I want to add heating to the cellar/basement, it measures 2.5m * 4.5m *
2.1m (L*W*H), there's a DG half glass door exiting to the garden and a
single window 400mm * 650mm...

anyone know what size rad I'll need ?

system is microbore currently running 7 rads off a combi if that makes a
difference ?

thanks
LJ


  #2   Report Post  
Andy Hall
 
Posts: n/a
Default

On Sat, 22 Jan 2005 16:11:15 -0000, "in2minds"
wrote:

I want to add heating to the cellar/basement, it measures 2.5m * 4.5m *
2.1m (L*W*H), there's a DG half glass door exiting to the garden and a
single window 400mm * 650mm...

anyone know what size rad I'll need ?


With a bit more info., a reasonable estimate could be made on the
basis of treating the cellar walls as exterior. THe situation should
be better than that so it will give you a worst case. More
information is needed, though.

- Which wall is the exterior one, and what is its construction? is it
the longer wall or the short? How thick?

- What is the construction of the interior cellar walls? How thick?

- What is the construction of ceiling, then floor of the rooms above?

- What is the temperature of the room above when the heating is
running in degrees Celsius?

- What temperature do you want in the cellar?

- Is the cellar reasonably dry?

One issue that you could have is condensation on the walls since they
will tend to be cold. It would be a good idea to insulate them with
Celotex or equivalent as that would also reduce heat requirement a
great deal.....




system is microbore currently running 7 rads off a combi if that makes a
difference ?


Difficult to say. Without knowing the size of the "rads", it is not
possible to say whether the boiler has sufficient spare capacity.
Usually with a combi it does unless it's a very small one. What make
and model?

If you can answer the first set of questions then I'll show you how to
do the calculations to get a reasonable idea.



--

..andy

To email, substitute .nospam with .gl
  #3   Report Post  
in2minds
 
Posts: n/a
Default

With a bit more info., a reasonable estimate could be made on the
basis of treating the cellar walls as exterior. THe situation should
be better than that so it will give you a worst case. More
information is needed, though.

- Which wall is the exterior one, and what is its construction? is it
the longer wall or the short? How thick?


short wall, has door, window and about 1.2m wall space, solid stone
450mm thick


- What is the construction of the interior cellar walls? How thick?


there'll be insulated stud wall errected along half of 1 long wall, the
rest of that wall is already rendered
the other long wall is rendered stone, both are about 2.5m thick (yes, 8
feet) with neighbours cellar either side (it's a terrace btw)
rear is a cavity wall of 100mm thermal block, 33mm kingspan (I had for
free) and concrete block

- What is the construction of ceiling, then floor of the rooms above?


ceiling will be insulated with rockwool (probably) and there's a tiled
chipboard floor above, joists are 6"

- What is the temperature of the room above when the heating is
running in degrees Celsius?


it varies constantly, it's the kitchen

- What temperature do you want in the cellar?


comfortable enough for children to play all year round, I think the
minimum we're allowed is 12'c

- Is the cellar reasonably dry?


yes, there's 1 damp corner but that will be behind the insulated stud
wall with a 150mm air gab between, the air gap is that big because it's
an alcove

One issue that you could have is condensation on the walls since they
will tend to be cold. It would be a good idea to insulate them with
Celotex or equivalent as that would also reduce heat requirement a
great deal.....


the cellar is relatively warn, even on the coldest days it's about 8'c,
unless you leave the door/window open that is



system is microbore currently running 7 rads off a combi if that makes
a
difference ?


Difficult to say. Without knowing the size of the "rads", it is not
possible to say whether the boiler has sufficient spare capacity.
Usually with a combi it does unless it's a very small one. What make
and model?


Worcester 28i
there are 2 rads 1500mm the rest are around 800mm to 1000mm and the
bathroom has a small towel rad

If you can answer the first set of questions then I'll show you how to
do the calculations to get a reasonable idea.


cheers
LJ


  #4   Report Post  
Andy Hall
 
Posts: n/a
Default

On Sat, 22 Jan 2005 19:25:40 -0000, "in2minds"
wrote:

With a bit more info., a reasonable estimate could be made on the
basis of treating the cellar walls as exterior. THe situation should
be better than that so it will give you a worst case. More
information is needed, though.

- Which wall is the exterior one, and what is its construction? is it
the longer wall or the short? How thick?


short wall, has door, window and about 1.2m wall space, solid stone
450mm thick


Right. This one is going to be difficult to calculate with much
accuracy, so I would tend to work on worst case.


Well the principle of calculating heat loss through surfaces is to use
the formula:

Heat loss (Watts) = U x T x A

where

U is the U value of the material

T is the temperature difference through the material in degrees C

A is the area in square metres


The principle is that you calculate the heat loss through each
component and add them up.

Strictly, where several types of material are involved in a component,
the U values of each should be taken and an overall U value for the
whole thing calculated. However, you may not have all the values,
and sometimes one of them dominates anyway - e.g. a piece of
insulation - and you can take its value and ignore the rest because
they make little difference to the total.

As you don't know some of the numbers, certain further assumptions
will be needed.

- You don't know the temperature of the rooms above. Let's be
conservative and say that they are chilly and at 10 degrees because
the heating is off upstairs.

- 12 degrees would be pretty nippy for the cellar for the kids unless
they are running around. Minimum workplace temperature is 16 degrees
AIUI, so for reasonable comfort, I'll use 18 degrees for the cellar.

You can change these numbers as you feel appropriate.

The norm is to work on the basis of an outside temperature of -3
degrees.

Window
=======

Area is 0.4 x 0.65
Temp diff is 21 degrees
U value from my table is 2.8

Heat loss = 15W.

Door
====

You didn't give the size, but assume it's 2m x 0.7m divided 50/50

Glass part

0.7 x 21 x 2.8 = 41W

Other part (wood)

0.7 x 21 x 3 = 44W


Wall (stone)
============

U value of 450mm stone is 2.2

Area is 2.5 x 2.1 = 5.25 sqm
less window and door areas gives net of 3.9 sqm.

Heat loss = 3.9 x 21 x 2.2 = 180W


Total for outside wall = 280W








- What is the construction of the interior cellar walls? How thick?


there'll be insulated stud wall errected along half of 1 long wall, the
rest of that wall is already rendered


It would be better to insulate the lot, but let's assume you insulate
half with 50mm Celotex. (U value = 0.3)

The thickest stone wall for which I have a U value is 610mm where U is
1.7. It's not linear with thickness, although thicker walls would
have less heat loss and lower values, so I will use 1.7 as being the
worst case number.

Where the wall has Celotex, the effective U value with this thickness
wall, would be 1/( 1/0.3 + 1/1.7) which is 0.25 - not a lot less
than 0.3. Therefore for this approximation, one can take the
insulation only and ignore the wall.

So for one half we have:


2.25 x 2.1 x 1.7 x 21 = 169W

for the other

2.25 x 2.1 x 0.3 x 21 = 30W

For the whole wall 200W.

Notice the difference the insulation makes.....





the other long wall is rendered stone, both are about 2.5m thick (yes, 8
feet) with neighbours cellar either side (it's a terrace btw)



On the same principle this would be

4.5 x 2.1 x 1.7 x 21 = 340W

This all assumes that the neighbour's cellar is at outside
temperature, which it may not be, but again worst case.




rear is a cavity wall of 100mm thermal block, 33mm kingspan (I had for
free) and concrete block


U value for this is 0.4 for the block and 33mm Celotex are both about
0.4


Heat loss is 2.1 x 2.5 x 0.4 x 21 = 44W




- What is the construction of ceiling, then floor of the rooms above?


ceiling will be insulated with rockwool (probably) and there's a tiled
chipboard floor above, joists are 6"


OK, I'll use the number for 50mm Celotex again, but you can substitute
if you like.

Earlier, I used 10 degrees for the room above and 18 for the cellar as
an example. This gives a temperature drop of 8 degrees.

Heat loss would be

4.5 x 2.5 x 8 * 0.3 = 27W.

For the floor of the cellar, you already mentioned insulation.

For a ground floor solid floor, there are U value corrections to
account for the effect of the edges where heat loss is higher.

THat won't apply here in the same way, but again, to get a worst case,
use 21 degrees as the drop and 0.3 for the U value of the 50mm
Celotex.

This gives 4.5 x 2.5 x 21 x 0.3 = 71W.



If you add this lot up, you get to total surface losses of 962W.


YOu now have to account for heat loss through air changes.

It's difficult to know what these will be, but 1.5 per hour is the
conventional figure for a habitable room that's not a bathroom etc.

The formula for heat loss is similar, but there is a volumetric
constant of 0.33 used for the calculation.

Formula is volume x temperature difference x ventilation rate x 0.33

This gives us 23.6 x 21 x 1.5 x 0.33 = 246W.


The grand total, with all of these assumptions is 1208W, so something
like 1500W would be reasonable, in all likelihood.


There are some dynamic effects as well. If you leave stone walls,
they will have the additional effect of delaying the rate at which the
room heats and cools. If you insulate everything, then that will
largely not happen.

Strictly, you should also calculate the heat output of the existing
radiators. This depends on size as well as number of panels and fins.
You can get the numbers from manufacturer data sheets.
Don't forget the correction factor for radiator data sheets. When the
boiler is run at 82 degrees, the numbers in the main tables of
radiator data sheets should be multiplied by 0.9 to get the real
output since the test temperature is higher. So if you measure
exsting radiators you need to multiply by 0.9 for what the boiler
needs to supply.

I would think that the boiler is plenty capable, but it would be as
well to do the sums.


For the new radiator(s) for the cellar, you know the heat output
required (1500W). For this, nominal radiator capacity of 1670W, say
1700W would be appropriate.

These should be comfortable minimum figures. If you want to heat the
room more quickly, you can oversize the radiator and control it with a
TRV or zone thermostat.

Having done all of this, because of the uncertainty of what the U
values really will be (although insulating makes that more
predictable), I would do a sanity check.

The first thing I'd do is to plug the above formulae and numbers into
a spreadsheet so that you can easily play around with the U values
and temperatures depending on circumstances.

Then use something like a 3KW fan heater with known settings of (e.g.)
1,2 and 3kW. Run it and measure the inside temperature when stable
and the outside temperature. Plug those temperatures into the
spreadsheet and see how reasonable the results are.







- What is the temperature of the room above when the heating is
running in degrees Celsius?


it varies constantly, it's the kitchen

- What temperature do you want in the cellar?


comfortable enough for children to play all year round, I think the
minimum we're allowed is 12'c

- Is the cellar reasonably dry?


yes, there's 1 damp corner but that will be behind the insulated stud
wall with a 150mm air gab between, the air gap is that big because it's
an alcove


OK. It would be an idea to try to do something about that, but I am
not sure what would be practicable. Perhaps some waterproof sealer?
At any rate, I would use pressure treated timber throughout and put
DPC strip where it contacts masonry.



One issue that you could have is condensation on the walls since they
will tend to be cold. It would be a good idea to insulate them with
Celotex or equivalent as that would also reduce heat requirement a
great deal.....


the cellar is relatively warn, even on the coldest days it's about 8'c,
unless you leave the door/window open that is



system is microbore currently running 7 rads off a combi if that makes
a
difference ?


Difficult to say. Without knowing the size of the "rads", it is not
possible to say whether the boiler has sufficient spare capacity.
Usually with a combi it does unless it's a very small one. What make
and model?


Worcester 28i
there are 2 rads 1500mm the rest are around 800mm to 1000mm and the
bathroom has a small towel rad

If you can answer the first set of questions then I'll show you how to
do the calculations to get a reasonable idea.


cheers
LJ



--

..andy

To email, substitute .nospam with .gl
  #5   Report Post  
in2minds
 
Posts: n/a
Default

For the new radiator(s) for the cellar, you know the heat output
required (1500W). For this, nominal radiator capacity of 1670W, say
1700W would be appropriate.


thanks Andy

I'll try an electric heater first (as you suggested) see what results I
get.

do you know if there're any useful sites with details on the running
cost of an oil filled (or other) electric heater ?

LJ




  #6   Report Post  
Andy Hall
 
Posts: n/a
Default

On Sun, 23 Jan 2005 10:20:41 -0000, "in2minds"
wrote:

For the new radiator(s) for the cellar, you know the heat output
required (1500W). For this, nominal radiator capacity of 1670W, say
1700W would be appropriate.


thanks Andy

I'll try an electric heater first (as you suggested) see what results I
get.

do you know if there're any useful sites with details on the running
cost of an oil filled (or other) electric heater ?

LJ


Not really, but it should be reasonably predictable.

What you could do is get a plug in wattage meter and measure it
directly. These are quite cheap from places like Maplin.



--

..andy

To email, substitute .nospam with .gl
  #7   Report Post  
Senior Member
 
Posts: 174
Default

Quote:
Originally Posted by in2minds
For the new radiator(s) for the cellar, you know the heat output
required (1500W). For this, nominal radiator capacity of 1670W, say
1700W would be appropriate.


thanks Andy

I'll try an electric heater first (as you suggested) see what results I
get.

do you know if there're any useful sites with details on the running
cost of an oil filled (or other) electric heater ?

LJ

No, but if you have gas heating an electric heater is a no brainer. Not only is it the most expensive fuel it is also the dirtiest, that is most Co2 emissions of all domestic heating use in the UK. When our Tony was signing us gas fitters up for condensing techknowlodgy he should have taken a look at the electricity generating plants if he had any real interest in Co2 emissions.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 12:25 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"