Peter Johnson[_4_] January 17th 21 02:26 PM

Room thermostat wiring conundrum
 
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.

Tricky Dicky[_4_] January 17th 21 02:40 PM

Room thermostat wiring conundrum
 
On Sunday, 17 January 2021 at 14:26:28 UTC, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.



The MRTE is a two wire device using batteries to power the electronics. I had a similar situation changing a previous 3 wire device to the MRTE last week.

Connect the red wire (L) to C (terminal 2) in the MRTE and the yellow which will be the switched live to NO (terminal 1). You do not need the Neutral (blue wire) and will have to terminate it off either as I did with a Wago connector or a single terminal off a terminal strip.

Richard

Graham.[_13_] January 17th 21 02:43 PM

Room thermostat wiring conundrum
 
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.
--

%Profound_observation%


----Android NewsGroup Reader----
http://usenet.sinaapp.com/

Mike Humphrey[_2_] January 17th 21 02:47 PM

Room thermostat wiring conundrum
 
On Sun, 17 Jan 2021 14:26:25 +0000, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id I'd like to
replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L (Another
picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Assuming the original thermostat is wired correctly:
Red is permanent live which will go to "C".
Yellow is switched live which will go to either NO or NC (I think NO, but
it depends which position the thermostat considers "normal" - the wrong
one will turn the heating on when it's hot and off when it's cold, so
just swap it over).
Blue is neutral, which the new thermostat doesn't need (presumably it's
battery powered?), so put a choc-block terminal on it.
There should be an earth wire too, though I don't see it - but the new
thermostat looks to be all plastic so doesn't need this either. Put a
choc-block on this too.


Mike

alan_m January 17th 21 03:08 PM

Room thermostat wiring conundrum
 
On 17/01/2021 14:40, Graham. wrote:
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.


+1
Red (live) to C (common)
Yellow (switched live) to NO (Normally Open)

Blue not used so should be made safe and not connected to anything.

The NC (Normally closed) terminal is also unused.

--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk

ARW January 17th 21 04:34 PM

Room thermostat wiring conundrum
 
On 17/01/2021 14:26, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Everyone has answered this. So I'll just add make sure it was a 3A fuse
that you fitted into the fused spur

--
Adam

Brian Gaff \(Sofa\) January 17th 21 06:27 PM

Room thermostat wiring conundrum
 
It kind of makes you wonder why they do not provide a place for any vacant
wire that goes nowhere for safety really.
Brian

--

This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"ARW" wrote in message
...
On 17/01/2021 14:26, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Everyone has answered this. So I'll just add make sure it was a 3A fuse
that you fitted into the fused spur

--
Adam




Roger Mills[_2_] January 17th 21 08:11 PM

Room thermostat wiring conundrum
 
On 17/01/2021 14:40, Tricky Dicky wrote:
On Sunday, 17 January 2021 at 14:26:28 UTC, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.



The MRTE is a two wire device using batteries to power the electronics. I had a similar situation changing a previous 3 wire device to the MRTE last week.

Connect the red wire (L) to C (terminal 2) in the MRTE and the yellow which will be the switched live to NO (terminal 1). You do not need the Neutral (blue wire) and will have to terminate it off either as I did with a Wago connector or a single terminal off a terminal strip.

Richard


For "do not need" read "*must* not connect". The blue (neutral) wire
would originally have been used in a mechanical stat as the return from
the accelerator heater (which reduced hysteresis). No longer used in
modern digital stats. If you connect it to *anything*, it will blow the
fuse under one condition or another.
--
Cheers,
Roger

The Natural Philosopher[_2_] January 18th 21 06:54 AM

Room thermostat wiring conundrum
 
On 17/01/2021 14:40, Graham. wrote:
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.

It depends what 'normal' means - you might want yellow to NC....

--
Climate is what you expect but weather is what you get.
Mark Twain

JohnP January 18th 21 08:59 AM

Room thermostat wiring conundrum
 
Peter Johnson wrote in
:

Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Connecting the neutral and blowing the fuse may have killed the new
therrmostat.

alan_m January 18th 21 09:41 AM

Room thermostat wiring conundrum
 
On 18/01/2021 06:54, The Natural Philosopher wrote:
On 17/01/2021 14:40, Graham. wrote:
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.

It depends what 'normal' means - you might want yellow to NC....



There are only 3 connections in the original back box which corresponds
to the wiring for a Drayton RTS1, RTS2 or RTS3 device where the yellow
wire is in the position for switched live from a normally open (NO)
switch contact.







--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk

alan_m January 18th 21 09:57 AM

Room thermostat wiring conundrum
 
On 18/01/2021 08:59, JohnP wrote:
Peter Johnson wrote in
:

Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Connecting the neutral and blowing the fuse may have killed the new
therrmostat.


Possible but unlikely. The 3 contacts in the new thermostat will be
three contacts to a relay inside the device and with no connections to
any of the electronics within the device. With no provision for a mains
neutral it indicates that the thermostat is battery operated and the
output switching is isolated from the electronics.

There is a possibility with a direct short between mains live and
neutral that relay contacts may have welded themselves together or there
has been some arcing. The fuse probably popped fast enough to prevent
any damage.

--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk

Tricky Dicky[_4_] January 18th 21 10:42 AM

Room thermostat wiring conundrum
 
On Monday, 18 January 2021 at 09:57:26 UTC, alan_m wrote:
On 18/01/2021 08:59, JohnP wrote:
Peter Johnson wrote in
:

Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Connecting the neutral and blowing the fuse may have killed the new
therrmostat.

Possible but unlikely. The 3 contacts in the new thermostat will be
three contacts to a relay inside the device and with no connections to
any of the electronics within the device. With no provision for a mains
neutral it indicates that the thermostat is battery operated and the
output switching is isolated from the electronics.

There is a possibility with a direct short between mains live and
neutral that relay contacts may have welded themselves together or there
has been some arcing. The fuse probably popped fast enough to prevent
any damage.
--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk


The enclosed installation notes show the same wiring diagram but go further by indicating which terminals are for heating and which for cooling.

https://www.myson.co.uk/static_files...structions.pdf

Richard

Pancho January 18th 21 11:03 AM

Room thermostat wiring conundrum
 
On 18/01/2021 09:57, alan_m wrote:

There is a possibility with a direct short between mains live and
neutral that relay contacts may have welded themselves together or there
has been some arcing. The fuse probably popped fast enough to prevent
any damage.


This is exactly what happened to me when the boiler installer misfitted
my new room thermostat.

The spot weld on the controller relay froze in the off position.

I called the boiler installer back and he seemed to get very stressed
when I took an interested in what he was doing, eventually he left
without fixing it. A bit of a shame really as he did a good job
otherwise. I probably went into software developer mode, we mess so much
up we are less ashamed about it, I hadn't expect him to be bothered.

After he had gone I opened up the controller and flicked the welded
relay apart. I then wired the thermostat up correctly. It's been working
fine for 6 years.

FWIW the old style thermostats needed three wires. When off they put a
small current though a big resistor to warm the thermostat slightly.
This created a hysteresis effect and stopped the thermostat switching on
an off too quickly.

The new thermostat is annoyingly noisy.



Peter Johnson[_4_] January 18th 21 01:15 PM

Room thermostat wiring conundrum
 
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7) when the fuse blew because when I reinstated the old
thermostat the boiler responded to it regardless of the settings on
the timer, so I got a click and collect Drayton LP822 from Wickes
yesterday and the boiler came on as soon as I'd finished configuring
it.
The old one had a warranty expiry date of July 2003 so it's served me
well.
Thanks again.

The Natural Philosopher[_2_] January 18th 21 01:16 PM

Room thermostat wiring conundrum
 
On 18/01/2021 11:03, Pancho wrote:
FWIW the old style thermostats needed three wires. When off they put a
small current though a big resistor to warm the thermostat slightly.
This created a hysteresis effect and stopped the thermostat switching on
an off too quickly.


Er no, it was to *reduce* the hysteresis...

--
Future generations will wonder in bemused amazement that the early
twenty-first centurys developed world went into hysterical panic over a
globally average temperature increase of a few tenths of a degree, and,
on the basis of gross exaggerations of highly uncertain computer
projections combined into implausible chains of inference, proceeded to
contemplate a rollback of the industrial age.

Richard Lindzen

Pancho January 18th 21 01:42 PM

Room thermostat wiring conundrum
 
On 18/01/2021 13:15, Peter Johnson wrote:
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7)


Mine is a Drayton Tempus 6, it's time of servitude isn't over yet. I
suspect you could have fixed it, but on the other hand you have a smart
shiny new one and I have a dull one with a cracked plastic lid.

If buying a new one I would have been tempted to look at a wifi/smart one.


Pancho January 18th 21 01:45 PM

Room thermostat wiring conundrum
 
On 18/01/2021 13:16, The Natural Philosopher wrote:
On 18/01/2021 11:03, Pancho wrote:
FWIW the old style thermostats needed three wires. When off they put a
small current though a big resistor to warm the thermostat slightly.
This created a hysteresis effect and stopped the thermostat switching
on an off too quickly.


Er no, it was to *reduce* the hysteresis...

Er no, surely you want hysteresis otherwise you get vacillation, rapid
switching on an off.

Dave Plowman (News) January 18th 21 02:53 PM

Room thermostat wiring conundrum
 
In article ,
Brian Gaff \(Sofa\) wrote:
It kind of makes you wonder why they do not provide a place for any
vacant wire that goes nowhere for safety really.


That would just confuse someone starting afresh. "What are all those spare
terminals for?"

--
*How does Moses make his tea? Hebrews it.*

Dave Plowman London SW
To e-mail, change noise into sound.

Dave Plowman (News) January 18th 21 02:55 PM

Room thermostat wiring conundrum
 
In article ,
Pancho wrote:
This is exactly what happened to me when the boiler installer misfitted
my new room thermostat.


Odd, isn't it? Now most boilers have electronic control, they are still
fitted by a monkey with a 'gas safe' badge.

--
*I don't know what your problem is, but I'll bet it's hard to pronounce

Dave Plowman London SW
To e-mail, change noise into sound.

Dave Plowman (News) January 18th 21 02:57 PM

Room thermostat wiring conundrum
 
In article ,
Pancho wrote:
On 18/01/2021 13:15, Peter Johnson wrote:
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7)


Mine is a Drayton Tempus 6, it's time of servitude isn't over yet. I
suspect you could have fixed it, but on the other hand you have a smart
shiny new one and I have a dull one with a cracked plastic lid.


If buying a new one I would have been tempted to look at a wifi/smart
one.


Do you really need the ability to control your thermostat from a mobile
phone, etc? Making it more expensive and less reliable? Purely to be in
fashion?

--
*Most people have more than the average number of legs*

Dave Plowman London SW
To e-mail, change noise into sound.

Roger Mills[_2_] January 18th 21 03:01 PM

Room thermostat wiring conundrum
 
On 18/01/2021 09:57, alan_m wrote:

With no provision for a mains
neutral it indicates that the thermostat is battery operated


Not necessarily - although it almost certainly is.

The traditional bi-metallic stat didn't need electricity to drive it.
The only reason for the neutral was to provide a return for the
accelerator heater - but the stat would still work if you didn't connect it.
--
Cheers,
Roger

Roger Mills[_2_] January 18th 21 03:16 PM

Room thermostat wiring conundrum
 
On 18/01/2021 13:45, Pancho wrote:
On 18/01/2021 13:16, The Natural Philosopher wrote:
On 18/01/2021 11:03, Pancho wrote:
FWIW the old style thermostats needed three wires. When off they put
a small current though a big resistor to warm the thermostat
slightly. This created a hysteresis effect and stopped the thermostat
switching on an off too quickly.


Er no, it was to *reduce* the hysteresis...

Er no, surely you want hysteresis otherwise you get vacillation, rapid
switching on an off.


There needs to be a *bit* of hysteresis to avoid rapid cycling - but
mechanical stats have this naturally, with a margin between the on and
off points. *However* if the room stat only switches the heating off
when the set point is reached, the rads are still hot and the room
temperature will go on rising. Not only does this waste heat, but the
room then takes a long time to cool and the occupants start to feel cold
before the heating comes on again.

The accelerator heater fools the stat into thinking that the set point
has been reached a bit before it is actually reached. This greatly
reduces the overshoot.
--
Cheers,
Roger

JohnP January 18th 21 04:26 PM

Room thermostat wiring conundrum
 
"Dave Plowman (News)" wrote in
:

In article ,
Pancho wrote:
This is exactly what happened to me when the boiler installer misfitted
my new room thermostat.


Odd, isn't it? Now most boilers have electronic control, they are still
fitted by a monkey with a 'gas safe' badge.


Yes - people call in a Plumber to fix a boiler! People expect an
electrician to be able to fix a washing machine.

What some tradesmen lack is an understanding of "Control Logic".

Time Served Qualified Plumber - what does this mean - can bend and fit
pipes?

I recall at a place where I worked we employed "Instalation Electricians!
and "Maintenance Electricians" Different aptitudes.

Pancho January 18th 21 05:04 PM

Room thermostat wiring conundrum
 
On 18/01/2021 15:16, Roger Mills wrote:


There needs to be a *bit* of hysteresis to avoid rapid cycling - but
mechanical stats have this naturally, with a margin between the on and
off points. *However* if the room stat only switches the heating off
when the set point is reached, the rads are still hot and the room
temperature will go on rising. Not only does this waste heat, but the
room then takes a long time to cool and the occupants start to feel cold
before the heating comes on again.

The accelerator heater fools the stat into thinking that the set point
has been reached a bit before it is actually reached. This greatly
reduces the overshoot.


You sound convincing. I would need to think long and hard to get it
straight in my head. It was six years ago and I may have confused things
then or in my memory now.

A provisional apology to TNP.

Pancho January 18th 21 05:09 PM

Room thermostat wiring conundrum
 
On 18/01/2021 14:57, Dave Plowman (News) wrote:
In article ,
Pancho wrote:
On 18/01/2021 13:15, Peter Johnson wrote:
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7)


Mine is a Drayton Tempus 6, it's time of servitude isn't over yet. I
suspect you could have fixed it, but on the other hand you have a smart
shiny new one and I have a dull one with a cracked plastic lid.


If buying a new one I would have been tempted to look at a wifi/smart
one.


Do you really need the ability to control your thermostat from a mobile
phone, etc? Making it more expensive and less reliable? Purely to be in
fashion?


Yebbut, I am a software developer, so the technology is slightly more
accessible to me.

Whist I appreciate this technology might not be there yet, it is useful
and the actual cpu chip part of the controller should only cost pennies.
Longterm/theoretically it could become very reliable.

ARW January 18th 21 07:07 PM

Room thermostat wiring conundrum
 
On 18/01/2021 06:54, The Natural Philosopher wrote:
On 17/01/2021 14:40, Graham. wrote:
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.

It depends what 'normal' means - you might want yellow to NC....



Not on a heating room stat.

--
Adam

Fredxx[_4_] January 18th 21 07:22 PM

Room thermostat wiring conundrum
 
On 18/01/2021 19:07, ARW wrote:
On 18/01/2021 06:54, The Natural Philosopher wrote:
On 17/01/2021 14:40, Graham. wrote:
Peter Johnson Wrote in message:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Red to "C"
Yellow to "N.O."
Insulate and do not connect the blue neutral.

It depends what 'normal' means - you might want yellow to NC....



Not on a heating room stat.


If the cylinder stat is remote from all the other wiring it might make
sense to swap cylinder stat and room stat over, and swap the ports on a
diverter accordingly.

Just to play devil's advocate :-)


http://wiki.diyfaq.org.uk/index.php/...on es:_Y-plan




Peter Johnson[_4_] January 18th 21 07:25 PM

Room thermostat wiring conundrum
 
On Sun, 17 Jan 2021 16:34:08 +0000, ARW
wrote:

On 17/01/2021 14:26, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Everyone has answered this. So I'll just add make sure it was a 3A fuse
that you fitted into the fused spur


It was 5A, which I suspect was my doing, when I installed the previous
timer, but I've been to B&Q and got a pack of 3A, so I am now
compliant, and have spares.
Thanks.

Roger Hayter[_2_] January 18th 21 10:01 PM

Room thermostat wiring conundrum
 
On 18 Jan 2021 at 15:01:02 GMT, "Roger Mills" wrote:

On 18/01/2021 09:57, alan_m wrote:

With no provision for a mains
neutral it indicates that the thermostat is battery operated


Not necessarily - although it almost certainly is.

The traditional bi-metallic stat didn't need electricity to drive it.
The only reason for the neutral was to provide a return for the
accelerator heater - but the stat would still work if you didn't connect it.


I've got a traditional one in my shower room, on a SELV circuit which wouldn't
work the heater anyway.

--
Roger Hayter



Roger Mills[_2_] January 18th 21 11:23 PM

Room thermostat wiring conundrum
 
On 18/01/2021 14:57, Dave Plowman (News) wrote:
In article ,
Pancho wrote:
On 18/01/2021 13:15, Peter Johnson wrote:
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7)


Mine is a Drayton Tempus 6, it's time of servitude isn't over yet. I
suspect you could have fixed it, but on the other hand you have a smart
shiny new one and I have a dull one with a cracked plastic lid.


If buying a new one I would have been tempted to look at a wifi/smart
one.


Do you really need the ability to control your thermostat from a mobile
phone, etc? Making it more expensive and less reliable? Purely to be in
fashion?


Most people probably don't. But the Hive system at my holiday flat has
been very useful during the Covid crisis - enabling me to see what is
happening temperature-wise when I'm unable to visit.
--
Cheers,
Roger

Dave Plowman (News) January 19th 21 12:42 AM

Room thermostat wiring conundrum
 
In article ,
Pancho wrote:
On 18/01/2021 14:57, Dave Plowman (News) wrote:
In article ,
Pancho wrote:
On 18/01/2021 13:15, Peter Johnson wrote:
Thanks everyone for your helpful comments and advice. New thermostat
now up and running.
My uneducated attempt to install it did do some damage to the timer (a
Drayton Tempus 7)


Mine is a Drayton Tempus 6, it's time of servitude isn't over yet. I
suspect you could have fixed it, but on the other hand you have a smart
shiny new one and I have a dull one with a cracked plastic lid.


If buying a new one I would have been tempted to look at a wifi/smart
one.


Do you really need the ability to control your thermostat from a mobile
phone, etc? Making it more expensive and less reliable? Purely to be in
fashion?


Yebbut, I am a software developer, so the technology is slightly more
accessible to me.


Whist I appreciate this technology might not be there yet, it is useful
and the actual cpu chip part of the controller should only cost pennies.
Longterm/theoretically it could become very reliable.


I can see the point of a wireless stat if a new installation. But not when
the cables are already there.

And having a boiler which can be programmed by Wi-Fi etc. But not a stat.

--
*Tell me to 'stuff it' - I'm a taxidermist.

Dave Plowman London SW
To e-mail, change noise into sound.

alan_m January 19th 21 01:29 AM

Room thermostat wiring conundrum
 
On 19/01/2021 00:42, Dave Plowman (News) wrote:

I can see the point of a wireless stat if a new installation. But not when
the cables are already there.


I've seen many room stats placed in positions where they were easy to
wire rather than in a room that you may want the most control. A
wireless room stat enables the receiver to remain in the previous
position and the transmitter to be moved to an alternative position in
the house.

My thermostat used to be upstairs in the stair well but now better
positioned in the "living room" where most TV is watched and most play
on the laptop occurs.






And having a boiler which can be programmed by Wi-Fi etc. But not a stat.



--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk

Dave Plowman (News) January 19th 21 11:03 AM

Room thermostat wiring conundrum
 
In article ,
alan_m wrote:
I've seen many room stats placed in positions where they were easy to
wire rather than in a room that you may want the most control. A
wireless room stat enables the receiver to remain in the previous
position and the transmitter to be moved to an alternative position in
the house.


I'd say if the theremostat has simply been put in the most convenient
position for the installer, it won't be the only bodge in your system. ;-)

--
*Verbs HAS to agree with their subjects *

Dave Plowman London SW
To e-mail, change noise into sound.

Andrew[_22_] January 19th 21 06:11 PM

Room thermostat wiring conundrum
 
On 17/01/2021 20:11, Roger Mills wrote:
On 17/01/2021 14:40, Tricky Dicky wrote:
On Sunday, 17 January 2021 at 14:26:28 UTC, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.



The MRTE is a two wire device using batteries to power the
electronics. I had a similar situation changing a previous 3 wire
device to the MRTE last week.

Connect the red wire (L) to C (terminal 2) in the MRTE and the yellow
which will be the switched live to NO (terminal 1). You do not need
the Neutral (blue wire) and will have to terminate it off either as I
did with a Wago connector or a single terminal off a terminal strip.

Richard


For "do not need" read "*must* not connect". The blue (neutral) wire
would originally have been used in a mechanical stat as the return from
the accelerator heater (which reduced hysteresis). No longer used in
modern digital stats. If you connect it to *anything*, it will blow the
fuse under one condition or another.


No-one seems to have used the magical phrase 'volt-free' which I
come across in other documentation. Presumably the replacement is
'volt-free' (even though it has a battery) ?.

bert[_7_] January 19th 21 09:23 PM

Room thermostat wiring conundrum
 
In article , ARW
writes
On 17/01/2021 14:26, Peter Johnson wrote:
Well it's a coundrum to me.
This is a photograph of the wiring of the existing Drayton thermostat:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp0...rU-7w?e=4lk9Id
I'd like to replace it with a Myson device, which is wired thus:
https://1drv.ms/u/s!AkhvgPvXD0_1jdp2...r-T9A?e=5zLx3L
(Another picture)
So what wire goes where?
My first attempt to install it blew the fuse in the switch.
Thanks.


Everyone has answered this. So I'll just add make sure it was a 3A fuse
that you fitted into the fused spur

Oh come on. You know the rule. If a fuse blows - fit a bigger one and
tune for maximum smoke.
--
bert

bert[_7_] January 19th 21 09:27 PM

Room thermostat wiring conundrum
 
In article , Pancho
writes
On 18/01/2021 13:16, The Natural Philosopher wrote:
On 18/01/2021 11:03, Pancho wrote:
FWIW the old style thermostats needed three wires. When off they put
a small current though a big resistor to warm the thermostat
slightly. This created a hysteresis effect and stopped the
thermostat switching on an off too quickly.

Er no, it was to *reduce* the hysteresis...

Er no, surely you want hysteresis otherwise you get vacillation, rapid
switching on an off.

Having had one of these wired without the neutral by the installer I can
assure you it is there to reduce the hysteresis. The old style had
enough without any assistance.
--
bert

bert[_7_] January 19th 21 09:35 PM

Room thermostat wiring conundrum
 
In article , Roger Mills
writes
On 18/01/2021 09:57, alan_m wrote:

With no provision for a mains neutral it indicates that the
thermostat is battery operated


Not necessarily - although it almost certainly is.

The traditional bi-metallic stat didn't need electricity to drive it.
The only reason for the neutral was to provide a return for the
accelerator heater - but the stat would still work if you didn't
connect it.

My very old (40 yrs+) mechanical stat worked very well without a
neutral. When the system was replaced about 10+ yrs ago the installer
didn't bother with neutral as none was present. So I used the earth wire
as neutral and performance was improved. ISTR I was advised in here that
that was a bit naughty so I have since replaced it with a Honeywell
battery operated electronic one which doesn't require neutral.
--
bert

John J[_2_] January 21st 21 06:09 AM

Room thermostat wiring conundrum
 
On Monday, 18 January 2021 at 16:26:09 UTC, JohnP wrote:
"Dave Plowman (News)" wrote in
:
In article ,
Pancho wrote:
This is exactly what happened to me when the boiler installer misfitted
my new room thermostat.


Odd, isn't it? Now most boilers have electronic control, they are still
fitted by a monkey with a 'gas safe' badge.

Yes - people call in a Plumber to fix a boiler! People expect an
electrician to be able to fix a washing machine.

What some tradesmen lack is an understanding of "Control Logic".

Time Served Qualified Plumber - what does this mean - can bend and fit
pipes?

I recall at a place where I worked we employed "Instalation Electricians!
and "Maintenance Electricians" Different aptitudes.


I spent some time training service leavers to become electricians. The company I worked for also ran training courses for plumbers and they came to me for basic electrics as part of their course. The intent was to educate them sufficient to safely install (in compliance with building and wiring regulations) power supplies, bonding and controls for central heating, showers etc. On completion of their course they had a portfolio folder with all the stuff they had covered and been assessed as doing correctly at least once. They could of course forget it all when they went out of the gate .......

Mike Clarke January 21st 21 09:51 AM

Room thermostat wiring conundrum
 
On 18/01/2021 16:26, JohnP wrote:
Yes - people call in a Plumber to fix a boiler! People expect an
electrician to be able to fix a washing machine.


It might have been common once for the same person to deal with both
plumbing and electrical work. Back in the 1950s I remember seeing
tradesmen advertising themselves as "plumber and electrician".


All times are GMT +1. The time now is 08:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter