Default Do I RCD protect the oven and hob or not?

Currently I have a split load consumer unit, boths sides have their own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this non
RCD CU?

Sparks...


  #2   Report Post  
waddy
 
Posts: n/a
Default


Sparks wrote:
Currently I have a split load consumer unit, boths sides have their

own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers

and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this

non
RCD CU?

Sparks...


  #3   Report Post  
waddy
 
Posts: n/a
Default

Hi Sparticus,

You should put the hob and oven on an rcd protective device if one is
available, obviously if they are not on rcd it will still comply with
the iee 16th ed regs (excluding outside/garden barbecues/sockets, etc),
though if you have a circuit available with rcd protection for the
hob/oven then use it.

You shouldn't really put lighting circuits on rcd protective circuits,
hence the idea of a split consumer unit, as a trip of the lighting
causes a hazard in itself, also alarm circuits i.e. fire/intruder
(without outlets should be dedicated circuits) should also not be rcd
proctected for similar reasons.

Regs Alan


Sparks wrote:
Currently I have a split load consumer unit, boths sides have their

own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers

and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this

non
RCD CU?

Sparks...


  #4   Report Post  
Fred
 
Posts: n/a
Default


"waddy" wrote in message
oups.com...
Hi Sparticus,



You shouldn't really put lighting circuits on rcd protective circuits,
hence the idea of a split consumer unit, as a trip of the lighting
causes a hazard in itself, also alarm circuits i.e. fire/intruder
(without outlets should be dedicated circuits) should also not be rcd
proctected for similar reasons.

Regs Alan




I have always been amazed in this day and of implied safety, you're still
allowed to have bare connectors associated with light fittings without any
protection at 230V AC.

What do you think will be in the 17th Edition?


  #5   Report Post  
Sparks
 
Posts: n/a
Default

They don't need RCD protecting, and oven elements can cause
tripping whilst not presenting any significant electrocution
risk which means it's not a brilliant idea to have them sharing
an RCD with anything else. So normally, they go on the non-RCD
protected side.


Another thing I should have said, or asked, What type of earthing
system do you have? If it's a TT system, you can't normally have
any non-RCD protected circuits (except possibly for some low
current ones if you can prove the earth fault loop impedance is
OK for them). This might be the reason you have all circuits RCD
protected (although some of them should be at = 100mA).


The house is a TN-S (Supplied by the electricity company's cable)

Incedently, this earth wire from the head to the CU seems to be about 4mm or
6mm - is this normal, or should it be replaced with heavier cable?

If so, do I ask the electricity company, as it is sealed in the lower part
of the cable head?

Sparks...




  #6   Report Post  
Sparks
 
Posts: n/a
Default

Sparks wrote:
Currently I have a split load consumer unit, boths sides have their

own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers

and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this

non
RCD CU?

Sparks...



"waddy" wrote in message
oups.com...
Hi Sparticus,

You should put the hob and oven on an rcd protective device if one is
available, obviously if they are not on rcd it will still comply with
the iee 16th ed regs (excluding outside/garden barbecues/sockets, etc),
though if you have a circuit available with rcd protection for the
hob/oven then use it.

You shouldn't really put lighting circuits on rcd protective circuits,
hence the idea of a split consumer unit, as a trip of the lighting
causes a hazard in itself, also alarm circuits i.e. fire/intruder
(without outlets should be dedicated circuits) should also not be rcd
proctected for similar reasons.



So, for the fridge and freezer, should these be hard wired, so not having a
socket on an unprotected circuit?

Sparks...


  #7   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Sparks wrote:

Would it be advisable to put the oven and induction hob feeds on this non
RCD CU?

My preference would be to put those fixed loads on the non RCD side. The
Regs certainly don't require them to be RCDed; and the older your oven
and grill elements get (also radiant and 'sealed' hotplates, but not
induction plates as you have) the more they pass a small leakage
current, especially when cold and a little damp (e.g. after a steamy
baking session as the elements cool down). Putting these on a shared RCD
predisposes that RCD to nuisance tripping.

But if you prefer the added reassurance that slopping salty spud-boiling
water about will cut the supply should it drip where it shouldn't,
there's nothing deeply bad about putting it on the RCD side. You could
always (assuming enough slack at the CU end) start off with it on the
RCD side, and move it across to the non-RCD CU if you get nuisance trips
which sort-of tie in with turning the cooker on.

In my direct experience of this, with a whole-house RCD (as used to be
the fashion), young kids (so making me keen on keeping the whole-house
RCD until they were past the fingerpoken age - 85, isn't it? ;-), a
coupla 'emergency' lights which came on if the power failed, and a
growing number of switched-mode-PSU computers and mains-filtered
appliances, *oh* and an RCD which on test showed it'd trip at under
14mA! - it was still only rare that turning on the cooker ring/grill
would make the RCD trip immediately; rather, it'd pop a minute or two
after you'd started to use the cooker. Maybe an element had to expand a
little first to bring a live conductor close enough to the earthed
casing to leak enough... maybe it was just pixies at work ;-)

HTH - Stefek
  #8   Report Post  
Lee
 
Posts: n/a
Default

Fred wrote:

I have always been amazed in this day and of implied safety, you're still
allowed to have bare connectors associated with light fittings without any
protection at 230V AC.


It comes down to which is the greater danger, being plunged into
darkness or being electrocuted...

FWIW our lighting circuits are RCD protected and are staying like it

Lee
--
Email address is valid, but is unlikely to be read.
  #9   Report Post  
Dave Jones
 
Posts: n/a
Default


"Sparks" wrote in message
.. .
Currently I have a split load consumer unit, boths sides have their own
30mA RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this non
RCD CU?

Sparks...


Why have you got 2 RCD's are you sure they are both RCD's? If so I'd remove
the one supplying the lighting and add the other circuits to it, if you have
room and don't overload the cu!

If the oven switch has a 13 amp outlet on it then it must be rcd protected,
otherwise up to u.


  #10   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Dave Jones wrote:


If the oven switch has a 13 amp outlet on it then it must be rcd protected,
otherwise up to u.

I can think of few downstairs sockets *less* likely to get an outdoor
appliance plugged in than the one permanently occupied by the
householder's kettle - so I don't understand why you hold with such
certainty that a cooker-control unit with integral socket 'must' be RCD
protected...


  #11   Report Post  
Sparks
 
Posts: n/a
Default

"Stefek Zaba" wrote in message
...
Sparks wrote:


The house is a TN-S (Supplied by the electricity company's cable)

Incedently, this earth wire from the head to the CU seems to be about 4mm
or 6mm - is this normal, or should it be replaced with heavier cable?

If so, do I ask the electricity company, as it is sealed in the lower
part of the cable head?

It will have been compliant when installed - maybe, say 14th Edn of
t'Regs. Theze Dayz it'd be 16mmsq or so. Not sure there's a *vast* benefit
in getting the supply co out to upgrade - they may then want you (or at
least suggest you should) up the rest of your own bonding to
10mmsq/16mmsq, and/or PMEify you...


So, if it was compliant at some point, it would still pass an inspection
now?

If that is that case. surely that is a bit stupid, as if the regulations
have changed, the older ones must now be deemed unsafe?

Sparks...


  #12   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
"Sparks" writes:
Currently I have a split load consumer unit, boths sides have their own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this non
RCD CU?


They don't need RCD protecting, and oven elements can cause
tripping whilst not presenting any significant electrocution
risk which means it's not a brilliant idea to have them sharing
an RCD with anything else. So normally, they go on the non-RCD
protected side.

--
Andrew Gabriel
  #14   Report Post  
Peter Parry
 
Posts: n/a
Default

On Wed, 30 Mar 2005 20:30:02 GMT, Lee
wrote:


It comes down to which is the greater danger, being plunged into
darkness or being electrocuted...


That one is a complete no brainer.

The number of people killed or severely injured by electrocution in
domestic accidents the UK each year is very small. Even if you
include accidents which are not electrocution but attributable to it
(such as falling off a ladder after touching a live cable) the
numbers involved in domestic accidents are still small, about 25
deaths and 2000 injuries of all severities (compare this with 70
deaths and 40,000 injuries caused by DIY!). Those figures have not
reduced since whole house RCD's started to be used but are expected
to rise with Part P dissuading people from installing extra sockets
and increasing the use of extension leads.

The total number of people killed in accidents in the home each year
is about 4,000, of this roughly half are due to falls and about 1,000
due to falls down stairs.

The number of people killed or injured in house fires is also
depressingly large, many times greater than those killed by
electrocution. Typically 500 people die and 18,000 are seriously
injured each year by fire in the home. Of these deaths about 20 are
attributable to electrical fires some of which an RCD might have
prevented. The remainder are caused by non-electrical ignition.

Of the 4,000 people killed in both falls and fires each year there is
no easily available breakdown of contributory factors. However some
police and fire reports do give further information. Of these I have
seen only a very small number from one area, however within these
there were a significant minority, probably about 10-20 which
mentioned that lights were out and could not be turned back on from
the light switch when the emergency services arrived. Only one or
two of these, usually fire service reports, specifically mention
RCD's having tripped. Nonetheless it is reasonable to infer even
from this imperfect data that the number of people killed in falls
and fires in which tripped RCD's were the cause or a major
contributory factor is significantly higher than the number of people
protected by them _in the home_. In the garden or garage is quite
another matter.

FWIW our lighting circuits are RCD protected and are staying like it


I suggest you invest in a book on basic risk assessment.

--
Peter Parry.
http://www.wpp.ltd.uk/
  #15   Report Post  
Peter Parry
 
Posts: n/a
Default

On 30 Mar 2005 10:32:58 -0800, "waddy"
wrote:


You should put the hob and oven on an rcd protective device if one is
available,


What benefit will this bring?

--
Peter Parry.
http://www.wpp.ltd.uk/


  #16   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Sparks wrote:


The house is a TN-S (Supplied by the electricity company's cable)

Incedently, this earth wire from the head to the CU seems to be about 4mm or
6mm - is this normal, or should it be replaced with heavier cable?

If so, do I ask the electricity company, as it is sealed in the lower part
of the cable head?

It will have been compliant when installed - maybe, say 14th Edn of
t'Regs. Theze Dayz it'd be 16mmsq or so. Not sure there's a *vast*
benefit in getting the supply co out to upgrade - they may then want you
(or at least suggest you should) up the rest of your own bonding to
10mmsq/16mmsq, and/or PMEify you...
  #17   Report Post  
Lee
 
Posts: n/a
Default

Peter Parry wrote:

I suggest you invest in a book on basic risk assessment.


Just because we chose one slight benefit over a possible risk does not
mean that we are unaware that risk.

We are unlikely to fall down stairs we don't have, for instance...

Lee
--
Email address is valid, but is unlikely to be read.
  #18   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Sparks wrote:
Would it be advisable to put the oven and induction hob feeds on this
non RCD CU?


Yes. There's no point in RCD protecting permanently connected devices like
this - and since they may well have mineral insulated heating elements
might cause nuisance tripping.

--
*Change is inevitable, except from a vending machine.

Dave Plowman London SW
To e-mail, change noise into sound.
  #19   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Fred wrote:
I have always been amazed in this day and of implied safety, you're
still allowed to have bare connectors associated with light fittings
without any protection at 230V AC.


I tend to agree. I know the arguments about a blown bulb plunging the
house into darkness - but think the hazards of Joe Bloggs replacing a bulb
on a possibly live circuit more of a risk. IMHO.

--
*Dance like nobody's watching.

Dave Plowman London SW
To e-mail, change noise into sound.
  #20   Report Post  
raden
 
Posts: n/a
Default

In message , Lee
writes
Peter Parry wrote:

I suggest you invest in a book on basic risk assessment.


Just because we chose one slight benefit over a possible risk does not
mean that we are unaware that risk.

We are unlikely to fall down stairs we don't have, for instance...

But for those of us with real stairs ...

No I'm not going there,

what are the upright bits of a bannister called, and where can you buy
them

Off to book my holiday to Indonesia, prolly safer

--
geoff


  #21   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Sparks wrote:

If that is that case. surely that is a bit stupid, as if the regulations
have changed, the older ones must now be deemed unsafe?

No - there's every difference between 'unsafe' and 'not to latest
standards for a new installation'. There's no obligation to keep an
installation continually updated in line with Regs changes (though I bet
the NICEIC would *lurv* such a principle to be established). There's a
specific category for 'not in line with latest Regs but not presenting
any problem' on the standard Periodic Inspection form (scrabbles for
OSG: ah yes, here it is.) There's a 4-level "recommendation" scale,
thus: "1 - requires urgent attention; 2 - requires improvement; 3 -
requires further investigation; 4 - does not comply with BS 7671:2001
amended to date. This does not imply that the electrical installation
inspected is unsafe."

HTH - Stefek
  #22   Report Post  
The Natural Philosopher
 
Posts: n/a
Default

Sparks wrote:

Currently I have a split load consumer unit, boths sides have their own 30mA
RCD
It is split into lighing one side, and everthing else the other.

I am adding a second CU for non-RCD protected things (Alarm, freezers and
feeds to smaller comsomer units in the shed & garage)

Would it be advisable to put the oven and induction hob feeds on this non
RCD CU?

Sparks...


No idea what regs apply, but I personally like a BIG RCD - 100mA - for
the whole house, and 30mA RCBO's for where the regs say its needed.

Cookers aint it though. I do not believe there is a requirement to RCD them

I believe the philosophy is where portable appliances have cables whose
earth may become cut or disconnected and/or the appliance may become damp.

  #23   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
"Fred" writes:

I have always been amazed in this day and of implied safety, you're still
allowed to have bare connectors associated with light fittings without any
protection at 230V AC.


When doing portable appliance testing and checking for IP2X
(fingers can't access live parts), lampholders is the one
exception allowed there. (The usual causes for failures on
this test are old electric fires with the grill guard spacing
large enough to poke a finger through.)

--
Andrew Gabriel
  #24   Report Post  
John Rumm
 
Posts: n/a
Default

raden wrote:

what are the upright bits of a bannister called, and where can you buy them


Newel post, or Spindles (depending on if you mean the thick ones at the
ends or dainty bits in the middle.

Screwfix have a small selection.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #25   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
John Rumm writes:
raden wrote:

what are the upright bits of a bannister called, and where can you buy them


Newel post, or Spindles (depending on if you mean the thick ones at the
ends or dainty bits in the middle.


or balustrades for a generic term that covers spindles and non-
turned/spun equivalents.

Screwfix have a small selection.


Richard Burbridge is a manufacturer stocked by B&Q and many of
the builders merchants. Wickes have their own equivalent range.
When I built my bannisters, I used a Richard Burbridge handrail,
but I made all the other parts from scratch from planed timber.

--
Andrew Gabriel


  #26   Report Post  
Fred
 
Posts: n/a
Default


"Andrew Gabriel" wrote in message
...
In article ,
"Fred" writes:

I have always been amazed in this day and of implied safety, you're

still
allowed to have bare connectors associated with light fittings without

any
protection at 230V AC.


When doing portable appliance testing and checking for IP2X
(fingers can't access live parts), lampholders is the one
exception allowed there. (The usual causes for failures on
this test are old electric fires with the grill guard spacing
large enough to poke a finger through.)

--
Andrew Gabriel


Can these fires be re-labelled as an incandescent light?


  #27   Report Post  
Lee
 
Posts: n/a
Default

Dave Plowman (News) wrote:

Yes. There's no point in RCD protecting permanently connected devices like
this - and since they may well have mineral insulated heating elements
might cause nuisance tripping.


One, admittedly tenuous, advantage to putting a cooker on an RCD, is
that it's more likely a "soft" failure when there is a fault - might be
better for those of a nervous disposition than a "bang" from a failed
element

Lee
--
Email address is valid, but is unlikely to be read.
  #28   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
Lee writes:

One, admittedly tenuous, advantage to putting a cooker on an RCD, is
that it's more likely a "soft" failure when there is a fault - might be
better for those of a nervous disposition than a "bang" from a failed
element


So you end up with an unusable oven which trips everything else.
If it wasn't on an RCD, it would continue working fine for years,
as the element will drive off the moisture causing the leak within
a few seconds of switching on. You don't generally get bangs from
failed elements -- they eventually just go open circuit, possibly
with a little arcing, but basically pretty harmlessly.

--
Andrew Gabriel
  #29   Report Post  
raden
 
Posts: n/a
Default

In message , John
Rumm writes
raden wrote:

what are the upright bits of a bannister called, and where can you buy them


Newel post, or Spindles (depending on if you mean the thick ones at the
ends or dainty bits in the middle.

I know, I wasn't really expecting a reply on that one

--
geoff
  #30   Report Post  
Lee
 
Posts: n/a
Default

Andrew Gabriel wrote:

You don't generally get bangs from
failed elements -- they eventually just go open circuit, possibly
with a little arcing, but basically pretty harmlessly.


It was meant tongue in cheek - did you spot the smilies?

Though I have seen some pretty noisy element failures in the past -
especially the old "ring" type hobs.
I take it modern designs don't fail like that any more then?

Lee
--
Email address is valid, but is unlikely to be read.


  #31   Report Post  
Dave Jones
 
Posts: n/a
Default


"Stefek Zaba" wrote in message
...
Dave Jones wrote:


If the oven switch has a 13 amp outlet on it then it must be rcd
protected, otherwise up to u.

I can think of few downstairs sockets *less* likely to get an outdoor
appliance plugged in than the one permanently occupied by the
householder's kettle - so I don't understand why you hold with such
certainty that a cooker-control unit with integral socket 'must' be RCD
protected...


Due to the current regulations, "all downstairs socket outlets must be rcd
protected".

Wouldn't that depends on the position of your cooker with location to the
nearest window, majority of council properties I've been to have the cooker
near a window or the back door, ideal for plugging in the lawnmower!


  #32   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Dave Jones wrote:


Due to the current regulations, "all downstairs socket outlets must be rcd
protected".

No, that's not the wording. The wording's closer to 'sockets it can
reasonably be foreseen that an outdoor appliance will be plugged in to'.
It's then a common interpretation to take that to mean 'all downstairs
sockets' - AFAIR that's what Whitfield suggests - but it's down to
common sense. If there are other kitchen sockets closer to door/window,
much more so if there's a handy outdoor socket on the outside wall -
*that*'s where yer lawnmower, hedge trimmer, yada yada is going to get
plugged in. You could even label the cooker-unit socket with a pretty
"INDOOR USE ONLY!" notice, to drive the point home.

Still, there's common-sense and let-Darwin-rule; and then there's
jobbing electricians who need to cover their posteriors lest Wayne and
Waynetta stick the where-there's-blame mob onto them, I guess...
  #33   Report Post  
Owain
 
Posts: n/a
Default

Stefek Zaba wrote:
If the oven switch has a 13 amp outlet on it then it must be rcd
protected, otherwise up to u.

I can think of few downstairs sockets *less* likely to get an outdoor
appliance plugged in than the one permanently occupied by the
householder's kettle


I don't know why kettles are plugged into cooker control units. In the
days when the cooker unit was the only outlet in the kitchen rated
higher than a BC lampholder adapter perhaps. My kettle's plugged in next
to the sink as that's where it gets filled for tea and emptied for the
odd top-up of boiling water for the washing-up.

The cooker socket at the other end of the kitchen (and nearest the
window, so most likely to be used for outdoor appliance apart from the
fact that this is an upstairs flat) is used for the fridge.

Owain

  #34   Report Post  
Dave Jones
 
Posts: n/a
Default


"Stefek Zaba" wrote in message
...
Dave Jones wrote:


Due to the current regulations, "all downstairs socket outlets must be
rcd protected".

No, that's not the wording. The wording's closer to 'sockets it can
reasonably be foreseen that an outdoor appliance will be plugged in to'.
It's then a common interpretation to take that to mean 'all downstairs
sockets' - AFAIR that's what Whitfield suggests - but it's down to common
sense. If there are other kitchen sockets closer to door/window, much more
so if there's a handy outdoor socket on the outside wall - *that*'s where
yer lawnmower, hedge trimmer, yada yada is going to get plugged in. You
could even label the cooker-unit socket with a pretty "INDOOR USE ONLY!"
notice, to drive the point home.

Still, there's common-sense and let-Darwin-rule; and then there's jobbing
electricians who need to cover their posteriors lest Wayne and Waynetta
stick the where-there's-blame mob onto them, I guess...


Common sense doesn't really come into it, the majority of people will wall
into a kitchen and plug the lead into any available socket, ie if the cooker
skt is empty they will use it, no matter if there is one by the back door
with the toaster in, they would rather run a lead across the room than take
out a plug of unused item.


  #35   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
"Dave Jones" writes:

"Stefek Zaba" wrote in message
...
Dave Jones wrote:
If the oven switch has a 13 amp outlet on it then it must be rcd
protected, otherwise up to u.

I can think of few downstairs sockets *less* likely to get an outdoor
appliance plugged in than the one permanently occupied by the
householder's kettle - so I don't understand why you hold with such
certainty that a cooker-control unit with integral socket 'must' be RCD
protected...


I never use those combined cooker control panel plus socket.
This is because I don't put cookers on RCDs for reasons explained
elsewhere recently, but I do RCD protect all the kitchen worktop
socket outlets (even when this isn't required by the regs).

Due to the current regulations, "all downstairs socket outlets must be rcd
protected".


This isn't the case. Only sockets which might be used to power
outdoor appliances need to be RCD protected. If you have a good
provision of sockets outdoors anyway, it's unlikely any of the
indoor ones are likely to be used for this purpose.

Actually, one place I have used a combined cooker control panel
is for the outdoor sockets. The panel is in the garage next to
the door with the switched socket handy for running tools just
outside the garage, and the large switch is used to isolate all
the other sockets which are outdoors in the front and back
gardens. I went for one with neon indicators so you can quickly
see if the RCD has tripped. The cooker control panel seemed
ideal for this task. The whole radial circuit is on a dedicated
20A/10mA RCBO with own TT earthing system.

--
Andrew Gabriel


  #36   Report Post  
Sparks
 
Posts: n/a
Default

Due to the current regulations, "all downstairs socket outlets must be
rcd
protected".


This isn't the case. Only sockets which might be used to power
outdoor appliances need to be RCD protected. If you have a good
provision of sockets outdoors anyway, it's unlikely any of the
indoor ones are likely to be used for this purpose.


If this is really the case, then surelly ALL sockets must be RCD protected
in the whole house, as at some point any of them *might* be used for an
outside appliance?
(For example, say there is a socket behind the fridge, it is not impossible
for this to be used for outdoor appliances - yes, it's highly unlikley, but
it just might happen!


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 09:59 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"