I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections to
it are sound (i.e. electrically, it's just a coil of wire) does anybody
have an explanation ?


--
geoff
  #2   Report Post  
Posted to uk.d-i-y
Harry Bloomfield
 
Posts: n/a
Default Strange RF problem

raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he swears
that it causes RF interference. I sent him another one which he says is OK.
We've also changed his pcb for him (to eliminate the possibility of it being
a relay problem

Now given the fact that it's a shaded pole motor and the connections to it
are sound (i.e. electrically, it's just a coil of wire) does anybody have an
explanation ?


None... Except the connections were not in fact tight, or a fault on
the PCB.

--

Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #3   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default Strange RF problem

In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which
he says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections
to it are sound (i.e. electrically, it's just a coil of wire) does
anybody have an explanation ?


None... Except the connections were not in fact tight, or a fault on
the PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler

--
geoff
  #4   Report Post  
Posted to uk.d-i-y
Brian Reay
 
Posts: n/a
Default Strange RF problem


"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections to
it are sound (i.e. electrically, it's just a coil of wire) does anybody
have an explanation ?


None... Except the connections were not in fact tight, or a fault on the
PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler



When you test it back at the factory, is it installed in way similar to in
the boiler?

It could be that the bonding arrangements are different (eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a well
bonded installation but not in a marginally bonded one.

--
73
Brian
www.g8osn.org.uk


  #5   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default Strange RF problem

In message , Brian Reay
writes

"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections to
it are sound (i.e. electrically, it's just a coil of wire) does anybody
have an explanation ?

None... Except the connections were not in fact tight, or a fault on the
PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler



When you test it back at the factory, is it installed in way similar to in
the boiler?

It could be that the bonding arrangements are different


In which case, the other fan I sent him should suffer from the same
problem. The two fans are identical (FSVO of course). The wires coming
of the fans are of the same construction and are fast into the
connections to the coil.

(eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a well
bonded installation but not in a marginally bonded one.

To generate RF really requires a spark of some sort if it's coming from
50Hz. This would represent a loss which would present itself as a less
efficient fan motor (I would think) and therefore would not activate the
air pressure switch)

It's a total mystery
--
geoff


  #6   Report Post  
Posted to uk.d-i-y
James Salisbury
 
Posts: n/a
Default Strange RF problem


"raden" wrote in message
...
In message , Brian Reay
writes

"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which
he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections
to
it are sound (i.e. electrically, it's just a coil of wire) does
anybody
have an explanation ?

None... Except the connections were not in fact tight, or a fault on the
PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler



When you test it back at the factory, is it installed in way similar to in
the boiler?

It could be that the bonding arrangements are different


In which case, the other fan I sent him should suffer from the same
problem. The two fans are identical (FSVO of course). The wires coming of
the fans are of the same construction and are fast into the connections to
the coil.

(eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a
well
bonded installation but not in a marginally bonded one.

To generate RF really requires a spark of some sort if it's coming from
50Hz. This would represent a loss which would present itself as a less
efficient fan motor (I would think) and therefore would not activate the
air pressure switch)

It's a total mystery
--
geoff



Have you tried a megger on the fan?


  #7   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default Strange RF problem

In message , James Salisbury
writes

"raden" wrote in message
...
In message , Brian Reay
writes

"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which
he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections
to
it are sound (i.e. electrically, it's just a coil of wire) does
anybody
have an explanation ?

None... Except the connections were not in fact tight, or a fault on the
PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler


When you test it back at the factory, is it installed in way similar to in
the boiler?

It could be that the bonding arrangements are different


In which case, the other fan I sent him should suffer from the same
problem. The two fans are identical (FSVO of course). The wires coming of
the fans are of the same construction and are fast into the connections to
the coil.

(eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a
well
bonded installation but not in a marginally bonded one.

To generate RF really requires a spark of some sort if it's coming from
50Hz. This would represent a loss which would present itself as a less
efficient fan motor (I would think) and therefore would not activate the
air pressure switch)

It's a total mystery
--
geoff



Have you tried a megger on the fan?


Funny you should say that - no

good idea, I'll do that on Monday

--
geoff
  #8   Report Post  
Posted to uk.d-i-y
James Salisbury
 
Posts: n/a
Default Strange RF problem


"raden" wrote in message
...
In message , James Salisbury
writes

"raden" wrote in message
...
In message , Brian Reay
writes

"raden" wrote in message
...
In message , Harry Bloomfield
writes
raden explained :
I sold someone a fan for his CH boiler a couple of months ago and he
swears that it causes RF interference. I sent him another one which
he
says is OK. We've also changed his pcb for him (to eliminate the
possibility of it being a relay problem

Now given the fact that it's a shaded pole motor and the connections
to
it are sound (i.e. electrically, it's just a coil of wire) does
anybody
have an explanation ?

None... Except the connections were not in fact tight, or a fault on
the
PCB.

Changed the pcb, checked the fan ctrl relay first

swapped the fan over several times

The fan works without generating RF when back at the factory

It's only when it's in the boiler


When you test it back at the factory, is it installed in way similar to
in
the boiler?

It could be that the bonding arrangements are different

In which case, the other fan I sent him should suffer from the same
problem. The two fans are identical (FSVO of course). The wires coming
of
the fans are of the same construction and are fast into the connections
to
the coil.

(eg the bonding in
the troublesome boiler isn't so good) and the fan is marginal- OK in a
well
bonded installation but not in a marginally bonded one.

To generate RF really requires a spark of some sort if it's coming from
50Hz. This would represent a loss which would present itself as a less
efficient fan motor (I would think) and therefore would not activate the
air pressure switch)

It's a total mystery
--
geoff



Have you tried a megger on the fan?


Funny you should say that - no

good idea, I'll do that on Monday

--
geoff


And the answer was?


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Strange electrical problem [email protected] Home Repair 13 May 2nd 06 08:10 AM
Sony GDM-F520 Monitor - Strange Blur Problem Scrim Electronics Repair 14 March 24th 06 09:41 AM
Very Strange Antenna Problem? M.Joshi Electronics Repair 7 February 22nd 05 02:32 PM
Very Strange Antenna Problem? M.Joshi Electronics Repair 1 February 22nd 05 12:43 AM
strange electrical AC problem (high/low voltage) [email protected] Home Repair 4 December 28th 04 02:50 AM


All times are GMT +1. The time now is 05:37 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"