Charlie Morgan wrote:
On Sun, 3 Dec 2006 16:42:17 -0500, "RBM" rbm2(remove
wrote:

Let me clarify. You can connect it to your main cold water pipe within five
feet of where it enters the building. You can also connect it to the fuse
box or anything that is grounding the fuse box


No you can't. Bad advice.

CWM


The gospel according to the US NEC is that you can. viz
"250.130 Equipment Grounding Conductor Connections.
Equipment grounding conductor connections at the source of separately
derived systems shall be made in accordance with 250.30(A)(1). Equipment
grounding conductor connections at service equipment shall be made as
indicated in 250.130(A) or (B). For replacement of non–grounding-type
receptacles with grounding-type receptacles and for branch-circuit
extensions only in existing installations that do not have an equipment
grounding conductor in the branch circuit, connections shall be
permitted as indicated in 250.130(C).
(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions.
The equipment grounding conductor of a grounding-type receptacle or a
branch-circuit extension shall be permitted to be connected to any of
the following:
(1) Any accessible point on the grounding electrode system as described
in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the
branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the
service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar within the
service equipment enclosure"
Copyright 2002 the National Fire Protection Association
--
Tom Horne