One of the RCDs in the split consumer unit tripped yesterday. It was the
side I'd previously had a problem with concerning the lighting wiring.
Not a good time for a wiring check...

However, a quick check turning off and then on each MCB in turn on that
side showed it wasn't the lighting wiring. I'd got out a 10" desk fan
which hadn't been used since last summer, and that had been on an hour
when it tripped the RCD. Resetting the RCD and turning on the fan had it
tripping again in a few minutes.

I've just dismantled the fan (not easy - many hidden plastic catches and
unreachable circlips) and put it on in free air. After an hour the
outside of the windings were at 87 deg C, and the laminations furthest
from them were at 67 dec C. I assume that if left on the enamel on the
wires would have reached a high enough temperature to fail and rubbed
against the laminations (which are earthed), so tripping the RCD.

Fortunately, I've always got a couple of spare fans and the tip is now
open for electrical goods.

--

Jeff
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default RCD tripping

On 29/05/2020 10:41, Jeff Layman wrote:
One of the RCDs in the split consumer unit tripped yesterday. It was the
side I'd previously had a problem with concerning the lighting wiring.
Not a good time for a wiring check...

However, a quick check turning off and then on each MCB in turn on that
side showed it wasn't the lighting wiring. I'd got out a 10" desk fan
which hadn't been used since last summer, and that had been on an hour
when it tripped the RCD. Resetting the RCD and turning on the fan had it
tripping again in a few minutes.

I've just dismantled the fan (not easy - many hidden plastic catches and
unreachable circlips) and put it on in free air. After an hour the
outside of the windings were at 87 deg C, and the laminations furthest
from them were at 67 dec C. I assume that if left on the enamel on the
wires would have reached a high enough temperature to fail and rubbed
against the laminations (which are earthed), so tripping the RCD.

Fortunately, I've always got a couple of spare fans and the tip is now
open for electrical goods.

My last and worst RCD tripper was an earth neutral short.
Other culprit have been wet electrics due to weeping plumbing, a stove
element whose insulation was breaking down, and a burned out washing
machine motor that showed a 2k short to earth on the armature windings.

Its easy enough to pop a meter across a disconnected fan switch it to
'on' and see if it has leakage




--
There is nothing a fleet of dispatchable nuclear power plants cannot do
that cannot be done worse and more expensively and with higher carbon
emissions and more adverse environmental impact by adding intermittent
renewable energy.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 48
Default RCD tripping

On Fri, 29 May 2020 11:52:14 +0100, The Natural Philosopher wrote:

On 29/05/2020 10:41, Jeff Layman wrote:
One of the RCDs in the split consumer unit tripped yesterday. It was
the side I'd previously had a problem with concerning the lighting
wiring. Not a good time for a wiring check...

However, a quick check turning off and then on each MCB in turn on that
side showed it wasn't the lighting wiring. I'd got out a 10" desk fan
which hadn't been used since last summer, and that had been on an hour
when it tripped the RCD. Resetting the RCD and turning on the fan had
it tripping again in a few minutes.

I've just dismantled the fan (not easy - many hidden plastic catches
and unreachable circlips) and put it on in free air. After an hour the
outside of the windings were at 87 deg C, and the laminations furthest
from them were at 67 dec C. I assume that if left on the enamel on the
wires would have reached a high enough temperature to fail and rubbed
against the laminations (which are earthed), so tripping the RCD.

Fortunately, I've always got a couple of spare fans and the tip is now
open for electrical goods.

My last and worst RCD tripper was an earth neutral short.
Other culprit have been wet electrics due to weeping plumbing, a stove
element whose insulation was breaking down, and a burned out washing
machine motor that showed a 2k short to earth on the armature windings.

Its easy enough to pop a meter across a disconnected fan switch it to
'on' and see if it has leakage



Not so obvious when the unit is cold.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default RCD tripping

On 29/05/2020 12:23, Smolley wrote:
On Fri, 29 May 2020 11:52:14 +0100, The Natural Philosopher wrote:

On 29/05/2020 10:41, Jeff Layman wrote:
One of the RCDs in the split consumer unit tripped yesterday. It was
the side I'd previously had a problem with concerning the lighting
wiring. Not a good time for a wiring check...

However, a quick check turning off and then on each MCB in turn on that
side showed it wasn't the lighting wiring. I'd got out a 10" desk fan
which hadn't been used since last summer, and that had been on an hour
when it tripped the RCD. Resetting the RCD and turning on the fan had
it tripping again in a few minutes.

I've just dismantled the fan (not easy - many hidden plastic catches
and unreachable circlips) and put it on in free air. After an hour the
outside of the windings were at 87 deg C, and the laminations furthest
from them were at 67 dec C. I assume that if left on the enamel on the
wires would have reached a high enough temperature to fail and rubbed
against the laminations (which are earthed), so tripping the RCD.

Fortunately, I've always got a couple of spare fans and the tip is now
open for electrical goods.

My last and worst RCD tripper was an earth neutral short.
Other culprit have been wet electrics due to weeping plumbing, a stove
element whose insulation was breaking down, and a burned out washing
machine motor that showed a 2k short to earth on the armature windings.

Its easy enough to pop a meter across a disconnected fan switch it to
'on' and see if it has leakage



Not so obvious when the unit is cold.

I have yet to see a direct short to earth that vanished when cold as a
failure mode on ANYTHING



--
You can get much farther with a kind word and a gun than you can with a
kind word alone.

Al Capone


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,699
Default RCD tripping

I had a uk made fan in which the oilite bearings were so soft they wore in a
year and the thing started to get hot as it started to brush the outside of
the laminations. I'd imagine it would eventually have seized up and the
Eddie currents would have overheated the winding.
The motor in it was a bit like the old induction motors you saw in
autochanger BSR record players in the 60s, but his was made in the 90s out
of crap.
When I think of the ever video machine I had having two of those motors,
which was hot enough to keep your food warm, yet the bearings outlasted the
electronics and apart from cleaning never had any trouble despite the Eddie
current breaking speed control used.
Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"Jeff Layman" wrote in message
...
One of the RCDs in the split consumer unit tripped yesterday. It was the
side I'd previously had a problem with concerning the lighting wiring. Not
a good time for a wiring check...

However, a quick check turning off and then on each MCB in turn on that
side showed it wasn't the lighting wiring. I'd got out a 10" desk fan
which hadn't been used since last summer, and that had been on an hour
when it tripped the RCD. Resetting the RCD and turning on the fan had it
tripping again in a few minutes.

I've just dismantled the fan (not easy - many hidden plastic catches and
unreachable circlips) and put it on in free air. After an hour the outside
of the windings were at 87 deg C, and the laminations furthest from them
were at 67 dec C. I assume that if left on the enamel on the wires would
have reached a high enough temperature to fail and rubbed against the
laminations (which are earthed), so tripping the RCD.

Fortunately, I've always got a couple of spare fans and the tip is now
open for electrical goods.

--

Jeff



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
RCD test button not tripping the RCD. Rednadnerb UK diy 4 July 17th 10 01:02 AM
Random RCD tripping N. Thornton UK diy 2 December 23rd 04 03:16 PM
Tripping RCD on main disribution board - Help Requested Steve Reeves UK diy 23 June 6th 04 10:08 AM
Help! RCD Keeps tripping on new wiring Seri UK diy 30 April 9th 04 07:41 PM
Indesit wdg1295w washer/drier tripping RCD on final fast spin spanner UK diy 6 February 6th 04 10:08 AM


All times are GMT +1. The time now is 08:39 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"