View Single Post
  #11   Report Post  
Posted to uk.d-i-y
charles charles is offline
external usenet poster
 
Posts: 5,061
Default Wylex plug-in breakers ("upgrade" for ancient fused CUs)

In article , ARW
wrote:
"charles" wrote in message
...
In article , ARW
wrote:
"Mike Tomlinson" wrote in message
...
En el artículo , charles
escribió:

I had to upgrade the 6A lighting breaker to 10A in our village hall
after 2 500w floodlights were added to the lighting circuit.

I was going to ask if the wiring is up to it, but on googling see
that 1mm^2 is ok to 10A and 1.5mm^2 to 15A.



It's not quite that simple.


1mm is OK for 16A when clipped in free air and 1.5mm for 20A.


Surround that cable with insulation and you half the current carrying
capacity.


Now that is usually only a problem IF you are near full load or IF you
have very long cable runs so that the earth loop is too high to trip
the MCB in the event of a fault.


The second one is not very likely to occur on most properties. The
first one depends on the lights that are fitted. A couple of 500W
halogens could shove things over the limits


I don't have any old copies of the Regs to give me current capacities,
but our hall was wired in 3/.029. ISTR it was a bit more than 1.5mm



http://www.electrical-contractor.net/PC/IEE1966_T3.JPG


any good sir?


Excellent - that was the small brown book?

Now what is this voltage drop per 100 ft:-)?


--
from KT24 in Surrey, England