Can I run this past some people to find out if I'm doing this
correctly...
I'm want to run power to an outbuilding that I'm going to use as a
workshop. (ok it's a shed, but outbuilding sounds grander!)
My plan is to run cable from a spare MCB in my house's consumer unit to
the shed (under a patio, so it'll be well protected) On entering the
shed it'll go into an auxilery consumber unit with build in RCD. This
consumner unit will have 3 MCBs to supply the lighting, power points
and a water feature in the garden
I've read around on the net and I like the idea of a consumer unit in
the outbuilding, but I was wondering if this was an ok way of doing it.
If so, what rating should the MCB be at my house's consumner unit end?
and also what do the ratings of RCD's actually mean? I've seen 63A 30ma
and 80A 30ma etc and I'm a tad confused... :-S

Thanks in advance for any help you can give,
Cheers,
Rob

  #2   Report Post  
Posted to uk.d-i-y
Sparks
 
Posts: n/a
Default Outbuilding power supply confusion...


wrote in message
oups.com...
Hi,
Can I run this past some people to find out if I'm doing this
correctly...
I'm want to run power to an outbuilding that I'm going to use as a
workshop. (ok it's a shed, but outbuilding sounds grander!)
My plan is to run cable from a spare MCB in my house's consumer unit to
the shed (under a patio, so it'll be well protected) On entering the
shed it'll go into an auxilery consumber unit with build in RCD. This
consumner unit will have 3 MCBs to supply the lighting, power points
and a water feature in the garden
I've read around on the net and I like the idea of a consumer unit in
the outbuilding, but I was wondering if this was an ok way of doing it.
If so, what rating should the MCB be at my house's consumner unit end?
and also what do the ratings of RCD's actually mean? I've seen 63A 30ma
and 80A 30ma etc and I'm a tad confused... :-S


How far is the cable run?
What are you likley to use in the workshop in the sockets?
is the spare MCB in the house protected with an RCD of just an isolator?

The A rating is the current they can cope with, and the mA rating is the
fault current they will trip at.

Sparks...


  #4   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default Outbuilding power supply confusion...

Hi,
Thanks for the quick reply :-)

The cable will run about 10m or so from the house's consumer unit to
the shed. I've already wired the shed in a radial circuit with 6mm
cable (a little big maybe, but I had it to hand). That circuit is only
about 4m.

The sockets in the shed will have to cope with a (small) table saw,
bench drill, uv exposure box and a tv. I'm working on some video
electronics stuff (12volts I'm ok with... but 240 _scares_ me!). Not
all of the above will be on at the same time tho

As for the MCB at the house end, the whole story is that I'm going to
change over the consumer unit in the house (before I connect up the
shed) to one with RCD protection because at the moment all my sockets
upstairs and down run off a single fuseway, as do the lights (I'll
change it to a split load one with the lighing in the house running off
2 unprotected MCB's and the remaining of the ciruits (sockets down and
up, shower and shed) off the protected ones.

Am I barking up the right tree? :-D

  #5   Report Post  
Posted to uk.d-i-y
Andy Hall
 
Posts: n/a
Default Outbuilding power supply confusion...

On 19 Feb 2006 11:17:03 -0800, "
wrote:

Hi,
Can I run this past some people to find out if I'm doing this
correctly...
I'm want to run power to an outbuilding that I'm going to use as a
workshop. (ok it's a shed, but outbuilding sounds grander!)
My plan is to run cable from a spare MCB in my house's consumer unit to
the shed (under a patio, so it'll be well protected) On entering the
shed it'll go into an auxilery consumber unit with build in RCD. This
consumner unit will have 3 MCBs to supply the lighting, power points
and a water feature in the garden
I've read around on the net and I like the idea of a consumer unit in
the outbuilding, but I was wondering if this was an ok way of doing it.
If so, what rating should the MCB be at my house's consumner unit end?
and also what do the ratings of RCD's actually mean? I've seen 63A 30ma
and 80A 30ma etc and I'm a tad confused... :-S

Thanks in advance for any help you can give,
Cheers,
Rob



Having an auxiliary CU in the shed is entirely reasonable. The main
points to consider a

- Power requirements at shed

- Cable type and sizing from house

- Earthing arrangements



You need to determine likely current requirements for all equipment
that will be used in or from the shed first and to base the supply
rating on that plus a margin.

For an installation with underground cable, the convention is to use
3way + shield SWA armoured cable. This needs to be sized
sufficiently large to meet current carrying requirements as well as
the maximum allowed volt drop for the length to be used - so you need
to know length as well. The reason for this is in part to make sure
of an adequate supply voltage under load for the equipment, but also
so that in the event of a short circuit at the shed CU or in the
cable, that the MCB at the house end will trip, cutting off the supply
and protecting the cable. Note that there is no problem in
oversizing.

For earthing, there is a choice of exporting the house earth as long
as the distance is short or separating the earth (using an insulating
fitting at the shed CU) and installing a ground rod at the shed.

If you export the house earth, you can fit either an MCB (either side
of an RCD in the house CU if there is one) or an RCBO (combined RCD
and MCB). Note that RCDs, on their own do not trip on excessive
current. Their rating in Amps is only their carrying capacity.
If you use an RCD or RCBO at the house, then any current imbalance
fault in the shed will cause all power to the shed to be cut. You
might not want that - e.g. lights going out or freezer going off. In
that case an MCB only should be used in the house CU and a 30mA RCD in
the shed CU with lights upstream of it etc.

If you go for the local earth rod option, then you are creating an
equivalent to TT earthing of the main supply - i.e. what happens with
overhead supplied power to a house. In this case, an MCB is fitted
at the house CU and a 100mA time delay RCD is used on the supply input
at the shed CU. You then install MCBs and 30mA RCD as before.

It is worth reading through the relevent sections at

http://www.tlc-direct.co.uk/Book/1.1.htm

for more details.




--

..andy



  #6   Report Post  
Posted to uk.d-i-y
Andy Hall
 
Posts: n/a
Default Outbuilding power supply confusion...

On 19 Feb 2006 12:08:48 -0800, "
wrote:

Hi,
Thanks for the quick reply :-)

The cable will run about 10m or so from the house's consumer unit to
the shed. I've already wired the shed in a radial circuit with 6mm
cable (a little big maybe, but I had it to hand). That circuit is only
about 4m.

The sockets in the shed will have to cope with a (small) table saw,
bench drill, uv exposure box and a tv. I'm working on some video
electronics stuff (12volts I'm ok with... but 240 _scares_ me!). Not
all of the above will be on at the same time tho

As for the MCB at the house end, the whole story is that I'm going to
change over the consumer unit in the house (before I connect up the
shed) to one with RCD protection because at the moment all my sockets
upstairs and down run off a single fuseway, as do the lights (I'll
change it to a split load one with the lighing in the house running off
2 unprotected MCB's and the remaining of the ciruits (sockets down and
up, shower and shed) off the protected ones.

Am I barking up the right tree? :-D



Given all of this, it's reasonable to export the house earth and use a
20A MCB in the house CU.

The only remaining thing to consider is whether you care if all power
in the shed goes off as a result of a trip on the house RCD. The
implication is that a fault in one could affect the other, so you need
to think about where essential equipment is connected.



--

..andy

  #7   Report Post  
Posted to uk.d-i-y
Sparks
 
Posts: n/a
Default Outbuilding power supply confusion...


wrote in message
ups.com...
Hi,
Thanks for the quick reply :-)

The cable will run about 10m or so from the house's consumer unit to
the shed. I've already wired the shed in a radial circuit with 6mm
cable (a little big maybe, but I had it to hand). That circuit is only
about 4m.

The sockets in the shed will have to cope with a (small) table saw,
bench drill, uv exposure box and a tv. I'm working on some video
electronics stuff (12volts I'm ok with... but 240 _scares_ me!). Not
all of the above will be on at the same time tho

As for the MCB at the house end, the whole story is that I'm going to
change over the consumer unit in the house (before I connect up the
shed) to one with RCD protection because at the moment all my sockets
upstairs and down run off a single fuseway, as do the lights (I'll
change it to a split load one with the lighing in the house running off
2 unprotected MCB's and the remaining of the ciruits (sockets down and
up, shower and shed) off the protected ones.

Am I barking up the right tree? :-D


Nearly :-)

Just to point out, under Part P, you are not permitted to just do this on
your own, unless you get building control involved (because it is a new
circuit, and also because it is also outside) you are also not permitted to
change the CU.
"Am I Bovvered" I hear you all cry :-)

It would be best to run the shed off the non RCD side really, or a problem
in the shed will probably trip both the shed RCD and the house one, this is
not unsafe, but is bloody irritating!

As you are changing the CU, I would also recommend you run a radial to the
kitchen fixed appliances (Freezer, fridge at least), the boiler and alarm if
you have one, from the non RCD side too (So if you are away, and something
trips the RCD you do not loose the freezer's content, or the alarm) again,
Part P says you can't just do this one either, as it is in the Kitchen and
also because it would be a new circuit.

So, back to the shed, sorry, workshop.

I assume the workshop is a wooden construction?

The 6mm cable is a little on the large side, 2.5mm would have been fine
here, however, this is not a problem (except when you try to jam in a load
of cables into one socket/spur etc., then you run out of room faster!)

As it is only 10M of cable, then you can use the house earthing (otherwise
you would need to install a TT system in the workshop, providing local earth
with an earth rod etc.)

It would probably be better to opt for a non RCD overall protected consumer
unit in the workshop, and use RCBO's here (these are a combined RCD and MCB,
but are quite expensive!)- the reason for this is mainly because you mention
potentially dangerous power tools (the table saw). If the lighting and this
saw were both needed (you were sawing something when it was dark outside)
and the RCD tripped, you would be plunged into darkness with a table saw
still spinning down. I have taken the emergency light route in my workshop
(overall protection is an RCD, and the emergency light is wired up to the
same circuit as the main lighting, so in the event of either the lighting
MCB or the RCD tripping, the emergency light illuminates) If cost is a
factor, then the emergency light route will be cheaper (It was when I did
it, and the fact I don't use this type of tool that often, made be choose
it!) It will also illuminate if the workshop MCB in the house trips.

It would probably be best to run SWA cable (Steel Wire Armour) from the
house to the workshop, as it provides very good protection (and can be
directly buried) If the run from the cable entry point in the house to the
CU is a bit tricky, then just terminate the SWA in a box (In the house, or a
box screwed to it) and run the rest in normal T&E (This is what I have done,
as it would have been a major pain in the arse to run SWA through the
house!)
I found the three core SWA (really meant for three phase) was more easily
available than the two core (The earth would have run through the armour on
two core) so I used this, and sleeved the wires each end accordingly. I did
use the third core as the earth, but also earthed the armour)

If you are going to dig up the patio, it may also be a good idea to lay some
conduit under there so you can run additional wires (network, phone,
doorbell etc.) at a later date (It is best to lay a draw string in there
too, but if you forget, or it breaks, a vacuum cleaner will usually suck
one through later!)

I would use 6mm SWA cable, but you could get away with 4mm (6mm will give
you room to expand a bit later)
I would use a 32A MCB in the house
A 20A MCB or RCBO for the sockets (as it is a radial)
A 6A MCB for the lighting
A 6A MCB or RCBO for the water feature (assuming this is enough, and you
don't have an imitation Niagara falls/Trafalgar square in the garden!

Sparks (Who is NOT a qualified electrician by the way!)


  #8   Report Post  
Posted to uk.d-i-y
Jim Gregory
 
Posts: n/a
Default Outbuilding power supply confusion...

wrote in message
oups.com...
Hi,
Can I run this past some people to find out if I'm doing this
correctly...
I'm want to run power to an outbuilding that I'm going to use as a
workshop. (ok it's a shed, but outbuilding sounds grander!)
My plan is to run cable from a spare MCB in my house's consumer unit to
the shed (under a patio, so it'll be well protected) On entering the
shed it'll go into an auxilery consumber unit with build in RCD. This
consumner unit will have 3 MCBs to supply the lighting, power points
and a water feature in the garden
I've read around on the net and I like the idea of a consumer unit in
the outbuilding, but I was wondering if this was an ok way of doing it.
If so, what rating should the MCB be at my house's consumner unit end?
and also what do the ratings of RCD's actually mean? I've seen 63A 30ma
and 80A 30ma etc and I'm a tad confused... :-S

Thanks in advance for any help you can give,
Cheers,
Rob

The A figures are max AC current capacities given in rms Amps.
The mA figure is the rated sensitivity of the trip mechanism to respond to a
naughty L-N imbalance. The lower, the faster the shut-off is in mSecs.
The Test button on an RCD or an older ELCB actually simulates such a leakage
by shunting a resistor in appropriate kOhms from L to E when it should
immediately trip! (This fault-making test should be practised every 2
months)


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power supply [email protected] Metalworking 15 December 25th 05 02:40 AM
Need help re power supply for new Digital (DLP) tv R. Bharat Rao Home Ownership 3 February 24th 05 03:43 AM
Switch mode power supply as a float charger Mike M. Electronics Repair 1 January 17th 04 12:40 AM
Sony KV-2782R and 2785R, power supply problems. Michael Parker Electronics Repair 1 October 23rd 03 08:56 AM
Sony KV-2782R Power supply, and KV-2785R same. John Wright Electronics Repair 0 October 23rd 03 02:15 AM


All times are GMT +1. The time now is 06:39 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"