On Nov 18, 3:47*pm, noname wrote:
So since this is the only and main panel, I think the answer is the neutral bar and the ground bar are one and the same, yes?



On Sunday, November 18, 2012 12:22:39 PM UTC-5, The Daring Dufas wrote:
On 11/18/2012 10:28 AM, wrote:


On Sun, 18 Nov 2012 06:54:30 -0800 (PST), noname


wrote:


In this load center are the ground bar and neutral bar interchangeable?


I have the model in the picture, he


http://i1321.photobucket.com/albums/...Shot2012-11-18....


No,


Even in the main panel (Service disconnect enclosure) you should hook


the white wires to the isolated neutral bus(s) and hook the grounds to


the grounding buses.


If you ever decided to make this a sub, all you would have to do is


remove the bonding screw/clip and add a 4 wire feeder but most


importantly, it is a NEC violation to use the grounding bus for


neutral wires (250.6) because you are using the enclosure as a circuit


current path.


"250.6 Objectionable Current.


(A) Arrangement to Prevent Objectionable Current. The grounding of


electrical systems, circuit conductors, surge arresters,


surge-protective devices, and conductive normally non–current-carrying


metal parts of equipment shall be installed and arranged in a manner


that will prevent objectionable current."


You can get a ground bar kit for that panel and keep both neutral bars


but I have seen the bottom buss removed in order to use the left side as


a ground. What I've done in the past is to install can mounted ground


bars on either side connected together with a #4 bare copper


which will keep the wiring a lot neater but everything depends on the


local inspectors. Around here, the city engineering department has their


own stricter requirements than the NEC but the county is much less


strict in their interpretation. Oh yea, what's seen in my area is a #4


bare copper attached to the ground bar going to the ground rod and cold


water pipe then a bonding screw at the main breaker panel tying the


neutral bar/s to the can or a specially made jumper supplied by the


panel manufacturer. The inspector may want a piece of #4 bare copper run


to the ground bar from the neutral bar in addition to the factory


supplied bonding method. It really depends on the local inspectors. O_o


TDD- Hide quoted text -


- Show quoted text -


I think the answer was the neutral wires go to the neutral bus.
The ground wires go to the ground bus. The two buses
are connected together right there, at the panel. That's different
than mixing grounds and neutrals any which way in
the panel.....