View Single Post
  #59   Report Post  
Posted to alt.home.repair
John Ross John Ross is offline
external usenet poster
 
Posts: 105
Default What is NEC Code For This Grounding Scheme ?



bud-- wrote:
John Ross wrote:


But as far as these wire sizes everyone is throwing around: is that
required or suggested? I hear this size 6 mentioned. Is that the code
from the rod to the panel or is that just suggested. Also, does that
change with the size of the service (this is 100 amp)? I think this
latest electrician said something about size 10 or 8.



Connecting ground rods minimum #6.

Services - depends on service conductors.
Generally 100A #6 is minimum used (can be #8 but the requirements on
installation are very restrictive).
200A service #4
#4 may be used instead of #6 because #6 also has some limitations on use
without 'protection'.

snip
The inspector can also allow variances.
In your case, the jurisdiction or inspector allows connecting the added
receptacle ground wires anywhere on the water pipe while the NEC now
allows that connection only to the first 5 ft of the water pipe. [If the
wire from electric service to water pipe electrode is not in the first 5
ft, as was permitted in the past, it does not make sense to connect
added ground wires in the first 5 ft. And the added ground wires can
usually be more conveniently connected elsewhere in the electrode system.]/snip

I spoke with the electrician today and he said he would use #8 wire
(he said that was for 100 amp panel). Not sure what you meant by "very
restrictive" in using that, I doubt he would do anything different.

Also, I am not so sure anymore that my city does allow the water pipe
connection for add on grounds. In any event, did I understand you
correctly that since the original "bonding" to the pipe was not
required to be 5 foot from entrance, and since it is still all metal,
it doesn't make sense to redo it to within 5 feet (if not required)
i.e. just leave that alone until plastic pipe enters the picture?

I hope this doesn't open up a new can of worms, but I remembered that
the way they did these houses, they didn't have a ground bar in the
panel--the grounds are connected to the neutral bar. I asked him about
that and he said he would just connect the new ground connections to
the neutral bar also and "that was legal." Do you see a problem with
that?

--