wrote in message
...
On Sat, 26 May 2018 05:41:56 -0000 (UTC), James Waldby
wrote:

On Fri, 25 May 2018 17:38:09 -0700, etpm wrote:
On Fri, 25 May 2018 08:40:22 -0700 (PDT), "Dave, I can't do that"
wrote:
I have a 1-1/2HP, 220v motor running from the dryer socket, all
good.

...
The house wiring uses the 3-wire 110-0-110 for the 220/240 but the
gen
has three pins for the 240-out. I am guessing one is Ground and
the
others are Neutral and 240v.

...
The reason neutral wires are called that is because they are tied
to
ground in the breaker panel which means there is no potential
voltage
between the neutral wire and the ground wire, at least in the
breaker
panel. So there is no neutral on the generator unless [...]


"The reason neutral wires are called that is because they are tied
to
ground" seems to me to be incorrect. True, in US wiring, neutral
wires
usually have near-ground voltages on them, but more generally a
neutral
wire is one with no current flowing in it when a system is in
balance.

In US wiring the neutral does have current running through it.
Eric


The neutral is the center tap of the pole transformer, and the return
for 120V loads. If you pull 50A from one hot leg and 40A from the
other, the 10A difference will flow back on the neutral.

A voltmeter tells you nothing about currents, you need a clamp-on
ammeter to measure them.