"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem
Now given the fact that it's a shaded pole motor and the connections to
it are sound (i.e. electrically, it's just a coil of wire) does anybody
have an explanation ?
None... Except the connections were not in fact tight, or a fault on the
PCB.
Changed the pcb, checked the fan ctrl relay first
swapped the fan over several times
The fan works without generating RF when back at the factory
It's only when it's in the boiler
When you test it back at the factory, is it installed in way similar to in
the boiler?
It could be that the bonding arrangements are different (eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a well
bonded installation but not in a marginally bonded one.
--
73
Brian
www.g8osn.org.uk