View Single Post
  #7   Report Post  
Set Square
 
Posts: n/a
Default Bolier Control Wiring Query

In an earlier contribution to this discussion,
Matthew Humphreys wrote:

On Sun, 11 Apr 2004 14:54:13 +0100, "Set Square"
wrote:


Matthew


Check the wiring in your junction box. When hot water only is
switched on, pins 1 and 6 in the junction box should be live. When
you turn the cylinder stat up to a high temperature, pin 8 should be
live (and pin 7 not live). When you turn the cylstat down to a low
temperature, pin 8 should cease to be live and pin 7 should become
live instead.

The boiler and pump (or just the boiler if the pump is connected via
an over-run stat on the boiler) should be connected to pin 8 - so
the boiler should fire when the cylstat is turned up.

Check these things, and let us know the score.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!




Thanks for the help - not bad support for an Easter Sunday!
OK,

If I ask for HW only, pins 6,7,8 and 9 of the Danfoss wiring box are
live! This doesn't sound right!

If I drop the stat temp, then 8 and 9 go off.

The boiler is on pin 9, which in turn is linked to pin 8 (as per the
installation sheet) - which seems OK.

Pin 7 is the "HW off" from the stat, I think

Hope this is starting to make sense to someone!


I was referring to the pin (connection) numbers in the 10-way junction box
shown under Y-plan in http://content.honeywell.com/uk/homes/systems.htm

It sounds like you have a different wiring scheme if the boiler is on 9! Do
you have a reference to a diagram which covers your setup? [On the Honeywell
diagram shown in my reference, 9 and 10 are not used!]

That aside, if - as you say - 8 and 9 are live when calling for HW only, and
the boiler is on 9, I'm at a loss to know why the boiler isn't coming on and
heating the water.

--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!