On 8/31/2010 1:18 AM, Josepi wrote:
12 Ga wire is just a waste of time and money.

A 20 amp breaker would not be allowed to feed most of the lamp fixtures
anyway, with their #18Ga internal wiring,


If you have visions of becoming an electrician, don't quit your day job.
The "internal wiring" of a UL listed lamp fixture has no bearing on
breaker size. If it did then those fixtures would not be allowed on a
15 amp breaker either. The general rule is that the breaker is to
protect the circuit, not the device served by that circuit.

let alone get the #12 under a
screw head terminal that is not rated for the mechanics of it.


Would you be kind enough to identify a UL listed light fixture currently
on the market that has screw head terminals that will not take #12 wire?

The #14 wire is way over engineered already for the recommended max device
rules etc.. and now people come along and try to use a safety factor on top
of all the safety factors built in?


Yep.

Usually, following recommendations and minimum requirements are the "best
practice" from a century of engineering design and field experience.


Nope. The code is a _minimum_ standard. No inspector is going to fault
an electrician for _exceeding_ code. I wish that code had been exceeded
in my house--they wired it all with 12 gage aluminum, barely meeting
code, which I'm slowly replacing with 12 gage copper.

Having said that, many long runs should have #12 used for voltage drop in
ling houses.


Whatever a "ling house" may be.

"J. wrote in message
...
On 8/29/2010 2:32 AM, Morgans wrote:
There is "code" and there is "best practice". Quite frankly if you are
the sort of contractor who does everything to barely pass inspection I