [cheap!] could readily be rigged,
and the solid state, hands-off use might well be
very reliable, barring lightning induced transients,
or some such.


Here's a more radical thought. The thread seems to
have converged on a pressure pulse occuring at
motor on.


Actually it seems like it turned into a shouting match...

Why an over pressure pulse.

One way to explain it is to use the transmission
line electrical analogy.

Put a voltage step onto a transmission line (like
a co ax) and the pulse travels to the far end - and
stops there if the end is matched to the line.

If the line is open circuit at the far end, the pulse
gets to the far end and bounces back at double
height.


Only if you continue to add power in resonance.

If the line is shorted at the far end, the pulse
bounces back as a negative image of the
incident pulse.


That doesn't sound right.

this case, because the start pulse seems to
come back twice as high - assume that the far
end is terminated in a high impedence. So the
far end pipework narrows or the far end bladder
is too stiff.


Narrowing has been eliminated to no effect. Bladder is about
1/10th of a second away at the speed of sound in water.
Resonance is contraindicated, since the phenomenon stops after a
short time.

THERE's a new insight!


You are bored!

David A. Smith


  #74   Report Post  
Brian Whatcott
 
Posts: n/a
Default

On Sun, 5 Jun 2005 21:42:56 -0700, "N:dlzc D:aol T:com \(dlzc\)" N:
dlzc1 D:cox wrote:

Dear Brian Whatcott:

"Brian Whatcott" wrote in message
.. .
On Sat, 04 Jun 2005 02:42:03 GMT, Brian Whatcott
wrote:

On Thu, 2 Jun 2005 21:13:27 -0700, "N:dlzc D:aol T:com
\(dlzc\)" N:
dlzc1 D:cox wrote:


Do you have any experience/history with soft starts
being used with jet pumps? Since the problem is
brought about by the "starting torque" of the motor,
if you slowed the startup, the "cause" of the
problem disappears (and it might even pay for
itself in reduced starting currents). I just don't
know how effective (long lasting) they are for high
rpm motors...

Something like the Telemechanique (Square D)
Altistart ATS01, or something of its ilk...
(McMaster Carr only has three phase soft
starters available).

Thoughts?

This line of thought has merit, I reckon. A start
current limiter would have something of the same
effect. Though if it is contactor driven, it's as easy
to get burned contacts as a malfunctioning bladder
tank, I suppose.

Then again, something like a light/motor
dimmer/controller [cheap!] could readily be rigged,
and the solid state, hands-off use might well be
very reliable, barring lightning induced transients,
or some such.


Here's a more radical thought. The thread seems to
have converged on a pressure pulse occuring at
motor on.


Actually it seems like it turned into a shouting match...

Why an over pressure pulse.

One way to explain it is to use the transmission
line electrical analogy.

Put a voltage step onto a transmission line (like
a co ax) and the pulse travels to the far end - and
stops there if the end is matched to the line.

If the line is open circuit at the far end, the pulse
gets to the far end and bounces back at double
height.


Only if you continue to add power in resonance.

If the line is shorted at the far end, the pulse
bounces back as a negative image of the
incident pulse.


That doesn't sound right.

this case, because the start pulse seems to
come back twice as high - assume that the far
end is terminated in a high impedence. So the
far end pipework narrows or the far end bladder
is too stiff.


Narrowing has been eliminated to no effect. Bladder is about
1/10th of a second away at the speed of sound in water.
Resonance is contraindicated, since the phenomenon stops after a
short time.

THERE's a new insight!


You are bored!

David A. Smith


Hehe....maybe - but transmission line mismatch is not a resonance
effect. You can easily demonstrate the effect (even the one that
doesn't sound right to you), with 50 ft of coax, a relay, a battery
and of course, a scope!

Brian W

  #75   Report Post  
Sylvan Butler
 
Posts: n/a
Default

On Mon, 06 Jun 2005 03:47:44 GMT, Brian Whatcott wrote:
In this case, because the start pulse seems to come back twice as high
- assume that the far end is terminated in a high impedence.
So the far end pipework narrows or the far end bladder is too stiff.
THERE's a new insight!


Only looks that way. Perhaps because you appear to have skipped much
of the thread... The far end pipe does narrow, but changing it may no
appreciable difference. The far end bladder is not too stiff, because
then the pressure would only increase, not be a spike.

The pressure spike it high, not because of a bounce back, but because
water is incompressible, water has mass hence inertia, and pipes have
friction. The pump starts, wants to move water, water does not start to
move instantly, so the pressure seen near to the pump has a high spike
that rapidly reduces as the water starts to move.

Not rocket science, well understood in well pump systems for many years.
That is why the proper installation puts the pressure switch near the
pressure tank. (My system, for example, has 150-200ft between pump and
tank, and less than 3ft between tank and pressure switch.)

sdb

--
Wanted: Omnibook 800 & accessories, cheap, working or not
sdbuse1 on mailhost bigfoot.com


  #76   Report Post  
 
Posts: n/a
Default

I would assume the pump power comes from the house? Why not put the
pressure switch in the house next to the tank and break the power
there? go from the breaker panel to the pressure switch, to the pump
house. Put a disconnect switch in the pump house so you can service
the pump and wire from there to the pump. You can use the existing
wire from the house to the pump, so it should be easy to do. The
voltage drop in the existing wiring should not change, as the wire
length is no different than before. You have just changed the location
of the switch, so everything should work just fine.

Of corse if the power feeds the pump house from somewhere else, forget
I said anything.

BTW, Every shallow well and booster pump I have ever worked on or
installed, said set air precharge to 2 PSI below switch cut-in setting
in the instructions. It gives you the biggest draw down on the bladder
tank.

Stretch

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 03:59 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"