(Wheelbarrowbob) wrote in message ...
If the cct you tested was circuit breaker protected by a 32 A mcb the value in
OSG for the Zs value is 1.2 so if you measure your R1 + R2 values and add to
your .19 I am sure you will be in spec
Took the Zs reading at my main intake and the board is all type 1 MCBs
of 32,16 and 6 amps. I shall be doing my R1+R2 test shortly as i
meggered it all a while back and got 200Megs on each circuit.
Though it was time for a full test to BS7671 after all my minor works.
Thanks for the info matey