External earth loop impedance
I did a Ze test on my TNS installation last night and the reading was
..19 ohms is this a good or bad reading ? I think the max is .8 but my regs book is with a friend at the moment. Jon. |
External earth loop impedance
If the cct you tested was circuit breaker protected by a 32 A mcb the value in
OSG for the Zs value is 1.2 so if you measure your R1 + R2 values and add to your .19 I am sure you will be in spec |