Default circuit tester indicates 'hot/neutral reverse at an outlet...but nothing works at it.

On Nov 4, 10:15 am, "RBM" rbm2(remove wrote:
It definitely sounds like an open circuit, but until you do the test, you
won't know if it's the hot or the neutral leg that's open. You will probably
find a badly back stabbed outlet is the culprit

"brian" wrote in message

oups.com...

Thanks,


I will check those tests later today. I have not changed any
connections yet.


On Nov 4, 8:06 am, "RBM" rbm2(remove wrote:
Those testers are not reliable in open circuit situations. If you use a
lamp
in a pigtail socket, test between the ground and hot(small slot), you
should
get a light. Then test between the hot and neutral, you should get a
light.
If you didn't get the first light, but did get the second, your hot and
neutrals are reversed, otherwise, you have an open circuit to one or the
other conductors. As outlet wiring is typically daisy chained, you want
to
look in the last working outlet on the chain or the first dead outlet ,
for
the loose connection.


"brian" wrote in message


groups.com...


In reading a few posts here, the H/N reversed readout seems not all
that uncommon (using a 3 bulb tester). But in my situation no
appliances work from this outlet, which seems atypical of the posts
I've seem, which seem to say things will work, just un-safely. The
same situation exists at (what I expect) is the next wall outlet along
this circuit.


Could the 'fix' for these outlets be something other than reversing
the connections in the box?


I should also add that I think the end of this circuit is at a never-
functioned ceiling light outlet.


House built 1974. One owner.


Thanks. I know this is very brief, just keeping it simple to start.


Brian


I ran the test with the lamp trster.

I got a light between the hot and neutral, but no light between the
ground and hot.

What worries me is that other posters say they get the same error
message, yet the outlet still allows appliances to work from it, but
un safely. Where these two outlet boxes I have don't allow any
appliances or light to work.

Is that some thing I should be unduly worried about before I attempt
to look for the 'bad' connection?

Thanks