Alan Braggins wrote:
In article , John
Rumm wrote:
On 11/09/2012 16:29, Thomas wrote:
The fan I fitted requires 4 connections: neutral, permanent live,
and two switched lives. I bought myself a length of 4 core cable
of the required
Sounds like your bought one wire too few...
If it really doesn't need an earth (double insulated), and he can
find four core in blue, brown, grey and black, that should be enough.
Its very bad practice to re-purpose a green/yellow CPC in a
cable/flex.
While not disagreeing with you, I notice that Googling for "For green
and yellow conductors in multicore cables, overmarking in another
colour at terminations is permitted. This is prohibited for single
core green-and-yellow conductors." has a few hits.
http://www.simptech-solutions.com/eb...egulations.pdf
Reg 514.4.2
The bi-colour combination green-and-yellow shall be used exclusively for the
identification of a protective conductor and this combination shall not be
used for any other purpose"
--
Adam