View Single Post
  #35   Report Post  
Posted to alt.home.repair
[email protected] trader4@optonline.net is offline
external usenet poster
 
Posts: 4,500
Default Electric Problem or overloading the circuit

On Dec 25, 4:38*pm, "Twayne" wrote:
,
fzbuilder typed:

Hey Guys, I have a double 20 amp breaker that is connected to each
other. I have one side running the kitchen and one side running the
washing machine in the garage. I was told this is a standard practice,


110Vac appliances, right?

A "ganged" 20A breaker? If one breaker resets, they both have to, right? Is
that what you mean?
* That's what it sounds like and definitely is non-code, NOT standard
practice, and as you're discovering can be dangerous! *


What he is describing is an Edsion circuit, aka shared neutral, and it
is completely compliant with the current code. Why not spend 5 mins
googling, instead of continuing to make an ass of yourself?






Such breakers are
intended to provide 220Vac to some piece of equpiment, NOT as you are using
it, to provide two 110Vac lines. If I'm right AND it's installed properly,
the right one for you box, etc, then you will measure 220Vac between the two
breaker hots, which is its intended use.


Uh, huh and you will also measure 120V between either hot and the
shared neutrals. Which is why it's an Edison circuit.



So if one breaker is overloaded and tries to break, it's going to try to
take the other breaker with it, right? *That's where it becomes DANGEROUS!
If one breaker starts to heat up due to overload, it can't break the ckt
because the other breaker ganged to it is holding it closed, especially if
it's nice and cool. *So who knows how high the overload will have to get
before that overloaded breaker can overcome the non-overloaded breaker and
open, carrying the other one along with it. *Or IF it can even do so period?


It's possible the overloaded breaker never will be able to overcome the
holding power of the other one, and maybe never open up but simply keep on
providing power until something burns open. As you are seeing. *This could
not happen if it were a 220Vac appliance having the problem and it were
wired properly and to code.


If that were true, the same problem would exist with ANY double ganged
breaker, regardless of what it is hooked to.



It's easy enough to fix, IF the overloaded breaker hasn't been ruined by the
overloads! *Just remove the pin/screw, whatever that gangs the levers
together and allow them to operate on their own.


And now you've just told him to take an Edison circuit that completely
conforms to the current NEC and change it into one that does not.
Also, I'd say it's reckless to be telling him to change ANYTHING until
a qualified electrician actuall goes there and figures out what is
wrong.


* *A much better fix would be to replace the ganged breaker set with two
single breakers, since you're using them for 110Vac anyway. *If you need
220Vac, THEN use a ganged breaker, and ONLY for the 220 equipment.

however, I have a portable hot tub that I use in my garage that I only
use when not using the washing machine. The hot tub is plugged into a
GFCI outlet located about 5 feet down the wall off the washer
receptical that was installed before I moved in.


Irrelevant, but; isn't the hot tub 220V? *Is this a case of mixing 110 and
220 on a ganged breaker? *Ouch! *Don't do that.


Clearly you're confused on this too. He made it clear the portable
hot tub is 120V, 20amps. Ever see a 220V hot tub that was only
20amps?







Here is the big problem, I have just noticed a piece of conduit that
comes off the furnace that was buzzing, getting hot and it stopped
after turning off the hot tub, the other day I was running items from
the kitchen and the conduit got so hot it was burning paint off the
wall. I shut off the double 20 amp breaker and it cooled down. It now
gets hot with that breaker off and running a space heater upstairs
that is on another breaker. I have the breaker off on the furnace and
am stumped to what is going on or how this my be wired. The conduit
going to the furnace goes to a junction box on the wall that has some
sort of relay on the top of it. Any help would be great. Thanks


If I've understood you properly, that's all explained by the preceding info
about ganged vs non-ganged breakers.


And even more stupidity. An Edison circuit, completely conforming to
the current NEC sure as hell doesn't explain what he is observing.
And again, suggesting that the simple cure is go to two seperate
breakers to fix a a serious fire hazard is stupid and reckless.
Let's add in that you didn't even tell him that if he screws around
with the existing ganged breakers he needs to make sure he keeps the
two breakers on OPPOSiITE phases or he will most definitely have
changed a code compliant Edison circuite into a fire trap.

Bottom line, once again, this guy needs to get a pro in and stop
listening to clueless posters who won't even do a simple google to
learn what an Edison circuit is.