I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps. I
would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have a
fair amount of machinery and can see 2 - 3 users larger pieces of equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts or
comments?

David


  #2   Report Post  
woodworker88
 
Posts: n/a
Default


DL wrote:
I am in the process of installing a subpanel to consolidate the

wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp

to
install in the main panel. I additionally have a 100amp breaker as

well.
The largest bound copper cable I can get without a special order from

the
local electrical supply house is 2/3 which will handle up to 95amps.

I
would prefer not to wait for the special order if I don't have to.

50amps
is the next size down at the local Home Depot, ( I need to see what

the
electric supply house has, I assume I can get a 70, 80, or 90)

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to

query
others to see what they have installed. (I am in the process of

totally up
the equipment and amps that I would expect would be needed at a given

time
to make sure I have all that I need, but that is not complete) I do

have a
fair amount of machinery and can see 2 - 3 users larger pieces of

equipment
plus auxillary air compressor, dust collection, air filtration,

general
power consumption that will add up. In my mind, it's not that much

more
expensive to add the extra amps at this point and would rather

overplan than
be under powered at a later date which would be much more expensive

to
upgade, if I needed it.

2. I can purchase Aluminum to handle the 125amp's but I have heard

bad
things about the aluminum connection corrosion. I know I can put the


special grease on the connections to prevent the corrosion. Any

thoughts or
comments?

David


  #3   Report Post  
Doug Miller
 
Posts: n/a
Default

In article iFD7e.1704$H53.1652@lakeread05, "DL" wrote:
I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps.


Unless the insulation is rated at only 60 deg C, a 2/3 cable ought to handle a
lot more than 95 amps. Where are you getting that figure from?

You can do 100A in a 4/3 cable if the conductor temperature is rated 85 deg C
or higher....

I would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


I would think so. I'm surprised you didn't find a 60 at HD.

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have a
fair amount of machinery and can see 2 - 3 users larger pieces of equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.


You certainly have the right idea about the cost of building bigger than you
need vs. the cost of upgrading later. But I think you're going bigger by a
larger margin than necessary. 60A at 240V will provide more power than you're
likely to need in a home shop.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts or
comments?


Under _no_ circumstances would I ever install an aluminum feed to a subpanel
in my home, or advise anyone else to. It's just too risky, and for what
benefit? Sure, you might save a few bucks, but it's a whole lot less safe than
copper unless it's installed _exactly_ right. Trouble is, it's a whole lot
more difficult to install correctly than copper is. It's not just a matter of
adding anti-oxidant compound to the connections. Bolt lugs must be tightened
with a torque wrench, both to make sure that they are tight enough, and to
make sure that they are not _too_ tight, because aluminum will cold-flow away
from an overtorqued connection, loosening it, and causing it to arc. All
equipment used must be rated for use with aluminum. And so on.

Don't do it. It isn't worth it.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #4   Report Post  
Jody
 
Posts: n/a
Default

DL wrote:
I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps. I
would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have a
fair amount of machinery and can see 2 - 3 users larger pieces of equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts or
comments?

David


I run my shop 24'x40' on 80 amps. It's 175' from the main panel running
on 3 #4's and a #6. I could have used less but I had the breaker. If
it's a one man shop then anything over I think would be overkill.
All I would say is stay away from aluminum, even if it's just for a feed.
  #5   Report Post  
Lew Hodgett
 
Posts: n/a
Default

DL wrote:
I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel.

snip

For a 120/240 VAC service, a 2P-60A main kit installed in a 125 MLO,
12/24 panel will handle everything a one man shop can throw at it.

The largest motor you can run on single phase is about 5HP, cap start,
cap run, normally found on an air compressor.

A 2P-40A branch c'bkr will handle the compressor.

Everything else incuding a table saw and a welder will be smaller loads.

HTH

Lew


  #6   Report Post  
Wilson Lamb
 
Posts: n/a
Default

I'm betting his whole house runs on an aluminum drop to his main panel. I
can't remember the last copper service I saw. With a big feed like that, no
sustained heavy loads, and no connections buried in the walls, I wouldn't
worry. But for a short run, copper might feel better, and be easy to
handle.
Wilson
"Doug Miller" wrote in message
m...
In article iFD7e.1704$H53.1652@lakeread05, "DL"
wrote:
I am in the process of installing a subpanel to consolidate the wiring in
my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps.


Unless the insulation is rated at only 60 deg C, a 2/3 cable ought to
handle a
lot more than 95 amps. Where are you getting that figure from?

You can do 100A in a 4/3 cable if the conductor temperature is rated 85
deg C
or higher....

I would prefer not to wait for the special order if I don't have to.
50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


I would think so. I'm surprised you didn't find a 60 at HD.

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have
a
fair amount of machinery and can see 2 - 3 users larger pieces of
equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan
than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.


You certainly have the right idea about the cost of building bigger than
you
need vs. the cost of upgrading later. But I think you're going bigger by a
larger margin than necessary. 60A at 240V will provide more power than
you're
likely to need in a home shop.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts
or
comments?


Under _no_ circumstances would I ever install an aluminum feed to a
subpanel
in my home, or advise anyone else to. It's just too risky, and for what
benefit? Sure, you might save a few bucks, but it's a whole lot less safe
than
copper unless it's installed _exactly_ right. Trouble is, it's a whole lot
more difficult to install correctly than copper is. It's not just a matter
of
adding anti-oxidant compound to the connections. Bolt lugs must be
tightened
with a torque wrench, both to make sure that they are tight enough, and to
make sure that they are not _too_ tight, because aluminum will cold-flow
away
from an overtorqued connection, loosening it, and causing it to arc. All
equipment used must be rated for use with aluminum. And so on.

Don't do it. It isn't worth it.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



  #7   Report Post  
DL
 
Posts: n/a
Default


"Doug Miller" wrote in message
m...
In article iFD7e.1704$H53.1652@lakeread05, "DL"
wrote:
I am in the process of installing a subpanel to consolidate the wiring in
my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps.


Unless the insulation is rated at only 60 deg C, a 2/3 cable ought to
handle a
lot more than 95 amps. Where are you getting that figure from?



The sales rep at the electrical supply stated the 95 and when I did research
on the internet for loads on copper wire, it said the same, even the board
at HD said the same as well. I didn't look in the temperature rating
though. I plan to call the county to see what they will approve. Simplest
would be that the 2/3 would be accepted for the 100amp breaker that I
currently have so I can make the connection and move on with the electrical
work.



You can do 100A in a 4/3 cable if the conductor temperature is rated 85
deg C
or higher....


I will check with the electrical supply to see what the temp rating is on
the 4/3 and 2/3 they stock.


I would prefer not to wait for the special order if I don't have to.
50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


I would think so. I'm surprised you didn't find a 60 at HD.


I expected to see the 60 and 70 as I have in the past. It could be possible
that they are starting to phase out the GE panels for the CH ones so the
selection of breakers is smaller.


My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have
a
fair amount of machinery and can see 2 - 3 users larger pieces of
equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan
than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.


You certainly have the right idea about the cost of building bigger than
you
need vs. the cost of upgrading later. But I think you're going bigger by a
larger margin than necessary. 60A at 240V will provide more power than
you're
likely to need in a home shop.



Given that I have already have the 100 and 125amp breakers for the main
panel which I would prefer to use, the cost difference in the wire is
minimal given that we are talking 50' distance. If I am correct, just
like the main panel at 200amps, if you only put one 20amp breaker in, there
won't be a problem having too many amps being fed into the subpanel, the
equipment will draw the necessary power it needs from the individual
breakers in the subpanel.

This does go to the point of equipment overload. If I have a piece of
equipment that draws 25amps and have a circuit consisting of a 50amp circuit
breaker, 6/3 wire from the breaker to the outlet, and a 50 amp outlet, I
should still be fine, isn't the logic the same? or do I need to worry about
overloading the equipment. It has always been my understanding that
equipment / motors draw the power they need from a circuit. The breaker is
designed to kick off when too much current is required thus causing a
situation where the wire would heat up and become unsafe. (goes to your
temp rating statement above)

Also, the rotary phase converter I have requires 70-80amp breaker IIRC (I
have to get with the manufacturer to confirm), though I am not exactly sure
why a 7.5hp 3 phase motor requires that much. I would figure that while it
doesn't draw those amps all the time, it is needed at some point, possibly
startup.



2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts
or
comments?


Under _no_ circumstances would I ever install an aluminum feed to a
subpanel
in my home, or advise anyone else to. It's just too risky, and for what
benefit? Sure, you might save a few bucks, but it's a whole lot less safe
than
copper unless it's installed _exactly_ right. Trouble is, it's a whole lot
more difficult to install correctly than copper is. It's not just a matter
of
adding anti-oxidant compound to the connections. Bolt lugs must be
tightened
with a torque wrench, both to make sure that they are tight enough, and to
make sure that they are not _too_ tight, because aluminum will cold-flow
away
from an overtorqued connection, loosening it, and causing it to arc. All
equipment used must be rated for use with aluminum. And so on.

Don't do it. It isn't worth it.



What I expected as a response, just wanted to confirm. The extra money of
the cooper wire is not the issue here. I am trying to get things done and
didn't want to have to wait for a special order if I didn't need to.

Thanks for the advise,

David


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?




  #8   Report Post  
DL
 
Posts: n/a
Default


"Wilson Lamb" wrote in message
ink.net...
I'm betting his whole house runs on an aluminum drop to his main panel. I
can't remember the last copper service I saw. With a big feed like that,
no sustained heavy loads, and no connections buried in the walls, I
wouldn't worry. But for a short run, copper might feel better, and be
easy to handle.
Wilson


Wilson,

The main service 200amps going to 400amps is Aluminum as you stated. Have
not had any problems with it, and I would suspect that most of the homes are
built with it as a service entrance.

Nothing buried in the walls for sure. I have been a bit obsessive on the
number of outlets to allow for easy reconfiguration down the road.

If the copper will handle the 100amp breaker I already have, then I will
most likefully go with that.

Thanks,

David

"Doug Miller" wrote in message
m...
In article iFD7e.1704$H53.1652@lakeread05, "DL"
wrote:
I am in the process of installing a subpanel to consolidate the wiring in
my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps.


Unless the insulation is rated at only 60 deg C, a 2/3 cable ought to
handle a
lot more than 95 amps. Where are you getting that figure from?

You can do 100A in a 4/3 cable if the conductor temperature is rated 85
deg C
or higher....

I would prefer not to wait for the special order if I don't have to.
50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


I would think so. I'm surprised you didn't find a 60 at HD.

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally
up
the equipment and amps that I would expect would be needed at a given
time
to make sure I have all that I need, but that is not complete) I do have
a
fair amount of machinery and can see 2 - 3 users larger pieces of
equipment
plus auxillary air compressor, dust collection, air filtration, general
power consumption that will add up. In my mind, it's not that much more
expensive to add the extra amps at this point and would rather overplan
than
be under powered at a later date which would be much more expensive to
upgade, if I needed it.


You certainly have the right idea about the cost of building bigger than
you
need vs. the cost of upgrading later. But I think you're going bigger by
a
larger margin than necessary. 60A at 240V will provide more power than
you're
likely to need in a home shop.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts
or
comments?


Under _no_ circumstances would I ever install an aluminum feed to a
subpanel
in my home, or advise anyone else to. It's just too risky, and for what
benefit? Sure, you might save a few bucks, but it's a whole lot less safe
than
copper unless it's installed _exactly_ right. Trouble is, it's a whole
lot
more difficult to install correctly than copper is. It's not just a
matter of
adding anti-oxidant compound to the connections. Bolt lugs must be
tightened
with a torque wrench, both to make sure that they are tight enough, and
to
make sure that they are not _too_ tight, because aluminum will cold-flow
away
from an overtorqued connection, loosening it, and causing it to arc. All
equipment used must be rated for use with aluminum. And so on.

Don't do it. It isn't worth it.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?





  #9   Report Post  
DL
 
Posts: n/a
Default


"Lew Hodgett" wrote in message
ink.net...
DL wrote:
I am in the process of installing a subpanel to consolidate the wiring in
my workshop. The panel is rated for 150amps, but I purchased a 125 amp
to install in the main panel.

snip

For a 120/240 VAC service, a 2P-60A main kit installed in a 125 MLO, 12/24
panel will handle everything a one man shop can throw at it.

The largest motor you can run on single phase is about 5HP, cap start, cap
run, normally found on an air compressor.

A 2P-40A branch c'bkr will handle the compressor.

Everything else incuding a table saw and a welder will be smaller loads.

HTH

Lew


Lew,

Thanks for the input.

David


  #10   Report Post  
sadler
 
Posts: n/a
Default

Lugs on panels and breakers are either rated copper only, or copper
and aluminum. If you use aluminum wire make sure the lugs on the
panel or breaker specifically are rated for aluminum.

It'll never hurt to oversize the wire. Larger sizes will lower the
voltage drop over distance.

If you are at all unsure, hire an electrician, or get advice from one.
I would not count on advice from your electrical supplier, any HD
employee, or even reccomendations for well meaning and mostly
intellegent members of this group.

my $0.02.

Alan


  #11   Report Post  
Swingman
 
Posts: n/a
Default


"DL" wrote in message
Lew,

Thanks for the input.


Take Lew's advice to heart and follow it ... I wired my shop according to
his suggestions a few years back and have not regretted it. Best advice I
ever got in exchange for a recipe, IIRC.

--
www.e-woodshop.net
Last update: 4/14/05


  #12   Report Post  
Doug Miller
 
Posts: n/a
Default

In article . net, "Wilson Lamb" wrote:
I'm betting his whole house runs on an aluminum drop to his main panel. I
can't remember the last copper service I saw. With a big feed like that, no
sustained heavy loads, and no connections buried in the walls, I wouldn't
worry. But for a short run, copper might feel better, and be easy to
handle.
Wilson


Yes, of course the whole house runs on an aluminum drop.

The difference is that the service entrance almost certainly was installed by
a professional who has the skills and knowledge to install it correctly -
skills and knowledge not possessed by the average homeowner.

_When_properly_installed_ aluminum wiring is as safe as copper. The trouble
is that aluminum is much more difficult to install properly than copper is.
It's just plain foolish for Joe Homeowner to take chances with it.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #13   Report Post  
Doug Miller
 
Posts: n/a
Default

In article FWF7e.1716$H53.475@lakeread05, "DL" wrote:

If the copper will handle the 100amp breaker I already have, then I will
most likefully go with that.


Note that if your copper cable will *not* handle it, neither will an aluminum
cable. If using aluminum [which I do *not* recommend], you need substantially
larger conductors to have the same ampacity as copper.

To carry 100A in a 3-conductor cable, you need at minimum:
4ga copper or 2ga aluminum, conductor temp 85 deg C or higher
3ga copper or 1ga aluminum, conductor temp 75 deg C or higher
1ga copper or 2/0 aluminum, conductor temp 60 deg C or higher
[National Electrical Code, Table B-310-3]

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #14   Report Post  
Doug Miller
 
Posts: n/a
Default

In article 2SF7e.1714$H53.1103@lakeread05, "DL" wrote:

Given that I have already have the 100 and 125amp breakers for the main
panel which I would prefer to use, the cost difference in the wire is
minimal given that we are talking 50' distance.


Well, it's not just the cost. Heavy cables are a PITA to work with. They don't
bend easily.

One thing I meant to mention in my first response to you, that I think I
omitted: make sure that the cable you use to feed the subpanel has a grounding
conductor. You need 2/3 WG (With Ground), not just 2/3. In the subpanel, the
equipment grounding bus bar and the neutral bus bar must *not* be connected.

If I am correct, just
like the main panel at 200amps, if you only put one 20amp breaker in, there
won't be a problem having too many amps being fed into the subpanel, the
equipment will draw the necessary power it needs from the individual
breakers in the subpanel.


Yes, that's correct.

This does go to the point of equipment overload. If I have a piece of
equipment that draws 25amps and have a circuit consisting of a 50amp circuit
breaker, 6/3 wire from the breaker to the outlet, and a 50 amp outlet, I
should still be fine, isn't the logic the same? or do I need to worry about
overloading the equipment. It has always been my understanding that
equipment / motors draw the power they need from a circuit. The breaker is
designed to kick off when too much current is required thus causing a
situation where the wire would heat up and become unsafe. (goes to your
temp rating statement above)


Your understanding is correct: the equipment draws the power it needs. The
purpose of the circuit breaker is to protect the wiring and the receptacle,
*not* what's plugged into the receptacle.

Also, the rotary phase converter I have requires 70-80amp breaker IIRC (I
have to get with the manufacturer to confirm), though I am not exactly sure
why a 7.5hp 3 phase motor requires that much. I would figure that while it
doesn't draw those amps all the time, it is needed at some point, possibly
startup.


I think you have that right, too.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #15   Report Post  
DL
 
Posts: n/a
Default


"Doug Miller" wrote in message
m...
In article 2SF7e.1714$H53.1103@lakeread05, "DL"
wrote:

Given that I have already have the 100 and 125amp breakers for the main
panel which I would prefer to use, the cost difference in the wire is
minimal given that we are talking 50' distance.


Well, it's not just the cost. Heavy cables are a PITA to work with. They
don't
bend easily.


The cost difference isn't that much so I would rather go with the heavier
wire. As for the bends, I am lucky that the routing of the wire has just a
few bends in it that can be done at a gentle curve. Once I find out wire
temp rating and what Amps the county will approve on rated 2/3, I plan to go
with the 2/3 and buy the the highest amp breaker if the 100 or 125 are too
much. Hopefully they will approve the at least the 100amp. This will
cover me for anything I have.

Thanks for the help,

David

One thing I meant to mention in my first response to you, that I think I
omitted: make sure that the cable you use to feed the subpanel has a
grounding
conductor. You need 2/3 WG (With Ground), not just 2/3. In the subpanel,
the
equipment grounding bus bar and the neutral bus bar must *not* be
connected.

If I am correct, just
like the main panel at 200amps, if you only put one 20amp breaker in,
there
won't be a problem having too many amps being fed into the subpanel, the
equipment will draw the necessary power it needs from the individual
breakers in the subpanel.


Yes, that's correct.

This does go to the point of equipment overload. If I have a piece of
equipment that draws 25amps and have a circuit consisting of a 50amp
circuit
breaker, 6/3 wire from the breaker to the outlet, and a 50 amp outlet, I
should still be fine, isn't the logic the same? or do I need to worry
about
overloading the equipment. It has always been my understanding that
equipment / motors draw the power they need from a circuit. The breaker
is
designed to kick off when too much current is required thus causing a
situation where the wire would heat up and become unsafe. (goes to your
temp rating statement above)


Your understanding is correct: the equipment draws the power it needs. The
purpose of the circuit breaker is to protect the wiring and the
receptacle,
*not* what's plugged into the receptacle.

Also, the rotary phase converter I have requires 70-80amp breaker IIRC (I
have to get with the manufacturer to confirm), though I am not exactly
sure
why a 7.5hp 3 phase motor requires that much. I would figure that while
it
doesn't draw those amps all the time, it is needed at some point, possibly
startup.


I think you have that right, too.

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?





  #16   Report Post  
Doug Miller
 
Posts: n/a
Default

In article rtP7e.443$lz1.234@lakeread01, "DL" wrote:

The cost difference isn't that much so I would rather go with the heavier
wire. As for the bends, I am lucky that the routing of the wire has just a
few bends in it that can be done at a gentle curve. Once I find out wire
temp rating and what Amps the county will approve on rated 2/3, I plan to go
with the 2/3 and buy the the highest amp breaker if the 100 or 125 are too
much. Hopefully they will approve the at least the 100amp. This will
cover me for anything I have.

Thanks for the help,


You're welcome. You did catch the part about needing three conductors PLUS
ground (below), right?

One thing I meant to mention in my first response to you, that I think I
omitted: make sure that the cable you use to feed the subpanel has a
grounding conductor. You need 2/3 WG (With Ground), not just 2/3. In the subpanel,
the equipment grounding bus bar and the neutral bus bar must *not* be
connected.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #17   Report Post  
DL
 
Posts: n/a
Default


"DL" wrote in message
news:iFD7e.1704$H53.1652@lakeread05...
I am in the process of installing a subpanel to consolidate the wiring in
my workshop. The panel is rated for 150amps, but I purchased a 125 amp to
install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps. I
would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)

My questions a

1. I am thinking that I really don't need 100amps, so I wanted to query
others to see what they have installed. (I am in the process of totally up
the equipment and amps that I would expect would be needed at a given time
to make sure I have all that I need, but that is not complete) I do have
a fair amount of machinery and can see 2 - 3 users larger pieces of
equipment plus auxillary air compressor, dust collection, air filtration,
general power consumption that will add up. In my mind, it's not that
much more expensive to add the extra amps at this point and would rather
overplan than be under powered at a later date which would be much more
expensive to upgade, if I needed it.

2. I can purchase Aluminum to handle the 125amp's but I have heard bad
things about the aluminum connection corrosion. I know I can put the
special grease on the connections to prevent the corrosion. Any thoughts
or comments?

David


Just spoke with the county and they will approve up to 115amps on 2/3 with
ground. With the rotary phase converter requiring a 70-80amp breaker, and
since I already have a 100amp breaker, that is what I plan to go with. The
extra cost in wire is offset by it being able to handle the smaller loads
better and I won't have to upgrade in the future.

Thanks to all that responded.

David


  #18   Report Post  
DL
 
Posts: n/a
Default


"Doug Miller" wrote in message
m...
In article rtP7e.443$lz1.234@lakeread01, "DL"
wrote:

The cost difference isn't that much so I would rather go with the heavier
wire. As for the bends, I am lucky that the routing of the wire has just
a
few bends in it that can be done at a gentle curve. Once I find out wire
temp rating and what Amps the county will approve on rated 2/3, I plan to
go
with the 2/3 and buy the the highest amp breaker if the 100 or 125 are too
much. Hopefully they will approve the at least the 100amp. This will
cover me for anything I have.

Thanks for the help,


You're welcome. You did catch the part about needing three conductors PLUS
ground (below), right?

Doug,

Yes I did, it's 2/3 with ground, and I do understand that the neutral and
ground bars are not to be connected in the subpanel as the are in the main
panel.

Thanks again,

David

One thing I meant to mention in my first response to you, that I think I
omitted: make sure that the cable you use to feed the subpanel has a
grounding conductor. You need 2/3 WG (With Ground), not just 2/3. In the
subpanel,
the equipment grounding bus bar and the neutral bus bar must *not* be
connected.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



  #19   Report Post  
Duane Bozarth
 
Posts: n/a
Default

DL wrote:
....
... With the rotary phase converter requiring a 70-80amp breaker, ...


Just out of curiousity, whose converter did you go with and reasons for
the particular choice???
  #20   Report Post  
Mike Marlow
 
Posts: n/a
Default


"Doug Miller" wrote in message
...

Yes, of course the whole house runs on an aluminum drop.

The difference is that the service entrance almost certainly was installed

by
a professional who has the skills and knowledge to install it correctly -
skills and knowledge not possessed by the average homeowner.

_When_properly_installed_ aluminum wiring is as safe as copper. The

trouble
is that aluminum is much more difficult to install properly than copper

is.
It's just plain foolish for Joe Homeowner to take chances with it.


While I do generally agree with what you've said about the advantages of
copper over aluminum in this whole thread Doug, I do disagree with what you
say here. There's just too many home across America that had their service
entrance installed by the home owner with absolutely no problems and no
reason to believe there will be any probles, for your assertion above to be
correct. It really does not take a professional to install a service with
aluminum wire. It really does not take any special skills or sage wisdom.
It's just a connection. The average homeowner is very capable of posessing
these skills and knowledge. Not to say that all are of course, but that'd
be another thread. Sometimes we can overly mystify this stuff.

--

-Mike-





  #21   Report Post  
Fly-by-Night CC
 
Posts: n/a
Default

In article ,
"Swingman" wrote:

Lew,

Thanks for the input.


Take Lew's advice to heart and follow it ... I wired my shop according to
his suggestions a few years back and have not regretted it. Best advice I
ever got in exchange for a recipe, IIRC.


And DL when you get to the point of installing new lighting, do a
newsgroup google search with Lew's name as author - I followed his
advice and am quite pleased with the brightness in my shop.
--
Owen Lowe
The Fly-by-Night Copper Company
____

"I pledge allegiance to the flag of the
Corporate States of America and to the
Republicans for which it stands, one nation,
under debt, easily divisible, with liberty
and justice for oil."
- Wiley Miller, Non Sequitur, 1/24/05
  #22   Report Post  
DL
 
Posts: n/a
Default


"Duane Bozarth" wrote in message
...
DL wrote:
...
... With the rotary phase converter requiring a 70-80amp breaker, ...


Just out of curiousity, whose converter did you go with and reasons for
the particular choice???


Duane,

I will have to get the information on the brand (I think S&S) for you as it
is stored currently while I am doing the buildout. The unit has a 7.5hp
Baldor motor that I purchased based on an original thought that I would
purchase older 3-phase equipment and restore it for use in my workshop since
I am unable to get 3-phase service. Primary reason for this one was
capacity and price. I bought it used in ebay for a good price IMO.

I am rethinking the need for the rotary phase converter at my current
location. Having a somewhat longer term goal to move where I should be able
to get the 3 phase power brought in directly into a dedicated workshop
building, I will hold off on purchasing anymore 3 phase equipment. For the
3 phase lathe I have, I am strongly considering moving to a variable
frequency drive that will convert the single to 3 phase, thus obviating my
current need for the phase converter at all. The rotary phase converter I
have not is way over spec for the lathe alone, but wouldn't be for a 7.5hp
DeWalt RAS or other larger machinery that I want to delve into at some
point.

David




  #23   Report Post  
DL
 
Posts: n/a
Default

"Fly-by-Night CC" wrote in message
news
In article ,
"Swingman" wrote:

Lew,

Thanks for the input.


Take Lew's advice to heart and follow it ... I wired my shop according to
his suggestions a few years back and have not regretted it. Best advice I
ever got in exchange for a recipe, IIRC.


And DL when you get to the point of installing new lighting, do a
newsgroup google search with Lew's name as author - I followed his
advice and am quite pleased with the brightness in my shop.
--
Owen Lowe
The Fly-by-Night Copper Company
____



Thanks, it is next on my list...

David



"I pledge allegiance to the flag of the
Corporate States of America and to the
Republicans for which it stands, one nation,
under debt, easily divisible, with liberty
and justice for oil."
- Wiley Miller, Non Sequitur, 1/24/05



  #24   Report Post  
Doug Miller
 
Posts: n/a
Default

In article , "Mike Marlow" wrote:

While I do generally agree with what you've said about the advantages of
copper over aluminum in this whole thread Doug, I do disagree with what you
say here. There's just too many home across America that had their service
entrance installed by the home owner with absolutely no problems and no
reason to believe there will be any probles, for your assertion above to be
correct. It really does not take a professional to install a service with
aluminum wire. It really does not take any special skills or sage wisdom.


I'm sorry, but that's not true, not completely, anyway. No, it doesn't require
a professional to install aluminum wire [and I did not say that it did], but
it *does* require special knowledge, if not special skills, and tools that are
not in the average homeowner's toolbox.

To install aluminum safely, connections must be coated with anti-oxidant
compound. This is not necessary with copper. And not everyone knows about the
difference.

Lugs holding aluminum wire must be tightened to a specific torque. Too loose,
and the wire arcs, or comes out - but too tight, and it cold-flows away, and
arcs. Again, not everyone knows this. And the average homeowner does not have
a torque wrench in his toolbox.

It's just a connection.


No, it's *not* "just a connection". It's a connection that needs to be made
with substantially more care than connections involving copper wire. And not
everybody knows this.

The average homeowner is very capable of posessing
these skills and knowledge.


I never said that the average homeowner was not *capable* of possessing the
requisite skills and knowledge. I do claim, though, that the average homeowner
possesses neither those skills, nor a torque wrench.

Not to say that all are of course, but that'd
be another thread. Sometimes we can overly mystify this stuff.


I'm not trying to make mysteries out of anything. Just pointing out that
installing aluminum wire correctly is not as simple as installing copper wire
correctly - and since *any* incorrectly installed wiring presents potentially
lethal hazards, Joe Homeowner is better off using copper simply because it's
harder to screw up.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #25   Report Post  
Duane Bozarth
 
Posts: n/a
Default

DL wrote:

....
I will have to get the information on the brand (I think S&S) for you as it
is stored currently while I am doing the buildout. The unit has a 7.5hp
Baldor motor that I purchased based on an original thought that I would
purchase older 3-phase equipment and restore it for use in my workshop since
I am unable to get 3-phase service. Primary reason for this one was
capacity and price. I bought it used in ebay for a good price IMO.

....

OK, thanks...it's been a low-level "onna-these-here-days" for some time
now. I eventually want the shop in the barn loft and would like a
couple larger pieces such as a 4-side moulder and thickness sander that
could be in the present shop area where the low ceilings aren't such an
issue...haven't found that bargain as yet (but haven't really searched
seriously yet, either)...

If one should wander off to SW KS sometime and were in need of a home,
I'm sure something could be arranged...


  #26   Report Post  
DL
 
Posts: n/a
Default

"Doug Miller" wrote in message
m...
In article , "Mike Marlow"
wrote:

While I do generally agree with what you've said about the advantages of
copper over aluminum in this whole thread Doug, I do disagree with what
you
say here. There's just too many home across America that had their
service
entrance installed by the home owner with absolutely no problems and no
reason to believe there will be any probles, for your assertion above to
be
correct. It really does not take a professional to install a service with
aluminum wire. It really does not take any special skills or sage wisdom.


I'm sorry, but that's not true, not completely, anyway. No, it doesn't
require
a professional to install aluminum wire [and I did not say that it did],
but
it *does* require special knowledge, if not special skills, and tools that
are
not in the average homeowner's toolbox.

To install aluminum safely, connections must be coated with anti-oxidant
compound. This is not necessary with copper. And not everyone knows about
the
difference.

Lugs holding aluminum wire must be tightened to a specific torque. Too
loose,
and the wire arcs, or comes out - but too tight, and it cold-flows away,
and
arcs. Again, not everyone knows this. And the average homeowner does not
have
a torque wrench in his toolbox.

It's just a connection.


No, it's *not* "just a connection". It's a connection that needs to be
made
with substantially more care than connections involving copper wire. And
not
everybody knows this.

The average homeowner is very capable of posessing
these skills and knowledge.


I never said that the average homeowner was not *capable* of possessing
the
requisite skills and knowledge. I do claim, though, that the average
homeowner
possesses neither those skills, nor a torque wrench.


I agree with Mike that it is not a overly complex connection to install as
long as someone has the proper knowledge, tools, and respect for the
potential dangers of not doing it correctly. I also agree with Doug that
the are inherent issues with the Al connection that don't arise with the
copper installation. When I added an addition on our old house, I needed to
redo a significant amount of the wiring the previous owner did when he added
a small addition on the house because it was installed wrong.

Also, the fact that I would need to go to #00 Al to get the same load
capacity, it as the #2 copper, going with the cooper will just be easier to
handle when I am routing the cable from the main to the subpanel.

It's great to know that I am not an average "Joe" homeowner. Not only do I
have a torque wrench and know how to use it, I have three of varing sizes

David


Not to say that all are of course, but that'd
be another thread. Sometimes we can overly mystify this stuff.


I'm not trying to make mysteries out of anything. Just pointing out that
installing aluminum wire correctly is not as simple as installing copper
wire
correctly - and since *any* incorrectly installed wiring presents
potentially
lethal hazards, Joe Homeowner is better off using copper simply because
it's
harder to screw up.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?




  #27   Report Post  
Backlash
 
Posts: n/a
Default

Dang, Lew, I've got ONE welder I'm gonna install that the data plate says
requires a 95 amp circuit.......One of the best things I ever did was
install a 200 amp main just for my one man shop.

RJ

"Lew Hodgett" wrote in message
ink.net...
DL wrote:
I am in the process of installing a subpanel to consolidate the wiring in
my workshop. The panel is rated for 150amps, but I purchased a 125 amp
to install in the main panel.

snip

For a 120/240 VAC service, a 2P-60A main kit installed in a 125 MLO, 12/24
panel will handle everything a one man shop can throw at it.

The largest motor you can run on single phase is about 5HP, cap start, cap
run, normally found on an air compressor.

A 2P-40A branch c'bkr will handle the compressor.

Everything else incuding a table saw and a welder will be smaller loads.

HTH

Lew



  #28   Report Post  
Electric Stu
 
Posts: n/a
Default

I installed a dedicated subpanel for my shop when I built it a couple
of years ago. I did a fair amount of research in preparation for the
shop wiring and ended up using a 10/20 125amp Siemens panelboard with a
copper bus. I had only a 10 foot run from the main service panel to the
subpanel. The electrical supply store I went to had 25' of already cut
2/3 w/ground copper that someone never picked up, so he gave it to me
for 40 cents/foot and he threw in a 90 amp DP breaker, so that's what I
used (even though the ampacity of the cable conductors is much
greater). I installed ten branch circuits using 12/2 w/ ground NM cable
with 220V and 110V Twist-Loc receptacles (Hubbell - ridiculously cheap
@ $2.50/each by the box on eBay at the time) generously spaced around
the shop for flexibility in tool placement. Next to each Twist-Loc, I
also installed conventional 110V receptacles (industrial grade
Hubbell's, once again dirt cheap on eBay). I installed industrial
fluorescent T8 electronic ballast fixtures as well, divided into two
zones, controlled by 3-way switches at each of two doors. There are
both 4' and 8' dual bulb fixtures with a total of 22 4' bulbs. I made
certain to wire the lighting into the main panel on its own 20A circuit
instead of into the subpanel, so the lights wouldn't go out if the
subpanel breaker tripped (e.g., while I was ripping a narrow piece of
maple). All in all, I used about 600-700' of 12/2 NM for all of the
wiring, but it came out beautiful and works like a charm.

To minimize accidental use of any tools by unauthorized people (i.e.,
kids), I habitually flip off the subpanel breaker in the main service
panel when I'm finished in the shop.

I did make sure that I pulled appropriate permits and had everything
inspected, not because I wasn't confident in my wiring skills, but for
insurance reasons, in the event of an unexpected catastrophe. The
electical inspector turned out to be a woodworker, so for the rough
inspection, he spent more time talking to me about woodworking than
actually inspecting. He said he normally scruntinizes homeowner's
wiring, but said the wiring job was better than most professional jobs
he inspects. We both agreed that this likely relates to the attention
to detail inherent to woodworkers.

Good luck.

Stu





In article , Duane Bozarth
wrote:

DL wrote:

...
I will have to get the information on the brand (I think S&S) for you as it
is stored currently while I am doing the buildout. The unit has a 7.5hp
Baldor motor that I purchased based on an original thought that I would
purchase older 3-phase equipment and restore it for use in my workshop since
I am unable to get 3-phase service. Primary reason for this one was
capacity and price. I bought it used in ebay for a good price IMO.

...

OK, thanks...it's been a low-level "onna-these-here-days" for some time
now. I eventually want the shop in the barn loft and would like a
couple larger pieces such as a 4-side moulder and thickness sander that
could be in the present shop area where the low ceilings aren't such an
issue...haven't found that bargain as yet (but haven't really searched
seriously yet, either)...

If one should wander off to SW KS sometime and were in need of a home,
I'm sure something could be arranged...

  #29   Report Post  
Brian Elfert
 
Posts: n/a
Default

"DL" writes:

I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to


I installed 100 amps, but I doubt I'll ever need that much. I could
envision the 220V dust collector, 220V Unisaw, and the 220V air compressor
all running at once, but they would take 40 amps or less.

install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps. I
would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


My local Home Depot has wire plenty big enough to handle 100 amps. It is
THHN and has to be run in a conduit. I used three seperate wires to feed
my subpanel.

Brian Elfert
  #30   Report Post  
Lee Cobb
 
Posts: n/a
Default

both home depot and lowes have mobile home feed cable. rated at 150
amps, i believe, capable of being buried without a conduit. sizes i
forget. it is actually 3 wires (2 aluminum and 1 copper, i believe)
twisted together. locally it runs $1.28 to $1.50 per foot. of course
installation above ground should have appropriate sized conduit where
contact could be made

On Mon, 18 Apr 2005 14:52:52 -0000, Brian Elfert
wrote:

"DL" writes:

I am in the process of installing a subpanel to consolidate the wiring in my
workshop. The panel is rated for 150amps, but I purchased a 125 amp to


I installed 100 amps, but I doubt I'll ever need that much. I could
envision the 220V dust collector, 220V Unisaw, and the 220V air compressor
all running at once, but they would take 40 amps or less.

install in the main panel. I additionally have a 100amp breaker as well.
The largest bound copper cable I can get without a special order from the
local electrical supply house is 2/3 which will handle up to 95amps. I
would prefer not to wait for the special order if I don't have to. 50amps
is the next size down at the local Home Depot, ( I need to see what the
electric supply house has, I assume I can get a 70, 80, or 90)


My local Home Depot has wire plenty big enough to handle 100 amps. It is
THHN and has to be run in a conduit. I used three seperate wires to feed
my subpanel.

Brian Elfert


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel Electrical Fire Seawulf Woodworking 39 March 10th 05 02:59 AM
Electric Subpanel fire Seawulf Home Repair 25 March 8th 05 03:54 AM
Workshop Wiring - Prep work before Electrician jonni UK diy 26 July 19th 04 08:48 AM
Installing a subpanel Gary Tait Home Repair 10 July 27th 03 03:06 PM


All times are GMT +1. The time now is 04:29 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"