The immersion heater in my house is of a type I haven't seen anywhere
else. There are no elements in the main tank. Instead the element is
mounted inside a small vertical cylinder plumbed into the side if the
tank but seperate from the main tank. Its mounted vertically with the
element upside down and fitted from the bottom (which makes it hard to
see the stat setting without a mirror). The secondary cylinder is 3
inches diameter and about 15 inches long.

A while back I noticed that running the immersion even for a short
time produced dangerously hot water. Ther was also a bubbling noise
from the cylinder when the immersion was on.

So I replaced the stat (7") set it for 60 and thought that would be
that. Same problem.

Any ideas....


Peter Hawkins
  #2   Report Post  
Owain
 
Posts: n/a
Default

"Peter Hawkins" wrote
| The immersion heater in my house is of a type I haven't seen
| anywhere else. There are no elements in the main tank. Instead
| the element is mounted inside a small vertical cylinder plumbed
| into the side if the tank but seperate from the main tank.
| Its mounted vertically with the element upside down and fitted
| from the bottom (which makes it hard to see the stat setting
| without a mirror). The secondary cylinder is 3 inches diameter
| and about 15 inches long.

Yes. It's called an external circulator and was often used to convert an
existing cylinder with an indirect heating coil that didn't have an
immersion heater boss. Because the position of the coil wasn't known, using
an external circulator avoided dealing with the obstruction inside the
cylinder.

It is possible the bottom connection to the cylinder is blocked which
prevents water circulating. A small quantity of extremely hot water is being
created at the top of the circulator and passing into the cylinder, but the
cooler water from the bottom of the cyclinder is not passing into the
circulator, allowing the heat to be dispersed through the whole of the
cylinder. This would also mean the thermistat at the bottom never has hot
water flowing over it. Bottom mounting of the heater/stat is normal.

Probably installed 1940s or 50s.

Owain


  #3   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Fri, 24 Sep 2004 19:03:07 +0100, Peter Hawkins wrote:

The immersion heater in my house is of a type I haven't seen anywhere
else. There are no elements in the main tank. Instead the element is
mounted inside a small vertical cylinder plumbed into the side if the
tank but seperate from the main tank. Its mounted vertically with the
element upside down and fitted from the bottom (which makes it hard to
see the stat setting without a mirror). The secondary cylinder is 3
inches diameter and about 15 inches long.

A while back I noticed that running the immersion even for a short
time produced dangerously hot water. Ther was also a bubbling noise
from the cylinder when the immersion was on.

So I replaced the stat (7") set it for 60 and thought that would be
that. Same problem.

Any ideas....


I've only seen one of these once before. IIRC the secondary cylinder was
horizontal?

I believe that the intention is that hot HW becomes available more
quickly, and/or the whole cylinder is eventually heated through.
So it combines the best features of the top and bottom positioned
conventional immersion heaters.
It is normal for some noises to occur even with brand new immersion
heaters.
The replacement for this type would be an 11"(?) unit which contains a 7"
thermostat (cf 27" and 11")
It might be that all you need to do is to replace the thermostat (will
this mean you have to cut a hole in the floor ?!?).



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #4   Report Post  
Peter Hawkins
 
Posts: n/a
Default

I've already replaced the themostat. I'm sort of at a loss now, hence
the posting! Could the element be at fault, causing the themostat to
stay on?

Peter


On Fri, 24 Sep 2004 20:19:10 +0100, "Ed Sirett"
wrote:

On Fri, 24 Sep 2004 19:03:07 +0100, Peter Hawkins wrote:

The immersion heater in my house is of a type I haven't seen anywhere
else. There are no elements in the main tank. Instead the element is
mounted inside a small vertical cylinder plumbed into the side if the
tank but seperate from the main tank. Its mounted vertically with the
element upside down and fitted from the bottom (which makes it hard to
see the stat setting without a mirror). The secondary cylinder is 3
inches diameter and about 15 inches long.

A while back I noticed that running the immersion even for a short
time produced dangerously hot water. Ther was also a bubbling noise
from the cylinder when the immersion was on.

So I replaced the stat (7") set it for 60 and thought that would be
that. Same problem.

Any ideas....


I've only seen one of these once before. IIRC the secondary cylinder was
horizontal?

I believe that the intention is that hot HW becomes available more
quickly, and/or the whole cylinder is eventually heated through.
So it combines the best features of the top and bottom positioned
conventional immersion heaters.
It is normal for some noises to occur even with brand new immersion
heaters.
The replacement for this type would be an 11"(?) unit which contains a 7"
thermostat (cf 27" and 11")
It might be that all you need to do is to replace the thermostat (will
this mean you have to cut a hole in the floor ?!?).


  #5   Report Post  
jim.
 
Posts: n/a
Default


"Peter Hawkins" TOP POSTED in message
...
I've already replaced the themostat. I'm sort of at a loss now, hence
the posting! Could the element be at fault, causing the themostat to
stay on?

Peter


I've just read a very plausible explanation for this problem posted above by
Owain.
Are you not getting all the posts?
No the stat is not cutting the element off because it's (probably) not
seeing hot water,
I've never seen a faulty element give the problem you describe, although
technicaly
I suppose it 'could' be partialy shorted out only allowing the top end to
warm up.
I favour the previous explanation though.




  #6   Report Post  
Peter Hawkins
 
Posts: n/a
Default

On Fri, 24 Sep 2004 20:03:12 +0100, "Owain"
wrote:

"Peter Hawkins" wrote
| The immersion heater in my house is of a type I haven't seen
| anywhere else. There are no elements in the main tank. Instead
| the element is mounted inside a small vertical cylinder plumbed
| into the side if the tank but seperate from the main tank.
| Its mounted vertically with the element upside down and fitted
| from the bottom (which makes it hard to see the stat setting
| without a mirror). The secondary cylinder is 3 inches diameter
| and about 15 inches long.

Yes. It's called an external circulator and was often used to convert an
existing cylinder with an indirect heating coil that didn't have an
immersion heater boss. Because the position of the coil wasn't known, using
an external circulator avoided dealing with the obstruction inside the
cylinder.

It is possible the bottom connection to the cylinder is blocked which
prevents water circulating. A small quantity of extremely hot water is being
created at the top of the circulator and passing into the cylinder, but the
cooler water from the bottom of the cyclinder is not passing into the
circulator, allowing the heat to be dispersed through the whole of the
cylinder. This would also mean the thermistat at the bottom never has hot
water flowing over it. Bottom mounting of the heater/stat is normal.

Probably installed 1940s or 50s.

Owain


Only thing is my house was built in 1995. Were these still in use then
?
  #7   Report Post  
Peter Hawkins
 
Posts: n/a
Default

On Sat, 25 Sep 2004 02:18:04 GMT, "jim." wrote:


"Peter Hawkins" TOP POSTED in message
.. .
I've already replaced the themostat. I'm sort of at a loss now, hence
the posting! Could the element be at fault, causing the themostat to
stay on?

Peter


I've just read a very plausible explanation for this problem posted above by
Owain.
Are you not getting all the posts?
No the stat is not cutting the element off because it's (probably) not
seeing hot water,
I've never seen a faulty element give the problem you describe, although
technicaly
I suppose it 'could' be partialy shorted out only allowing the top end to
warm up.
I favour the previous explanation though.


I'm getting all the posts, but not neccesarily in the order they're
posted, suppose it depends on service providers. I was replying to
Ed's post, Owains hadn't appeared at that time. The house was only
built in 1995 so its less than 10 years old. Seems like a strange
system for a modern house. Obviously it now seems that either the
thermostat isn't being exposed to the hot water and therfore is
staying shorted, or the flow is obstructed.

Just out of curiousity I put the old themostat in hot water, it trips
fine...

So its not a themostat problem. Looks like I'm going to have to darin
the tank whatever.

Peter
  #8   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
Peter Hawkins writes:
I'm getting all the posts, but not neccesarily in the order they're
posted, suppose it depends on service providers. I was replying to
Ed's post, Owains hadn't appeared at that time. The house was only
built in 1995 so its less than 10 years old. Seems like a strange


I wonder if the plumber had just removed it from someone else's
house? I know of a case where that had happened (unless you can
buy new hot water cylinders with so much hard water scale in them
that the coil is very effectively insulated from the water).

system for a modern house. Obviously it now seems that either the
thermostat isn't being exposed to the hot water and therfore is
staying shorted, or the flow is obstructed.


--
Andrew Gabriel
  #9   Report Post  
Pete C
 
Posts: n/a
Default

On Fri, 24 Sep 2004 19:03:07 +0100, Peter Hawkins
wrote:

The immersion heater in my house is of a type I haven't seen anywhere
else. There are no elements in the main tank. Instead the element is
mounted inside a small vertical cylinder plumbed into the side if the
tank but seperate from the main tank. Its mounted vertically with the
element upside down and fitted from the bottom (which makes it hard to
see the stat setting without a mirror). The secondary cylinder is 3
inches diameter and about 15 inches long.

A while back I noticed that running the immersion even for a short
time produced dangerously hot water. Ther was also a bubbling noise
from the cylinder when the immersion was on.

So I replaced the stat (7") set it for 60 and thought that would be
that. Same problem.


Hi,

If the thermostat is set to 60°C, the reading might not be that
accurate. 60°C is 'hand hot', you should be able put your hand in for
short while with only temporary discomfort! It's still way above
shower temperatures, if you're concerned about kids/elderly in your
house it might be worth fitting a TMV blending valve to reduce the
temperature of the hot water from the cylinder.

Also is the secondary cylinder connected to the main cylinder top and
bottom? If the thermostat is reading the temperature of the water from
the bottom of the cylinder you might be better off connecting it via a
pipe stat on the top pipe returning to the main cylinder. Also check
the second cylinder is not scaled up.

cheers,
Pete.
  #10   Report Post  
Owain
 
Posts: n/a
Default

"Pete C" wrote
| Also is the secondary cylinder connected to the main cylinder
| top and bottom? If the thermostat is reading the temperature
| of the water from the bottom of the cylinder you might be better
| off connecting it via a pipe stat on the top pipe returning to
| the main cylinder.

However the top connecting pipe will get hot very quickly, before the heater
has made much difference to the bulk of the water in the cylinder.

| Also check the second cylinder is not scaled up.

I suspect scale in the lower pipe between the two.

Owain




  #11   Report Post  
Owain
 
Posts: n/a
Default

"Peter Hawkins" wrote
| Probably installed 1940s or 50s.
| Only thing is my house was built in 1995. Were these still in use
| then
| ?

I have not seen one physically, or in any contemporary literature. I think
they were developed as an addition to coal-fired back boiler systems with
indirect cylinders.

Owain


  #12   Report Post  
Peter Hawkins
 
Posts: n/a
Default

On Sat, 25 Sep 2004 15:04:06 +0100, Pete C
wrote:

On Fri, 24 Sep 2004 19:03:07 +0100, Peter Hawkins
wrote:

The immersion heater in my house is of a type I haven't seen anywhere
else. There are no elements in the main tank. Instead the element is
mounted inside a small vertical cylinder plumbed into the side if the
tank but seperate from the main tank. Its mounted vertically with the
element upside down and fitted from the bottom (which makes it hard to
see the stat setting without a mirror). The secondary cylinder is 3
inches diameter and about 15 inches long.

A while back I noticed that running the immersion even for a short
time produced dangerously hot water. Ther was also a bubbling noise
from the cylinder when the immersion was on.

So I replaced the stat (7") set it for 60 and thought that would be
that. Same problem.


Hi,

If the thermostat is set to 60°C, the reading might not be that
accurate. 60°C is 'hand hot', you should be able put your hand in for
short while with only temporary discomfort! It's still way above
shower temperatures, if you're concerned about kids/elderly in your
house it might be worth fitting a TMV blending valve to reduce the
temperature of the hot water from the cylinder.

Also is the secondary cylinder connected to the main cylinder top and
bottom? If the thermostat is reading the temperature of the water from
the bottom of the cylinder you might be better off connecting it via a
pipe stat on the top pipe returning to the main cylinder. Also check
the second cylinder is not scaled up.

cheers,
Pete.



The secondary cylinder has its bottom attachement pint about 6 incles
from the main cylinder bottom. The top disappears via pipe into the
wall.

I drained the tank and removed the secondary cylinder today. It was
full of gunk. Flushed it out with high hopes that it might be the
problem that Owain mentioned about. Howver the problem is still there.
I notice that when the immersion runs the top 1/3 of the 2nd cylinder
is extremley hot while the bottom 2/3 is cold. So the t'stat isn't
seeing the really hot stuff. Next thing to try is a new element. Jim
mentioned above that only the top may be heating, thats what it feels
like.

Mind you getting the element out will be a *******. The little
secondary gives no purchase for the element spanner, and the fixing
looks seized up. I imagine if I apply too much wellie the cylinder
will distort !

If anyone is interested see this link for a picture

http://www.fortbaxter.demon.co.uk/hot_tank.jpg

Peter
  #13   Report Post  
Pete C
 
Posts: n/a
Default

On Sat, 25 Sep 2004 17:54:54 +0100, Peter Hawkins
wrote:

The secondary cylinder has its bottom attachement pint about 6 incles
from the main cylinder bottom. The top disappears via pipe into the
wall.


Really....?


Mind you getting the element out will be a *******. The little
secondary gives no purchase for the element spanner, and the fixing
looks seized up. I imagine if I apply too much wellie the cylinder
will distort !

If anyone is interested see this link for a picture

http://www.fortbaxter.demon.co.uk/hot_tank.jpg


Questions...

Does the lowest connection visible on the main cylinder go to the
secondary one and do the other two visible go to the CH?

Where do the top and middle connections visible on the cylinder go?

Does the main cylinder have another connection at the bottom out of
the picture?

Is there provision for fitting an immersion heater to the main
cylinder?

When the CH is run to heat DHW, which connections heat up?

Once the cylinder is heated by the CH, which pipes heat up when
different hot taps around the house are used?

cheers,
Pete.
  #14   Report Post  
Owain
 
Posts: n/a
Default

"Peter Hawkins" wrote
| The secondary cylinder has its bottom attachement pint about 6
| incles from the main cylinder bottom. The top disappears via
| pipe into the wall.

Oh. Well, the hot out of the circulator needs to get back into the cylinder
somehow so the water circulates.

| If anyone is interested see this link for a picture
| http://www.fortbaxter.demon.co.uk/hot_tank.jpg

I wonder if someone has tried to boost the output from the HW cylinder ie
the heater heats the output and does not heat the tank? Does not look like
the picture in Newnes c.1950

Owain


  #15   Report Post  
Pete C
 
Posts: n/a
Default

On Sat, 25 Sep 2004 17:54:54 +0100, Peter Hawkins
wrote:

The secondary cylinder has its bottom attachement pint about 6 incles
from the main cylinder bottom. The top disappears via pipe into the
wall.


Really....?


Mind you getting the element out will be a *******. The little
secondary gives no purchase for the element spanner, and the fixing
looks seized up. I imagine if I apply too much wellie the cylinder
will distort !

If anyone is interested see this link for a picture

http://www.fortbaxter.demon.co.uk/hot_tank.jpg


Looking at the whole picture =), it looks like the top of the
secondary cylinder should connect up with the main cylinder so hot
water can circulate back into it.

Do you know where the pipe at the top of the cylinder goes? My guess
is that might connect to the pipe from the other cylinder elsewhere in
the house, but whoever installed or modified the plumbing didn't have
an appreciation for how convection works!

Is there an immersion heater boss on the main cylinder at all? If not,
maybe the secondary cylinder is a way of retrofitting one where there
is no provision for one, or a means of heating the whole cylinder with
economy 7.

My guess is that the secondary cylinder could be connected back to the
main cylinder, but making the hot connection as direct from the top of
the main cylinder as possible, so that when hot water is used it is
taken from the top of the main cylinder and not the bottom via the
secondary one.

Also is there another pipe blanked off on the top of the main cylinder
out of the picture? If so that might be the best place to connect the
secondary cylinder.

cheers,
Pete.


  #16   Report Post  
Peter Hawkins
 
Posts: n/a
Default

On Sun, 26 Sep 2004 00:12:11 +0100, "Owain"
wrote:

"Peter Hawkins" wrote
| The secondary cylinder has its bottom attachement pint about 6
| incles from the main cylinder bottom. The top disappears via
| pipe into the wall.

Oh. Well, the hot out of the circulator needs to get back into the cylinder
somehow so the water circulates.

| If anyone is interested see this link for a picture
| http://www.fortbaxter.demon.co.uk/hot_tank.jpg

I wonder if someone has tried to boost the output from the HW cylinder ie
the heater heats the output and does not heat the tank? Does not look like
the picture in Newnes c.1950

Owain


One other thing to point out. I have been in this house since day 1,
so this is the builders original work. The immersion is on a timer in
the kitchen so I assume it heats the tank somehow.

You would think that anyway, but if that was the case, why take th
etop pipe from the 2nd cylinder into the wall. Why not joint it here
in the cupboard the easy way ???

There is not fitting anywhere on the tank for a standard element

The only fittings on the tank a

2 at front for indirect coil.
1 top for drawing hot water off
1 at the bootom rear for cold feed in.

The other thing is, this all used to work OK till about 4 weeks ago...
  #17   Report Post  
Owain
 
Posts: n/a
Default

"Peter Hawkins" wrote
| One other thing to point out. I have been in this house since day
| 1, so this is the builders original work. The immersion is on a
| timer in the kitchen so I assume it heats the tank somehow. ...
| The other thing is, this all used to work OK till about 4 weeks
| ago...

Did you turn your CH on around that time by any chance?

I think most people are agreed that something, somewhere, has stopped the
water from the circulator circulating round the cylinder. Switching on the
CH or something elsewhere in the system could block the circuit or
interefere with the gravity circulation (convection).

Owain


  #18   Report Post  
Peter Hawkins
 
Posts: n/a
Default

On Sun, 26 Sep 2004 14:27:17 +0100, "Owain"
wrote:

"Peter Hawkins" wrote
| One other thing to point out. I have been in this house since day
| 1, so this is the builders original work. The immersion is on a
| timer in the kitchen so I assume it heats the tank somehow. ...
| The other thing is, this all used to work OK till about 4 weeks
| ago...

Did you turn your CH on around that time by any chance?

I think most people are agreed that something, somewhere, has stopped the
water from the circulator circulating round the cylinder. Switching on the
CH or something elsewhere in the system could block the circuit or
interefere with the gravity circulation (convection).

Owain

Owain,

No, as its an indirect cylinder, when the CH is on we have loads of
hot water. This is only ever used when the CH is not on.

I now think its the element, top half only is heating. I have the 2nd
cylinder off and can see clearly down its feed pipe into the main
cylinder, clear as a bell. So there is nothing to stop circulation. I
can't get the element off, so I need to get a new secondary cylinder
and element. I have since been told it may be called a *circulator* or
*instantaneous line heater*

Thanks


peter
  #19   Report Post  
Pete C
 
Posts: n/a
Default

On Sun, 26 Sep 2004 14:27:17 +0100, "Owain"
wrote:

"Peter Hawkins" wrote
| One other thing to point out. I have been in this house since day
| 1, so this is the builders original work. The immersion is on a
| timer in the kitchen so I assume it heats the tank somehow. ...
| The other thing is, this all used to work OK till about 4 weeks
| ago...

Did you turn your CH on around that time by any chance?

I think most people are agreed that something, somewhere, has stopped the
water from the circulator circulating round the cylinder. Switching on the
CH or something elsewhere in the system could block the circuit or
interefere with the gravity circulation (convection).

Hi,

Sounds like an air lock. Would be useful to know if/how the pipe from
the secondary cylinder connects to the pipe at the top of the main
cylinder.

cheers,
Pete.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AquaTherm Furnace - No Hot Water Issue David Home Repair 11 January 25th 18 08:44 PM
Power cost of idle electric water heater Phil Sherrod Home Repair 57 April 2nd 04 10:51 PM
Hot product for hot water ...products compaed [email protected] Home Repair 16 January 30th 04 04:07 AM
Thankless or Tankless hot water heaters [email protected] Home Repair 6 January 29th 04 03:01 AM
hot water recirculator, instant hot water but not a water heating unit, saves water, gas, time, money HeatMan Home Repair 0 August 24th 03 12:26 PM


All times are GMT +1. The time now is 01:45 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"