On Sep 27, 11:36 am, (Doug Miller) wrote:
False. If metal water pipe is present, it is *required* to use it as a grounding electrode in addition to the other electrodes. It metal water pipe is present, it is *required* to be bonded. Interior metal water pipes must be bonded if the underground pipe is plastic or metal. Makes no difference whether the water pipe does or does not also do earthing. 1) it still must be bonded. 2) the water pipe earth ground is considered so inferior that some other earth ground electrode must be installed. We must remove electricity (electrical faults) from pipes by bonding pipes to breaker box safety grounds. Some jurisdictions also want gas pipe bonded. All water pipes must be bonded so that electricity is not flowing in those pipes. Bonding is essential to human safety. Some jurisdictions so worry about electricity in the plumbing as to require a dedciated bond to steel bathtubs. Are we earthing the bathtub? No. We are bonding it so that electric fault currents will trip a circuit breaker. That also has nothing to do with earthing. When the water pipe is bonded 'less than 5 feet' from earth, then it also acts as an earth ground. But code says the building is still not properly earthed. The building is not earthed until some other earthing electrode is installed. Code still says that water pipe is an earthing electrode (paragraph one). Code also says that water pipe earthing electrode is not sufficient. Some other earthing (from paragraphs two through seven) must be installed so that the building is sufficiently earthed. That cold water pipe must be bonded even if the water pipe makes no earthing connection. Why? We connect to pipes to remove electricity - for human safety. |
#42
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Folks:
"He who argues with a fool makes two" For everybody's benefit but the silly goose's, the reason we must now supplement the water-pipe ground with a driven electrode is because the city might use plastic pipe or dielectric unions. An all-metal city water system, miles of metal pipe full of water buried in damp ground, is a very very very good ground, but we can't always depend on it staying that way. G P |
#43
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, w_tom wrote:
On Sep 27, 11:36 am, (Doug Miller) wrote: False. If metal water pipe is present, it is *required* to use it as a grounding electrode in addition to the other electrodes. It metal water pipe is present, it is *required* to be bonded. Isn't that what I just said? Restoring the part that you just snipped, you wrote: " If using any other earthing electrode, then a water pipe earthing electrode is not required. " That's what I said is false. And it is. You got it right the second time around. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#44
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com,
John Ross wrote: It seems my city doesn't have one competent electrician! Yeah, there's one. He's so busy that he doesn't do any advertising, has an unlisted number, and doesn't even paint a sign on his truck. He works alone because every time he's tried to hire someone, the guy didn't live up to expectations. Keep asking everyone you know, you'll find the guy eventually. |
#45
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
If the water pipe entrance to your house is metal, it must be part of the
grounding electrode system. If it's plastic, obviously not. Any internal sections of piping likely to become energized, must be bonded to the grounding system. The code requires only one ground rod, however it requires you prove with a special meter, the quality of that rod. If you don't have one of these meters, you can just drive the second rod. In this NG there is a newer post about ground rods and Tom Horne pasted the Code section 250.50 which spells this out "John Ross" wrote in message oups.com... RBM remove this wrote: John, the thing you're not getting is that it's a grounding electrode system. Everything that is part of it is connected together and becomes one. If your outlet ground was connected to the panel or the water pipe (first 5 feet) or a ground rod, it's all the same, as they are interconnected I think one thing that throws me off is that when they built these houses, they just connected to the nearest water pipe to the panel (which is on the opposite side of house where water pipe enters). I had an electrician come out and told me he would drive a ground rod and just leave the pipe bond alone (since it is "already connected"). I asked about the 5 foot thing and as EVERY electrician in this town I have talked to, get a blank look or a "I never heard of that." You can see why I am going crazy. But back to your comment about the "grounding electrode system." I thought that 5 foot rule was because of people replacing pipes with plastic. OK, so that makes sense if you look at it as a ground to earth. In other words, if someone adds a plastic pipe past the 5 foot, you now have the earth ground, but I thought the idea of "bonding" pipes was to (also) protect the pipes from becoming energized if a hot wire touches one. So wouldn't you want a requirement to have it bonded to other parts beyond the 5 foot also? Another thing: Not one electrician has told me anything about 2 ground rods; they just say one. Is that a requirement, or just something you think is better? Thanks for the patience It seems my city doesn't have one competent electrician! -- John |
#46
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Tell me you don't wear a tin foil hat
"w_tom" wrote in message ups.com... On Sep 26, 10:04 pm, "RBM" rbm2(remove wrote: Virtually everything you wrote is baseless incoherent gibberish, otherwise you'd be able to produce some NEC documentation to back it up An intelligent reply would have cited what you have problems with. But since you post insults, citing code numbers would not change your mind. Shame on RBM for not even knowing what can and cannot be conductors. Code is specific about what can be conductors. Pipes are no longer permitted. Those who are still living in 1970s would not know that pipes are not acceptable electrical conductors. If spending more time reading, then your responses would be devoid of insults. Profanity identifies one who typically finds reading difficult - who do not know. It explains why RBM knows pipes are acceptable as conductors. Profanity does not change the fact. Water pipes are no longer approved for electrical conductors. RBM should know that if posting recommendations here. Instead he posts profanity - will not even state which parts he has problems with. Note to self. Don't take RBM seriously. His intelligence is defined by his reasoning - insults rather than facts. |
#47
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 12:34 pm, wrote:
On Thu, 27 Sep 2007 08:51:05 -0700, w_tom wrote: Using water pipes as conductors is not acceptable. http://esteroriverheights.com/electrical/ground.jpg 250.21 from the 2002 handbook Ahh, but that picture is not using pipes as a conductor. That 'less than five feet' is where the pipe is an earthing electrode according to code. Code defines a difference between an electrode and a conductor. To be an electrode, the connection to that pipe must be "less than 5 feet". If connecting the breaker box to earth via a cold water pipe anywhere inside the building, then those pipes are being used a conductors - not legal. Some jurisdictions will reject your picture IF those ground connections are not together. Others may reject it altogether; want the ring ground (halo ground) or ground rod 6 AWG wire to be attached directly to the 6 AWG wire from breaker box with a split bolt or something that connects those wires together without the pipe. All jurisdictions will reject that connection if the various grounds do not connect 5 feet from earth. If the pipe is being used as a conductor - if the pipe connected between those various clamps is many meters apart - then it is not legal. Since those wires bond adjacent to each other, then most jurisdictions will consider that pipe an electrode - not a conductor. From that pictu "Connection made within 5 ft of point of entrance of pipe." At that point, the pipe is considered an electrode - not a conductor. Using pipes as a conductor to connect a ground rod to breaker box is not acceptable. In John Ross's situation, the breaker box was earthed to a pipe much more than 5 feet from where pipe contacts earth. Therefore the pipe (as an earthing connection) was being used as a conductor - no longer acceptable. That connection was sufficient for bonding pipes to the breaker box. But it is no longer acceptable as an earth ground. IOW from the perspective of code. John Ross had no earth ground until the electrician connected a ground rod to breaker box (again, a connection not made using his pipes). For the pipe to be an electrode, code says that pipe connection must be less than five feet from earth. Electrode conductors can merge on one electrode. Connection to earth on pipes farther than 5 feet means the pipe is being used as a conductor. Yes, some jurisdictions may permit merging connections from various electrodes on one pipe too far from earth. Others may not if the pipe is not considered an electrode. But that picture clearly shows connection made adjacent where the pipe is a earthing electrode; is not a conductor. |
#48
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 12:40 pm, (Doug Miller) wrote:
It metal water pipe is present, it is *required* to be bonded. Isn't that what I just said? Restoring the part that you just snipped, you wrote: " If using any other earthing electrode, then a water pipe earthing electrode is not required. " That's what I said is false. And it is. You got it right the second time around. "If using any other earthing electrode" is not even a valid "IF" here. Replace "If using" with "Required is using" any other earthing electrode. Does not matter whether the water pipe is or is not an earthing electrode to breaker box. The error was that the state of the water pipe (if or if not an electrode) is completely irrelevant. The code now says some other earthing electrode from paragraphs two through seven MUST be installed. Yes exceptions exist. But those exceptions do not apply here. John had no earthing electrode. What John considered an earth ground was not connected 'less than 5 feet' from earth; therefore was not an earthing electrode. He must install one that meets current codes. That is what one electrician would have done if connecting a earth ground rod directly to breaker box - no other changes. Relevant in John Ross's situation: John had no earthing electrode. His breaker box was earthed by using pipes as a conductor. John has no choice. His breaker box needs an earthing electrode that connects to breaker box via 6 AWG wire; not connected via pipes. Connecting a ground rod to his pipe where pipe is an electrode still would not meet code. Both pipe and ground rod electrode would still be using pipes as a conductor. Not acceptable. He must connect a new earth ground rod to breaker box only via approved conductors such as 6 AWG bare copper wire. |
#49
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
w_tom wrote:
That '5 foot' requirement is for numerous reasons. One is due to currents existing outside the building. A water pipe entering the building must be bonded to the breaker box safety ground where those currents would enter the building. Those currents would only travel inside the builiding on less than 5 feet. Obviously high on drugs when he wrote this. And as Roy suspects, w_ protects himself with these: http://zapatopi.net/afdb/ I am appauled that you would have Bud do any electrical work. He is a salesman - all about presentation and severely short on electrical knowledge. His knowledge comes only from reading books and taking seminars. He is a promoter - a snake oil salesman - has been exposed lying. I am an electrical engineer and master electrician **** head. What are your qualifications for pontificating on the electrical code? In this thread you are arguing against at least 2 electricians and an electrical inspector. Plus others. Plus a cast of thousands in your previous idiotic posts on this subject. And it is you who regularly posts lies. Like in this thread. -- bud-- |
#50
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
w_tom wrote:
Does not matter whether the water pipe is or is not an earthing electrode to breaker box. The error was that the state of the water pipe (if or if not an electrode) is completely irrelevant. The code now says some other earthing electrode from paragraphs two through seven MUST be installed. Only for new installations. Adding ground wires for receptacles is not likely to trigger installation of a “supplemental” electrode. Yes exceptions exist. But those exceptions do not apply here. John had no earthing electrode. John has a water service pipe electrode. What John considered an earth ground was not connected 'less than 5 feet' from earth; therefore was not an earthing electrode. What John has was code compliant when it was installed. There is no requirement to change the connection unless he changes the service. He must install one that meets current codes. Bullcrap. He also doesn’t have to bring his whole house up to the current electrical code. Your stupidity is breathtaking. -- bud-- |
#51
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article . com, w_tom wrote:
On Sep 27, 12:40 pm, (Doug Miller) wrote: It metal water pipe is present, it is *required* to be bonded. Isn't that what I just said? Restoring the part that you just snipped, you wrote: " If using any other earthing electrode, then a water pipe earthing electrode is not required. " That's what I said is false. And it is. You got it right the second time around. "If using any other earthing electrode" is not even a valid "IF" here. Replace "If using" with "Required is using" any other earthing electrode. Does not matter whether the water pipe is or is not an earthing electrode to breaker box. The error was that the state of the water pipe (if or if not an electrode) is completely irrelevant. And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#52
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
bud-- wrote: w_tom wrote: Does not matter whether the water pipe is or is not an earthing electrode to breaker box. The error was that the state of the water pipe (if or if not an electrode) is completely irrelevant. The code now says some other earthing electrode from paragraphs two through seven MUST be installed. Only for new installations. Adding ground wires for receptacles is not likely to trigger installation of a "supplemental" electrode. Yes exceptions exist. But those exceptions do not apply here. John had no earthing electrode. John has a water service pipe electrode. What John considered an earth ground was not connected 'less than 5 feet' from earth; therefore was not an earthing electrode. What John has was code compliant when it was installed. There is no requirement to change the connection unless he changes the service. He must install one that meets current codes. Bullcrap. He also doesn't have to bring his whole house up to the current electrical code. Your stupidity is breathtaking. -- bud-- Even though I probably don't *have* to to it, I assume adding the ground rod would be a good idea since the added cost is minimal--I assume you agree? One thing on that aspect: this area generally has hardpan soil condition. Is that good or bad news? But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. And, if it is bonded correctly to the first five feet of pipe, what size of wire is require for that (that would be around a 30 foot run)? I never would have imagined trying to ground a receptacle would turn into such an ordeal! And, like I said, not one of these electricians know what I am talking about when I qquote the NEC codes you guys mention. Scary...Had I not asked in here, I would have gone with that one guy who had the isolated ground rod that made no sense now that it was explained to me here. BTW, I thought I was clever and called the electrical supply places for a recommendation for an electrician. They were of no help. Can anyone think of another source that would know a good electrician? -- John |
#53
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Fri, 28 Sep 2007 06:02:49 -0700, John Ross
wrote: BTW, I thought I was clever and called the electrical supply places for a recommendation for an electrician. They were of no help. Can anyone think of another source that would know a good electrician? They probably didn't want to risk the loss of future business from all possible electricians by appearing to endorse one over the others. I get all my best contractor references from friends and colleagues; works every time. Ask around. Or tell us your location, and someone here might be able to recommend someone local to you. |
#54
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. Connecting ground rods minimum #6. Services - depends on service conductors. Generally 100A #6 is minimum used (can be #8 but the requirements on installation are very restrictive). 200A service #4 #4 may be used instead of #6 because #6 also has some limitations on use without 'protection'. I never would have imagined trying to ground a receptacle would turn into such an ordeal! And, like I said, not one of these electricians know what I am talking about when I qquote the NEC codes you guys mention. Scary...Had I not asked in here, I would have gone with that one guy who had the isolated ground rod that made no sense now that it was explained to me here. It should be noted that comments are based on the National Electrical Code. The NEC has authority only as adopted by entities that have control over electrical installations - states, cities, ... The NEC is the basis for the local code everywhere I know of, but can (and is) modified by many jurisdictions. The inspector can also allow variances. In your case, the jurisdiction or inspector allows connecting the added receptacle ground wires anywhere on the water pipe while the NEC now allows that connection only to the first 5 ft of the water pipe. [If the wire from electric service to water pipe electrode is not in the first 5 ft, as was permitted in the past, it does not make sense to connect added ground wires in the first 5 ft. And the added ground wires can usually be more conveniently connected elsewhere in the electrode system.] The NEC chapter on grounding is probably the most confusing of the commonly used chapters. -- bud-- |
#55
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 27, 3:40?pm, "RBM" rbm2(remove wrote:
Tell me you don't wear a tin foil hat "w_tom" wrote in message ups.com... On Sep 26, 10:04 pm, "RBM" rbm2(remove wrote: Virtually everything you wrote is baseless incoherent gibberish, otherwise you'd be able to produce some NEC documentation to back it up An intelligent reply would have cited what you have problems with. But since you post insults, citing code numbers would not change your mind. Shame on RBM for not even knowing what can and cannot be conductors. Code is specific about what can be conductors. Pipes are no longer permitted. Those who are still living in 1970s would not know that pipes are not acceptable electrical conductors. If spending more time reading, then your responses would be devoid of insults. Profanity identifies one who typically finds reading difficult - who do not know. It explains why RBM knows pipes are acceptable as conductors. Profanity does not change the fact. Water pipes are no longer approved for electrical conductors. RBM should know that if posting recommendations here. Instead he posts profanity - will not even state which parts he has problems with. Note to self. Don't take RBM seriously. His intelligence is defined by his reasoning - insults rather than facts.- Hide quoted text - - Show quoted text - your better off using 2 ground rods because during wet weather one might pass the resistance check but not during a dry spell. in addition all grounds for things like telephone NID and satellite dishes must be joined together to meet code. |
#56
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 28, 9:02 am, John Ross wrote:
I never would have imagined trying to ground a receptacle would turn into such an ordeal! And, like I said, not one of these electricians know what I am talking about when I qquote the NEC codes you guys mention. Scary...Had I not asked in here, I would have gone with that one guy who had the isolated ground rod that made no sense now that it was explained to me here. Minimum that was required was an earth ground rod near breaker box and connected direct to breaker box. Your description implies no proper earthing existed. A ground rod connected as close as possible to the breaker box is the only upgrade required and serves other useful purposes beyond what is addressed by code. Other utilities (cable and telephone) should connect to that same ground so that those utilities provide minimally sufficient electronics protection (as hallerb suggests elsewhere). That suggested to meet current code even though other marginal earthing is not required to be upgraded. I no longer rememeber if this recommendation was posted. Other simplest corrections to consider for human safety were summarized by volts500 in alt.home.repair entitled "Grounding Rod Info" on 12 July 2003 at http://tinyurl.com/hkjq Those recommendations are so simple, so easy, so inexpensive, and so improve human safety issues as to also be performed - to upgrade basic safety grounding closer to what current code requires. The only thing you do not have (according to your description) and that you must correct is earthing of AC electric. Those additions to safety grounding inside the house (from volts500) and the tying of all incoming utilities to a common ground are required by current code; not necessary for you to upgrade; but should be performed anyway because those little improvements provide significant human safety improvements for so little effort. What size should a ground wire be? That varies based on things such as the amperage of electric service as summarized by gfretwell. Standard used in most all homes is 6 AWG. Ground wire is usually larger than what is required by code. 6 AWG copper is an industry default standard for residential electric. |
#57
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 28, 8:06 am, (Doug Miller) wrote:
And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. However code is written so that a water pipe may also be an earthing electrode - albeit insufficient. If water pipe is used as an earthing electrode, that still in not sufficient to meet code requirements for earthing as stated in article 250.52(D). Earthing must be provided by any one of items listed in article 250.52(A) paragraphs two through seven. Paragraph one defines how a water pipe might be an earthing electrode. Code requires any one of those other earthing electrodes - in paragraphs two through seven - to exist. Code says an earthing electrode must exist AND lists the only valid six electrodes that meet that requirement. |
#58
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article . com, w_tom wrote:
On Sep 28, 8:06 am, (Doug Miller) wrote: And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. False. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present ... shall be bonded together to form the grounding electrode system. ... 250.52(A)(1) Metal underground water pipe." If it's there, Code requires it to be used "to form the grounding electrode system" i.e. as an earth ground. However code is written so that a water pipe may also be an earthing electrode Wrong -- it MUST be a grounding electrode if it's present. - albeit insufficient. If water pipe is used as an earthing electrode, that still in not sufficient to meet code requirements for earthing as stated in article 250.52(D). True -- but not relevant to the question of whether using it is optional or required. If it's present at all, its use as part of the grounding electrode system is MANDATORY. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#59
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
bud-- wrote: John Ross wrote: But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. Connecting ground rods minimum #6. Services - depends on service conductors. Generally 100A #6 is minimum used (can be #8 but the requirements on installation are very restrictive). 200A service #4 #4 may be used instead of #6 because #6 also has some limitations on use without 'protection'. snip The inspector can also allow variances. In your case, the jurisdiction or inspector allows connecting the added receptacle ground wires anywhere on the water pipe while the NEC now allows that connection only to the first 5 ft of the water pipe. [If the wire from electric service to water pipe electrode is not in the first 5 ft, as was permitted in the past, it does not make sense to connect added ground wires in the first 5 ft. And the added ground wires can usually be more conveniently connected elsewhere in the electrode system.]/snip I spoke with the electrician today and he said he would use #8 wire (he said that was for 100 amp panel). Not sure what you meant by "very restrictive" in using that, I doubt he would do anything different. Also, I am not so sure anymore that my city does allow the water pipe connection for add on grounds. In any event, did I understand you correctly that since the original "bonding" to the pipe was not required to be 5 foot from entrance, and since it is still all metal, it doesn't make sense to redo it to within 5 feet (if not required) i.e. just leave that alone until plastic pipe enters the picture? I hope this doesn't open up a new can of worms, but I remembered that the way they did these houses, they didn't have a ground bar in the panel--the grounds are connected to the neutral bar. I asked him about that and he said he would just connect the new ground connections to the neutral bar also and "that was legal." Do you see a problem with that? -- John |
#60
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Doug Miller wrote: In article . com, w_tom wrote: On Sep 28, 8:06 am, (Doug Miller) wrote: And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. False. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present ... shall be bonded together to form the grounding electrode system. .. 250.52(A)(1) Metal underground water pipe." If it's there, Code requires it to be used "to form the grounding electrode system" i.e. as an earth ground. However code is written so that a water pipe may also be an earthing electrode Wrong -- it MUST be a grounding electrode if it's present. - albeit insufficient. If water pipe is used as an earthing electrode, that still in not sufficient to meet code requirements for earthing as stated in article 250.52(D). True -- but not relevant to the question of whether using it is optional or required. If it's present at all, its use as part of the grounding electrode system is MANDATORY. -- Regards, Doug Doug, as it is now the only ground is to the water pipe, but back then they just connected it any convenient place near panel--not within 5 foot of pipe entrance. So if I have the ground rod installed AND leave the current situation, am I right in that it will still serve as a earth ground AND a bonding to the pipes. BTW, it is still all metal, so if not required, I would assume it is ok just to leave that as is. Does that satisfy what you said above? -- John |
#61
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
wrote: On Fri, 28 Sep 2007 06:02:49 -0700, John Ross wrote: But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. It is really based on the size of the service entrance cables 250.66, which is usually based on the service disconnect size but that varies between residential and commercial. Residential generally gets away with a smaller SE cable because of load diversity. The other rules refer to the particular electrode used. You never need more than a #6 to a ground rod/plate, #4 to a UFER. When you are stringing several electrodes togerther you need the minimum size for the best electrode down stream up to the 250.66 size. Water pipes always use the 250.66 size. 250.66 (short version) SE cable GEC size copper aluminum Cu Al Res service 2 or smaller 1/0 or smaller 8 6 typical 100a 1 or 1/0 2/0 or 3/0 6 4 typical 150a 2/0 or 3/0 4/0 or 250 4 2 typical 200a Thanks for the chart, but I have to admit I have no idea what those abbreviations mean. I asked the electrician today what size wire would go from ground rod to panel and he said #8 since it was a 100 amp. It sounds like you are saying it should be #6? -- John |
#62
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
bud-- wrote: w_tom wrote: Does not matter whether the water pipe is or is not an earthing electrode to breaker box. The error was that the state of the water pipe (if or if not an electrode) is completely irrelevant. The code now says some other earthing electrode from paragraphs two through seven MUST be installed. Only for new installations. Adding ground wires for receptacles is not likely to trigger installation of a "supplemental" electrode. Yes exceptions exist. But those exceptions do not apply here. John had no earthing electrode. John has a water service pipe electrode. What John considered an earth ground was not connected 'less than 5 feet' from earth; therefore was not an earthing electrode. What John has was code compliant when it was installed. There is no requirement to change the connection unless he changes the service. He must install one that meets current codes. Bullcrap. He also doesn't have to bring his whole house up to the current electrical code. Your stupidity is breathtaking. -- bud-- Even though I probably don't *have* to to it, I assume adding the ground rod would be a good idea since the added cost is minimal--I assume you agree? One thing on that aspect: this area generally has hardpan soil condition. Is that good or bad news? But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. And, if it is bonded correctly to the first five feet of pipe, what size of wire is require for that (that would be around a 30 foot run)? I never would have imagined trying to ground a receptacle would turn into such an ordeal! And, like I said, not one of these electricians know what I am talking about when I qquote the NEC codes you guys mention. Scary...Had I not asked in here, I would have gone with that one guy who had the isolated ground rod that made no sense now that it was explained to me here. BTW, I thought I was clever and called the electrical supply places for a recommendation for an electrician. They were of no help. Can anyone think of another source that would know a good electrician? -- John John I'll get grief for this but I suggest you call the nearest office of the International Brotherhood of Electrical Workers (IBEW). Numerous people will now tell you that they will cost too much but that just isn't so. On average a unionized shop employs twelve electricians. The pricing of Electrical work is very competitive. The difference between a unionized shop and a non union shop is not what the customer pays but that more of what you pay goes to wages and benefits. Better pay attracts better electricians. A union inside wireman has four years of formal training. A union residential wireman has at least two years of formal training and four years of supervised field experience before they can work unsupervised. I am self employed but I was trained by the Joint Apprenticeship and Training Program of the National Electrical Contractors Association (NECA) and the IBEW. The Union local office will be happy to give you the names of three NECA member contractors that do residential work. You will then have a better chance of getting a quality job. No group of electricians is completely free of dunderheads but using a union shop will at least improve your odds. -- Tom Horne |
#63
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
bud-- wrote: John Ross wrote: But as far as these wire sizes everyone is throwing around: is that required or suggested? I hear this size 6 mentioned. Is that the code from the rod to the panel or is that just suggested. Also, does that change with the size of the service (this is 100 amp)? I think this latest electrician said something about size 10 or 8. Connecting ground rods minimum #6. Services - depends on service conductors. Generally 100A #6 is minimum used (can be #8 but the requirements on installation are very restrictive). 200A service #4 #4 may be used instead of #6 because #6 also has some limitations on use without 'protection'. snip The inspector can also allow variances. In your case, the jurisdiction or inspector allows connecting the added receptacle ground wires anywhere on the water pipe while the NEC now allows that connection only to the first 5 ft of the water pipe. [If the wire from electric service to water pipe electrode is not in the first 5 ft, as was permitted in the past, it does not make sense to connect added ground wires in the first 5 ft. And the added ground wires can usually be more conveniently connected elsewhere in the electrode system.]/snip I spoke with the electrician today and he said he would use #8 wire (he said that was for 100 amp panel). Not sure what you meant by "very restrictive" in using that, I doubt he would do anything different. 2005 NEC 250.64-B "Securing and protection against physical damage" "Grounding electrode conductors smaller than 6AWG [#8} shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metalic tubing, or cable armor." All of them are a form of pipe (some are light weight pipe) except cable armor which is a spiral metal protection like BX. If the conductor is run through ferrous tubing/pipe there are additional requirements that directly or indirectly bond both ends of the pipe to the grounding conductor. If you use one of the required protection methods #6 should be cheaper. "A 6AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; other wise it shall" use one of the protective methods above. "A 4AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage." Also, I am not so sure anymore that my city does allow the water pipe connection for add on grounds. In any event, did I understand you correctly that since the original "bonding" to the pipe was not required to be 5 foot from entrance, and since it is still all metal, it doesn't make sense to redo it to within 5 feet (if not required) i.e. just leave that alone until plastic pipe enters the picture? My intent was if the electrode connection to the water pipe is not within 5 ft of the building entrance, the restriction of connecting your added receptacle ground wires within 5 ft of the entrance does not make sense. I would usually split bolt the receptacle ground wires to one of the heavy grounding electrode wires anyway. If the electrode connection to the water pipe is not withing 5 ft of the entrance it is safe as a grounding electrode as long as the metal water pipe is intact. Your call whether you move the connection. [Note that when w_ talks about "bonding" the water pipe, it is not for using it as a grounding electrode, but is the connection required if the water service is plastic.] I hope this doesn't open up a new can of worms, but I remembered that the way they did these houses, they didn't have a ground bar in the panel--the grounds are connected to the neutral bar. I asked him about that and he said he would just connect the new ground connections to the neutral bar also and "that was legal." Do you see a problem with that? At the service panel only (not downstream subpanels) the neutral and ground are connected. The neutral bar is usually insulated from the enclosure, but they should [almost] always be connected together at the service panel. The connection is often by a screw that goes through the neutral bar and screws into the enclosure behind - not at all obvious. The neutral-ground connection at the service is part of providing a low resistance metal path for short circuit currents to trip breakers. The path is ground wire to neutral-ground bond to service neutral to transformer. -- bud-- |
#64
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Doug Miller wrote:
In article . com, w_tom wrote: On Sep 28, 8:06 am, (Doug Miller) wrote: And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. False. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present ... shall be bonded together to form the grounding electrode system. .. 250.52(A)(1) Metal underground water pipe." If it's there, Code requires it to be used "to form the grounding electrode system" i.e. as an earth ground. As I'm sure you are aware, this has been pointed out by numerous people in numerous threads. It is incredible how someone could be so stupid to say water pipe is not required to be an electrode. The code, as you quote it, is absolutely clear. -- bud-- |
#65
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, John Ross wrote:
Doug Miller wrote: In article . com, w_tom wrote: On Sep 28, 8:06 am, (Doug Miller) wrote: And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. False. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present ... shall be bonded together to form the grounding electrode system. .. 250.52(A)(1) Metal underground water pipe." If it's there, Code requires it to be used "to form the grounding electrode system" i.e. as an earth ground. However code is written so that a water pipe may also be an earthing electrode Wrong -- it MUST be a grounding electrode if it's present. - albeit insufficient. If water pipe is used as an earthing electrode, that still in not sufficient to meet code requirements for earthing as stated in article 250.52(D). True -- but not relevant to the question of whether using it is optional or required. If it's present at all, its use as part of the grounding electrode system is MANDATORY. Doug, as it is now the only ground is to the water pipe, but back then they just connected it any convenient place near panel--not within 5 foot of pipe entrance. So if I have the ground rod installed AND leave the current situation, am I right in that it will still serve as a earth ground AND a bonding to the pipes. No, not unless the connection to the water pipe is within 5 feet of the entrance. BTW, it is still all metal, so if not required, I would assume it is ok just to leave that as is. Does that satisfy what you said above? Ground rod, and connection to the metal water pipe within 5' of the point at which it enters the building. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#66
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
|
#67
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 30, 11:15 am, (Doug Miller) wrote:
No, not unless the connection to the water pipe is within 5 feet of the entrance. ... Ground rod, and connection to the metal water pipe within 5' of the point at which it enters the building. Code demands that the AC electric have a proper connection to earth ground. Any one of the electrodes in paragraphs two through seven are sufficient. The electrode defined in paragraph one (water pipe) is not sufficient. Assume that John Ross was correct - that ALL earthing electrodes must be connected. Then every steel I-beam concreted in earth must be bonded to the breaker box. Water well casing must be bonded to AC breaker box. All rebar inside concrete footing must be bonded. Rebar inside any concrete basement floor must be bonded. Any steel plate buried in earth must be bonded. Any "other local metal underground system or structure such as piping systems and underground tanks" (quoted from paragraph seven) must also be connected to breaker box. According to John, if any of those six items exist, then they also must be bonded to the breaker box. Why are bonding wires not attached to every of six items? Because Doug Miller is wrong. The breaker box only needs one earthing electrode that conforms to paragraphs two through seven. Code says that any electrode used for earthing must be bonded together to form a single earth grounding system. Any of those other six electrodes not being used for earthing need not be connected to the breaker box - in direct contradiction to Doug Miller and the naive salesman Bud. Code says that any electrode connected for earth must also be bonded to the breaker box. If used to earth the telephone line protector, then that electrode must also be bonded to AC electric box. If cable TV is earthed to any of those electrodes, then that electrode also must bond to breaker box. Any electrode used as earth ground must be bonded together. Listed are six earthing electrodes that would not be connected to breaker box because nothing was using them for earth ground. According to Doug Miller, all six of those electrodes also must be connected by 6 AWG wire. If you want to bond the 'first five feet of water pipe' to breaker box, then by all means do so. But that is beyond what code would require of John Ross. What is most clearly required: a connection from breaker box to any other earthing electrode used to ground telephone, cable TV, satellite dish, TV antenna, etc. Those connection are required by code so that all 'being used electrodes' are bonded into one earthing system. Yes, the phone line and cable TV earthing electrodes also must earth the AC breaker box because those electrodes are being used to earth telephone and cable - as also required by code. A metal underground tank is an earthing electrode according to paragraph seven. But if not being used by anything as an earth ground, then AC breaker box also need not be bonded to that underground tank ... in direct contradiction to what Doug Miller and naive salesman Bud have posted. |
#68
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Sep 30, 8:00 pm, w_tom wrote:
According to John, if any of those six items exist, then they also must be bonded to the breaker box. Correction. This should have read "According to Doug Miller, if any of those six tiems exists, then ..." |
#69
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, w_tom wrote:
On Sep 30, 8:00 pm, w_tom wrote: According to John, if any of those six items exist, then they also must be bonded to the breaker box. Correction. This should have read "According to Doug Miller, if any of those six tiems exists, then ..." Correction: according to the National Electrical Code. I even quoted the relevant portions of it. Here, I'll do it again. Pay attention this time. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present at each building or structure served SHALL BE bonded together to form the grounding electrode system." [2005 NEC, Article 250.50] -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#70
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, w_tom wrote:
On Sep 30, 11:15 am, (Doug Miller) wrote: No, not unless the connection to the water pipe is within 5 feet of the entrance. ... Ground rod, and connection to the metal water pipe within 5' of the point at which it enters the building. Code demands that the AC electric have a proper connection to earth ground. Any one of the electrodes in paragraphs two through seven are Actually, it's one through six: 250.52(A)(1) through 250.52(A)(6). sufficient. The electrode defined in paragraph one (water pipe) is not sufficient. Code *also* demands that all of those electrodes be bonded together. Assume that John Ross was correct - that ALL earthing electrodes must be connected. They must be, per Article 250.50 -- you really ought to read it some time. Then every steel I-beam concreted in earth must be bonded to the breaker box. False. Code requires the "metal frame of the building or structure" to be bonded to the grounding electrode system. It does not require every individual component of the frame to be so bonded. Water well casing must be bonded to AC breaker box. False. There is no requirement that it be bonded separately from the pipe(s) it is connected to. All rebar inside concrete footing must be bonded. Rebar inside any concrete basement floor must be bonded. False. Rebar less than 1/2" in diameter, or less than 20' in length, is not required to be bonded. There also is no requirement that individual pieces of rebar be separately bonded to the grounding electrode system; Code specifically permits them to be bonded to _each_other_ "by the usual steel tie wires or other effective means." Any steel plate buried in earth must be bonded. False. Again, as with rebar, there are size requirements of which you appear completely ignorant. Any "other local metal underground system or structure such as piping systems and underground tanks" (quoted from paragraph seven) must also be connected to breaker box. Ahh, finally you got one correct. According to John, if any of those six items exist, then they also must be bonded to the breaker box. According to the NEC. Why are bonding wires not attached to every of six items? Probably because you, or someone who listened to your ignorant ravings, installed the grounding electrode system. Because Doug Miller is wrong. The breaker box only needs one earthing electrode that conforms to paragraphs two through seven. Try again, bozo. Yes, one such electrode is sufficient. But if there are *two* such electrodes present, they must *both* be used as grounding electrodes. Code says that any electrode used for earthing must be bonded together to form a single earth grounding system. Any of those other six electrodes not being used for earthing need not be connected to the breaker box - in direct contradiction to Doug Miller and the naive salesman Bud. Absolutely false. You simply do not have the first clue what you are talking about. Code specifically and clearly says that ALL such electrodes that are present SHALL BE bonded together. If one of those electrodes is present and *not* being used for grounding, that's a clear Code violation. Now go get yourself a copy of the 2005 Code, read Article 250.50, and STFU. Code says that any electrode connected for earth must also be bonded to the breaker box. If used to earth the telephone line protector, then that electrode must also be bonded to AC electric box. If cable TV is earthed to any of those electrodes, then that electrode also must bond to breaker box. Any electrode used as earth ground must be bonded together. Listed are six earthing electrodes that would not be connected to breaker box because nothing was using them for earth ground. According to Doug Miller, all six of those electrodes also must be connected by 6 AWG wire. No, not according to me. According to the National Electrical Code. Try reading it some time. If you want to bond the 'first five feet of water pipe' to breaker box, then by all means do so. But that is beyond what code would require of John Ross. False again. Metal water pipe is required to be bonded as part of the grounding electrode system. Water pipe more than 5' from the point at which it enters the building is not permitted to be used as part of the grounding electrode system -- therefore, the bonding must be within the first five feet. What is most clearly required: What is most clearly required is for you to read the Code, before you try to talk about what it means. A metal underground tank is an earthing electrode according to paragraph seven. But if not being used by anything as an earth ground, ... then it's a Code violation: it's present, but it's not bonded. then AC breaker box also need not be bonded to that underground tank ... in direct contradiction to what Doug Miller and naive salesman Bud have posted. What part of "ALL ... that are present ... SHALL BE BONDED TOGETHER" are you having such a hard time understanding?? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#71
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
bud-- wrote: John Ross wrote: bud-- wrote: John Ross wrote: I spoke with the electrician today and he said he would use #8 wire (he said that was for 100 amp panel). Not sure what you meant by "very restrictive" in using that, I doubt he would do anything different. 2005 NEC 250.64-B "Securing and protection against physical damage" "Grounding electrode conductors smaller than 6AWG [#8} shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metalic tubing, or cable armor." All of them are a form of pipe (some are light weight pipe) except cable armor which is a spiral metal protection like BX. If the conductor is run through ferrous tubing/pipe there are additional requirements that directly or indirectly bond both ends of the pipe to the grounding conductor. If you use one of the required protection methods #6 should be cheaper. It will need protection where it is located. The cable armor sounds the easiest (to bend), does that contain ferrous? snip If the electrode connection to the water pipe is not withing 5 ft of the entrance it is safe as a grounding electrode as long as the metal water pipe is intact. Your call whether you move the connection. If it HAS to be moved, did you or someone say it has to be one contiuous wire all the way back to panel? I'm not sure how he could do that without wall damage. Can it be clamped to the point where it currently is at pipe and then jumpered to within 5 feet of entrance? I hope this doesn't open up a new can of worms, but I remembered that the way they did these houses, they didn't have a ground bar in the panel--the grounds are connected to the neutral bar. I asked him about that and he said he would just connect the new ground connections to the neutral bar also and "that was legal." Do you see a problem with that? At the service panel only (not downstream subpanels) the neutral and ground are connected. The neutral bar is usually insulated from the enclosure, but they should [almost] always be connected together at the service panel. The connection is often by a screw that goes through the neutral bar and screws into the enclosure behind - not at all obvious. The neutral-ground connection at the service is part of providing a low resistance metal path for short circuit currents to trip breakers. The path is ground wire to neutral-ground bond to service neutral to transformer. This panel (there is only one at house) has NO ground bar--grounds and neutrals are on the "neutral" bar. So he is proposing just adding these new ground connections there as well. Is that OK? If they are bonded together anyway, I can't see how it could hurt, but as you know this is all new to me. -- John |
#72
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Doug Miller wrote: In article .com, John Ross wrote: Doug Miller wrote: In article . com, w_tom wrote: On Sep 28, 8:06 am, (Doug Miller) wrote: And now you've gone and gotten it wrong again. Metal water pipe is *required* to be used as a grounding electrode. You said it's not. That's not true. Code only requires water pipe must be bonded. That 'bonding' to remove fault currents from pipes. Code does not require water pipe to be used as an earth ground. False. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present ... shall be bonded together to form the grounding electrode system. .. 250.52(A)(1) Metal underground water pipe." If it's there, Code requires it to be used "to form the grounding electrode system" i.e. as an earth ground. However code is written so that a water pipe may also be an earthing electrode Wrong -- it MUST be a grounding electrode if it's present. - albeit insufficient. If water pipe is used as an earthing electrode, that still in not sufficient to meet code requirements for earthing as stated in article 250.52(D). True -- but not relevant to the question of whether using it is optional or required. If it's present at all, its use as part of the grounding electrode system is MANDATORY. Doug, as it is now the only ground is to the water pipe, but back then they just connected it any convenient place near panel--not within 5 foot of pipe entrance. So if I have the ground rod installed AND leave the current situation, am I right in that it will still serve as a earth ground AND a bonding to the pipes. No, not unless the connection to the water pipe is within 5 feet of the entrance. BTW, it is still all metal, so if not required, I would assume it is ok just to leave that as is. Does that satisfy what you said above? Ground rod, and connection to the metal water pipe within 5' of the point at which it enters the building. Doug, I understand what you are saying about current code. My point was that in 1960 they didn't care where on the pipe it was located. As it is now, it IS the ground for the house, but probably nowhere near 5 feet from entrance. My understanding is that rule was simply because of worry of plastic pipes being used in repairs etc. So what I was saying was that IF they don't require the current code for that if installing a ground rod, I still will have a ground to earth through the pipes since it is still all metal. Someone said there were "other" reasons to do with stray currents in the first 5 feet etc. and you ridiculed him. So I assume that code or no code, just adding a ground rod won't magically make my present pipe earth ground disappear. Agree? -- John |
#73
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article .com, John Ross wrote:
Doug, I understand what you are saying about current code. My point was that in 1960 they didn't care where on the pipe it was located. As it is now, it IS the ground for the house, but probably nowhere near 5 feet from entrance. Yes, but new work needs to be done to current code. Check with your local electrical inspection authority to be sure -- but I imagine they'll construe that to require you to bond the water pipe within 5' of the entrance. My understanding is that rule was simply because of worry of plastic pipes being used in repairs etc. So what I was saying was that IF they don't require the current code for that if installing a ground rod, I still will have a ground to earth through the pipes since it is still all metal. Someone said there were "other" reasons to do with stray currents in the first 5 feet etc. and you ridiculed him. Nope, not me. That was someone else. Better go back and check that again. So I assume that code or no code, just adding a ground rod won't magically make my present pipe earth ground disappear. Agree? Quite true. Just make sure that they *are* bonded together -- preferably within 5' of where the pipe enters the building -- to make sure that they are at the same potential. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#74
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
Doug - why is that underground tank not connected to breaker box?
It completely meets paragraph seven as an' earthing electrode. Using your reasoning, then that underground tank must be connected to breaker box. But nothing is using the tank as an electrode. Therefore it does not exist - is not 'present' - as an earthing electrode. It exists only as a tank even though it 'could' become an earthing electrode according to code. Please learn what that paragraph really says. If we drive a ground rod into earth and don't connect anything to it, then according to Doug Miller's interpretation, we must connect that rod to breaker box with a 6 AWG wire. Obviously not. It 'could' be an earthing electrode. But it is not because nothing else is using it for earthing. Therefore - and in direct contradiction to what Doug has posted - we need not connect it to the breaker box. The phrase is "that is present". That underground tank and that isolated ground rod are not 'present' because nothing is using it as an earthing electrode. If we earth an overhead TV antenna (as required by code), then that ground rod must also connects to the earthing system being used by AC breaker box. Why? That TV antenna ground rod is 'present'. It now exists as an earthing electrode and therefore must be interconnected to other earth grounds. Code only requires John Ross to have one earthing electrode. Minimum to meet that requirement is one earth ground rod located and connected as short as practicable to breaker box. Being earthed by a wire as short as possible is also a code requirement. For other reasons, we want that wire to be 'less than 10 feet' and routed separated from other wires. That one earth ground then meets a minimum code requirement for earthing. If John Ross is using some other earth ground for telephone or cable TV, then that earthing electrode is 'present' - must also connect to the breaker box. Code also says those other utilities must connect less than 20 feet to the earth ground. Just another reason why all incoming utilities should enter at a common service entrance - since all must use the same earthing 'system'. Doug - please learn that what code paragraph says. You keep quoting it and do not understand what it is saying. Accroding to you, then every underground tank also must be connected by 6 AWG wire to the breaker box. Any steel plate buried in earth must be connected. Obviously that is not true. Your interpretation obviously is in error. On Sep 30, 8:45 pm, (Doug Miller) wrote: In article On Sep 30, 8:00 wrote: According to John, if any of those six items exist, then they also must be bonded to the breaker box. Correction. This should have read "According to Doug Miller, if any of those six tiems exists, then ..." Correction: according to the National Electrical Code. I even quoted the relevant portions of it. Here, I'll do it again. Pay attention this time. "All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present at each building or structure served SHALL BE bonded together to form the grounding electrode system." [2005 NEC, Article 250.50] |
#75
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
John Ross wrote:
bud-- wrote: John Ross wrote: bud-- wrote: John Ross wrote: I spoke with the electrician today and he said he would use #8 wire (he said that was for 100 amp panel). Not sure what you meant by "very restrictive" in using that, I doubt he would do anything different. 2005 NEC 250.64-B "Securing and protection against physical damage" "Grounding electrode conductors smaller than 6AWG [#8} shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metalic tubing, or cable armor." All of them are a form of pipe (some are light weight pipe) except cable armor which is a spiral metal protection like BX. If the conductor is run through ferrous tubing/pipe there are additional requirements that directly or indirectly bond both ends of the pipe to the grounding conductor. If you use one of the required protection methods #6 should be cheaper. It will need protection where it is located. The cable armor sounds the easiest (to bend), does that contain ferrous? Never used it. I hope this doesn't open up a new can of worms, but I remembered that the way they did these houses, they didn't have a ground bar in the panel--the grounds are connected to the neutral bar. I asked him about that and he said he would just connect the new ground connections to the neutral bar also and "that was legal." Do you see a problem with that? At the service panel only (not downstream subpanels) the neutral and ground are connected. The neutral bar is usually insulated from the enclosure, but they should [almost] always be connected together at the service panel. The connection is often by a screw that goes through the neutral bar and screws into the enclosure behind - not at all obvious. This panel (there is only one at house) has NO ground bar--grounds and neutrals are on the "neutral" bar. So he is proposing just adding these new ground connections there as well. Is that OK? If they are bonded together anyway, I can't see how it could hurt, but as you know this is all new to me. That is standard in service panels. -- bud-- |
#76
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
w_tom wrote:
On Sep 30, 11:15 am, (Doug Miller) wrote: No, not unless the connection to the water pipe is within 5 feet of the entrance. I disagree with Doug on this point. If the connection to the water pipe was code compliant when installed - connection used to be allowed other than within 5 ft - the installation is OK now unless modifications are made that trigger new construction requirements. And on to the village idiot. Code demands that the AC electric have a proper connection to earth ground. Any one of the electrodes in paragraphs two through seven are sufficient. The electrode defined in paragraph one (water pipe) is not sufficient. As Doug points out, the village idiot rewrites the code. The code says paragraph *1-6*. Paragraph *1* is water pipe - required by code to be used as a grounding electrode. When reality conflicts with the beliefs of the village idiot, he tries to change reality. Assume that John Ross was correct - that ALL earthing electrodes must be connected. Then every steel I-beam concreted in earth must be bonded to the breaker box. The steel frame of a commercial buildings is one of the lowest earth resistance electrodes. As Doug points out, the frame (generally) must be used as a grounding electrode. It does not apply to each member. Anyone who can read and think could figure that out from the NEC. All rebar inside concrete footing must be bonded. Rebar inside any concrete basement floor must be bonded. Completely idiotic statement. The NEC does not required rebar be used at all - a length of copper wire can be used. And only required for new construction. And does not apply to floor. Any steel plate buried in earth must be bonded. If the village idiot would read the NEC, this applies to a plate that is specifically buried to be used as an earthing electrode. Any "other local metal underground system or structure such as piping systems and underground tanks" (quoted from paragraph seven) must also be connected to breaker box. This is “paragraph 7". The NEC does not require these items be used as grounding electrodes. Only w_’s renumbering includes “7". According to John, if any of those six items exist, then they also must be bonded to the breaker box. Not according to Doug, according to the NEC. Why are bonding wires not attached to every of six items? Because Doug Miller is wrong. Because w_ is unable to read and understand what the NEC really requires. Truly incomprehensible misrepresentations. The breaker box only needs one earthing electrode that conforms to paragraphs two through seven. The electrical system needs only one earthing electrode *system* than conforms to paragraphs *1-6*. The NEC says “All grounding electrodes... that are present”, not just your favorite one. Listed are six earthing electrodes that would not be connected to breaker box because nothing was using them for earth ground. They are used as earthing electrodes because they improve the connection of the electrical system to earth. It is totally irrelevant whether the 6 electrode types are used by phone or other utilities. According to Doug Miller, all six of those electrodes also must be connected by 6 AWG wire. Where did Doug say that? “Concrete encased electrode” is #4. Water pipe and structural steel the size of the conductor goes up with the service size reflecting their superior connection to the earth. If you want to bond the 'first five feet of water pipe' to breaker box, then by all means do so. For those without a mental impairment, water pipe (10 ft ....) is *required* to be used as an earthing electrode. A metal underground tank is an earthing electrode according to paragraph seven. But if not being used by anything as an earth ground, then AC breaker box also need not be bonded to that underground tank ... in direct contradiction to what Doug Miller and I never said underground tank must be used as a grounding electrode because the NEC does not say the tank must be used. naive salesman Bud have posted. To quote w_ "It is an old political trick. When facts cannot be challenged technically, then attack the messenger." Not able to compete on facts, w_ has to try to discredit those who challenge his bullcrap. Poor w_ seems to have a significant mental impairment. Virtually everything he said was wrong. Perhaps the institution should limit his use of the internet. –- bud-- |
#77
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article . com, w_tom wrote:
Doug - why is that underground tank not connected to breaker box? Because the installer was listening to you, instead of reading the Code. It completely meets paragraph seven as an' earthing electrode. Using your reasoning, then that underground tank must be connected to breaker box. No, not using "my reasoning" -- using the plain language of the Code. But nothing is using the tank as an electrode. Then that's a Code violation. Therefore it does not exist - is not 'present' - as an earthing electrode. You have a peculiar understanding of "present". It exists only as a tank even though it 'could' become an earthing electrode according to code. Please learn what that paragraph really says. I'm perfectly well aware of what that paragraph says, but it appears that you are not. The Code says, simply, that if the items are present, then they must be bonded together to form the grounding electrode system. If we drive a ground rod into earth and don't connect anything to it, then according to Doug Miller's interpretation, we must connect that rod to breaker box with a 6 AWG wire. Obviously not. It 'could' be an earthing electrode. But it is not because nothing else is using it for earthing. Therefore - and in direct contradiction to what Doug has posted - we need not connect it to the breaker box. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? The phrase is "that is present". That underground tank and that isolated ground rod are not 'present' because nothing is using it as an earthing electrode. What, you mean they're not there? What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? If we earth an overhead TV antenna (as required by code), then that ground rod must also connects to the earthing system being used by AC breaker box. Why? That TV antenna ground rod is 'present'. It now exists as an earthing electrode and therefore must be interconnected to other earth grounds. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? Code only requires John Ross to have one earthing electrode. Minimum to meet that requirement is one earth ground rod located and connected as short as practicable to breaker box. Being earthed by a wire as short as possible is also a code requirement. For other reasons, we want that wire to be 'less than 10 feet' and routed separated from other wires. That one earth ground then meets a minimum code requirement for earthing. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? If John Ross is using some other earth ground for telephone or cable TV, then that earthing electrode is 'present' - must also connect to the breaker box. Code also says those other utilities must connect less than 20 feet to the earth ground. Just another reason why all incoming utilities should enter at a common service entrance - since all must use the same earthing 'system'. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? Doug - please learn that what code paragraph says. Tom - please don't attempt to lecture me on what the Code says, when you clearly don't understand it yourself. You keep quoting it and do not understand what it is saying. You keep *not* quoting it, and *not* understanding it. Accroding to you, then every underground tank also must be connected by 6 AWG wire to the breaker box. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? Any steel plate buried in earth must be connected. As I've already pointed out to you, this is not true. Obviously that is not true. Your interpretation obviously is in error. What part of 250.50 "ALL ... that are present ... SHALL BE BONDED TOGETHER..." are you having such a hard time understanding? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#78
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
In article , bud-- wrote:
w_tom wrote: On Sep 30, 11:15 am, (Doug Miller) wrote: No, not unless the connection to the water pipe is within 5 feet of the entrance. I disagree with Doug on this point. If the connection to the water pipe was code compliant when installed - connection used to be allowed other than within 5 ft - the installation is OK now unless modifications are made that trigger new construction requirements. IMO local inspection authority is likely to regard the installation of a second grounding electrode as a mod that will trigger new construction requirements -- but the OP should check with local inspection authority. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#79
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
|
#80
Posted to alt.home.repair
|
|||
|
|||
What is NEC Code For This Grounding Scheme ?
On Oct 1, 12:58 pm, (Doug Miller) wrote:
Tom - please don't attempt to lecture me on what the Code says, when you clearly don't understand it yourself. So those millions of fuel oil tanks buried outside homes to provide fuel for winter heat - all tanks are code violations? How curious that electrical inspectors did not see them as code violations. According to Doug Miller, all those fuel oil tanks are code violations because a 6 AWG wire does not connect them to the breaker box. Doug - you don't do this stuff, do you? You are assuming a layman's interpretation of the word 'present'. A tank that meets paragraph (A)(7) as an electrode also is not 'present' according to the code. If word definitions were so obvious, then explain why a rope does not bond two items together. Code says two items must be bonded. They look bonded together to me. We cannot pull them apart. Therefore they must be bonded - by a rope. Clearly that meets code since the meaning of bonding is obvious to any layman. Or maybe words have context. Obvious is that millions of household oil tanks are not in code violation as you have just posted. Please learn the code before lecturing others. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
I want to test C#code ,how Can i study ,? I want to get C# code What site.? | Home Repair | |||
electrical questions GFCIs, grounding, and code | Home Repair | |||
[Fwd: Self-grounding outlets vs. grounding wire] | Home Repair | |||
Self-grounding outlets vs. grounding wire | Home Repair | |||
Doulble Receptacle Grounding Question/ Switch Grounding | Home Repair |