A method I have seen used around here (Ontario, Canada) is to run the
incoming ground wire under the box ground screw with a 4 to 6 inch length
extending past the screw, then use a wire nut to attach all the other ground
wires together. It keeps the wire bulk down to a minimum.
"HorneTD" wrote in message
nk.net...
Robert11 wrote:
Hi,
I posted a question a while back regarding whether it was code
permissible
to ground
the green wire grounds in a gang box by using a single screw that was
also
used to secure the
box to a wooden joist. Responses were that it was not, and you must use
a
dedicated screw.
Good information.
One reply also said that:
"The code also requires that a suitable connector
must be used to splice the EGCs. just twisting them around each other
is no enough. "
Questions:
a. What's an EGC ?
Grounding Conductor, Equipment. The conductor used to connect the
non–current-carrying metal parts of equipment, raceways, and other
enclosures to the system grounded conductor, the grounding electrode
conductor, or both, at the service equipment or at the source of a
separately derived system.
b. does this mean that if I have, e.g., two green ground wires in a
box, I
should twist them together with an Additional pigtail, put a screw
twist-type connector over them, and then just run the new single pigtail
to
the ground screw ?
You will need a second pig tail for the device if it needs one.
What's wrong with just twisting together the two green ground leads and
running them together to the
screw (perhaps adding a small flat washer over them if the buildup looks
a
bit large for the screw head) ?
Adding an additional pigtail seems like a bit much.
Thoughts on ?
Thanks,
B.
That is in fact what the US NEC requires. There is a listed pressure
connector that has a hole in the tip for the longer EGC to be extended
to the grounding screw. It is commonly called a greenie. A crimp
sleeve can be used in the same way.
--
Tom H
|