"YAPH" wrote in message
...
On Mon, 09 Feb 2009 20:32:20 +0000, Heliotrope Smith wrote:
It could be that the regs that I use are out of date.
BS 6172:2004 11.1.1 A gas hob shall be connected to the termination
point
by means of rigid pipework or, unless stated otherwise in the
manufacture's
instructions , a flexible connector and self sealing plug device
conforming
to
BS 669.1.
Perhaps someone can point me to the correct regulation.
That's not in my copy of BS 6172:2004. Mine says:
"""""""""""""""""""""""""""""""""""""""""""""""""" """"""""""""""""""""""
11 Gas Connections
11.1 General
11.1.1 Only gas installation pipes and connectors of sufficient size to
maintain the maximum heat input of a cooking appliance, as specified by
the appliance manufacturer, shall be used.
11.1.2 A cooking range shall be connected to the termination point with
rigid pipework.
11.1.3 Unless stated otherwise in the manufacturer's instructions, a gas
hob shall be connected to the termination point by a rigid fixed
connection.
"""""""""""""""""""""""""""""""""""""""""""""""""" """"""""""""""""""""""
--
John Stumbles -- http://yaph.co.uk
Hypnotising Hypnotists Can Be Tricky
Interesting.
I did quote the reg number wrongly. Should have read 11.1.3 and not
11.1.1
What amendment number do you have?
Mine is 16116 5 January 2006.
It would seem that of our copies has been superseded.