I have a new boiler (finally) and am considering doing some of the gas pipe
re-routing myself (a possible topic for another time), before I even
consider this I thought it was a great excuse to purchase an 'okay' little
flammable gas detector and add another toy to the toolbox.

I'm a paranoid type of person when it comes to things that can kill me, so
as soon as the thing arrived today I carried it over to the existing cooker
a opened a hob the minimum amount to measure the amount (over 1000ppm but
less than 10000ppm).
Next I recalibrated it and tested the existing gas piping put in some years
ago by the previous owner, one of the joins in the existing pipework manages
to just get the detector to tick over to the first level (above 100ppm but
less an 1000ppm), this made me realise, I don't actually know if this is an
allowed amount, I had (possibly stupidly) assumed that no gas would be
allowed.

To cut this simpler, what is the allowed maximum PPM of flammable gas from a
join?

Thanks for any answers.

Seri


  #2   Report Post  
Jim Ingram
 
Posts: n/a
Default Maximum allowed gas PPM from joints?


"Seri" wrote in message
.. .
I have a new boiler (finally) and am considering doing some of the

gas pipe
re-routing myself (a possible topic for another time), before I

even
consider this I thought it was a great excuse to purchase an 'okay'

little
flammable gas detector and add another toy to the toolbox.

I'm a paranoid type of person when it comes to things that can kill

me, so
as soon as the thing arrived today I carried it over to the

existing cooker
a opened a hob the minimum amount to measure the amount (over

1000ppm but
less than 10000ppm).
Next I recalibrated it and tested the existing gas piping put in

some years
ago by the previous owner, one of the joins in the existing

pipework manages
to just get the detector to tick over to the first level (above

100ppm but
less an 1000ppm), this made me realise, I don't actually know if

this is an
allowed amount, I had (possibly stupidly) assumed that no gas would

be
allowed.

To cut this simpler, what is the allowed maximum PPM of flammable

gas from a
join?

I am not a gasfiitter however I can tell you that the Lower
explosive limit of methane in air is ~5%(v/v) (the minimum
concentration of gas required to sustain flame propagation) which
equates to 50,000 ppm so not much chance of an explosion in your
case. I suspect that the regs quote an allowable amount of leakage in
terms of volume of gas. I think what gasmen actually do is to turn
off the gas supply and connect a manometer (pressure gauge) to the
gas pipe work for a period of time and calculate the amount leaked
from the pipework volume and the pressure drop.

Jim


  #3   Report Post  
Ed Sirett
 
Posts: n/a
Default Maximum allowed gas PPM from joints?

On Fri, 21 May 2004 18:36:36 +0100, Jim Ingram wrote:


"Seri" wrote in message
.. .
I have a new boiler (finally) and am considering doing some of the

gas pipe
re-routing myself (a possible topic for another time), before I

even
consider this I thought it was a great excuse to purchase an 'okay'

little
flammable gas detector and add another toy to the toolbox.

I'm a paranoid type of person when it comes to things that can kill

me, so
as soon as the thing arrived today I carried it over to the

existing cooker
a opened a hob the minimum amount to measure the amount (over

1000ppm but
less than 10000ppm).
Next I recalibrated it and tested the existing gas piping put in

some years
ago by the previous owner, one of the joins in the existing

pipework manages
to just get the detector to tick over to the first level (above

100ppm but
less an 1000ppm), this made me realise, I don't actually know if

this is an
allowed amount, I had (possibly stupidly) assumed that no gas would

be
allowed.

To cut this simpler, what is the allowed maximum PPM of flammable

gas from a
join?

I am not a gasfiitter however I can tell you that the Lower
explosive limit of methane in air is ~5%(v/v) (the minimum
concentration of gas required to sustain flame propagation) which
equates to 50,000 ppm so not much chance of an explosion in your
case. I suspect that the regs quote an allowable amount of leakage in
terms of volume of gas. I think what gasmen actually do is to turn
off the gas supply and connect a manometer (pressure gauge) to the
gas pipe work for a period of time and calculate the amount leaked
from the pipework volume and the pressure drop.


Have a look in the Gas Fitting FAQ below.
Whilst a Flammable Gas Detector is a useful (but not absolutely essential)
gadget for tracing leaks it is NOT the tool used to certify that gas pipe
work is gas tight.
The limit for Domestic Natural gas pipework is NO drop of pressure in
2minutes when measured with a U-gauge and less than 0.25mBar when measured
electronically.

The method is fully explained in the FAQ.

Even tiny leaks can have gas concentrations by the pipe that
are approaching the 'LEL'. This means that were you to
be so foolish as to trace them with a naked flame they would be big enough
to ignite and support a flame.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #4   Report Post  
Set Square
 
Posts: n/a
Default Maximum allowed gas PPM from joints?

In an earlier contribution to this discussion,
Seri wrote:

I have a new boiler (finally) and am considering doing some of the
gas pipe re-routing myself (a possible topic for another time),
before I even consider this I thought it was a great excuse to
purchase an 'okay' little flammable gas detector and add another toy
to the toolbox.

I'm a paranoid type of person when it comes to things that can kill
me, so as soon as the thing arrived today I carried it over to the
existing cooker a opened a hob the minimum amount to measure the
amount (over 1000ppm but less than 10000ppm).
Next I recalibrated it and tested the existing gas piping put in some
years ago by the previous owner, one of the joins in the existing
pipework manages to just get the detector to tick over to the first
level (above 100ppm but less an 1000ppm), this made me realise, I
don't actually know if this is an allowed amount, I had (possibly
stupidly) assumed that no gas would be allowed.

To cut this simpler, what is the allowed maximum PPM of flammable gas
from a join?

Thanks for any answers.

Seri


I don't know what the official answer is - but I wouldn't be happy with
*any* detectable leakage from a joint. Rather than using fancy kit, buy a
can of leak detection fluid (such As Screwfix 12266) and spray it onto each
joint. If you can see *any* bubbles coming out - even one per 10 seconds -
remake the joint.

--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #5   Report Post  
Seri
 
Posts: n/a
Default Maximum allowed gas PPM from joints?


"Ed Sirett" wrote in message
news | "Seri" wrote
| I have a new boiler snip I thought it was a great excuse to purchase
a snip
| flammable gas detector snip I tested the existing gas piping snip,
one of the joins in the existing
| pipework manages
| to just get the detector to tick over to the first level (above
| 100ppm but less an 1000ppm),
| What is the allowed maximum PPM of flammable gas from a join?
|
| Have a look in the Gas Fitting FAQ below.
| Whilst a Flammable Gas Detector is a useful (but not absolutely essential)
| gadget for tracing leaks it is NOT the tool used to certify that gas pipe
| work is gas tight.
| The limit for Domestic Natural gas pipework is NO drop of pressure in
| 2minutes when measured with a U-gauge and less than 0.25mBar when measured
| electronically.
|
| The method is fully explained in the FAQ.
|
| Even tiny leaks can have gas concentrations by the pipe that
| are approaching the 'LEL'. This means that were you to
| be so foolish as to trace them with a naked flame they would be big enough
| to ignite and support a flame.
|
| --
| Ed Sirett - Property maintainer and registered gas fitter.

I read through the FAQ in its entirity, and whilst the sections on testing I
can mostly adhere to, the fact that there's already a boiler and cooker
fitted to the gas piping I can't easily perform a 'pipes only test'.
Today I purchased a 12"/30mBar Manometer and tested at the gas meter test
point, I followed the instructions in the FAQ, brought the pressure slowly
to 20mBar, timed two minutes and noted the difference.
I know the FAQ says up to 4mBar drop over 2 minutes is allowed, but I wanted
to triple check.
I have 1mBar drop (1.2 if being pedantic) testing at the meter test point
over the space of 2 minutes, this is with the cooker and boiler connected to
the pipework but in an 'off' state, is this a natural and allowable drop?

Thanks again for any responses

Seri




  #6   Report Post  
Ed Sirett
 
Posts: n/a
Default Maximum allowed gas PPM from joints?

On Mon, 24 May 2004 14:31:51 +0000, Seri wrote:


"Ed Sirett" wrote in message
news | "Seri" wrote
| I have a new boiler snip I thought it was a great excuse to purchase
a snip
| flammable gas detector snip I tested the existing gas piping snip,
one of the joins in the existing
| pipework manages
| to just get the detector to tick over to the first level (above
| 100ppm but less an 1000ppm),
| What is the allowed maximum PPM of flammable gas from a join?
|
| Have a look in the Gas Fitting FAQ below.
| Whilst a Flammable Gas Detector is a useful (but not absolutely essential)
| gadget for tracing leaks it is NOT the tool used to certify that gas pipe
| work is gas tight.
| The limit for Domestic Natural gas pipework is NO drop of pressure in
| 2minutes when measured with a U-gauge and less than 0.25mBar when measured
| electronically.
|
| The method is fully explained in the FAQ.
|
| Even tiny leaks can have gas concentrations by the pipe that
| are approaching the 'LEL'. This means that were you to
| be so foolish as to trace them with a naked flame they would be big enough
| to ignite and support a flame.
|
| --
| Ed Sirett - Property maintainer and registered gas fitter.

I read through the FAQ in its entirity, and whilst the sections on testing I
can mostly adhere to, the fact that there's already a boiler and cooker
fitted to the gas piping I can't easily perform a 'pipes only test'.
Today I purchased a 12"/30mBar Manometer and tested at the gas meter test
point, I followed the instructions in the FAQ, brought the pressure slowly
to 20mBar, timed two minutes and noted the difference.
I know the FAQ says up to 4mBar drop over 2 minutes is allowed, but I wanted
to triple check.
I have 1mBar drop (1.2 if being pedantic) testing at the meter test point
over the space of 2 minutes, this is with the cooker and boiler connected to
the pipework but in an 'off' state, is this a natural and allowable drop?

Thanks again for any responses

Seri


It would be best at this point to turn the cooker and boiler off at their
respective isolators or remove the bayonet hose. The boiler will likely
have some sort of 1/4 turn cut off.
If you then get a 0 drop (you did allow a 1 min settling time before
beggining the test?) AND there is no smell of gas then that is adequate.

If you still get a non zero drop then the leak MUST be found.
It could be anywhere from the MCV, meter, govenor or pipe work.


Likely placed where it is good to start looking:
1) any place where the pipe comes out of a concrete floor.
2) anywhere the pipe goes unprotected through a wall.
3) around the meter especially if it has been changed recently.
4) New pipe work.
5) The anaconda (flexible corrugated stainless pipe) especially if it had
flux on it and/or got wet.

A pro will probably
1) test the U guage for leaks (to eliminate the wild goose chase).
2) Put a disc in the meter outlet to split the problem between the meter
and your pipes.

Appliances are allowed to leak slightly provided they don't smell.
Pipes are never allowed to leak, any.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #7   Report Post  
Seri
 
Posts: n/a
Default Maximum allowed gas PPM from joints?

"Ed Sirett" wrote in message
news | On Mon, 24 May 2004 14:31:51 +0000, Seri wrote:
|
|
| "Ed Sirett" wrote in message
| news | | "Seri" wrote
| | I have a new boiler snip I thought it was a great excuse to
purchase a
| | flammable gas detector snip I tested the existing gas piping
snip,
| one of the joins in the existing pipework manages
| | to just get the detector to tick over to the first level (above
| | 100ppm but less an 1000ppm),
| | What is the allowed maximum PPM of flammable gas from a join?
| |
| | Have a look in the Gas Fitting FAQ below.
| | The limit for Domestic Natural gas pipework is NO drop of pressure in
| | 2minutes when measured with a U-gauge and less than 0.25mBar when
measured
| | electronically.
|
| I read through the FAQ in its entirity, snip I can't easily perform a
'pipes only test'.
snip
| I know the FAQ says up to 4mBar drop over 2 minutes is allowed, but I
wanted
| to triple check.
| I have 1mBar drop (1.2 if being pedantic) testing at the meter test
point
| over the space of 2 minutes, this is with the cooker and boiler
connected to
| the pipework but in an 'off' state, is this a natural and allowable
drop?
|
| It would be best at this point to turn the cooker and boiler off at their
| respective isolators or remove the bayonet hose. The boiler will likely
| have some sort of 1/4 turn cut off.
| If you then get a 0 drop (you did allow a 1 min settling time before
| beggining the test?) AND there is no smell of gas then that is adequate.
|
| If you still get a non zero drop then the leak MUST be found.
| It could be anywhere from the MCV, meter, govenor or pipe work.
|
|
| Likely placed where it is good to start looking:
| 1) any place where the pipe comes out of a concrete floor.
| 2) anywhere the pipe goes unprotected through a wall.
| 3) around the meter especially if it has been changed recently.
| 4) New pipe work.
| 5) The anaconda (flexible corrugated stainless pipe) especially if it had
| flux on it and/or got wet.
|
| A pro will probably
| 1) test the U guage for leaks (to eliminate the wild goose chase).
| 2) Put a disc in the meter outlet to split the problem between the meter
| and your pipes.
|
| Appliances are allowed to leak slightly provided they don't smell.
| Pipes are never allowed to leak, any.

Thanks for the continued help, unfortunately the previous owner of this
property (well, his dad) installed everything himself and had 'interesting'
ideas about the way things should have been done, this has ranged from the
water plumbing to the electrics to the extension to the gas fittings, the
entire thing.

I can't locate any easy way of isolating either the hob or the central
heating boiler, the upstairs water on demand boiler has a master gas 'off'
valve which I turned off before starting any testing but the same doesn't
seem to be possible for the other two devices.

I left the gauge to settle for a minute before starting testing, but as
said, the hob and the heating boiler were off but not isolated from the gas
supply.

I also ensured that the testing screw was tested with gas leak detection
fluid and the new electronic gas detector before turning on the gas supply.

Basically, my question now is this, from what's been said so far, the gas
here needs some extensive testing.
I've been in this property with the current state of affairs for just over
two years.
All of the 15mm gas pipe will need to be replaced with 22mm pipe to
accomodate the new boiler (this would take it almost all the way back to the
meter)
The hob is fed from an entirely seperate feed from the meter.
The replacement pipework and the installation of the boiler will be
happening in about 4 weeks.

Q: Should this be okay as it is until the new boiler is installed?
Q: With no device other than the hob connected is it normal that I'll notice
any drop? (I seem to recall hobs can be a little 'lossy')

thanks again

Seri


  #8   Report Post  
Ed Sirett
 
Posts: n/a
Default Maximum allowed gas PPM from joints?

On Mon, 24 May 2004 19:22:24 +0000, Seri wrote:

"Ed Sirett" wrote in message
news | On Mon, 24 May 2004 14:31:51 +0000, Seri wrote:
|
|
| "Ed Sirett" wrote in message
| news | | "Seri" wrote
| | I have a new boiler snip I thought it was a great excuse to
purchase a
| | flammable gas detector snip I tested the existing gas piping
snip,
| one of the joins in the existing pipework manages
| | to just get the detector to tick over to the first level (above
| | 100ppm but less an 1000ppm),
| | What is the allowed maximum PPM of flammable gas from a join?
| |
| | Have a look in the Gas Fitting FAQ below.
| | The limit for Domestic Natural gas pipework is NO drop of pressure in
| | 2minutes when measured with a U-gauge and less than 0.25mBar when
measured
| | electronically.
|
| I read through the FAQ in its entirity, snip I can't easily perform a
'pipes only test'.
snip
| I know the FAQ says up to 4mBar drop over 2 minutes is allowed, but I
wanted
| to triple check.
| I have 1mBar drop (1.2 if being pedantic) testing at the meter test
point
| over the space of 2 minutes, this is with the cooker and boiler
connected to
| the pipework but in an 'off' state, is this a natural and allowable
drop?
|
| It would be best at this point to turn the cooker and boiler off at their
| respective isolators or remove the bayonet hose. The boiler will likely
| have some sort of 1/4 turn cut off.
| If you then get a 0 drop (you did allow a 1 min settling time before
| beggining the test?) AND there is no smell of gas then that is adequate.
|
| If you still get a non zero drop then the leak MUST be found.
| It could be anywhere from the MCV, meter, govenor or pipe work.
|
|
| Likely placed where it is good to start looking:
| 1) any place where the pipe comes out of a concrete floor.
| 2) anywhere the pipe goes unprotected through a wall.
| 3) around the meter especially if it has been changed recently.
| 4) New pipe work.
| 5) The anaconda (flexible corrugated stainless pipe) especially if it had
| flux on it and/or got wet.
|
| A pro will probably
| 1) test the U guage for leaks (to eliminate the wild goose chase).
| 2) Put a disc in the meter outlet to split the problem between the meter
| and your pipes.
|
| Appliances are allowed to leak slightly provided they don't smell.
| Pipes are never allowed to leak, any.

Thanks for the continued help, unfortunately the previous owner of this
property (well, his dad) installed everything himself and had 'interesting'
ideas about the way things should have been done, this has ranged from the
water plumbing to the electrics to the extension to the gas fittings, the
entire thing.

I can't locate any easy way of isolating either the hob or the central
heating boiler, the upstairs water on demand boiler has a master gas 'off'
valve which I turned off before starting any testing but the same doesn't
seem to be possible for the other two devices.

I left the gauge to settle for a minute before starting testing, but as
said, the hob and the heating boiler were off but not isolated from the gas
supply.

I also ensured that the testing screw was tested with gas leak detection
fluid and the new electronic gas detector before turning on the gas supply.

Basically, my question now is this, from what's been said so far, the gas
here needs some extensive testing.
I've been in this property with the current state of affairs for just over
two years.
All of the 15mm gas pipe will need to be replaced with 22mm pipe to
accomodate the new boiler (this would take it almost all the way back to the
meter)
The hob is fed from an entirely seperate feed from the meter.
The replacement pipework and the installation of the boiler will be
happening in about 4 weeks.

Q: Should this be okay as it is until the new boiler is installed?
Q: With no device other than the hob connected is it normal that I'll notice
any drop? (I seem to recall hobs can be a little 'lossy')


IME appliances rarely leak, leaks are usually the pipework.

Well if you were registered and you found a leaking installation you need
to do one of two things:
a) Fix it.
b) Turn it off and label it as dangerous.

Anything else is not competant gas fitting so you are invited to make you
own assessment.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Concrete expansion joints Dave UK diy 3 May 3rd 04 09:57 PM
Soldering close joints mike ring UK diy 2 August 30th 03 06:18 PM
Paving Stone Joints chris French UK diy 0 July 14th 03 08:32 AM


All times are GMT +1. The time now is 03:34 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"