On 2005-01-04, HorneTD wrote:

Wayne Whitney wrote:

Doesn't doing this require that both circuits be protected by the same
circuit breaker, i.e. a double-pole breaker? It soounds like the OP
had separate OCPDs on the two legs of the multiwire duplex receptacle.


In new installations all of the devices on a yoke or strap must be
deenergized by a single switch, breaker, or pull out but that
requirement is relatively recent. There is no requirement to alter
existing circuits when the code changes.


OK, but I believe the OP was moving a split-circuit receptacle. I
would assume that this requires meeting the new code requirements.

Cheers, Wayne