W November 17th 04 02:53 PM

Boiler sizing from heatloss calculations
 
Hi,

I've done the heatloss calculations on my house and came out with a
figure of 8.4kW. What factor would I need to multiply this figure
with to get the boiler size? I am assuming that I will need to allow
7kW for the DHW.

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).

FYI: I plan to get a heatbank like the McDonald Thermflow.

Cheers, W


Christian McArdle November 17th 04 03:04 PM

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).


Modern condensing boilers are usually sized at 24kW or above, which will be
enough for your needs.

Christian.



W November 17th 04 04:37 PM

On Wed, 17 Nov 2004 15:04:33 -0000, "Christian McArdle"
wrote:

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).


Modern condensing boilers are usually sized at 24kW or above, which will be
enough for your needs.


The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?

Thanks, W


MikeS November 17th 04 04:46 PM


"Christian McArdle" wrote in message
. net...
Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).


Modern condensing boilers are usually sized at 24kW or above, which will
be
enough for your needs.

Christian.

Wish there where self modulating biolers when I installed my system 25
years ago. I note some boilers have the ability to self modulate via built
in electronics.

MikeS



Christian McArdle November 17th 04 04:49 PM

The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


No. It is a marketing strategy of theirs. 2 years ago, they only did a 24kW
version (which could be "reprogrammed" to 28kW).

However, the "heating" versions should normally be avoided, although they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system components
internally (and sometimes a pump).

Christian.



Andrew Gabriel November 17th 04 05:04 PM

In article ,
W writes:
On Wed, 17 Nov 2004 15:04:33 -0000, "Christian McArdle"
wrote:

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).


Modern condensing boilers are usually sized at 24kW or above, which will be
enough for your needs.


The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


I'm not familiar with this boiler, but presumably the lower modulation
limit also increases? It's going to end up cycling on and off if you
are routinely needing less heat from it than it's lowest level. (If
it's like the Keston, there's quite a bit of hysteresis before the
boiler will fire up again when this happens.) If you calculated 8.4kW
at -3C outdoors, then most of the time your heating is on, you won't
need anything like that amount of power.

If your existing gas pipe run was marginal on pressure drop, it might
be that you could get away with it on one power rating, but not the
next one up without replacing the gas pipework (maybe only some of it).

--
Andrew Gabriel

IMM November 17th 04 05:09 PM


"W" wrote in message
...
Hi,

I've done the heatloss calculations on my house and came out with a
figure of 8.4kW. What factor would I need to multiply this figure
with to get the boiler size? I am assuming that I will need to allow
7kW for the DHW.


Most boilers modulate somewhere around 5kW to around 25kW. Glow worm have a
5 to 18kW and 5 to 28kW system boiler. You may not see much difference in
price.

Is there any disadvantages in oversizing
a modern (modulating) condensing boiler
(ignoring the slight difference in purchase costs).


FYI: I plan to get a heatbank like the McDonald Thermflow.


I assume the integrated one withy the heating circuit taken from the store.
Make sure the thermal store has two stats to prevent boiler cycling. The
bigger the boiler the better with a thermal store

http://www.uselessenergy.org.uk/boil...s.asp#wallhung

Glow worm 30HXi "heating" boiler for £438.50 + VAT.

This is a basic. modulating heating boiler and you, or the thermal store
maker, supplies the pump. It will re-heat the store pronto. The biz.

The Worcester Bosch Greenstar 28HE is a similar boiler.

The modulation when using a thermal store doesn't matter that much as the
store controls the boiler. Set the store to 75C.

Try the Range, which is a heat bank with a plate heat exchanger. Better.
http://rangecylinders.co.uk/products/flowmax/index.html

Look at the picture of the Range. They will provide all the pumps, and a
second anti-cycle stat. All you do is connect up the boiler with two pipes
and a gas supply. Have a simple single channel time clock for the DHW, and
Honeywell CM67 to control and turn on the heating side.

Sorted.



IMM November 17th 04 05:28 PM


"Andrew Gabriel" wrote in message
...
In article ,
W writes:
On Wed, 17 Nov 2004 15:04:33 -0000, "Christian McArdle"
wrote:

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).

Modern condensing boilers are usually sized at 24kW or above, which will

be
enough for your needs.


The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


I'm not familiar with this boiler, but presumably the lower modulation
limit also increases? It's going to end up cycling on and off if you
are routinely needing less heat from it than it's lowest level. (If
it's like the Keston, there's quite a bit of hysteresis before the
boiler will fire up again when this happens.) If you calculated 8.4kW
at -3C outdoors, then most of the time your heating is on, you won't
need anything like that amount of power.

If your existing gas pipe run was marginal on pressure drop, it might
be that you could get away with it on one power rating, but not the
next one up without replacing the gas pipework (maybe only some of it).

--
Andrew Gabriel


He is going thermal store so the lower level of modulation is not an issue
at all.



IMM November 17th 04 05:30 PM


"W" wrote in message
...
On Wed, 17 Nov 2004 15:04:33 -0000, "Christian McArdle"
wrote:

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).


Modern condensing boilers are usually sized at 24kW or above, which will

be
enough for your needs.


The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?

Thanks, W


This is all irrelevant as you are going thermal store . Get the biggest
boiler to your budget as you can. Then a super fast re-heat.




W November 17th 04 10:46 PM

On Wed, 17 Nov 2004 16:49:55 -0000, "Christian McArdle"
wrote:

The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


No. It is a marketing strategy of theirs. 2 years ago, they only did a 24kW
version (which could be "reprogrammed" to 28kW).

However, the "heating" versions should normally be avoided, although they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system components
internally (and sometimes a pump).


I am interested to know why the heating versions should be avoided. I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel anywhere.

Cheers, W


W November 17th 04 10:50 PM

On 17 Nov 2004 17:04:57 GMT, (Andrew
Gabriel) wrote:

In article ,
W writes:
On Wed, 17 Nov 2004 15:04:33 -0000, "Christian McArdle"
wrote:

Is there any disadvantages in oversizing a modern (modulating)
condensing boiler (ignoring the slight difference in purchase costs).

Modern condensing boilers are usually sized at 24kW or above, which will be
enough for your needs.


The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


I'm not familiar with this boiler, but presumably the lower modulation
limit also increases? It's going to end up cycling on and off if you
are routinely needing less heat from it than it's lowest level. (If
it's like the Keston, there's quite a bit of hysteresis before the
boiler will fire up again when this happens.) If you calculated 8.4kW
at -3C outdoors, then most of the time your heating is on, you won't
need anything like that amount of power.


According to the specs I have the lower modulation limit is the same
for all these boilers.

BTW: I did my calculations at -1C outdoors.

If your existing gas pipe run was marginal on pressure drop, it might
be that you could get away with it on one power rating, but not the
next one up without replacing the gas pipework (maybe only some of it).


An 18kW boiler would be about the same power as the one I have now so
I don't think they'll be a problem with the supply.

W.


IMM November 17th 04 10:52 PM


"W" wrote in message
...
On Wed, 17 Nov 2004 17:09:26 -0000, "IMM" wrote:


"W" wrote in message
.. .
Hi,

I've done the heatloss calculations on my house and came out with a
figure of 8.4kW. What factor would I need to multiply this figure
with to get the boiler size? I am assuming that I will need to allow
7kW for the DHW.


Most boilers modulate somewhere around 5kW to around 25kW. Glow worm

have a
5 to 18kW and 5 to 28kW system boiler. You may not see much difference

in
price.


I was tending away from a system boiler because of the additional cost
& complexity (which I don't think is necessary in my situation).

Is there any disadvantages in oversizing
a modern (modulating) condensing boiler
(ignoring the slight difference in purchase costs).


FYI: I plan to get a heatbank like the McDonald Thermflow.


I assume the integrated one withy the heating circuit taken from the

store.
Make sure the thermal store has two stats to prevent boiler cycling. The
bigger the boiler the better with a thermal store

http://www.uselessenergy.org.uk/boil...s.asp#wallhung

Glow worm 30HXi "heating" boiler for £438.50 + VAT.


Thanks. I'll look into this one.

This is a basic. modulating heating boiler and you, or the thermal store
maker, supplies the pump. It will re-heat the store pronto. The biz.

The Worcester Bosch Greenstar 28HE is a similar boiler.


... and this one.

The modulation when using a thermal store doesn't matter that much as the
store controls the boiler. Set the store to 75C.

Try the Range, which is a heat bank with a plate heat exchanger. Better.
http://rangecylinders.co.uk/products/flowmax/index.html

Look at the picture of the Range. They will provide all the pumps, and a
second anti-cycle stat. All you do is connect up the boiler with two

pipes
and a gas supply. Have a simple single channel time clock for the DHW,

and
Honeywell CM67 to control and turn on the heating side.


I've considered a heat bank but I'm not (yet) convinced that they are
worth the extra money. Considering that they are about double the
price (AFAIK) of a thermal store then they would have to be a _lot_
better to convince me (unless you know different).

Cheers, W


What prices have you been quoted?




IMM November 17th 04 10:55 PM


"W" wrote in message
...
On Wed, 17 Nov 2004 16:49:55 -0000, "Christian McArdle"
wrote:

The Ideal Icos HE heating boilers come in 12, 15, 18, and 24kW
versions. This is the boiler recommended to me by a tank
manufacturer. The 24kW version is only about £35 more than the 18kW
one. Is there any reason to go for the 18kW version?


No. It is a marketing strategy of theirs. 2 years ago, they only did a

24kW
version (which could be "reprogrammed" to 28kW).

However, the "heating" versions should normally be avoided, although they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system

components
internally (and sometimes a pump).


I am interested to know why the heating versions should be avoided. I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel anywhere.


In your case the basic heating boiler heating they store directly is the
one. The system boiler is fine if you want a sealed system as all is inside
the case.

Don't forget to put enough inhibitor in the thermals store.



W November 17th 04 10:56 PM

On Wed, 17 Nov 2004 17:09:26 -0000, "IMM" wrote:


"W" wrote in message
.. .
Hi,

I've done the heatloss calculations on my house and came out with a
figure of 8.4kW. What factor would I need to multiply this figure
with to get the boiler size? I am assuming that I will need to allow
7kW for the DHW.


Most boilers modulate somewhere around 5kW to around 25kW. Glow worm have a
5 to 18kW and 5 to 28kW system boiler. You may not see much difference in
price.


I was tending away from a system boiler because of the additional cost
& complexity (which I don't think is necessary in my situation).

Is there any disadvantages in oversizing
a modern (modulating) condensing boiler
(ignoring the slight difference in purchase costs).


FYI: I plan to get a heatbank like the McDonald Thermflow.


I assume the integrated one withy the heating circuit taken from the store.
Make sure the thermal store has two stats to prevent boiler cycling. The
bigger the boiler the better with a thermal store

http://www.uselessenergy.org.uk/boil...s.asp#wallhung

Glow worm 30HXi "heating" boiler for £438.50 + VAT.


Thanks. I'll look into this one.

This is a basic. modulating heating boiler and you, or the thermal store
maker, supplies the pump. It will re-heat the store pronto. The biz.

The Worcester Bosch Greenstar 28HE is a similar boiler.


.... and this one.

The modulation when using a thermal store doesn't matter that much as the
store controls the boiler. Set the store to 75C.

Try the Range, which is a heat bank with a plate heat exchanger. Better.
http://rangecylinders.co.uk/products/flowmax/index.html

Look at the picture of the Range. They will provide all the pumps, and a
second anti-cycle stat. All you do is connect up the boiler with two pipes
and a gas supply. Have a simple single channel time clock for the DHW, and
Honeywell CM67 to control and turn on the heating side.


I've considered a heat bank but I'm not (yet) convinced that they are
worth the extra money. Considering that they are about double the
price (AFAIK) of a thermal store then they would have to be a _lot_
better to convince me (unless you know different).

Cheers, W


W November 18th 04 09:12 AM

On Wed, 17 Nov 2004 22:52:05 -0000, "IMM" wrote:

I've considered a heat bank but I'm not (yet) convinced that they are
worth the extra money. Considering that they are about double the
price (AFAIK) of a thermal store then they would have to be a _lot_
better to convince me (unless you know different).

Cheers, W


What prices have you been quoted?


I've been quoted about £700 for a large 250L thermal store. I haven't
had a quote for a heat bank but I thought they were around the £1400
mark for a similar size. Maybe I'm wrong though :-)

W


Christian McArdle November 18th 04 09:33 AM

However, the "heating" versions should normally be avoided, although they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system

components
internally (and sometimes a pump).


I am interested to know why the heating versions should be avoided. I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel anywhere.


Use to reheat a direct heat bank is one of the "have their uses" noted
above.

Christian.




IMM November 18th 04 10:14 AM


"Christian McArdle" wrote in message
. net...
However, the "heating" versions should normally be avoided, although

they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system

components
internally (and sometimes a pump).


I am interested to know why the heating versions should be avoided. I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel anywhere.


Use to reheat a direct heat bank is one of the "have their uses" noted
above.


I Installed one of these to an existing open vented system. The reason was
to keep the old cast iron boiler in the garage as a back up. Throw a switch
and the old boiler comes in and the new one is out. Full backup of heating
and DHW.





Andy Hall November 18th 04 12:01 PM

On Thu, 18 Nov 2004 10:14:54 -0000, "IMM" wrote:


"Christian McArdle" wrote in message
.net...
However, the "heating" versions should normally be avoided, although

they
have their uses. It is usually best to upgrade to a sealed pressurised
system and use the "system" version, which has the sealed system

components
internally (and sometimes a pump).

I am interested to know why the heating versions should be avoided. I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel anywhere.


Use to reheat a direct heat bank is one of the "have their uses" noted
above.


I Installed one of these to an existing open vented system. The reason was
to keep the old cast iron boiler in the garage as a back up. Throw a switch
and the old boiler comes in and the new one is out. Full backup of heating
and DHW.

Does CORGI know about all this fitting work that you're doing?



--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 12:04 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 10:14:54 -0000, "IMM" wrote:


"Christian McArdle" wrote in message
.net...
However, the "heating" versions should normally be avoided, although

they
have their uses. It is usually best to upgrade to a sealed

pressurised
system and use the "system" version, which has the sealed system
components
internally (and sometimes a pump).

I am interested to know why the heating versions should be avoided.

I
would have thought they would be more efficient in my situation since
the boiler heats the heatbank directly without the need for an
additional heat exchanger in the tank or an expansion vessel

anywhere.

Use to reheat a direct heat bank is one of the "have their uses" noted
above.


I Installed one of these to an existing open vented system. The reason

was
to keep the old cast iron boiler in the garage as a back up. Throw a

switch
and the old boiler comes in and the new one is out. Full backup of

heating
and DHW.

Does CORGI know about all this fitting work that you're doing?


Not their business.




Andy Hall November 18th 04 12:34 PM

On Thu, 18 Nov 2004 12:04:40 -0000, "IMM" wrote:


e.

I Installed one of these to an existing open vented system. The reason

was
to keep the old cast iron boiler in the garage as a back up. Throw a

switch
and the old boiler comes in and the new one is out. Full backup of

heating
and DHW.

Does CORGI know about all this fitting work that you're doing?


Not their business.


Ah so you do have a CORGI card for your professional fitting? .. or is
it that you are not professional or breaking the law?





--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 12:47 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 12:04:40 -0000, "IMM" wrote:


e.

I Installed one of these to an existing open vented system. The reason

was
to keep the old cast iron boiler in the garage as a back up. Throw a

switch
and the old boiler comes in and the new one is out. Full backup of

heating
and DHW.

Does CORGI know about all this fitting work that you're doing?


Not their business.


Ah so you do have a CORGI card for your professional fitting?


Everything I do is ultra professional.

.. or is
it that you are not professional
or breaking the law?


The most professional of professional. Not breaking the law.




Andy Hall November 18th 04 01:03 PM

On Thu, 18 Nov 2004 12:47:57 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 12:04:40 -0000, "IMM" wrote:


e.

I Installed one of these to an existing open vented system. The reason
was
to keep the old cast iron boiler in the garage as a back up. Throw a
switch
and the old boiler comes in and the new one is out. Full backup of
heating
and DHW.

Does CORGI know about all this fitting work that you're doing?

Not their business.


Ah so you do have a CORGI card for your professional fitting?


Everything I do is ultra professional.

.. or is
it that you are not professional
or breaking the law?


The most professional of professional. Not breaking the law.

By definition you are......




--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 01:50 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 12:47:57 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 12:04:40 -0000, "IMM" wrote:


e.

I Installed one of these to an existing open vented system. The

reason
was
to keep the old cast iron boiler in the garage as a back up. Throw

a
switch
and the old boiler comes in and the new one is out. Full backup of
heating
and DHW.

Does CORGI know about all this fitting work that you're doing?

Not their business.


Ah so you do have a CORGI card for your professional fitting?


Everything I do is ultra professional.

.. or is
it that you are not professional
or breaking the law?


The most professional of professional. Not breaking the law.

By definition you are......


I said "not breaking the law". And not a bit of plastic pipe in sight.
Fabulous!




Andy Hall November 18th 04 02:59 PM

On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message



I said "not breaking the law". And not a bit of plastic pipe in sight.
Fabulous!


Thank goodness for that. At least it's one cock up possibility less
for you.....




--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 03:02 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message



I said "not breaking the law". And not a bit of plastic pipe in sight.
Fabulous!


Thank goodness for that. At least it's one cock up possibility less
for you.....


Exactly. The likes of Speedfit fittings can't fail.



Andy Hall November 18th 04 04:11 PM

On Thu, 18 Nov 2004 15:02:14 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message



I said "not breaking the law". And not a bit of plastic pipe in sight.
Fabulous!


Thank goodness for that. At least it's one cock up possibility less
for you.....


Exactly. The likes of Speedfit fittings can't fail.

They don't anyway if you follow the instructions........

--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 04:13 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 15:02:14 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message


I said "not breaking the law". And not a bit of plastic pipe in

sight.
Fabulous!

Thank goodness for that. At least it's one cock up possibility less
for you.....


Exactly. The likes of Speedfit fittings can't fail.

They don't anyway if you follow the instructions........


Being inexperienced at pies and life in gerneral , I can a assure my dear
chap they fail on a regular basis. Sad but true.

Now rip all that suff out you put in your house ASAP.




Christian McArdle November 18th 04 04:21 PM

They don't anyway if you follow the instructions........

Now rip all that suff out you put in your house ASAP.


Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.



Andy Hall November 18th 04 04:23 PM

On Thu, 18 Nov 2004 16:13:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 15:02:14 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message


I said "not breaking the law". And not a bit of plastic pipe in

sight.
Fabulous!

Thank goodness for that. At least it's one cock up possibility less
for you.....

Exactly. The likes of Speedfit fittings can't fail.

They don't anyway if you follow the instructions........


Being inexperienced at pies and life in gerneral ,
I can a assure my dear
chap they fail on a regular basis.


We know about your inexperience, but this sentence is incoherent even
for you. Have you been on the sauce already?





--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 04:27 PM


"Christian McArdle" wrote in message
t...
They don't anyway if you follow the instructions........


Now rip all that suff out you put in your house ASAP.


Why would he need to do that? You didn't use a hacksaw did you Andy?


Probably an axe. Or was it his £1000 Makita chop saw.



IMM November 18th 04 04:28 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 16:13:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 15:02:14 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 13:50:48 -0000, "IMM" wrote:


"Andy Hall" wrote in message


I said "not breaking the law". And not a bit of plastic pipe in

sight.
Fabulous!

Thank goodness for that. At least it's one cock up possibility less
for you.....

Exactly. The likes of Speedfit fittings can't fail.

They don't anyway if you follow the instructions........


Being inexperienced at pipes and life in gerneral ,
I can assure you my dear
chap they fail on a regular basis.


We know about your inexperience, but this sentence is incoherent even
for you. Have you been on the sauce already?


Uh!



Christian McArdle November 18th 04 04:46 PM

Why would he need to do that? You didn't use a hacksaw did you Andy?

Probably an axe. Or was it his £1000 Makita chop saw.


Well, either would probably produce a better cut with less swarf than a
hacksaw.

Christian.



Andy Hall November 18th 04 05:22 PM

On Thu, 18 Nov 2004 16:21:39 -0000, "Christian McArdle"
wrote:

They don't anyway if you follow the instructions........


Now rip all that suff out you put in your house ASAP.


Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.


Definitely not. I always read the instructions and am not an armature
in a tutu.



--

..andy

To email, substitute .nospam with .gl

Owain November 18th 04 06:04 PM

"Andy Hall" wrote
| "IMM" wrote:
| I said "not breaking the law". And not a bit of plastic pipe
| in sight. Fabulous!
| Thank goodness for that. At least it's one cock up possibility
| less for you.....

Be fair, IMM needs all the cock up possibilities going if he's to have any
form of sex life

Owain



IMM November 18th 04 09:37 PM


"Christian McArdle" wrote in message
. net...
Why would he need to do that? You didn't use a hacksaw did you Andy?


Probably an axe. Or was it his £1000 Makita chop saw.


Well, either would probably produce a better cut with less swarf than a
hacksaw.


The axe?



IMM November 18th 04 09:38 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 16:21:39 -0000, "Christian McArdle"
wrote:

They don't anyway if you follow the instructions........

Now rip all that suff out you put in your house ASAP.


Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.


Definitely not. I always read the instructions


You started from the wrong page.



IMM November 18th 04 09:39 PM


"Owain" wrote in message
...
"Andy Hall" wrote
| "IMM" wrote:
| I said "not breaking the law". And not a bit of plastic pipe
| in sight. Fabulous!
| Thank goodness for that. At least it's one cock up possibility
| less for you.....

Be fair, IMM needs all the cock up possibilities going if he's to have any
form of sex life


Wow!



Andy Hall November 18th 04 09:46 PM

On Thu, 18 Nov 2004 21:38:44 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 16:21:39 -0000, "Christian McArdle"
wrote:

They don't anyway if you follow the instructions........

Now rip all that suff out you put in your house ASAP.

Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.


Definitely not. I always read the instructions


You started from the wrong page.


How would you know? You can't write coherently, probably can read,
but not to understand it and otherwise cut and paste.



--

..andy

To email, substitute .nospam with .gl

IMM November 18th 04 10:05 PM


"Andy Hall" wrote in message
...
On Thu, 18 Nov 2004 21:38:44 -0000, "IMM" wrote:


"Andy Hall" wrote in message
.. .
On Thu, 18 Nov 2004 16:21:39 -0000, "Christian McArdle"
wrote:

They don't anyway if you follow the instructions........

Now rip all that suff out you put in your house ASAP.

Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.

Definitely not. I always read the instructions


You started from the wrong page.


How would you know?


It is obvious.




The Natural Philosopher November 19th 04 01:40 PM

IMM wrote:

"Andy Hall" wrote in message
...

On Thu, 18 Nov 2004 16:21:39 -0000, "Christian McArdle"
wrote:


They don't anyway if you follow the instructions........

Now rip all that suff out you put in your house ASAP.

Why would he need to do that? You didn't use a hacksaw did you Andy?

Christian.


Definitely not. I always read the instructions



You started from the wrong page.


Better than starting in the wrong book.


All times are GMT +1. The time now is 08:10 AM.