RBM (remove this) wrote:
If the compressor draws 20 amps, you will need a 30 amp cable to feed it.
That would be 10gauge wire. From what you describe of your shop, you would
do well to run a 6/3 feed from the main and install something like an 8
circuit sub panel in the shop, then run the machine outlets and lights from
the sub



"Woody2" u30143@uwe wrote in message news:6a9d3a4aaaca2@uwe...
I am going to have a 200amp. heavy up done , but later plan to add to
Garage/workshop area. What type of wire is suitable for use of air
compressor
rated @ 20amp. also would like to add overhead fluorescent light, run power
saws grinder etc. Should I have dedicated circuits, please advise best
route
to go.
Thanks Woody2

If compressor 'draws' 20 amps at 230 volts that's 4600 watts,
suggesting a fairly heavy motor (5 HP) etc. Or at 115 volts that's 2300
watts possibly a 3 or 3 HP motor?
In either case the starting current surge could be considerable! and
voltage drop over 100 feet (one way????) so that could be 200 feet of
current carrying conductors. Along with compressor will be other
devices; lights etc. Possibly as much current draw as a whole house?