On Saturday, March 5, 2016 at 8:41:02 AM UTC-5, Stormin Mormon wrote:
On 3/5/2016 8:16 AM, DerbyDad03 wrote:
On Saturday, March 5, 2016 at 7:46:12 AM UTC-5, Stormin Mormon wrote:
Anyone wish to answer the OP's OQ?


It was answered within hours of your question, with a qualifying "if".
Since you never directly addressed the "if" it's on you.

I'll make it easy for you:

If this "if" is true, then you already have your answer:

"No if this is the service disconnect enclosure where the ground
electrode conductor lands and the main disconnect resides..."

If that "if" is not true, then you need to tell us more about
the installation. In other words, if the service disconnect is
not in the panel you are asking about, then where is it?


The power comes from the pole to a meter box,
which is outside the house. The power company
can remove the meter and put plastic boots over
the contacts, so I'd dare to say that is a
primitive service disconnect.


It's not a service disconnect per code. Good reason too,
it's not meant to be an easy, accessible means for anyone
to disconnect the service.


I've not been out that side of the house in
several years. don't know how the ground
bar in the ground connects in to the matter.
But, I do know the meter is outdoors.

There is some kind of cable from the meter box
to the circuit breaker panel. The question is
about the circuit breaker panel.

The ground wire in question comes in from outdoors
(in a plastic wrapped sheath with two hots and a
neutral). The ground wire presently connects to
the same metal bar, about an inch from where the
neutral connects.


As previously explained, the ground and the neutral are supposed
to be connected together at the service disconnect. Exactly how
they are connected may vary depending on the panel. Did you pull
up the instructions for the specific panel?


It is possible (enough wire to work with) to move
the ground wire (from outdoors) to a screw connector
on one of the two ground screw bars.


Why do you think you need to move anything?


I'm not a code reading electrician, and thank you
for making it easy for me.

--
.